Old 07-26-2011, 11:24 AM   #1
Rivet Master
 
Trex's Avatar

 
1981 20' International
Shasta Lake City , California
Join Date: Sep 2010
Posts: 1,113
Blog Entries: 7
30 amp/120v Wiring question...

Last nite I moved Rita to do some repairs on the leveling jacks.... This is when I noticed some burning within my new extention cord on the female plug, (it has a clear body, so you can see the wire conections inside). This is for the 30 amp/120v main plug... used to connect shore power.

Also, there is a GFI box, that I think is an add-on to the wiring system. Looking at Barts comments on another thread, I think I have a loose connection and/or corosion at the plug-in location between the GFI and the extention cord that I purchased when I got Rita.

I've been unplugging at the other end so I didn't notice this new problem before.

My questions are; 1. Should I leave the GFI in place, or remove from system? 2. Rewire system and remove the male/female plugs in front of the GFI, (wire the extension cord direct)? Hire an RV tech to look at my wiring system? 3. Purchase new male/female plugs, (so I can remove the 30 amp extension cord section)... in-front of the GFI?

Or sale Rita....and take the money and run? (just kidding)

Three pics of the GFI box and the male/female plugs.....

Click image for larger version

Name:	DSC02178.jpg
Views:	207
Size:	385.4 KB
ID:	136022Click image for larger version

Name:	DSC02179.jpg
Views:	205
Size:	227.5 KB
ID:	136023

Click image for larger version

Name:	DSC02180.jpg
Views:	162
Size:	191.1 KB
ID:	136024
__________________
"Sometimes you eat the bear, and sometimes, well, he eats you." -the Stranger-

Come and see me at: https://www.airforums.com/forums/f185...-71804-60.html
Trex "Airstream Nomad"
Trex is offline   Reply With Quote
Old 07-26-2011, 11:33 AM   #2
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,455
Images: 7
What gage wire and how long is the extension cord ?

When you unplug from the GFI what does the prongs look like?

From your description it sounds like a poor fit between the GFI and the extension cord causing pitting and corrosion. If so I would replace the male side of the GFI and the female side of the extension cord.
__________________
Garry
garry is offline   Reply With Quote
Old 07-26-2011, 12:25 PM   #3
Rivet Master
 
Trex's Avatar

 
1981 20' International
Shasta Lake City , California
Join Date: Sep 2010
Posts: 1,113
Blog Entries: 7
Quote:
Originally Posted by garry View Post
What gage wire and how long is the extension cord ?

When you unplug from the GFI what does the prongs look like?

From your description it sounds like a poor fit between the GFI and the extension cord causing pitting and corrosion. If so I would replace the male side of the GFI and the female side of the extension cord.
Not sure on the gage of the extension cord....But it's made for RV use... rated at 30 amp, and purchased from Walmart, (15 footer). And there is corrosion on the male plug, in-front of the GFI. And when you plug the male and female together, there is an electrical spark on the one prong that has the most corrosion.
__________________
"Sometimes you eat the bear, and sometimes, well, he eats you." -the Stranger-

Come and see me at: https://www.airforums.com/forums/f185...-71804-60.html
Trex "Airstream Nomad"
Trex is offline   Reply With Quote
Old 07-26-2011, 01:30 PM   #4
banjobill
 
wmarsha's Avatar
 
2000 30' Limited
battle ground, , Washington
Join Date: Jun 2009
Posts: 516
one piece at a time

if the melting/burning is in the clear end of the extension cord, that means the current being passed by the cord is too much for its contacts. So, either a bigger cord (wire gauge) or less current draw is required. Whenever an extension cord is added to a circuit, it becomes "wounded" to some degree. a fifteen foot cord aint much wire to add to a circuit, but if it is marginal for 30 amps, it will (and apparently has) become a fusible link. Eliminate the ex. cord if possible. I think the GFI box is also a TVSS unit (transient voltage and surge supressor) which means it isn't absolutely required for the circuit to work correctly. So eliminating it will not hurt your experiment. It should draw a small amount of current, but not much. Check your other connections for tell-tale signs of over current-dark, oxidized prongs on the male ends; loose sloppy female ends. if you are unsure of the age of your electrical connectors, then you may wish to replace them-it will be good insurance. run your hand along the length of your shoreline and check for obvious cuts, but also bulges inside the insulation-a sign of a possible kinking of the cable and possible conductor damage. Just check the integrity of one section of your connections at a time until you find what is causing the problem. Now remember, running the air conditioning and a microwave and a heating element (h2o or hair dryer or coffee pot, etc) all at once can easily exceed 30 amps. the EER (easy electrical 'rithmetic) for converting watts to amps is: VA=watts. watts divided by volts will give an approximate amp value; add 'em up and see where you are at. good luck ol' bill
wmarsha is offline   Reply With Quote
Old 07-26-2011, 03:16 PM   #5
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Rex

The GFI box was added later and is not a necessary or customary wiring practice. It should be removed.

On your trailer the original wiring would have involved a permanently attached shore power cord approximately 25' long. That is what you should put in place now unless you plan to install a Marinco inlet instead.
Jammer is offline   Reply With Quote
Old 07-26-2011, 03:29 PM   #6
4 Rivet Member
 
1972 25' Tradewind
Madison , Wisconsin
Join Date: Apr 2005
Posts: 396
plug

If you have a meter, you may want to check the resistance on that prong that sparked. could be a short in the plug itself. It is also possible that a single failure can cause other failures.

Another thought , not the specific problems of shorting, but this possibly could contribute to troubleshooting the problem...is the circuit you are plugged into also on a GFI, is it a 30 amp? If two GFI's are set somewhat sensitive, it could be a minor problem and make diagnosis a bit of a pain.
Smokin Camel is offline   Reply With Quote
Old 07-26-2011, 04:04 PM   #7
Rivet Master
 
Trex's Avatar

 
1981 20' International
Shasta Lake City , California
Join Date: Sep 2010
Posts: 1,113
Blog Entries: 7
Quote:
Originally Posted by Smokin Camel View Post
If you have a meter, you may want to check the resistance on that prong that sparked. could be a short in the plug itself. It is also possible that a single failure can cause other failures.

Another thought , not the specific problems of shorting, but this possibly could contribute to troubleshooting the problem...is the circuit you are plugged into also on a GFI, is it a 30 amp? If two GFI's are set somewhat sensitive, it could be a minor problem and make diagnosis a bit of a pain.
There is a GFI in the Pool/pump room and that is where the 30 amp 125v comes from.... Power going to the Pool room is 220v, and the line going to the shorepower box, (next to the trailer), from the pool room is 10 gage wire, 30 amp/125v.

The extension cord that I am taking about, (which has the burn marks on the female side of the plug), is my shoreline power cord from the trailer to the 30 amp plug-in box next to the trailer. So there is no other extension cords attached to my system here in the backyard.

I'm thinking about removing the male & female plugs and wire direct to the GFI coming out of the back of the trailer....that way, it will be more water proof than the current setup. I keep thinking there must be a reason the PO installed that GFI inline. I may have more of an eletrical problem than just a bad connection between the 30 amp cord from walmart and the male plug, in front of the inline GFI.

I was going to post some photos, but my camera battery just died...so I'll post once the battery is charged.
__________________
"Sometimes you eat the bear, and sometimes, well, he eats you." -the Stranger-

Come and see me at: https://www.airforums.com/forums/f185...-71804-60.html
Trex "Airstream Nomad"
Trex is offline   Reply With Quote
Old 07-26-2011, 04:11 PM   #8
Rivet Master
 
1988 25' Excella
1987 32' Excella
Knoxville , Tennessee
Join Date: Oct 2010
Posts: 5,119
Blog Entries: 1
for what it is worth, I always get a spark when I plug my trailer in. The power converter draws quite a bit of power on startup.
Bill M. is offline   Reply With Quote
Old 07-26-2011, 05:59 PM   #9
Rivet Master
 
Trex's Avatar

 
1981 20' International
Shasta Lake City , California
Join Date: Sep 2010
Posts: 1,113
Blog Entries: 7
Quote:
Originally Posted by wmarsha View Post
if the melting/burning is in the clear end of the extension cord, that means the current being passed by the cord is too much for its contacts. So, either a bigger cord (wire gauge) or less current draw is required. Whenever an extension cord is added to a circuit, it becomes "wounded" to some degree. a fifteen foot cord aint much wire to add to a circuit, but if it is marginal for 30 amps, it will (and apparently has) become a fusible link. Eliminate the ex. cord if possible. I think the GFI box is also a TVSS unit (transient voltage and surge supressor) which means it isn't absolutely required for the circuit to work correctly. So eliminating it will not hurt your experiment. It should draw a small amount of current, but not much. Check your other connections for tell-tale signs of over current-dark, oxidized prongs on the male ends; loose sloppy female ends. if you are unsure of the age of your electrical connectors, then you may wish to replace them-it will be good insurance. run your hand along the length of your shoreline and check for obvious cuts, but also bulges inside the insulation-a sign of a possible kinking of the cable and possible conductor damage. Just check the integrity of one section of your connections at a time until you find what is causing the problem. Now remember, running the air conditioning and a microwave and a heating element (h2o or hair dryer or coffee pot, etc) all at once can easily exceed 30 amps. the EER (easy electrical 'rithmetic) for converting watts to amps is: VA=watts. watts divided by volts will give an approximate amp value; add 'em up and see where you are at. good luck ol' bill
Thank-you so much, for the feedback/information... The extension cord that I'm tak'in about is the main shorepower-cord, I don't have any other extension cords connected. The GFI add-on is rated at 30amp, 120v and it says that it is for RV's. Looks like they, (the PO), cut the original shoreline and put this GFI in-place and a one foot line, with a male plug. So that is the reason for the use of the 30 amp extension cord. Here's more pics of the issue.

1st Pic shows the burn mark inside the female plug-head.
2nd pic shows 30 amp shorepower box next to trailer.
3rd pic is location of main power...pool room/bathroom.
4th pic is main power box in pool room.


Click image for larger version

Name:	DSC02183.jpg
Views:	166
Size:	237.0 KB
ID:	136056Click image for larger version

Name:	DSC02185.jpg
Views:	177
Size:	190.1 KB
ID:	136057

Click image for larger version

Name:	DSC02186.jpg
Views:	154
Size:	271.9 KB
ID:	136058Click image for larger version

Name:	DSC02187.jpg
Views:	151
Size:	182.4 KB
ID:	136059
__________________
"Sometimes you eat the bear, and sometimes, well, he eats you." -the Stranger-

Come and see me at: https://www.airforums.com/forums/f185...-71804-60.html
Trex "Airstream Nomad"
Trex is offline   Reply With Quote
Old 07-26-2011, 06:36 PM   #10
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
if the main feed for the trailer is already on a gfci the box on the trailer is redundant. get a gfci tester and verify that it works.

the burnt contact ends need to be replaced.

reconnect with the new end on the power cord, put a heavy load on the cord and check the voltage, if the ends heat up and report back.

each connection increases the possibility of corrosion and higher resistance.

have you had any brown outs (low voltage) while using this setup?
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 07-26-2011, 06:54 PM   #11
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Rex my Man,
I highly recommend you cut that add on stuff off and throw it out with Wednesday's trash. Get yourself a new 25' RV cord and have Porno Bob, Wino Wayne, or whichever friend of yours is an electrician to properly wire it into Rita's AC service box. The original version from 1972 was a good design.
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 07-26-2011, 07:41 PM   #12
Rivet Master
 
jdalrymple's Avatar
 
2009 27' FB Flying Cloud
1982 31' International
1991 35' Airstream 350
Jay , Oklahoma
Join Date: Oct 2006
Posts: 1,706
I'll jump in too. The more connections in any circuit, the more resistance. Each plug, male or female, adds a point that is not pure copper wire. It's like having to add 10 psi to your friction loss calculation for each appliance in the line.

I would be completely comfortable with no GFI in the incoming line. My newer trailer has the marinco twist lock on the side of the trailer with the removable cord. I always thought that would be handy. But, I see about a 3-4 volt drop inside the trailer, even when I measure 120 volts at the outlet I'm plugged into. I agree with TOP, the most bestus would be a 20-25' 10 gauge SJ cord wired directly into the main breaker.
__________________
Jeff & Cindy
'09 27FB Flying Cloud;'82 31 International
'91 350 LE MH; '21 Interstate 24GT


jdalrymple is offline   Reply With Quote
Old 07-26-2011, 07:44 PM   #13
Rivet Master
 
Trex's Avatar

 
1981 20' International
Shasta Lake City , California
Join Date: Sep 2010
Posts: 1,113
Blog Entries: 7
Quote:
Originally Posted by richinny View Post
if the main feed for the trailer is already on a gfci the box on the trailer is redundant. get a gfci tester and verify that it works.

the burnt contact ends need to be replaced.

reconnect with the new end on the power cord, put a heavy load on the cord and check the voltage, if the ends heat up and report back.

each connection increases the possibility of corrosion and higher resistance.

have you had any brown outs (low voltage) while using this setup?
Thank-you for your feedback.... I'll give it a go in the morning...remove the add-on GFI and wire a new shoreline cord to Rita.
__________________
"Sometimes you eat the bear, and sometimes, well, he eats you." -the Stranger-

Come and see me at: https://www.airforums.com/forums/f185...-71804-60.html
Trex "Airstream Nomad"
Trex is offline   Reply With Quote
Old 07-26-2011, 07:47 PM   #14
Rivet Master
 
Trex's Avatar

 
1981 20' International
Shasta Lake City , California
Join Date: Sep 2010
Posts: 1,113
Blog Entries: 7
Quote:
Originally Posted by jdalrymple View Post
I'll jump in too. The more connections in any circuit, the more resistance. Each plug, male or female, adds a point that is not pure copper wire. It's like having to add 10 psi to your friction loss calculation for each appliance in the line.

I would be completely comfortable with no GFI in the incoming line. My newer trailer has the marinco twist lock on the side of the trailer with the removable cord. I always thought that would be handy. But, I see about a 3-4 volt drop inside the trailer, even when I measure 120 volts at the outlet I'm plugged into. I agree with TOP, the most bestus would be a 20-25' 10 gauge SJ cord wired directly into the main breaker.

10-4...thanks for the feed back Mr. jda & TOP. I hear what you're say'in.
__________________
"Sometimes you eat the bear, and sometimes, well, he eats you." -the Stranger-

Come and see me at: https://www.airforums.com/forums/f185...-71804-60.html
Trex "Airstream Nomad"
Trex is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
1991 Excella 1000 - New Radio need wiring help! jbbaldwin Audio, Video & TV 4 11-28-2022 07:33 AM
A/C and wiring question Hoosierdaddy Furnaces, Heaters, Fireplaces & Air Conditioning 20 08-20-2011 06:15 AM
Steel / Aluminum wheel question polarlyse Wheels, Hubs & Bearings 12 05-29-2011 07:49 PM
Blasphemous question woytovich General Repair Forum 15 04-09-2011 08:36 AM
nagging wiring question DanielB 1973-1974 Excella 500 4 03-19-2011 06:00 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 06:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.