Question Need help with Armstrong TR 21-12 problems please

I have a small problem. Whenever it rains, the A/C circuit pops the GFCI of the house circuit I'm plugged into. It only happens when it rains. When it dries out, it works just fine. If I shut off the A/C breaker at the box, I can reset the GFCI and all the other 110 outlets work fine in the trailer. Even with the A/C off at the thermostat, when I turn on the CB at the CB box it will trip the GFCI. Not the main CB, just the GFCI at the outlet. I have removed the A/C shroud and opened up the little wiring box and tightened all the wire nuts and made sure everything was in order. I found one wire a tad loose the other day so I thought I had the culprit, but It just rained and did it again. I sealed the little Jbox with sealant when I closed her up. The A/C is the original Armstrong unit. Any ideas?
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-20-2011, 10:25 PM   #2
Maniacal Engineer
 
barts's Avatar
 
1971 25' Tradewind
Lopez Island , Washington
Join Date: Jan 2010
Posts: 1,244
Images: 1
Blog Entries: 4
GFCI breakers trip when a imbalance exists between the current in the hot leg and the current in the neutral leg. Some things to check:

1) make sure relay/starter on A/C is interrupting hot leg, not neutral leg.
2) look for leakage paths on any of the wiring to the relay/starter. Note that dirt, wetness, etc. can easily conduct the milliamp necessary to trip the GFCI.

Another way of doing this is to get a mister bottle on a dry day and gently mist connections, etc. to find the leakage path. Plug something into the 110 outlet in the trailer so you know exactly when it trips. Of course, be careful while doing this....

- Bart
__________________
Bart Smaalders
Lopez Island, WA
https://tinpickle.blogspot.com
barts is offline   Reply With Quote
Old 05-20-2011, 10:33 PM   #3
Site Team
 
Aage's Avatar
 
1974 31' Sovereign
Ottawa , ON
Join Date: May 2008
Posts: 11,219
Images: 25
Wonder if the GFCI unit is marginally defective?

Did you try replacing it?
Aage is offline   Reply With Quote
Old 05-20-2011, 10:56 PM   #4
Rivet Master
 
NevadaGeo's Avatar
 
1978 31' Excella 500
Genoa , Nevada
Join Date: Jul 2007
Posts: 1,554
I had that problem in a buried line once. When it rains, it trips. Best bet is to find the wire that collects rain and replace it or waterproof it. Probably be a small slit in the protective covering from a siding nail that you can't find.
__________________
I admit to being powerless over housecleaning and social niceities
Airforums 22655 and now, WBCCI 22655

NevadaGeo
NevadaGeo is offline   Reply With Quote
Old 05-20-2011, 11:18 PM   #5
Rivet Master
 
Silver Goose's Avatar
 
2008 27' Classic FB
Burkburnett , Texas
Join Date: Jul 2010
Posts: 985
Do you have an outside 110v outlet? Considering your symptoms I would start there and inspect the gaskets to be sure moisture isn't getting in.
__________________
AIR 47751
Silver Goose is offline   Reply With Quote
Old 05-21-2011, 05:11 AM   #6
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Thanks for the help guys.

Barts,
I'll try those things you mentioned.

Aage,
I haven't replaced the outlet. I don't have any problems from it any other uses. Just when I have the trailer A/C circuit breaker on and it rains. When it trips I can shut off the A/C CB, reset the GFCI and everything else works fine.

NevadaGeo,
I have it isolated to the A/C circuit of the trailer. I don't think it is anything with the house or the house wiring. I have a 100' extension cord that I use to plug the trailer into an outlet inside the house.

YankeeDoodle,
My trailer doesn't have an exterior outlet.

I guess I need to do some more trouble shooting.
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-21-2011, 07:44 AM   #7
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
You'll want to pull the shroud off the A/C unit. Check the capacitors and make sure they aren't in a position to get water on top of them, where the connections are. Our '72 had this problem, I found out about it one day when it had rained, and I touched a metal part of the air conditioner.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 05-21-2011, 09:36 AM   #8
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Thanks for the help y'all. I think I've fixed it. These two wires were draped down over the blower motor sitting in a puddle of water. The black rubber boot for the (capacitor? Relay?) Is all torn up and was puddling water where these two wires connect to the componnent.
I cut off the old blade connectors and used two of these $1.10 crimp/solder/heat shrink super connectors I bought at Fastenal. I did my best to seal up the top and sides of the rubber boot. I'll have to keep an eye on it. It seems to be working fine right now.
Thanks guys. Once again the Forum knowledge base comes through!
Attached Thumbnails
Click image for larger version

Name:	ForumRunner_20110521_103524.png
Views:	154
Size:	559.0 KB
ID:	130319   Click image for larger version

Name:	ForumRunner_20110521_103544.png
Views:	172
Size:	545.9 KB
ID:	130320  

Click image for larger version

Name:	ForumRunner_20110521_103602.png
Views:	154
Size:	501.6 KB
ID:	130321   Click image for larger version

Name:	ForumRunner_20110521_103623.png
Views:	173
Size:	571.0 KB
ID:	130322  

Click image for larger version

Name:	ForumRunner_20110521_103640.png
Views:	170
Size:	550.0 KB
ID:	130323  
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-21-2011, 01:27 PM   #9
Site Team
 
Aage's Avatar
 
1974 31' Sovereign
Ottawa , ON
Join Date: May 2008
Posts: 11,219
Images: 25
Congratulations on finding the fault, Top. It does sound logical, that the wires that got a soaking would trigger the GFCI.

Here's a tester that I think I will put in my toolbox for future questions like you were going through. It tests for seven conditions and indicates faults by simple LEDs, hopefully it would have given you a hint as to what was going on.

"GFCI and receptacle tester tests ground fault receptacles by overloading circuit and tripping GFCI."
Aage is offline   Reply With Quote
Old 05-21-2011, 05:19 PM   #10
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
More tools=good

Quote:
Originally Posted by Aage View Post
Congratulations on finding the fault, Top. It does sound logical, that the wires that got a soaking would trigger the GFCI.

Here's a tester that I think I will put in my toolbox for future questions like you were going through. It tests for seven conditions and indicates faults by simple LEDs, hopefully it would have given you a hint as to what was going on.

"GFCI and receptacle tester tests ground fault receptacles by overloading circuit and tripping GFCI."
Thanks Aage! I'll see if I can find one of those. I'm not an electrician, but I do make them do push ups now and then. Electricians are always the ones in the smoke break area at the hangar. Whenever you see three Soldiers in my unit wasting time, two of them are electricians. The third is usually a pneudraulics (aircraft plumber) mechanic. You know what I think of plumbers these days!
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-21-2011, 05:35 PM   #11
x
 
XXXX , XXXX
Join Date: Jun 2010
Posts: 2,601
Quote:
Originally Posted by Top View Post
Thanks Aage! I'll see if I can find one of those. I'm not an electrician, but I do make them do push ups now and then. Electricians are always the ones in the smoke break area at the hangar. Whenever you see three Soldiers in my unit wasting time, two of them are electricians. The third is usually a pneudraulics (aircraft plumber) mechanic. You know what I think of plumbers these days!
Lance I'm LMAO about the pushups. Electricians are the only ones that get paid to pull their wire all day long.
Plumbers only need to know the two rules of plumbing.
1) poop flows downhill
2) Payday is Friday.
wasagachris is offline   Reply With Quote
Old 05-21-2011, 05:44 PM   #12
Rivet Master
 
2019 27' Globetrotter
Missouri Valley , Iowa
Join Date: Sep 2008
Posts: 512
Chris,
I heard the same plumbers admonitions with one more bit of advice : Don't chew your nails !!!!

Dan
Farmer Dan is offline   Reply With Quote
Old 05-21-2011, 06:03 PM   #13
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Quote:
Originally Posted by wasagachris View Post
Lance I'm LMAO about the pushups. Electricians are the only ones that get paid to pull their wire all day long.
Plumbers only need to know the two rules of plumbing.
1) poop flows downhill
2) Payday is Friday.
My Dad always said that about plumbers when I was a kid. After actually trying to find a good plumber, I know what he was talking about!
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-21-2011, 06:08 PM   #14
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
Quote:
Originally Posted by wasagachris View Post
Plumbers only need to know the two rules of plumbing.
1) poop flows downhill
2) Payday is Friday.
I have always heard:
Hot on the left
Cold on the right
Crap flows downhill
Most plumbers around here only have one out of those three correct
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 05-21-2011, 06:19 PM   #15
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Ha Ha! That's a funny one! So Terry, what is the little thing on the top of the motor called?
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-21-2011, 07:53 PM   #16
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
Quote:
Originally Posted by Top View Post
Ha Ha! That's a funny one! So Terry, what is the little thing on the top of the motor called?
That's a capacitor. If you grab the terminals, it can really "light up your life".
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 05-21-2011, 07:59 PM   #17
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Quote:
Originally Posted by overlander63 View Post
That's a capacitor. If you grab the terminals, it can really "light up your life".
It did just that a few days ago when I was prodding around with the juice on!
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-21-2011, 09:57 PM   #18
Rivet Master
 
soldiermedic's Avatar
 
Currently Looking...
Florissant , USA
Join Date: Oct 2006
Posts: 5,083
Cardiac Dysrhythmias.....shocking
__________________
Streaming Soldiers Blog
soldiermedic is offline   Reply With Quote
Old 05-24-2011, 08:12 PM   #19
Always learning
 
Lance M's Avatar
 
1972 29' Ambassador
1962 19' Globetrotter
1951 21' Flying Cloud
Central , Texas
Join Date: Oct 2010
Posts: 2,881
Images: 24
Blog Entries: 2
Send a message via Yahoo to Lance M
Angry No rain just heat

Looks like another problem with the A/C and popping the GFCI. Today after having the A/C on for about six hours, the GFCI popped again. No rain. Just a lot of heat. I shut off the A/C and moved the thermostat to the hottest setting. I reset the GFCI and turned on the A/C/ The blower fan came on and ran fine. When I turned the thermostat down, the compressor kicked in and immediately the GFCI popped. That pretty much narrows it down to the compressor and compressor wiring. Maybe something melted. Any ideas?
__________________
Lance

Work is never done, so take time to play!
Lance M is offline   Reply With Quote
Old 05-24-2011, 08:24 PM   #20
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
How big

What size is the circuit breaker that keeps tripping?
TG Twinkie is offline   Reply With Quote
Reply

Tags
armstrong, wiring, gfi


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Free 1973 Armstrong A/C parts w/shipping costs rich2002 Furnaces, Heaters, Fireplaces & Air Conditioning 13 06-19-2017 11:43 AM
Armstrong VCT - Any gluing issues with Cold? robwok Floor Finishes 4 08-08-2013 11:49 AM
Armstrong 10 AC Unit BadKarma226 Furnaces, Heaters, Fireplaces & Air Conditioning 7 08-11-2011 08:50 AM