Strange(?) Electrical Issue. Power my AS trailer off of my AS Interstate

Issues such as this caused be to quit my electrical engineering education and switch to mechanical engineering...

I received delivery of a 1969 AS Sovereign trailer the other day. It is currently sitting on a plot of land without available shore power. It has a 30 AMP voltage center installed (Parallax Power Supply 5300 series power converter) with a standard round 30AMP type plug input.

I can power it with no problem off of a portable generator. I have an adaptor that I use to convert the 30AMP round plug to a standard 15AMP plug. I plug it into the generator and everything works well.

I use the same setup to plug my Airstream Interstate into 15AMP shore power when I'm at home.

Seeing that I don't want to constantly run the generator to power the trailer, I figured that I would try to power it from my Interstate (I have a fair amount of battery storage and a rocking solar system). When I initially plugged the cord into the Interstate outlet, I immediately tripped the Interstate's GFCI outlet. I figured the trailer load was too high, so I shut everything down in the trailer and tried it again. Same result. I thought maybe it was a wiring issue with the trailer, so I just plugged in the 15AMP side with the 30AMP side disconnected. Same thing. The GFCI trips immediately without any load present. Seems like it is wiring issue, however the wire setup works fine when powered by the generator.

Being that it was dark and cold while I was doing this, I just fired up the generator and plugged into it without issue. We left the next day and I didn't get a chance to troubleshoot any further.

The Airstream has a Magnum MMS1012 inverter and runs all of the AC in the Interstate without issue.

My guess is that the problem has to do something with the power cord or 30-15AMP adapter. Something that the generator doesn't mind, but the GFIC is sensitive to.

I head back down this weekend with the Interstate and will trouble shoot some more. In the meantime, anyone have any suggestions?

Thanks,

- Kaylorsan
kaylorsan is offline   Reply With Quote
Old 12-09-2015, 07:11 PM   #2
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
Strange(?) Electrical Issue. Power my AS trailer off of my AS Interstate

My off the cuff guess is that the line and the neutral are crossed in the trailer plug, if your generator neutral is un-bonded, as many are, then the generator wont care, where your interstate, if the neutral is bonded to ground may care.


Brevi tempore!
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 12-09-2015, 07:11 PM   #3
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
GFCI's can drive you crazy with their incompatibility with certain equipment. It only takes .005 amps (5 mA) going where they think it should not to cause them to trip.

Although I hesitate to suggest this, can you plug into a non GFIC outlet and see what happens? I don't know how the Magnum inverter in the Interstate works, is the entire output GFCI protected so that is not an option?

Lewster might have some insight into the issue, he knows Magnum inverters very well. Lets see if he chimes in here.
idroba is offline   Reply With Quote
Old 12-09-2015, 07:14 PM   #4
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
Fwiw, if the line and neutral are swapped in your trailer plug it is a serious hazard when plugged into shore power.


Brevi tempore!
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 12-09-2015, 07:45 PM   #5
Rivet Master
 
Southwestern , Ohio
Join Date: Nov 2006
Posts: 1,671
Quote:
Originally Posted by idroba View Post
GFCI's can drive you crazy with their incompatibility with certain equipment. It only takes .005 amps (5 mA) going where they think it should not to cause them to trip.
What Idroba said. 30 Amp trailer outlets do not contain GFCIs because certain loads may have enough current leakage to ground to trip them. Some common culprits are electric heating elements (refrigerator, water heater), wet connections (outside outlets or inside switches and outlets if the shell is leaking) and converters (RFI filters on the 120 Volt input).

By all means check for proper connection of hot, neutral, and safety ground wires in the trailer, but if they are all OK you will need to start looking for leakage paths. Might try a VOM on high resistance range (with power disconnected from the trailer!) A "megger" (high voltage insulation tester) might come in handy. This kind of problem is often tough to find.
Nuvite-F is offline   Reply With Quote
Old 12-09-2015, 08:07 PM   #6
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Turn off any GFCI breakers in the trailer, and it should work fine.

If you're plugging into one of the Interstate's external outlets on the passenger-side quarter panel, it's a GFCI outlet (being outdoors where it can get wet, it has to be). Having two GFCIs in series typically causes the one further "upstream" to trip, because the same circuitry that allows a GFCI to detect as ground fault reads AS a ground fault when plugged into another GFCI.

We used to see the same thing all the time on construction sites when I was still working for a living; it took us ages to figure out the source of "nuisance trips" like these, but once we learned not to have two GFCIs in series, the problem went away.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2014 Interstate 3500 Electrical Issue Kevin Madiso Electrical - Systems, Generators, Batteries & Solar 11 09-06-2016 08:45 AM
Strange Air Conditioner issue Landrum Furnaces, Heaters, Fireplaces & Air Conditioning 15 06-28-2015 10:53 PM
Strange Water Pump Issue ktgsmokey General Repair Forum 10 06-16-2015 11:04 AM
Are you feeling like Sherlock? Strange ignition issue, need advice scottf3334 Mechanics Corner - Engines, Transmission & More... 15 08-28-2009 08:45 PM
Strange Electrical Problem DaveJ Electrical - Systems, Generators, Batteries & Solar 5 11-11-2003 12:00 PM