Post EMS-HW30C install problem

I just installed an EMS-HW30C on our 2016 23FB Flying Cloud. Prior to the install I was plugging the trailer into a 15 amp garage circuit with no problem. I was even able to run the AC on this circuit after installing a Micro - Air Easy Start 364 as long as we didn't run anything else besides lights.

Now after I installed the EMS-HW30C on the intial plug in of shore power with the 30 amp main breaker in the trailer off I got the expected codes on the display indicating proper opertation. Then I started turning on the A/C breakers, 30 amp main 1st followed by 20 amp circuit 1, 2, 3, 4, with no problem. Then when I flip 20 amp circuit 5 on it causes the circuit breaker for the 15 amp circuit in my garage to pop. I repeated this proces three times with the same results. There is nothing else plugged in on that circuit other than the trailer. According to the Owners Manual circuit five supplies power to Water Heater, 100W inverter, 7 amp breaker, 10 amp transfer switch, fInverted bedroom tv receptacle, inverted dinetted receptacle, inverted blu-ray player receptacle. I have nothing plugged in to any of these receptacles. Water heater switch is in the off position.

Any help would be appreciated as I am dead in the water and we are looking toward a June 18 two night maiden voyage.
Big_Gar is offline   Reply With Quote
Old 06-12-2021, 07:49 PM   #2
Rivet Master
 
tjdonahoe's Avatar
 
2013 31' Classic
billings , Montana
Join Date: Feb 2010
Posts: 3,577
Try leaving ac breaker off
tjdonahoe is offline   Reply With Quote
Old 06-12-2021, 07:50 PM   #3
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,550
Quote:
Originally Posted by Big_Gar View Post
I just installed an EMS-HW30C on our 2016 23FB Flying Cloud. Prior to the install I was plugging the trailer into a 15 amp garage circuit with no problem. I was even able to run the AC on this circuit after installing a Micro - Air Easy Start 364 as long as we didn't run anything else besides lights.

Now after I installed the EMS-HW30C on the intial plug in of shore power with the 30 amp main breaker in the trailer off I got the expected codes on the display indicating proper opertation. Then I started turning on the A/C breakers, 30 amp main 1st followed by 20 amp circuit 1, 2, 3, 4, with no problem. Then when I flip 20 amp circuit 5 on it causes the circuit breaker for the 15 amp circuit in my garage to pop. I repeated this proces three times with the same results. There is nothing else plugged in on that circuit other than the trailer. According to the Owners Manual circuit five supplies power to Water Heater, 100W inverter, 7 amp breaker, 10 amp transfer switch, fInverted bedroom tv receptacle, inverted dinetted receptacle, inverted blu-ray player receptacle. I have nothing plugged in to any of these receptacles. Water heater switch is in the off position.

Any help would be appreciated as I am dead in the water and we are looking toward a June 18 two night maiden voyage.
1. Is the garage outlet GFCI protected by a GFCI outlet or a GFCI breaker?
2. Did you try switching the EMS to bypass?
__________________
Brian
ITSNO60 is online now   Reply With Quote
Old 06-12-2021, 08:51 PM   #4
2 Rivet Member
 
2016 23' Flying Cloud
Sioux Falls , SD
Join Date: Apr 2021
Posts: 38
Yes the garage has GFIC but that is not the circuit breaker that opens. It is the main breaker for the garage in the main house electrical panel that opens. what is the use of having the EMS system if I use the bypass switch?
Big_Gar is offline   Reply With Quote
Old 06-12-2021, 09:00 PM   #5
2 Rivet Member
 
2016 23' Flying Cloud
Sioux Falls , SD
Join Date: Apr 2021
Posts: 38
Also, Air Conditioner was not one when I was powering up circuits. Nothing was one except things that are on all the time like the propane sensor.
Big_Gar is offline   Reply With Quote
Old 06-12-2021, 09:04 PM   #6
Rivet Master
 
waninae39's Avatar
 
2022 25' Flying Cloud
NCR , Ontario
Join Date: Feb 2017
Posts: 3,108
The EMS-HW30C CANT be plugged into a GFCI outlet.

call the OEM and they will tell you why.

it needs to be plugged into a non-GFCI outlet
waninae39 is offline   Reply With Quote
Old 06-13-2021, 06:23 AM   #7
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,550
Quote:
Originally Posted by Big_Gar View Post
what is the use of having the EMS system if I use the bypass switch?
I am only suggesting the bypass to rule out a
coincidental problem in the trailer.(testing purposes only)
__________________
Brian
ITSNO60 is online now   Reply With Quote
Old 06-13-2021, 07:13 AM   #8
2 Rivet Member
 
2016 23' Flying Cloud
Sioux Falls , SD
Join Date: Apr 2021
Posts: 38
After further testing this moring:

Yes I tried the bypass. The same thing happened when I turned circuit 5 on. The breaker opened on my house main pane.

I have a 25 ft. 10 gage 30amp extension cord so I tried plugging in to different circuits in my house for shore power.

I tried plugging into my home kitchen circuit which is GCFI. The GCFI to the kitchen circuit opened when I turned on trailer circuit number 5.

I tried plugging into my living room outlets which is not a GCFI circuit. When I turned trailer circuit number 5 on the breaker in my main house panel for the living room outlets opened.

I have a call in to Progressive Industires so I will be waiting for a call back on Monday.

Maybe I am in over my head. Does anyone know of a good reliable honest electrician or RV dealer somewhere in my region (MN, SD, ND, IA, Nebraska) I could pay to finish this job for me. I don't have the EMS unit mounted yet nor do I have the cover on as I was testing before I did that. I also see that my shore power 30 amp wire jacket (just the exterior) is compomised between the EMS unit and the exterior trailer shore power outlet.
Big_Gar is offline   Reply With Quote
Old 06-13-2021, 07:29 AM   #9
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,550
You've already done some of the things I was about to suggest so saved me some typing A couple more things to try and narrow this down. If you have a multimeter, with the trailer unplugged record the Ohms between the two flat blades of your plug. Then turn on the first 4 breakers and measure, record again. Then turn on the 5th breaker, measure and record. Then turn off the first 4 and measure/record just with #5 turned on.
Also: Did you try turning on #5 only and see if that trips the breaker?

The facts are pointing to an issue with circuit #5 in your trailer especially since it trips even when bypassing the EMS. When you say the water heater is on #5 is it for an electric heating element?

Also, did you try #5 with the Inverter and converter turned off?
__________________
Brian
ITSNO60 is online now   Reply With Quote
Old 06-13-2021, 07:29 AM   #10
Rivet Master
 
1988 25' Excella
1987 32' Excella
Knoxville , Tennessee
Join Date: Oct 2010
Posts: 5,119
Blog Entries: 1
It sure sounds like there is something wrong with the #5 circuit. It sounds like the EMS is okay and just doing its job. Was circuit 5 working before the install? Any chance you damaged that circuit during the install? Drill hole or screw or something? Drilling or screwing into a wire is a big concern for me when working on the trailer. I think I would unplug the trailer and test #5 with a meter looking for a short or load before I did anything else.
Bill M. is offline   Reply With Quote
Old 06-13-2021, 07:43 AM   #11
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,550
Quote:
Originally Posted by waninae39 View Post
The EMS-HW30C CANT be plugged into a GFCI outlet.

call the OEM and they will tell you why.

it needs to be plugged into a non-GFCI outlet
Not saying this is incorrect but it doesn't make a lot of sense The OP's problem doesn't appear to be the GFCI as it trips on short circuit/overload not on ground fault, the garage GFCI did not trip, also it worked fine on 4 of his circuits. Everything at this point indicates a problem with one of his circuits.

The documentation for the HW30C doesn't mention this either but you have got me curious and later today I am going to try a side experiment and try mine on a GFCI and see what happens, This would not be good because one of the big reasons for the EMS is to protect from low voltage when hooking up at a friends garage or outdoor circuit overnight and running the AC.
__________________
Brian
ITSNO60 is online now   Reply With Quote
Old 06-13-2021, 08:12 AM   #12
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,550
If checking resistance between the flat blades does not turn up an overload then check again from the hot blade to the ground pin to check for a ground fault (short)
__________________
Brian
ITSNO60 is online now   Reply With Quote
Old 06-13-2021, 09:43 AM   #13
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,746
Hi

Best guess: You bumped / nicked / crushed something associated with circuit 5 while putting in the EMS. Start out looking at the circuit 5 wires near your install location.

Bob
uncle_bob is offline   Reply With Quote
Old 06-13-2021, 10:28 AM   #14
2 Rivet Member
 
2008 27' International FB
Hillsboro , Texas
Join Date: Aug 2008
Posts: 51
The EMS is not seeing a ground causing it to think the circuit is bad. You can put the EMS on by pass if its a hardwired unit.
grwalk is offline   Reply With Quote
Old 06-13-2021, 10:31 AM   #15
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,550
Quote:
Originally Posted by grwalk View Post
The EMS is not seeing a ground causing it to think the circuit is bad. You can put the EMS on by pass if its a hardwired unit.
How does an EMS trip upstream circuit breakers because of lack of ground??
__________________
Brian
ITSNO60 is online now   Reply With Quote
Old 06-13-2021, 10:54 AM   #16
New Member
 
2020 27' Globetrotter
Littleton , Massachusetts
Join Date: Feb 2020
Posts: 2
My electrical knowledge is extremely limited, so I can't provide much detail or explanation, but we occasionally have a problem tripping a breaker at home when we plug in and we seem to have found a solution. We turn the inverter ON before plugging in - something about a relay in the inverter causing the EMS to detect a fault?? We just turn it off after a moment and everything runs fine.
We may have come across this suggestion in a forum post in the past.
__________________
Zolla
27' 2020 Globetrotter
2020 Ram 2500
RZolla is offline   Reply With Quote
Old 06-13-2021, 11:19 AM   #17
:SPACE A" S/O 11 Air19745
 
guskmg's Avatar
 
2006 34' Classic S/O
Fort Worth , Texas
Join Date: Feb 2007
Posts: 1,766
I agree. It seems like a fault in circuit #5. I would disconnect the water heater element and see if the problem goes away. I have heard of WH elements doing strange thing as they are buried in water which is a great conductor.
guskmg
guskmg is offline   Reply With Quote
Old 06-13-2021, 11:57 AM   #18
3 Rivet Member
 
2018 16' Sport
St. Louis , Missouri
Join Date: May 2019
Posts: 218
I have the same EMS on a Sport 16.
Mine does trip a GFCI when I hook up at home.
I don't have any issues with the main house breakers.
Sport 16 STL is offline   Reply With Quote
Old 06-13-2021, 07:18 PM   #19
2 Rivet Member
 
2016 23' Flying Cloud
Sioux Falls , SD
Join Date: Apr 2021
Posts: 38
Thank you all for your suggestions. First, yes the circuit will open if just #5 is turned on when I was on the GCFI circuits. Then, I tried ITSNO60's suggestion and the ohmeter read "infinity" in all situations. I then plugged in to shore power using my house living room outlet circuit (not GFCI). I then I tried RZolla's suggestion of turning the inverter on. In all situation previous the inverter and the converter were off. Now no matter how I turned on circuit 5 either by itself or after turning on other circuits no house breaker opened, Yay! However the EMS was opening and giving me error code E4 "Low Voltage." I tried turning the inverter off and had the same results, no house breaker opening but the EMS opened and gave me the error code of E4. So I don't think it has to do with wether the inverter is on or off. I also believe now that the EMS unit doesn't like the GFIC circuits. I have a message in to Progressive Industries and I will talk to them about this tomorrow and then report back.
Big_Gar is offline   Reply With Quote
Old 06-13-2021, 07:22 PM   #20
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,746
Quote:
Originally Posted by Big_Gar View Post
Thank you all for your suggestions. First, yes the circuit will open if just #5 is turned on when I was on the GCFI circuits. Then, I tried ITSNO60's suggestion and the ohmeter read "infinity" in all situations. I then plugged in to shore power using my house living room outlet circuit (not GFCI). I then I tried RZolla's suggestion of turning the inverter on. In all situation previous the inverter and the converter were off. Now no matter how I turned on circuit 5 either by itself or after turning on other circuits no house breaker opened, Yay! However the EMS was opening and giving me error code E4 "Low Voltage." I tried turning the inverter off and had the same results, no house breaker opening but the EMS opened and gave me the error code of E4. So I don't think it has to do with wether the inverter is on or off. I also believe now that the EMS unit doesn't like the GFIC circuits. I have a message in to Progressive Industries and I will talk to them about this tomorrow and then report back.
Hi

When you check the voltage with your multimeter, does it read low?

Bob
uncle_bob is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
EMS-PT30X Permanent install inside AI, Still portable, Quick connect/disconnect Alex AVI Sprinter and B-van Forum 23 10-05-2020 11:46 PM
Permanent EMS Install 25ft FB gandttimes Electrical - Systems, Generators, Batteries & Solar 41 08-28-2019 08:12 AM
Progrssive Industries EMS-HW30C Boog Electrical - Systems, Generators, Batteries & Solar 7 05-23-2017 08:55 PM
EMS from Progressive Industries markjoandall Electrical - Systems, Generators, Batteries & Solar 0 08-02-2005 07:14 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.