Old 03-06-2019, 07:01 PM   #201
Wolfwhistle
 
Fair_Enough's Avatar
 
Margaritaville , Banana Republic
Join Date: Jul 2018
Posts: 705
Quote:
Originally Posted by TouringDan View Post
Clint

The MC4s hanging below the trailer is how I connect the portable panels to my solar controller. The short pigtail goes from the MC4s to the controller.Attachment 335059
You are correct, when you divide 208 watts by 13.58 volts, you get 15.3 amps which exceeds the 15 amp perceived rating. I am not concerned since the manufacturer states that the controller is good for 220 watts @ 12v. This is over 18 amps. Obviously some margin is built into the controller to handle situations like I experienced where the panels were putting out more than their rated power.

DanAttachment 335060
Thanks Dan,
That is what my SC2030 will do also, limits throughput if current exceeds rated amps.
Clint
__________________
Is taking it all with you, really getting away from it all?
Fair_Enough is offline   Reply With Quote
Old 03-10-2019, 02:50 PM   #202
2 Rivet Member
 
2012 27' FB International
Victor , New York
Join Date: Jan 2013
Posts: 30
Solar/battery upgrade diagram

Hi everyone, I am adding a panel to my PV system and upgrading my battery bank from two 105AH AGM to four 100AH LiFePO4.

In doing so, I plan to move the batteries from outside to the storage area under the bed. I think I will also take this opportunity to rewire the PV controller, batteries, inverter and a few other DC components such as the LP detector.

I am looking for advice or feedback on how I have diagramed my upgrade --anything in terms of things I may have overlooked or components I've included that aren't needed. For example, one thing I'm not sure of is whether 1 GA wire is overkill and 2 or 4 GA wire would be sufficient.

Thanks, everyone!
Attached Thumbnails
Click image for larger version

Name:	PV.jpg
Views:	295
Size:	268.8 KB
ID:	335358  
Meddle is offline   Reply With Quote
Old 03-10-2019, 04:02 PM   #203
Site Team
 
wulfraat's Avatar

 
2017 30' International
Broomfield , Colorado
Join Date: Apr 2009
Posts: 3,555
Images: 1
1ga is overkill for standard 12v loads and a 600w inverter but I would not go any less, to future proof your install if you want to move to a larger inverter at some point.
wulfraat is offline   Reply With Quote
Old 03-10-2019, 04:15 PM   #204
Wolfwhistle
 
Fair_Enough's Avatar
 
Margaritaville , Banana Republic
Join Date: Jul 2018
Posts: 705
Nice drawing Meddle.

You are "missing" protection / breaker on the 12vdc supply side of the inverter and one on the battery side of the MPPT, IMO.

If the inverter can make 1200W surge, the breaker somewhere between there and batteries should be in the order of around 100 / 120 amps DC. 1 AWG doesn't seem like enough.

Also, check with product information, because I doubt you can terminate a 1 AWG at the MPPT (gauge seems overly large) and possibly not onto the Inverter without a proper method.

Plugging 100A into a VD calculator shows to attain less than 1% you will need #1/0 (inverter to batteries) for 6 feet of total one-way wire run.

You are not showing the Converter or the frame ground.

I also question the need for a temperature probe. Depending on the batteries you use, the BMS should take care of all that.



Edit: I would wire MPPT Inverter to the (+) buss. with proper sized breakers / fuses and battery cut off switches.


Hopefully a true expert will chime in.
Clint
__________________
Is taking it all with you, really getting away from it all?
Fair_Enough is offline   Reply With Quote
Old 03-10-2019, 04:27 PM   #205
4 Rivet Member
 
Currently Looking...
Fort Davis , Texas
Join Date: May 2017
Posts: 257
Quote:
Originally Posted by Meddle View Post
Hi everyone, I am adding a panel to my PV system and upgrading my battery bank from two 105AH AGM to four 100AH LiFePO4.

In doing so, I plan to move the batteries from outside to the storage area under the bed. I think I will also take this opportunity to rewire the PV controller, batteries, inverter and a few other DC components such as the LP detector.

I am looking for advice or feedback on how I have diagramed my upgrade --anything in terms of things I may have overlooked or components I've included that aren't needed. For example, one thing I'm not sure of is whether 1 GA wire is overkill and 2 or 4 GA wire would be sufficient.

Thanks, everyone!

Before anyone here can help you need much more information:

1. Make and Model of your batteries
2. Make and Model of your Battery Monitor
3. Make and Model of your Solar Charge Controller
4. Make and Model of your Solar Panels
5. Make and Model of your Inverter

Something seems off, most LFP batteries are capable of absorbing and producing 1C, which means 4 100Amp Hour batteries, in parallel, are capable of producing 400 Amps of current. Please give us some more information to go on.

Thanks,
Pat
pdavitt is offline   Reply With Quote
Old 03-10-2019, 05:49 PM   #206
2 Rivet Member
 
2012 27' FB International
Victor , New York
Join Date: Jan 2013
Posts: 30
Quote:
Originally Posted by pdavitt View Post
Before anyone here can help you need much more information:

1. Make and Model of your batteries
2. Make and Model of your Battery Monitor
3. Make and Model of your Solar Charge Controller
4. Make and Model of your Solar Panels
5. Make and Model of your Inverter
Sorry Pat, was trying to keep the diagram make/model agnostic to make it as straight forward as possible.

1. Batteries - Battle Born 100Ah 12V LiFePO4 Deep Cycle
2. Battery Monitor - Bogart TM-2030-A-F TriMetric
3. PV Controller - Blue Sky Solar Boost 3000i
4. PV Panels - AM Solar: (2) W135GS + (1) ZS90L
5. Inverter - WFCO 600W Pure Sine Wave WF-600TH
6. Converter (not diagramed) - PD4655V
Meddle is offline   Reply With Quote
Old 03-10-2019, 06:40 PM   #207
2 Rivet Member
 
2012 27' FB International
Victor , New York
Join Date: Jan 2013
Posts: 30
Quote:
Originally Posted by Wolfwhistle View Post

You are "missing" protection / breaker on the 12vdc supply side of the inverter and one on the battery side of the MPPT, IMO.

If the inverter can make 1200W surge, the breaker somewhere between there and batteries should be in the order of around 100 / 120 amps DC. 1 AWG doesn't seem like enough.

Also, check with product information, because I doubt you can terminate a 1 AWG at the MPPT (gauge seems overly large) and possibly not onto the Inverter without a proper method.
Thank you, Wolfwhistle. These are excellent points you bring up. And you are correct about the 1 AWG not fitting for the MPPT and inverter. It looks like the largest I can go is 4 GA. I highlighted changes to the diagram. I think I am following you on the breaker positioning (makes sense when I think about it) but want to be sure that's what you meant.

Thanks again. This kind of help is what makes this community so special!
Attached Thumbnails
Click image for larger version

Name:	PV2.jpg
Views:	250
Size:	235.5 KB
ID:	335375  
Meddle is offline   Reply With Quote
Old 03-10-2019, 07:58 PM   #208
Rivet Master
 
TouringDan's Avatar

 
1966 24' Tradewind
1995 34' Excella
Lynchburg , Virginia
Join Date: Jun 2006
Posts: 4,226
Meddle

Looks like you are in great shape with comments from the folks that know.

I have completed my upgrade but I am sure I probably need to make some changes, but I don’t have a nice wiring drawing like you have. What software did you use?

Thanks, Dan
TouringDan is offline   Reply With Quote
Old 03-10-2019, 08:42 PM   #209
2 Rivet Member
 
2012 27' FB International
Victor , New York
Join Date: Jan 2013
Posts: 30
Quote:
Originally Posted by TouringDan View Post
What software did you use?
Thanks, Dan

I used Adobe Illustrator for this.
Meddle is offline   Reply With Quote
Old 03-11-2019, 07:15 AM   #210
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,744
Quote:
Originally Posted by Meddle View Post
Hi everyone, I am adding a panel to my PV system and upgrading my battery bank from two 105AH AGM to four 100AH LiFePO4.

In doing so, I plan to move the batteries from outside to the storage area under the bed. I think I will also take this opportunity to rewire the PV controller, batteries, inverter and a few other DC components such as the LP detector.

I am looking for advice or feedback on how I have diagramed my upgrade --anything in terms of things I may have overlooked or components I've included that aren't needed. For example, one thing I'm not sure of is whether 1 GA wire is overkill and 2 or 4 GA wire would be sufficient.

Thanks, everyone!
Hi

Two 100AH AGM's give you 100AH net usable capacity. Four 100AH Lithiums give you 400AH net usable capacity (for a *lot* more money). If indeed the credit card is happy both ways, the higher capacity likely will be of more use to you.

Wire wise, the inverter capacity is most likely to be the big factor. The bigger the inverter the larger the wire. Run length also matters a bit. Yes, you *could* put in a 5,000W solar array or a 400A converter / charger. Most people don't do that ....

Since things like inverter size and the rest relate back to battery capacity (and type), this all is an interactive problem. Change one thing and that likely impacts the rest of the system.

So is $4,000 for the lithium's in the budget? Unless some solar is involved, that's at least 2/3 of what this will cost on a DIY basis.

Bob
uncle_bob is offline   Reply With Quote
Old 03-11-2019, 08:14 AM   #211
Rivet Master
 
AirMiles's Avatar
 
2018 27' Globetrotter
Apollo Beach , Florida
Join Date: Feb 2017
Posts: 1,401
Meddle, your revised diagram looks good to me.

I am wondering why 400AH of Lithium? That's a huge battery bank for a 600W inverter and typical Airstream loads, especially when you have solar that will be recharging the battery bank each day. I typically use about 100AH per day when running my furnace all night and typical Airstream loads. With a 400AH battery bank, I could boondock for four days in complete shade with 50 degree temperatures. If I had 400W of lithiums, I'd install at least a 2000W inverter so I could run my microwave and my wife's hairdryer. To me, something seems out of balance with the battery bank and inverter size.

Also why a mix of solar panels? Wouldn't four 100W panels fit on the four corners of your roof like I have on my FC25FB? (picture here: http://www.airforums.com/forums/f448...ml#post2102019 ) Do MPPT controllers prefer matching panels so the most efficient Maximum Power Point can be utilized for all the panels? I would use matching panels if possible on the roof.
__________________
2021 Northern-Lite 10-2 & F350 DRW PSD, 600W Solar/Victron/600A BattleBorn
146 nights 31,000 miles (first 10 months!)
Sold: 2018 GT27Q, 74 nights 12,777 miles
Sold: 2017 FC25FB, 316 nights 40,150 miles
Sold: 2013 Casita SD17 89 nights 16,200 miles
AirMiles is offline   Reply With Quote
Old 03-11-2019, 08:41 AM   #212
Rivet Master
 
TouringDan's Avatar

 
1966 24' Tradewind
1995 34' Excella
Lynchburg , Virginia
Join Date: Jun 2006
Posts: 4,226
Solar Show and Tell

Meddle

If you are sure that you want the capacity of 400 AH then of course go with it. If you aren’t sure then maybe start with 200 AH or even 100 AH, you can add more capacity easily later. It doesn’t affect the design of your planned modifications.

Dan
TouringDan is offline   Reply With Quote
Old 03-11-2019, 10:46 AM   #213
2 Rivet Member
 
2012 27' FB International
Victor , New York
Join Date: Jan 2013
Posts: 30
Quote:
Originally Posted by AirMiles View Post
I am wondering why 400AH of Lithium? That's a huge battery bank for a 600W inverter and typical Airstream loads, especially when you have solar that will be recharging the battery bank each day.

Also why a mix of solar panels? Wouldn't four 100W panels fit on the four corners of your roof like I have on my FC25FB?
Hi AirMiles, we hardly have a need for the inverter, in fact I think we've powered it up maybe twice in 6 years. It came with the trailer, but everything we run is 12V. I figure I'd keep it and wire it in just in case the occasional need does come up.

I have two 135W AM Solar PVs already, but AM Solar isn't making that panel anymore, so unfortunately I have to go with a mix if I want to add more panels. I did speak to AM Solar about this and they said the panel I have in mind, another AM Solar panel, would be compatible with my system.

We do a lot of boondocking in tree-shaded sites and the weather can be overcast a lot of the time. Our AGMs with 100 AH (useable) typically lasts us 4-5 days under these conditions. That was our thought process with moving to 400 AH usable. We want to be able to last 10+ days under less than ideal solar conditions and not have to worry about it. That to me is worth the $4K investment.
Meddle is offline   Reply With Quote
Old 03-12-2019, 08:42 AM   #214
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,744
Quote:
Originally Posted by Meddle View Post
Hi AirMiles, we hardly have a need for the inverter, in fact I think we've powered it up maybe twice in 6 years. It came with the trailer, but everything we run is 12V. I figure I'd keep it and wire it in just in case the occasional need does come up.

I have two 135W AM Solar PVs already, but AM Solar isn't making that panel anymore, so unfortunately I have to go with a mix if I want to add more panels. I did speak to AM Solar about this and they said the panel I have in mind, another AM Solar panel, would be compatible with my system.

We do a lot of boondocking in tree-shaded sites and the weather can be overcast a lot of the time. Our AGMs with 100 AH (useable) typically lasts us 4-5 days under these conditions. That was our thought process with moving to 400 AH usable. We want to be able to last 10+ days under less than ideal solar conditions and not have to worry about it. That to me is worth the $4K investment.
Hi

Pretty much exactly the same though process that got me to go from two AGM's to four lithium's. With a modern Classic, I could not go 4 days on the AGM's in the shade, but otherwise same sort of numbers. So far I'm quite happy with the choice I made. We'll add a third solar panel to the roof soon. I'm not counting on that for a lot most of the time. We like the shade .....

Bob
uncle_bob is offline   Reply With Quote
Old 03-15-2019, 10:34 AM   #215
2 Rivet Member
 
czunc's Avatar
 
2017 25' Flying Cloud
Dallas , Texas
Join Date: Aug 2017
Posts: 79
I have a quick question about attaching the AM Solar feet.



We finally have a warm dry weekend ahead of us so I want to finish my install. All I have left is to stick my 4 panels to the roof but I,m not sure how long I need to let the VHB tape cure before covering with sealant. My plan is to clean the roof in the morning, wait until after lunch to install the feet and maybe seal them on Monday night?? We are leaving for Big Bend on Weds. night so I want everything to be cured before leaving on a 9 hour drive.
__________________
2017 25FB Flying Cloud
2022 Ford F-350 Platinum FX4

"Life is a team sport"
czunc is offline   Reply With Quote
Old 03-15-2019, 11:46 AM   #216
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
You don't really have to wait for sealing the panels. I use SikaFlex 221 for that purpose......in grey. After you set and seal the panels, they are really stuck down, but require 2-3 days to start curing, and a full 30 days for the tape to fully set.

Careful application of the sealant will allow use of the trailer in the 2-3 day window.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 03-15-2019, 12:49 PM   #217
2 Rivet Member
 
czunc's Avatar
 
2017 25' Flying Cloud
Dallas , Texas
Join Date: Aug 2017
Posts: 79
Thanks Lewster! I plan to clean with carb cleaner 1st then stick the foot in place. I did go with the 221 but in white to match my roof. I've read where alcohol will effect the 221.
__________________
2017 25FB Flying Cloud
2022 Ford F-350 Platinum FX4

"Life is a team sport"
czunc is offline   Reply With Quote
Old 03-15-2019, 12:54 PM   #218
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Sounds like a plan!!!!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 03-18-2019, 05:21 AM   #219
Rivet Master
 
AirMiles's Avatar
 
2018 27' Globetrotter
Apollo Beach , Florida
Join Date: Feb 2017
Posts: 1,401
This past weekend I was dry camping in Punta Gorda Florida on a rainy and overcast day. Occasionally, the sun would pop out of the overcast for a moment. During one sunny moment my 400W solar array, using the factory 10 gauge prewire, peaked at 434 Watts of production. This is a new record level for my system. Attached is a screen shot documenting this production.

I believe there were two reasons for exceeding my 400W panel rating. First, when the sun is at the edge of a cloud it intensifies in the same way as a magnifying glass increases the sun. Second, and similarly, the same magnifying affect occurs when water droplets sit on the panels. I believe much of the dramatic increase in power was due to this magnifying effect. Also, due to the overcast conditions for most of the day, my Victron 100/30 controller was still in bulk mode at 1 pm when the sun was at its peak. Typically, bulk mode is done before peak sun so the Victron controller starts reducing amperage, an therefore solar wattage, to hold the voltage at its absorption level setting.

Even though the rainy and overcast conditions continued for the rest of the day, the system completely charged my batteries by obtaining float stage at 3:45 pm. The 400W array produced 830 Watt Hours to obtain float status. At a 13.5V average output, this would total 61.5AH of charging (830WH/13.5V=61.5AH). I'm satisfied with getting 60+ Amp Hours of battery charging on a rainy and overcast day.
Attached Thumbnails
Click image for larger version

Name:	F7014540-7EAC-48A1-B20E-C169CCB5992A.jpg
Views:	122
Size:	113.3 KB
ID:	335978  
__________________
2021 Northern-Lite 10-2 & F350 DRW PSD, 600W Solar/Victron/600A BattleBorn
146 nights 31,000 miles (first 10 months!)
Sold: 2018 GT27Q, 74 nights 12,777 miles
Sold: 2017 FC25FB, 316 nights 40,150 miles
Sold: 2013 Casita SD17 89 nights 16,200 miles
AirMiles is offline   Reply With Quote
Old 03-19-2019, 03:43 AM   #220
3 Rivet Member
 
gregwall's Avatar
 
2014 25' FB Flying Cloud
2005 30' Classic
Keswick , Virginia
Join Date: Nov 2012
Posts: 158
Images: 6
Quote:
Originally Posted by AirMiles View Post
This past weekend I was dry camping in Punta Gorda Florida on a rainy and overcast day. Occasionally, the sun would pop out of the overcast for a moment. During one sunny moment my 400W solar array, using the factory 10 gauge prewire, peaked at 434 Watts of production. This is a new record level for my system. Attached is a screen shot documenting this production.

I believe there were two reasons for exceeding my 400W panel rating. First, when the sun is at the edge of a cloud it intensifies in the same way as a magnifying glass increases the sun. Second, and similarly, the same magnifying affect occurs when water droplets sit on the panels. I believe much of the dramatic increase in power was due to this magnifying effect. Also, due to the overcast conditions for most of the day, my Victron 100/30 controller was still in bulk mode at 1 pm when the sun was at its peak. Typically, bulk mode is done before peak sun so the Victron controller starts reducing amperage, an therefore solar wattage, to hold the voltage at its absorption level setting.

Even though the rainy and overcast conditions continued for the rest of the day, the system completely charged my batteries by obtaining float stage at 3:45 pm. The 400W array produced 830 Watt Hours to obtain float status. At a 13.5V average output, this would total 61.5AH of charging (830WH/13.5V=61.5AH). I'm satisfied with getting 60+ Amp Hours of battery charging on a rainy and overcast day.
Those are very impressive numbers. Love the explanation and seeing the history panel. Can't wait to get on the road.

Hello Lewster! Hope all is well in Florida!
__________________
Greg
2014 25' Flying Cloud FB
2015 GMC Sierra Denali 6.6L diesel
Charlottesville, Virginia
gregwall is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
I'll Show You My Dent If You Show Me Yours! Rubyslipper Ribs, Skins & Rivets 42 12-22-2016 07:10 AM
If you show me yours, I'll show you mine... SKEETER 1993 Excella 1000 38 01-08-2008 11:01 PM
Show and tell (thinking caps) rebel beck Off Topic Forum 5 08-16-2006 06:21 PM
Cyber finds - show and tell Janet H Off Topic Forum 6 04-01-2006 05:39 PM
I'll Show you Mine If you'll show Me yours... joossens Link Archive 0 05-12-2004 12:51 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:04 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.