Old 06-19-2008, 10:17 PM   #1
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
Get More 110 V amps from generators

Thisis a little nuts, but for a long time I've been agitated about not being able to run the A/C from a 3500 W generator. Why doesn't that work? Well, because all generators that have a 220 capability split the power betwen the two 110 V outlets/circuits. I've seen a few recent generators that have a switch with two positions -- (1) keep the 220, or (2) all power to 110.

You can do this, too, if you're really adventurous. Here's the before (top) and after (bottom) wiring diragram for my generator:

Click image for larger version

Name:	gen mod.jpg
Views:	2879
Size:	609.6 KB
ID:	62611

In order to completely understand what's going on here, the generator has two windings, each providing 110 volts. If they are wired in series and 180 degrees out of phase, you get 220 volts across them and still can have 110 across each winding, with a common neutral. That's the top schematic.

But if you can wire the windings in parallel (and in phase), you lose the 220 capability, but you can now get full power at 110.

Forutnately, my generator neutral wire was easily accessible on top of the wire bundle on the windings. Cutting a bit of the linen and lacquer freed up the wire (be extremely cautious not to nick the insulation on the windings (it's just lacquer) or cut a wire by accident!!!). Cutting one winding away from the neutral and providing a fourth wire from this winding out to the sockets was all that was needed to provide full power at 110V. Here's the business end of the generator with the rotor support frame removed:

Click image for larger version

Name:	IMG_8280 windings-s.jpg
Views:	1656
Size:	226.2 KB
ID:	62612

Here'sthe two windings soldered to the neutral wire. Just cut one of the windings away and attach a fourth lead to the lose winding.

Click image for larger version

Name:	IMG_8280 cut-s.jpg
Views:	592
Size:	88.7 KB
ID:	62613

I retained the separate 110 circuits and wired the existing 220 connector so that you need a pigtail to short the two 110 circuits together.

I'm not sure that retaining the two independent 110 V circuits is of any value, but if the pigtail is not plugged in, the electrical characteristics of the generator are unchanged, except you don't have 220 volts available any longer. The existing circuit breakers still function to independently limit the current in each winding. If you happen to screw up the phasing of the windings, the circuit breakers will tell you right away!

Yay! Now I can run my A/C no problem. I never did use the 220 capability anyway. (took about 3 hours, including missteps...)

Zep
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Old 06-19-2008, 11:00 PM   #2
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Nice job Zep!

Makes perfect sense to me .......really!!!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 06-20-2008, 06:15 AM   #3
4 Rivet Member
 
AirstreamGypsy's Avatar
 
1961 16' Bambi
Mancos , Colorado
Join Date: Jan 2006
Posts: 472
Send a message via Skype™ to AirstreamGypsy
If I remember correctly I did something similar. I do not however remember if my generator had 220 capacity or if it just had it's power split between 2 110 circuits. As per someone's instructions, I wired the two together to get a full 3500w of power on one 110v circuit. Yes, it worked, but it is my unscientific belief that it GREATLY reduced the life of the generator. ie. It conked out... practically blew itself to bits.
__________________
AirstreamGypsy
___________
Charter Member FCU • WBCCI 1818 • CP(Courtesy Parking) • Wi-Fi
My Earthship
AirstreamGypsy is offline   Reply With Quote
Old 06-20-2008, 06:44 AM   #4
4 Rivet Member
 
AirstreamGypsy's Avatar
 
1961 16' Bambi
Mancos , Colorado
Join Date: Jan 2006
Posts: 472
Send a message via Skype™ to AirstreamGypsy
p.s.
Kudos....
I do believe this is different than what I did?

AG
AirstreamGypsy is offline   Reply With Quote
Old 06-20-2008, 07:08 AM   #5
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
Quote:
Originally Posted by AirstreamGypsy View Post
... I wired the two together to get a full 3500w of power on one 110v circuit. Yes, it worked, but it is my unscientific belief that it GREATLY reduced the life of the generator. ie. It conked out... practically blew itself to bits.
No, you can't just wire the two 110 outlets together--that would be like a dead short across both of them. Unless, of course, your generator had split windings already and you could wire the outlets in phase instead of out of phase.

Changing the wiring like I did does not increase the load on the generator, necessarily. The 220 socket was always able to deliver the full 3500 W, and you could always have plugged in two 110V loads that each used 1500 W. Taking all the power to one 110V load is no different as far as the horsepower required from the engine is concerned. It is possible, however, that the advertised capability is 3500 W, but in reality the design is intended to deliver something less on a continuous basis.

BTW, the lower photo in post #1 is a little misleading--each winding has two wires, so you have to cut both of those wires at the arrow.

Zep
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Old 06-20-2008, 08:23 AM   #6
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
I thought I'd better insert a a remark about paralleling generators. Honda can do it because their generators are really DC with a high power inverter. The inverters can be kept in perfect phase by tieing the inverter clocks together, even though the generator RPM and DC power output aren't necessarily matched.

In most generators, however, the frequency of the AC depends directly on generator RPM, which in small generators is not very stable, nor is it locked to 60 hertz. So you can't tie two non-inverter generators together because they would not be in phase and you'd pop circuit breakers, like right now.

In my example above, not only are the windings always in perfect phase, but they are really just one winding with four wires (which can be split into two windings 180 degrees out of phase to get 220V), so the voltage output is also essentially identical. Consequently, paralleling the windings is no big deal, electrically speaking.

Zep
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Old 06-20-2008, 09:37 AM   #7
Rivet Master
 
Aerowood's Avatar
 
1971 21' Globetrotter
Currently Looking...
Currently Looking...
Currently Looking...
Arvada , Colorado
Join Date: May 2006
Posts: 3,530
How about taking two two different size AC gensets plug them into two transformer rectifiers and run the output of them through a single inverter
Aerowood is offline   Reply With Quote
Old 06-20-2008, 09:55 AM   #8
Site Team
 
azflycaster's Avatar

 
2002 25' Safari
Dewey , Arizona
Join Date: Mar 2005
Posts: 15,618
Images: 62
Blog Entries: 1
Quote:
Originally Posted by Aerowood View Post
How about taking two two different size AC gensets plug them into two transformer rectifiers and run the output of them through a single inverter
I think you will need one of these to do that.



I will post the details yesterday...
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is offline   Reply With Quote
Old 06-20-2008, 02:09 PM   #9
4 Rivet Member
 
AirstreamGypsy's Avatar
 
1961 16' Bambi
Mancos , Colorado
Join Date: Jan 2006
Posts: 472
Send a message via Skype™ to AirstreamGypsy
Smile Why does everything have to be a science project?

Quote:
Originally Posted by Zeppelinium View Post
I thought I'd better insert a a remark about paralleling generators. Honda can do it because their generators are really DC with a high power inverter. The inverters can be kept in perfect phase by tieing the inverter clocks together, even though the generator RPM and DC power output aren't necessarily matched.

In most generators, however, the frequency of the AC depends directly on generator RPM, which in small generators is not very stable, nor is it locked to 60 hertz. So you can't tie two non-inverter generators together because they would not be in phase and you'd pop circuit breakers, like right now.

In my example above, not only are the windings always in perfect phase, but they are really just one winding with four wires (which can be split into two windings 180 degrees out of phase to get 220V), so the voltage output is also essentially identical. Consequently, paralleling the windings is no big deal, electrically speaking.

Zep
It was you that said this, yes? My head just spun around as much as the windings.....
__________________
AirstreamGypsy
___________
Charter Member FCU • WBCCI 1818 • CP(Courtesy Parking) • Wi-Fi
My Earthship
AirstreamGypsy is offline   Reply With Quote
Old 06-20-2008, 03:21 PM   #10
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
good one zep, now you know how we stack coils in transformers to make 120/208 three phase service at the power company!

looking for work? i know a couple of engineers here that you could outsmart!

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 06-20-2008, 04:21 PM   #11
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
Quote:
Originally Posted by john hd View Post
good one zep, now you know how we stack coils in transformers to make 120/208 three phase service ...
Is that Wye or Delta?
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Old 06-21-2008, 04:02 AM   #12
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
wye would you ask?

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 06-21-2008, 09:19 AM   #13
3 Rivet Member
 
jkcru's Avatar
 
2010 28' Flying Cloud
Escondido , California
Join Date: Feb 2007
Posts: 196
Excellent info, but not for the timid.
jkcru is offline   Reply With Quote
Old 06-20-2010, 12:08 PM   #14
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
The final design is a bit modified from the above description. I decided it wasn't safe to have a standard connector that really was going to perform the shorting plug function. So a standard 110V, 30A connector is installed on the genset. Now, when you plug in you get power from just one winding or, when you close the switch, you get it from both windings. This allows the two 15A connectors to function on separate circuits with separate circuit breakers.

Click image for larger version

Name:	gen-mod2.jpg
Views:	190
Size:	235.1 KB
ID:	105249

I have a 10-gauge umbilicial with a standard 30A male on one end and a 30A trailer female on the other, in order to connect the trailer to the genset.

I tested this by running the old Armstrong AC and found less than 1 volt voltage drop. Happy, Happy. Burning man dust storms, take that. Pow. Wham. Zap.

Zep
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Old 06-20-2010, 12:58 PM   #15
Maniacal Engineer
 
barts's Avatar
 
1971 25' Tradewind
Lopez Island , Washington
Join Date: Jan 2010
Posts: 1,244
Images: 1
Blog Entries: 4
Interesting info....

Note that you can actually parallel regular generators, as they will self-synchronize . This is what the power grid does.

Generator synchronization (John De Armond)

- Bart
__________________
Bart Smaalders
Lopez Island, WA
https://tinpickle.blogspot.com
barts is offline   Reply With Quote
Old 06-20-2010, 04:57 PM   #16
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
Oops, I was a bit fast and loose with the schematic. This one is correct, I think.

Click image for larger version

Name:	gen-mod2.jpg
Views:	449
Size:	159.1 KB
ID:	105256

I looked at the thread and realized I didn't put any data in regarding how closely matched the windings were. It turns out the voltage was less than 1/2 volt and the resistance of the windings were near two ohms. So the circulating current is on the order of 1/4 Amp, or 25 Watts. That amount of heat can be easily dissipated by a small generator and is way less than what is being dissipated when there is an external load of 3,000 Watts (500 Watts).

Bart, thanks for the synchronization info. I always wondered how the big guys did that. Makes perfect sense, but I never would have thought of it.

Zep
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Old 06-17-2014, 10:37 PM   #17
Rivet Master
 
Zeppelinium's Avatar

 
1973 23' Safari
1977 23' Safari
2018 25' Flying Cloud
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 4,092
Send a message via Skype™ to Zeppelinium
Making this modification is a bit tricky, since it's mostly a mechanical problem of identifying the ends of the windings. Note that on my generator, each winding had two wires, so there are a total of 4 wires, but each pair are soldered together to create two windings.

In the top drawing below, the basic generator consists of two windings, each delivering 115 volts. In order to provide 240 volts (the second drawing), the windings are connected in series via the green wire (that's a notional green wire. In practice the ends of the windings are close enough together that they can be directly connected).

To double the current at 115 volts, you need to put the windings in parallel (third drawing). You will need to study the wires until you can identify the two windings and the connection between them. Sever that connection and reconnect the windings in parallel. If you screw up and connect the windings anti-parallel, eg, backwards, you'll get zero output and the generator will either blow the breakers or will overheat very quickly (but not instantaneously, so you will have 10 or 15 seconds to figure it out).

Click image for larger version

Name:	generator modification-page-001.jpg
Views:	161
Size:	103.7 KB
ID:	214444

Zep
__________________
Zep@Charmedquark.net
Zeppelinium is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What Amps??? Sundance Electrical - Systems, Generators, Batteries & Solar 8 03-31-2015 09:32 AM
Breaking up the 30 Amps soldiermedic Electrical - Systems, Generators, Batteries & Solar 11 07-20-2007 03:53 AM
How Big AC Input Amps??? Sundance Batteries, Univolts, Converters & Inverters 9 07-19-2007 11:59 AM
How many Amps??? Sundance Batteries, Univolts, Converters & Inverters 3 07-02-2007 11:32 PM
Meter for amps davidz71 Electrical - Systems, Generators, Batteries & Solar 5 05-09-2002 10:21 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 07:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.