Old 04-10-2013, 02:49 PM   #1
4 Rivet Member
 
JourneytoRet's Avatar
 
2000 36' Land Yacht XC Diesel
Gaffney , South Carolina
Join Date: Feb 2013
Posts: 254
50 Amp Service

If a campground has a 30A, 220VAC service and a non-GFCI 20A 120VAC service, could someone (not me!) use a cheater box and get maybe 45As?

Camco 55025 RV Power Grip Maximizer 45 Amp Adapter : Amazon.com : Automotive
JourneytoRet is offline   Reply With Quote
Old 04-10-2013, 03:07 PM   #2
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
The answer to your question is yes. But, I have never seen a 30A 220 volt socket at a campground, and seriously doubt they exist.

The 50 amp service socket, is actually 50 amps at 220 Volts AC, but it is used as two 120 volt circuits by the RV. In other words, the RV is wired internally at the breaker box for two 120 VAC circuits.

(a 240 VAC line is actually two 120 VAC lines, 180 degrees out of phase from one another)
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 03:19 PM   #3
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
That adaptor was made to use with an RV with a 50 amp service cord. The 15(or 20) amp plug side goes to one of the two hot legs of the 50 amp outlet and the 30 amp plug side goes to the other leg of that same 50 amp outlet. Then, in the RV itself some of the equipment is supplied by the 15(20) amp outlet and some by the 30 amp outlet.

The main problem is that the National Electric Code has required GFIC outlets in RV park systems for many years now and thus finding a park without one is rare, and if you do find one, you probably should leave anyway.... it is old and illegal by todays standards.

Second problem is that most AS (don't know about your Land Yacht XC) only had 30 amp power cords to begin with, so for most this is an academic question... but maybe not for your rig.

Third problem is that some of the interior electrical panel will be on the 15(20) amp leg and some on the 30 amp leg. If, lets say one AC unit was on the 15(20) leg, and the microwave was also on that leg, you would pop that park breaker no matter what. In other words there is no way to guarantee how the internal coach wiring has been done and if it will work out for you.

The statement in the ad for it saying you get a 45 amp service is misleading in many ways.

These adaptors are very limited in how useful they could be to you, due to the above reasons.
idroba is offline   Reply With Quote
Old 04-10-2013, 03:27 PM   #4
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Quote:
Originally Posted by SteveH View Post
(snip)
(a 240 VAC line is actually two 120 VAC lines, 180 degrees out of phase from one another)
Sorry, but I have to get technical here, the 120/240 volt system we use is a single phase center taped and grounded secondary. The two hot lines are called legs, not phases and are not out of phase with each other. They are on either side of the center taped grounded neutral leg of the transformer which supplies the power.

I did miss the statement in the original post about the 30 amp 240 volt outlet, and you are right, they don't exist, especially when you look at the plug on the device in the photo, which is a standard 30 amp 120 volt RV plug.
idroba is offline   Reply With Quote
Old 04-10-2013, 03:31 PM   #5
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
Quote:
Originally Posted by idroba View Post
Sorry, but I have to get technical here, the 120/240 volt system we use is a single phase center taped and grounded secondary. The two hot lines are called legs, not phases and are not out of phase with each other. They are on either side of the center taped grounded neutral leg of the transformer which supplies the power.
I don't want to argue with you, so I advise you to take an AC volt meter, and test a 50 amp 240 VAC circuit (or any other 240 VAC single phase circuit), each leg to ground, and you will see they each measure 120 VAC. The only way you get 240 VAC out of that is if each 120 VAC leg, or whatever you want to call it, is 180 degrees out of phase from each other.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 03:44 PM   #6
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
You are absolutely correct between each leg and ground is 120 volts, and between the two hot legs there is 240 volts. But the come from a center taped secondary on the single phase transformer and are NOT out of phase with each other, as there is only one phase supplying the transformer. The power company generally has 3 phase power available at the pole, but only one phase of the three is used in residential (and campground) services.

It takes a scope or graphing meter to see that both the 120 and 240 connections are on the same phase, or a look at the transformer connections to see how it has been wired.

I am not trying to be smart ass here, or a know it all, just that the system we use is single phase and the legs are not out of phase with each other. They are two sides (legs) of a center taped secondary single phase system.
idroba is offline   Reply With Quote
Old 04-10-2013, 03:49 PM   #7
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
From Wikipedia:

Leg as in “hot leg” refers to one of multiple hot conductors in an electrical system. The most common residential and small commercial service in the U.S., single split-phase, 240 V, features a neutral and two hot legs, 240 V to each other, and 120 V each to the neutral.

There is no way you can measure 240 volts between the two legs if they are not 180 degrees out of phase from each other. Yes, as opposed to three phase, it is still single phase in the AC power world/lingo, but they are 180 degree out of phase from each other.

If you don't believe it, look at each leg at the same time with a dual trace oscilloscope.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 04:06 PM   #8
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
We will have to have a battle of oscilloscopes... lol. A single phase system cannot produce multiple phase traces. The legs are halves of one winding on a single phase transformer and thus cannot be out of phase with each other.

It is a one winding transformer which supplies the power, single phase. It is taped in the center, which is the neutral and is also grounded for safety sake. Between the center tap and either of the ends of the winding is half the voltage, in this case 120 volts. Between the ends of the winding the full 240 volts appears. It is still a single phase system, and we call the connections to that transformer "legs".

Thats my story and i'm sticking to it, and my last post on the matter.
idroba is offline   Reply With Quote
Old 04-10-2013, 04:29 PM   #9
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
Look at it with an O'scope. If you were here, I'd draw you a diagram to prove it to you.

"Electricians" use terminology frequently that is not "technically correct". I'm a retired Electronics/Telecommunications Engineer.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 05:15 PM   #10
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
I agree with idroba.
Single phase is single phase. The power company delivers power thru either a 3 wire or 4 wire system.
Typically the 3 wire systems are used for commercial and industrial systems. A 4 wire system is used for light industry and residential service.
The single phase transformer on the high voltage side (primary) is tapped to one and only one phase of a "Y" connection. The other primary wire of the transformer is connected to a grounded center tap. The secondary of the transformer has 3 wires or taps
. The potential difference across the transformer is 240 volts. The center tap is there to split that voltage to provide for the 120 volts. The center tap on the secondary is grounded in most cases.
There may be a slight and I mean very slight shift between the current and voltage because of the inductance of the transformer. But there is only single phase power available from the secondary side.
It takes two legs (or phases) of primary power and at least two separate transformers to produce multi phase power.
You can produce 3 phase power with only 2 transformers by using connections like a "SCOTT CONNECTION" but the results are you get an unbalanced three phase power where one leg will read a higher voltage than the other two legs.
Rural Electric Power Companies use Scott connected transformers (or similar tapping methods) to save on wire and transformers when providing 3 phase power to their agricultural customers.
You will not normally find multi phase power in a camp ground or RV park.
A three phase "Y" connected 4 wire 240 volt will read 240 volts between each of the phases and 138 volts between any phase and the center tap.
The voltage difference is determined by the potential difference across the windings. Not the phase relationship.
The phase relationship is created by the rotation of the alternator (still referred to today as a generator) that powers the system. It has nothing to do with the transformer. The phase shift created by the alternator is simply carried thru the transformer.
The reason there are different phases is the fact that the alternator at the power company has 3 sets of windings that are 120 degrees apart, in the rotation circle of the device.
Again, it has nothing to do with the transformer.
TG Twinkie is offline   Reply With Quote
Old 04-10-2013, 05:24 PM   #11
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
Then you are both probably electricians, and you are both wrong, sorry.

I didn't say it is not "single phase", which is an electricians term. I said, in a 240 VAC circuit, each hot leg is 180 degrees out of phase from the other. If it were not, you would measure 0 volts with a meter between the two.

Both of you go look at it with a dual trace O-scope.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 06:03 PM   #12
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
I am an electrician and I am also an electrical and electronics engineer.
I am no sure what kind of scope you are using to see the multi phase you claim you are seeing. But there will only be one sine wave on the scope. Crossing the 0 volts line on the scope at 180 degree intervals. Just because the sine wave crosses the zero line and the positive peak is 180 degrees along time line and the negative peak is 180 degrees along the time line. It doesn't mean there are more than one phase. It is still a SINGLE sine wave.
If you were to look at a 3 phase system with a scope, you would see THREE sine waves, each of which would be 120 degrees apart as they cross the 0 volts line on the scope.
You can prove this very easily by connecting your scope to an automotive alternator. It is in fact a 3 phase AC device. Which uses a full wave bridge and voltage regulator to create the DC power to charge a battery.
You will have to connect the scope ahead of the rectifier to see the 3 phase AC.
When I get time I will post pics on the single phase sine wave and a multi phase sine wave as the scope sees it.
And here is your quote. There is no way you can measure 240 volts between the two legs if they are not 180 degrees out of phase from each other.
TG Twinkie is offline   Reply With Quote
Old 04-10-2013, 06:14 PM   #13
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
I am NOT talking about 3 phase power!

What I said was "a 240 VAC line is actually two 120 VAC lines, 180 degrees out of phase from one another".

If you take a dual trace O-scope, attach channel A probe to one leg of the 240, and channel B probe to the other leg of the 240, you will see that reference the ground, or neutral, when one leg is positive 120volts, the other leg will be negative 120 volts. That is 180 degrees out of phase with each other, but it is NOT multi, or three phase.

Look at it with a dual trace O-scope the way I said, and you will see it.

And, this whole discussion started about 50 amp service into an Airstream. There is nothing in a 50 amp service Airstream that uses 240 VAC. It is utilized in the trailer as two 120 VAC circuits.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 06:28 PM   #14
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
I'm no electrician. I'm not an electronic engineer. But I know unless you bring impedance and phase shifting into the discussion you guys will never reach an accord.
markdoane is offline   Reply With Quote
Old 04-10-2013, 06:41 PM   #15
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
This statement you made is not true.

What I said was "a 240 VAC line is actually two 120 VAC lines, 180 degrees out of phase from one another".

You are using the word "phase" when referring to the point on a time line. That is where the confusion is. Here is a comparison to multiphase as compared to single phase.
It is not the 180 degree swings from the positive side to the negative side of the zero line that create the 240 volts. It is the number of turns of wire in the transformer that determine the voltage or potential difference. There are twice as many turns in the windings between the 2 points that measure 240 volts as compared to the 2 points that create the 120 volts.
The sign wave represents the frequency and peak voltages both negative and positive. The frequency is determined by the design and rotation speed of the Alternator. 50 cycle; 60 cycle; 400 cycle and so on.

http://i1166.photobucket.com/albums/...eSineWaves.jpg
TG Twinkie is offline   Reply With Quote
Old 04-10-2013, 06:50 PM   #16
Rivet Master
 
JimGolden's Avatar
 
Vintage Kin Owner
1977 31' Excella 500
Berkeley Springs , West Virginia
Join Date: Sep 2005
Posts: 1,638
Images: 7
My Fender Hot Rod DeVille all tube guitar amp is 60 watts and will peel the paint off the walls! Now that's power!


Sorry to poke fun. Hate to see you guys arguing, but I have to admit this is a very good and technical thread.

Yes, I like Star Trek, The Hobbit, and even Harry Potter.

I am a fellow Engi-Nerd
__________________
- Jim
JimGolden is offline   Reply With Quote
Old 04-10-2013, 07:21 PM   #17
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
Look at it with a dual trace O-scope like I said, and you will understand it. I know it's difficult for an Electrician to understand when you are thinking of three phase.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 07:28 PM   #18
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
I'm tired of the innuendo that we don't know what you are talking about.
You need to take a refresher course in electrical engineering if you think you are right.
Dual trace scope or not. You don't have a clue about how the 240 and 120 volts are created.
I'm done here.
TG Twinkie is offline   Reply With Quote
Old 04-10-2013, 07:37 PM   #19
Rivet Master
 
SteveH's Avatar
 
2005 39' Land Yacht 390 XL 396
Common Sense , Texas
Join Date: Sep 2007
Posts: 5,319
Ok, you want to talk about transformer output....think of a transformer with a 240 VAC secondary. When one end of the output winding is positive, the other end of the secondary winding is negative in the sinusoidal waveform. On the other part of the cycle, the voltages reverse. Do you agree with this basic theory?

Now, with the same transformer output of 240 VAC, ground the center of the transformer secondary output winding. Then if you measure from either end of the secondary output winding to the center tap, you will measure 120 VAC, but the total secondary output is still 240VAC, and the output is still positive on one end when it is negative on the other end.

This, my friends, is exactly how the two 120 VAC legs are 180 degrees out of phase in a 240 VAC circuit.
__________________
Regards,
Steve
SteveH is offline   Reply With Quote
Old 04-10-2013, 07:54 PM   #20
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
I'll give it ONE MORE TRY.
Reference your scope to one end of the transformer. Then connect the channel 1 lead to the 240 tap on the transformer. Connect the channel 2 lead to the 120 volt tap on the transformer.
When you look at the screen, the only difference you will see is in amplitude. Both in the positive and negative.
There is no 180 degree thing involved.
I know it's hard for a telecommunications person to grasp the concept.
But you are still, way off base in this "electricians" mind.
I have done all I can do to try to explain it in layman s terms. Including pictures.
TG Twinkie is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why no 50 amp service? 92landyacht Land Yacht/Legacy Motorhomes 25 07-14-2013 05:49 PM
Yay! 50 amp Service upgrade - Done yve79 Batteries, Univolts, Converters & Inverters 34 10-25-2012 07:23 PM
2008 Airstream Classic 31! 50 Amp Service, 2 AC Units! eBay Watch Airstreams on eBay 0 08-30-2011 08:20 PM
3 Amp Availability gaylejoe WBCCI Forum 27 08-06-2011 03:38 PM
Question on using 50 amp sevice RLS Electrical - Systems, Generators, Batteries & Solar 16 02-04-2011 01:14 PM