Originally Posted by
92landyacht
In theory, adding additional circuits seems like it would be an easy job. Just add circuits to the existing box, beef up the transfer switches…
Seems to me like the hardest part is to fish the new wires. From what I can tell, they didn't provide any conduits to fish wires through. Just bundles of wires tie wrapped to frame members. Any additional circuits would require disassembly of the ceiling panles or runs under the floor of the unit. Please correct me if I'm wrong.
Anyone know where the transfer switches are on a 92 36' LY?
Unfortunately, you don't just 'add a few circuits' and 'beef up the transfer switch'.
To do it right (which is the ONLY WAY), you need
to replace the
30 amp transfer switch with a 50 amp version, replace your
30 amp 10/3AWG shore cord with a 50 amp 6/4 AWG unit, replace your
30 amp single line circuit breaker box with a 50 amp dual line breaker box and then add the extra circuits (like your #2 roof A/C) and split and balance the circuits so the load is even across both incoming legs in the breaker box.
Sounds simple, doesn't it?
Then you need
to be sure that your generator has the capability
to be re-wired for dual 120VAC circuits and run the 6/4 AWG wire from the genny
to the new transfer switch.
Still with me?
If you're not
completely familiar with 120VAC and 240VAC wiring, this is NOT a DIY job.
__________________
Lew Farber...
RVIA Certified Master Tech...ABYC Certified Master Marine Electrician
MASTER TECH ENERGY SYSTEMS, INC.
AM SOLAR ...
MAGNUM…VICTRON ENERGY...LITHIUM & LIFELINE BATTERIES…MARINE REFRIGERATION
So the short answer is it can be done with the right knowledge. Or you can take a chance on being a pile of ashes....