Heat Pumps on a Classic 30' 2018

Does anyone know if there is a temperature in which the heat pumps (by themselves, Alde turned off) will not operate? Meaning not come on at all when turned on at Firefly. The outside temp this morning was 33/34 and that also reflected the inside temp and when I tried to turn on one unit I got a click and that was it. Now I'm only connected to 30 amp service so only tried one unit at a time with the same response. I also lowered the temp to be within 5 degrees of temp in the trailer so it wouldn't be calling for the Alde to help out. I have the breaker to the Alde turned off anyway because it is winterized. Now having said all of that I put a heater inside and got the temp up to 63 or so and in the mean time the outside temp got up to 43 or so. I decided to try once more before making a phone call and what do you know it came on. Anyone have this experience? Of course I got no manual for the heat pumps with this unit and Dometic couldn't help me with it either.
Airhead2018 is offline   Reply With Quote
Old 02-10-2018, 10:04 AM   #2
Rivet Master
 
BigSxyWhtGuy's Avatar
 
2018 30' Classic
Thousand Oaks , California
Join Date: Mar 2017
Posts: 1,637
Yes, below 50 is tough and below 30 is no longer ideal. You are really close to that mark.
__________________
BigSxyWhtGuy

Follow our adventures!
@airstreamvagabond on Instagram and YouTube
BigSxyWhtGuy is offline   Reply With Quote
Old 02-10-2018, 02:04 PM   #3
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
I'm not referring to its heating capabilities while running in cold weather, I am talking about the units being held off (will not run) until a certain temp is reached. Be it an outside temp or an inside temp. Like the heat pump at my house will not run below 40 degrees.
Airhead2018 is offline   Reply With Quote
Old 02-10-2018, 02:21 PM   #4
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
It's a bit lower that that for my Penguin 13.5k. At about 36 or 37 it won't come on....and if on, switches to furnace.
Still puts out good heat all the way down as well.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 02-10-2018, 03:16 PM   #5
Reads a lot
 
2017 30' Classic
Titusville , Florida
Join Date: Dec 2016
Posts: 1,209
Images: 1
Hi Air2018, I have a 2017 Classic so mine is a bit different than yours because of how the Firefly interfaces with the Alde. I used mine last year in temps way below 32 and didn’t have a problem with the Alde system. I did try to use the heat pump a couple of times just to see if it would work, it does ok in temps at or around 40 or higher but the Alde is so good and so quite that I never use the heat pump anymore. Sorry this wasn’t more helpful but for most of us with the Alde system there is no reason to bother with the heat pump.
__________________
Lauri

She Believed She Could so She Did.
kendrick.l.j is offline   Reply With Quote
Old 02-10-2018, 04:51 PM   #6
Overkill Specialist
Commercial Member
 
GMFL's Avatar
 
2020 30’ Globetrotter
2014 23' International
Dadeville , Alabama
Join Date: Oct 2015
Posts: 4,516
Images: 4
Blog Entries: 52
Quote:
Originally Posted by dznf0g View Post
It's a bit lower that that for my Penguin 13.5k. At about 36 or 37 it won't come on....and if on, switches to furnace.
Still puts out good heat all the way down as well.
My 23 has a 13.5K and does the same thing. Temps in mid to low 30’s it switches over to furnace
GMFL is offline   Reply With Quote
Old 02-11-2018, 04:22 AM   #7
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
Quote:
Originally Posted by dznf0g View Post
It's a bit lower that that for my Penguin 13.5k. At about 36 or 37 it won't come on....and if on, switches to furnace.
Still puts out good heat all the way down as well.
Thanks Rich, that is the answer I was looking for!
Airhead2018 is offline   Reply With Quote
Old 02-11-2018, 04:24 AM   #8
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
Also thanks to all for their responses!
Airhead2018 is offline   Reply With Quote
Old 02-11-2018, 10:03 AM   #9
3 Rivet Member
 
2017 25' International
Framingham , Massachusetts
Join Date: Oct 2015
Posts: 142
Quote:
Originally Posted by Airhead2018 View Post
Also thanks to all for their responses!
The answer is yes. It will shut off automatically when the outside temp gets too low. It is explained in my owner's manual. I don't have it in front of me so can't give exact numbers but somewhere in the mid 40's the HP goes into alternating heating/defrosting cycles and will no longer keep the trailer at the desired selected temp. A few degrees colder (somewhere around 38-42...again don't have manual in front of me) and it shuts down completely and your only source of heat will be your furnace (or boiler if a newer Classic).
quietguy is offline   Reply With Quote
Old 02-11-2018, 10:06 AM   #10
2 Rivet Member
 
Nightmare67's Avatar
 
2018 30' International
Prescott , Arizona
Join Date: Sep 2017
Posts: 59
Every heat pump has a “cross-over temp” based on its efficiency, below which, it will be locked out. On my home system, it’s 37.
Basically, that means that below 37, the heat pump is unable to extract enough heat from atmosphere to use effectively.
Nightmare67 is offline   Reply With Quote
Old 02-11-2018, 02:11 PM   #11
1 Rivet Member
 
2018 33' Classic
1995 36' Classic 36
Akron , Ohio
Join Date: Jul 2016
Posts: 11
I have a 2018 Classic 33 and the heat pumps will NOT turn on if the outside temperature is below 35, above 35 they work fine.
fkiehl is offline   Reply With Quote
Old 02-12-2018, 07:19 AM   #12
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
Quote:
Originally Posted by Nightmare67 View Post
Every heat pump has a “cross-over temp” based on its efficiency, below which, it will be locked out. On my home system, it’s 37.
Basically, that means that below 37, the heat pump is unable to extract enough heat from atmosphere to use effectively.
Not exactly, we have an older heat pump in the house we live in now and it will run until the cows come home. Just saying
Airhead2018 is offline   Reply With Quote
Old 02-12-2018, 07:25 AM   #13
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
Quote:
Originally Posted by fkiehl View Post
I have a 2018 Classic 33 and the heat pumps will NOT turn on if the outside temperature is below 35, above 35 they work fine.
Thanks, I need to get the model number of the units so I can get a manual. I tried the heat pumps later when the outside temps got up and they worked fine. Had some issues with Firefly/Alde configuration previously and was hoping it was something simple like that.
Airhead2018 is offline   Reply With Quote
Old 02-12-2018, 08:32 PM   #14
Rivet Master
 
mikeinca's Avatar

 
2020 25' Globetrotter
Santa Rosa , California
Join Date: Feb 2017
Posts: 1,846
Images: 2
It's interesting that this topic came up because we recently had the same issue with one of the heat pumps on our 2018 30' Classic. What was curious was that at an ambient temp of around 40 degrees the rear unit came on and produced warm air but the front unit just gave a "click" and did not activate. While I know that heat pumps don't work at low temperatures, since one unit functioned and the other didn't I assumed that something must be wrong. But at the dealership they couldn't replicate the problem (of course) and both units performed perfectly. Maybe the temp threshold varies slightly from unit to unit.
__________________
Mike

2020 25' Globetrotter Twin | 2024 GMC Sierra 2500HD Denali Ult. 4x4 Duramax
400Ah Battle Born lithium battery string | 580W solar (400W roof 180W portable)
mikeinca is offline   Reply With Quote
Old 02-13-2018, 04:48 AM   #15
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
Quote:
Originally Posted by mikeinca View Post
It's interesting that this topic came up because we recently had the same issue with one of the heat pumps on our 2018 30' Classic. What was curious was that at an ambient temp of around 40 degrees the rear unit came on and produced warm air but the front unit just gave a "click" and did not activate. While I know that heat pumps don't work at low temperatures, since one unit functioned and the other didn't I assumed that something must be wrong. But at the dealership they couldn't replicate the problem (of course) and both units performed perfectly. Maybe the temp threshold varies slightly from unit to unit.
Sounds like the outdoor temperature sensor might be a little off on that unit, where ever that might be. Everything works at the dealer, funny how that works.
Airhead2018 is offline   Reply With Quote
Old 02-14-2018, 05:42 AM   #16
ObviouslyKnot
 
james.mileur's Avatar
 
Currently Looking...
KAILUA , HI
Join Date: Nov 2016
Posts: 862
My 17 Classic dometic thermostat manual says, 30 degrees and above for heat pump to work. No run time to validate how low it will go, Alde does such a good job.
__________________
James Mileur, HY80-2-Al,
2017 Classic Twin, 2016 RAM 3500 Megacab, ProPride hitch
james.mileur is offline   Reply With Quote
Old 02-14-2018, 08:12 AM   #17
4 Rivet Member
 
mojoe7009's Avatar
 
Currently Looking...
Green Cove Springs , Florida
Join Date: Oct 2016
Posts: 479
Quote:
Originally Posted by james.mileur View Post
My 17 Classic dometic thermostat manual says, 30 degrees and above for heat pump to work. No run time to validate how low it will go, Alde does such a good job.


I agree with James. Alde does such a great job I can only imagine using my heat pumps if the Alde system completely failed. We use the night timer function every night. We set the system to not go above 58 from 9:30 pm until 5:30 am then it is set to 65. By the time we get up at 6:30 the trailer is nice and warm. Just set once, turn on and forget it.
__________________
Breathe In, Breathe Out, Move On
mojoe7009 is offline   Reply With Quote
Old 02-15-2018, 06:13 AM   #18
4 Rivet Member
 
2018 30' Classic
Cumberland , Maryland
Join Date: Jul 2017
Posts: 335
Alde system is winterized, otherwise I would be using it. In any case I want to know if all systems are operational. Thanks for the info on the Dometic thermostat which I don't have, but will look up just for info purpose. Thanks again!!
Airhead2018 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Alde Heating 2018 Classic 30 - Radiant Heat madogkenno 2016 - Current Classic (all lengths) 11 01-09-2018 06:03 AM
Heat Pump on 2018 Classic ajwbarnard 2016 - Current Classic (all lengths) 9 09-19-2017 08:00 PM
Why do they put heat pumps in trailers? Bill M. Airstream Lifestyle 23 02-26-2014 02:27 PM
Thermostat-Dual Heat Pumps carlose Electronics & Connectivity 0 10-09-2011 04:02 PM
Heat Pumps Brianv512 Furnaces, Heaters, Fireplaces & Air Conditioning 8 01-19-2011 05:15 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 06:49 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.