Old 02-01-2006, 10:38 PM   #1
New Member
 
Currently Looking...
Currently Looking...
Homer , Alaska
Join Date: Jan 2006
Posts: 4
duo-therm not working

I have an old dura-therm propane furnace , probably an early seventies or late sixties, no electricity or blower or circut board . It worked fine untill a few days ago. It seems like a real simple unit and it is driving me nutz. The pilot lights and stays on , when I turn the knob to on , it flares on, runs for a few seconds and them groans a bit and goes out, a couple of times it would stay on for a couple of hours if I only turned the knob aprox. half way to on, now it doesnt do that. it gets gas and then seems to run out. Ive cleaned the pilot nozzell, adjusted the pilot, removed a few kinks from the gas line, installed a new thermalcouple and made sure it is in the pilot flame, Ive disassembled it and cleaned out all the dead rodents and bugs, Ive made sure the propane tank is full, Ive checked to be sure it is almost level. My magic chef oven , right next to it works fine, Ive shut that off to possible increase the preasure to the furnace with no success. Im in alaska , its 4 degress outside, Im a week from any parts i may need and two weeks from a new furnace. My question is , does anyone know of any quick fixes, fixes , or bandaids that may make this work? Sorry about the wordyness , Bob
toolman5252 is offline   Reply With Quote
Old 02-02-2006, 06:17 AM   #2
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Toolman,

I'm not familiar with your unit, but these are some basic tests. Even though you have a new thermocouple, it might not be working. If you have a VOM, you can chack it by heating it with a lighter and see what millivolt reading you get from it. Also, it might be a faulty gas valve in that it is not staying open when it senses the signal from the t/couple. It that case, you would need a new gas valve.

Are you holding the pilot on long enough to completely heat the t/couple so the gas alve knows that it is 'on' ?

Hope this helps.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-02-2006, 06:56 PM   #3
New Member
 
Currently Looking...
Currently Looking...
Homer , Alaska
Join Date: Jan 2006
Posts: 4
Thankyou for replying , the pilot will stay on all day long as long as I dont turn the knob to on . Something else i did today, that made an improvement, was to take it apart and reseal all the gaskets and remove the small screen from the gas inlet line, and take the gas valve apart and make sure there was no obstructions Now it will light and stay on for aprox. 10 minutes , then sputter , groan and go out. It will relight instantly, go another 10 or so minutes and then go out again with the same noises. I've watched it and when it starts groaning , it apears to run out of gas, but I can put a lighter on the light port and it will fire back up right away, go another ten minutes and then go out again. Was any of that any help or did I just make it work a little better by sealing the gaskets ? Thanks again for your reply , bob
toolman5252 is offline   Reply With Quote
Old 02-03-2006, 06:06 AM   #4
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Bob,

Have you checked your gas feed line leading up to the orifice and the orifice itself for any obstructions? Just last week I had 2 fairly new furnaces that were either NO/OP or doing a similar pattern as yours, and after dis-assembly, found insects in the gas line and burner orifice.

Cleaning the orifice is a good idea anyway. Be sure to use only compressed air, carb cleaner, etc to clean it. Never but anything into the orifice opening as this is a precision drilled hole and any ateration will negatively effect the unit. Maybe a tooth pick, but nothing metal.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 02-03-2006, 09:34 AM   #5
4 Rivet Member
 
WayWard Wind's Avatar
 
2004 25' Safari
Join Date: Jan 2003
Posts: 424
Sounds to me that it's either has a hole or small crack, in the venting system & or gaskets or the vent is partialy obstructed, causing the main burner flame to "float" which causes the pilot flame to go out & then the safety shuts down.
Best,
__________________
Home of the Wayward Wind

Bogfrog & Mr. Turbo

If in life you stumble, make it part of the dance
WayWard Wind is offline   Reply With Quote
Old 02-03-2006, 02:23 PM   #6
3 Rivet Member
 
Join Date: Oct 2002
Posts: 186
Images: 4
gas regulator

Is it possible that the propane gas regulator at the tank is malfunctioning. Sounds somewhat familiar as I had a problem with my furnace until I had the regulator replaced. Turned out to be a defective pressure regulator on a relatively new unit.
rtaylor537 is offline   Reply With Quote
Old 02-03-2006, 11:24 PM   #7
New Member
 
Currently Looking...
Currently Looking...
Homer , Alaska
Join Date: Jan 2006
Posts: 4
many thanks for all the replies, I will check and try all of them and post back with the results, respectfully , bob
toolman5252 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Brakes working correctly? Dbraw Electrical - Systems, Generators, Batteries & Solar 8 02-27-2007 07:16 AM
vent fans missing/not working Rog0525 Roof Vents, Skylights & Fans 2 07-02-2002 04:23 PM
Duo Therm Brisk Air JAG Furnaces, Heaters, Fireplaces & Air Conditioning 6 06-06-2002 08:29 PM
Duo Therm Penguin A/C Installation JAG Furnaces, Heaters, Fireplaces & Air Conditioning 1 03-18-2002 10:11 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:33 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.