Rooftop Penguin A/C ran fine yesterday. Turned it on today and all I am getting is a "hum" and no fan running. It is the original in a 1994 trailer, and the control board was replaced 7 years ago. Does this sound like the capacitor is gone? Is the capacitor replaceable on these old units with the new easy start? Any thoughts would be appreciated.
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1994 Excella 34'
1987 Limited 34', 1976 31', 1976 Argosy 22' Gone to new homes
Hensley Hitch
|
|
|
06-26-2022, 05:40 PM
|
#2
|
4 Rivet Member
2018 25' International
Full-time
, Traveler
Join Date: May 2018
Posts: 313
|
We had a similar issue with an AC unit at a house we owned awhile back. It was the capacitor, and was replaceable on it. Not sure about the Dometic, but it seems like it should be a replaceable part.
|
|
|
06-26-2022, 06:50 PM
|
#3
|
Rivet Master
1973 21' Globetrotter
Houston
, Texas
Join Date: Sep 2009
Posts: 3,322
|
yes, sounds like a cap, and yes, it should be replaceable with an EasyStart--but you should probably check the tech support line with the company. I have found them to be very responsive.
|
|
|
06-26-2022, 07:20 PM
|
#4
|
Site Team
2017 30' International
Broomfield
, Colorado
Join Date: Apr 2009
Posts: 3,555
|
There is a start cap inside the easy start enclosure. Call micro air.
Compressor could be siezed as well.
|
|
|
06-27-2022, 07:40 AM
|
#5
|
Rivet Master
1994 34' Excella
Warren
, Manitoba
Join Date: Apr 2006
Posts: 1,253
|
Thanks for the replies. This unit always has the fan start first, and the compressor would start about 2 minutes after the fan. We are on the road now but should be home in 2 days, so will get up and remove the shroud and see what I can. Somehow I seem to remember that the capacitor was on the board when it was replacedyears ago. Maybe just as wise to replace the unit completely!!
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1994 Excella 34'
1987 Limited 34', 1976 31', 1976 Argosy 22' Gone to new homes
Hensley Hitch
|
|
|
06-27-2022, 04:56 PM
|
#6
|
Site Team
2017 30' International
Broomfield
, Colorado
Join Date: Apr 2009
Posts: 3,555
|
Penguin A/C isssue
Quote:
Originally Posted by CBWELL;
Thanks for the replies. This unit always has the fan start first, and the compressor would start about 2 minutes after the fan. We are on the road now but should be home in 2 days, so will get up and remove the shroud and see what I can. Somehow I seem to remember that the capacitor was on the board when it was replacedyears ago. Maybe just as wise to replace the unit completely!!
|
Fan starting first is normal behavior in cool mode. In heat pump mode compressor starts first I believe.
There are 2 capacitors with those earlier penguin units. A start cap and a smaller run cap.
When you install east start you remove the start cap, and wire in the easy start unit in its place. Inside the easy start unit is a start cap who’s current is controlled by a microprocessor board.
If you are having starting issues it’s likely either the compressor motor itself (they can go bad) or it is possible that the start cap in the easy start failed…. It happens.
Depending on the version of easy start you have there are leds that show status / error codes. If you have an earlier version you need to open the unit to see the lights.
Easy start support is great, not sure if Matteo (lead engineer) is still there but they can help likely. [emoji4]
Be careful up on the roof!
|
|
|
07-07-2022, 09:20 PM
|
#7
|
Rivet Master
1994 34' Excella
Warren
, Manitoba
Join Date: Apr 2006
Posts: 1,253
|
Problem has been solved!! Took the cover off today, turned off the power, went to the "parts cupboard" and got a start capacitor that I bought years ago for a friends project that never got completed. Put in the new capacitor. and everything worked as normal. Just glad I didn't have to search for a new A/C unit, as they are hard to find in Canada. Thanks for all the input!
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1994 Excella 34'
1987 Limited 34', 1976 31', 1976 Argosy 22' Gone to new homes
Hensley Hitch
|
|
|
07-07-2022, 09:40 PM
|
#8
|
Site Team
2017 30' International
Broomfield
, Colorado
Join Date: Apr 2009
Posts: 3,555
|
Quote:
Originally Posted by CBWELL;
Problem has been solved!! Took the cover off today, turned off the power, went to the "parts cupboard" and got a start capacitor that I bought years ago for a friends project that never got completed. Put in the new capacitor. and everything worked as normal. Just glad I didn't have to search for a new A/C unit, as they are hard to find in Canada. Thanks for all the input!
|
Awesome. Good work! Simple fix
|
|
|
|