SmartPlug, and EMS surge protector

Quote:
Originally Posted by rmkrum View Post
Molded plugs and sockets tend to be a bit marginal at best. Your new ones, properly installed, are more likely to survive better. The fact that the generator end isn’t toasted points real strong to just the molded connectors that melted being at fault.
There is a different system for plugs and sockets that was on display at the 2018 International. It is called SmartPlug. https://smartplug.com/rv/
They claim their plug system has 20x more electrical contact than the old twist type connector. I have two 30amp external power supply plugs on my trailer. I replaced one of them with the SmartPlug setup, and I have been happy with it. It is easier to plug in for my wife and me, and since it eliminates the securing ring, there is no risk of cross threading. The down side is how expensive it is, but I reason that the extra theoretical margin of safety justifies my decision. I travel with a standard cable/plug for the second outlet on the trailer just in case. My standard backup power cord was used at the Blackout rally (total eclipse rally in Oregon 2017), when someone had an issue with their power cord, but otherwise I have not used the standard cord since I installed the SmartPlug.
Since your connection was between the power cord, and an extension cord, you would have to do some planning on how to set it up. If you plan on using the generator often enough, I would just buy a really long power cord, so you would not have the extra connection. I think anytime you can avoid an extra connection, there is less chance for a problem.
I started out with an external EMS surge protector, but that results in an additional external connection (between the power cable, and the EMS unit). With a hardwired internal EMS surge protector, you get a much more reliable, weather protected connection. You also get to see the real time amp usage on the display. It is real easy to exceed 30 amps with the AC/heatpump, water heater, and microwave. When I am getting close to 30 amps, I quickly turn something off.
John
3DRad is offline   Reply With Quote
Old 03-31-2019, 02:11 PM   #22
2 Rivet Member
 
Currently Looking...
Clearlake , California
Join Date: Jan 2019
Posts: 77
Quote:
Originally Posted by rmkrum View Post
Possibly the blankets and other stuff overheated the generator and reduced the output voltage, which led to excess current. However, the damage you showed is most likely to be from an overheated, bad connection. I’d say time to replace the toasted parts and drive on. I’d also have a few rather strong words with the bozo that darn near fried your generator by covering it up. His actions could have caused a bad fire.

Also, just because a breaker is marked 30 amps does not mean it will open at exactly 30 amps. They are rated at 30, but it may take a lot more to trip it. They have manufacturing tolerances and are not that precise. The extension cord and plug overheated, yes. But didn’t draw enough current to open the breaker. That to me says the connection was marginal. Replace with a heavy duty set is your best bet. If you can get the bozo to pay for the toasted parts, that would be nicer, but highly unlikely IMHO.

Molded plugs and sockets tend to be a bit marginal at best. Your new ones, properly installed, are more likely to survive better. The fact that the generator end isn’t toasted points real strong to just the molded connectors that melted being at fault. Also says your generator is rather well built...and any third party that messes with your generator needs to be stopped. I wouldn’t put up with that at all.
Right as rain about breakers not opening when you would expect. When I redid the wiring in my house there was an old Western Electric breaker panel in the hall closet. Did a little research and discovered that they had the nickname "Firestarters" because after a number of years and a few trips, the breakers would just not trip out. The more times a breaker has tripped the more likely it will malfunction.
napabill is offline   Reply With Quote
Old 03-31-2019, 08:58 PM   #23
1 Rivet Member
 
Currently Looking...
Currently Looking...
Centennial , Colorado
Join Date: Feb 2014
Posts: 5
My take: your “4750” generator is actually a “3800 running watt” generator (on gasoline)... drops down to 3420 running watts on propane... is this your genny?

https://www.championpowerequipment.c...uel-generator/

You didn’t say how big your A/C is or how many any what kind of lights you were running... only that it “worked last time”... what was the temp like in the two shows? A/C working harder? More lights?

A previous poster stated bad voltage wouldn’t cause that melting... I’m no electrician so I’ll bow to his knowledge... but running your generator on gasoline might give you the extra oomph you need...
S854 is offline   Reply With Quote
Old 04-01-2019, 03:17 PM   #24
2 Rivet Member
 
1977 21' Globetrotter
Davis , California
Join Date: Aug 2009
Posts: 33
Probably due to added insulation, high draw, resistance

Fundamentally, you were drawing very high, i.e. too much amperage through the plugs. If not seated completely, high current + resistance = added heat, and even more resistance, heating and melting, . The blanket might have allowed even more heat to accumulate, but that probably wasn't the main issue.

Long, small gauge extension cords and high draw = increased resistance, heat and possible damage to plugs. The blanket might have allowed even more heat to accumulate, but that probably wasn't the main issue.

So, add up wattage of appliances/lights, divide by voltage to get current. Check that vs. output of generator, rating of plugs, and esp, use beefy extension cords to minimize voltage drop and increased current (i.e. heat).
flyflinger is offline   Reply With Quote
Old 04-01-2019, 06:03 PM   #25
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
Just an FYI, if your neighbor felt compelled to attempt to muffle the sound of your contractor generator in a trade show setting, you probably should look into finding a generator that is less than the 68 decibels of your current unit. If not, your next "neighbor" might not be inclined to merely try to make it quiet enough that they can talk to their customers without shouting.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 04-01-2019, 09:31 PM   #26
2 Rivet Member
 
2018 Basecamp
Fairview , TX
Join Date: May 2018
Posts: 34
You threw a blanket & boxes over an AIR COOLED generator? Really? You are lucky if the generator still even starts and you are quite fortunate that the blanket and boxes did not ignite.
Airkeeper is offline   Reply With Quote
Old 04-02-2019, 12:20 AM   #27
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,801
Lot of threads about the difference between "contractor" generators and quieter RV ones.

Many rallys and events ban noisy generators or restrict their use to the edges of the event. Yours doesnt look to be super noisy, but is much louder than Honda's in the EU series. Being a.good neighbor in a crowd? Priceless.
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 04-02-2019, 05:45 AM   #28
Rivet Master
 
r carl's Avatar
 
Vintage Kin Owner
Lin , Ne
Join Date: Dec 2009
Posts: 2,430
Quote:
Originally Posted by overlander63 View Post
You had a bad connection at that plug.
Yes, wire to blade connection needed to be tightened with a screwdriver.
__________________
The higher your expectations the fewer your options.
r carl is offline   Reply With Quote
Old 04-02-2019, 07:43 AM   #29
1 Rivet Member
 
1976 31' Sovereign
Karnes City , Texas
Join Date: Jul 2018
Posts: 19
Responding to everyone at once to clarify a few things.
  1. The extension I used is the same gauge as the trailer plug and fairly new. Rated at 30 Amp, 3750 Watt, 10-Gauge.
  2. The connection between them was tight and not near the generator. So tight that the plastic melted together without a gap.
  3. The temperature outside was in the 80's but enough to warrant turning on the A/C. The generator was in complete shade.
  4. The generator was behind our trailer, between the trailer and a wooden fence, and I had a partition at the rear of the trailer to block additional noise near our neighbor.
  5. The event owner knew we would be using our generator ahead of time and still positioned us near other vendors. A food truck with a louder generator was near the street and away from other vendors. Poor planning on the owner's part.
  6. The noise near the lady complaining was minimal. She could whisper and her customer could hear her.
  7. I didn't put a blanket or boxes over the generator. The husband of the woman running the event did. Apparently, he's an idiot.
  8. We were running an LED light string and a Coleman Mach 1 A/C, which would use around 300w (lights) + 1300w (A/C). So I don't think wattage was an issue, since the total wattage draw would be half the generator output on propane (3420w).
Kevio is offline   Reply With Quote
Old 04-02-2019, 09:53 AM   #30
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 9,180
Melted Plugs Due to Hot Generator?

So, from that, it sounds like something in the plug, possibly a bad crimp connection in the socket or blade might have been the cause. It’s real hard to pin it down without sawing the toasted cable ends apart to examine them.

I’m just glad your helpful ‘idiot’ didn’t cause a fire in the generator or worse that close to your trailer.

I believe you replaced the cable ends with heavier duty parts. Probably the best thing is to inspect for any overheated connections next time you are running close to full load.

Maybe get one of those infrared thermometers. They are handy for checking tire and running gear temps as well. I use mine to checking temps when I’m cooking as well. True multi-tasked tool.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot hot hot aluminum! 58cruzer General Repair Forum 23 06-24-2013 01:08 AM
AC just quit working and it's Hot Hot Hot!!! SaabLover Furnaces, Heaters, Fireplaces & Air Conditioning 9 07-27-2010 09:03 PM
How Can it Be? 2 Plugs work, 2 Plugs dont Aluminumb Electrical - Systems, Generators, Batteries & Solar 10 07-27-2009 07:44 PM
Alternator wire melted airstream963 Mechanics Corner - Engines, Transmission & More... 5 05-07-2005 06:46 PM
Melted lens? Rickj Electrical - Systems, Generators, Batteries & Solar 3 01-02-2004 11:17 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:51 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.