Open Neutral voltage at campground

We are staying overnight at a campground outside of DC now on our way north to get air conditioning since it is 100 degrees.

We have a Camco surge protector and circuit analyzer and it gave me an “open neutral” indication - first error I have seen. I had campground look at it and it is showing about 118v hot and 6v or a little more on neutral. Campground says that is some stray current and no big deal. That is with camper unplugged. Inside camper when plugged in, at outlet, I measure about 115v/8v. Are we safe to use this electricity? I did run A/C a bit to cool trailer off but unplugged it since we were going to be gone for a couple hours.

We are a little over a week in to a year long trip full-timing, so I don’t want to mess up this early in.

Thanks!
Jared
www.astreamcometrue.com
@astreamcometrue
SabaRocks is offline   Reply With Quote
Old 07-20-2019, 02:29 PM   #2
Overkill Specialist
Commercial Member
 
GMFL's Avatar
 
2020 30’ Globetrotter
2014 23' International
Dadeville , Alabama
Join Date: Oct 2015
Posts: 4,516
Images: 4
Blog Entries: 52
Some neutral-to-ground voltage should be present under load conditions, typically 2V or less. This is due to AC current variations. Some electronic devices “bleed” voltage back a noise and that could come from another camp site and be causing your problem.
There are a lot of connections and things running in a camp ground.
__________________
Instagram @Airstream_Nuts_And_Bolts
DoItYourselfRV Articles
Certified Victron Installer
GMFL is offline   Reply With Quote
Old 07-20-2019, 04:48 PM   #3
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,673
Under heavy load conditions, the current in the neutral will raise its voltage with respect to the ground wire since the ground should be carrying no current. If you are a long way from the main power panel where the ground and neutral are bonded together, this can happen. The bad news is that the heavy load will also be lowering the voltage of the hot line. The hot line is going down, the neutral is going up - can lead to measured low voltage hot-neutral at your site. This can cause excess current, particularly in the air conditioner.

Measure the voltage from the hot to neutral. As long as this is at or above 115 volts under load you should be OK. I have a plug-in voltmeter that I leave in the outlet ear the door. Every time I come in I can look at it and check the voltage level.


Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 07-20-2019, 06:53 PM   #4
2 Rivet Member
 
2015 27' Flying Cloud
Currently traveling , Varies
Join Date: May 2016
Posts: 40
Images: 1
Thanks, y’all. I feel better and also learned something today!
SabaRocks is offline   Reply With Quote
Old 07-21-2019, 09:36 AM   #5
4 Rivet Member
 
2019 25' Flying Cloud
Greeneville , Tennessee
Join Date: Jul 2008
Posts: 436
They need a better ground. Period. Back in the day I worked as a telecom engineer. We had a site in eastern NC that would go goofy in dry weather. It was a digital switch. In order to settle it down, someone would have to take a garden hose and soak the dead man.
jimfa440 is offline   Reply With Quote
Old 07-21-2019, 09:38 AM   #6
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,744
Hi

Assuming you are measuring both voltages to ground, phase is going to matter. 8V on the neutral can either add to or subtract from what's on the hot lead. That's why you *must* measure from hot to neutral. Otherwise you really have no idea what's what with a simple multimeter.

The real question is what happens when the A/C turns on. One would *guess* that the campground electric system is loaded at or past its capacity. You might see a pretty significant "droop" in the voltage. That's not going to make your compressor happy. It may trip out the surge protector with a "low voltage" alarm. If the neutral has an issue, it could. spike an "open neutral" as well.

Lots of variables .....

Bob
uncle_bob is offline   Reply With Quote
Old 07-21-2019, 10:02 AM   #7
Rivet Master
 
waninae39's Avatar
 
2022 25' Flying Cloud
NCR , Ontario
Join Date: Feb 2017
Posts: 3,108
yikes disconnect

it looks like a ground loop

these are more common on long legs

it can be deadly dangerous.

move to a better campground.
NOT SAFE
waninae39 is offline   Reply With Quote
Old 07-21-2019, 11:11 AM   #8
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,673
If the load is perfectly balanced (it seldom is) between the two legs of a 120/240 circuit, the neutral current will be close to zero. Current in the neutral from an unbalanced load set will result in voltage drop on the neutral. As uncle bob says, if the 120V leg you are on is the one that is loaded more heavily the voltage on the neutral will subtract from the hot. If the other leg is loaded more heavily it will add. There should never be any current on the ground line and therefore no voltage drop so any current on the neutral will result in voltage with respect to ground.



In my opinion, 6V neutral to ground is not unsafe.


Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 07-21-2019, 11:45 AM   #9
Rivet Master

 
2015 27' Flying Cloud
Portland , Oregon
Join Date: Nov 2009
Posts: 685
Send a message via AIM to hhendrix Send a message via Yahoo to hhendrix
I've run into this before too. One trick that might help if the water line is metal is to use one leg of battery jumper cable. Attach one end to the water line and the to the metal box of the post.
__________________
The ability to follow instructions is highly underrated.
Always be wary of stupid people in large numbers.
hhendrix is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Converter outlet in battery compartment showing open neutral Talollie Electrical - Systems, Generators, Batteries & Solar 3 04-04-2017 03:36 PM
How do y'all check voltage at the campground pedestal? m.hony Electrical - Systems, Generators, Batteries & Solar 36 09-07-2016 04:23 PM
30 amp "open neutral" adonh Electrical - Systems, Generators, Batteries & Solar 15 11-18-2013 01:47 PM
Open Neutral in a Motorhome.. Keyair Electrical - Systems, Generators, Batteries & Solar 16 12-17-2012 10:52 AM
Open neutral diagnosis? markdoane Lights - Interior & Exterior 3 08-07-2009 07:33 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.