Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 


Reply
 
Thread Tools Search this Thread Display Modes
 
Old 07-23-2021, 01:58 PM   #1
Rivet Master
 
DaveP's Avatar

 
2004 28' Classic
Monument , Colorado
Join Date: Nov 2015
Posts: 1,566
Need Your Expert Electrical Analysis on SOC

I have spent about two hours on the phone with two different Renogy techs and they cannot figure this out. I have the Renogy smart lithium batteries. The four of them are networked together with the Renogy battery monitor. I also have a Magnum MS 3012M charger/inverter with the Magnum battery monitor/shunt. I use a Victron Energy SmartSolar MPPT 100V 30 amp when charging with 400 watts of Renogy solar panels. When I charge the batteries with the Magnum or the solar, the SOC often comes out different on the two systems. It may be just a few percentage points as seen in the below picture but I have also seen higher differences (of 10 to 20 percentage points) when charging partially with solar (like a cloudy afternoon). The Renogy system usually shows a lower SOC than the Magnum. Do any of you have any ideas what might cause these discrepancies? Should I be worried about it? It seems to me that they are measuring power in and power out. Everything else with the system seems to be OK.

Just as reference, the Victron Smartsolar is set to lithium. Magnum advised me to set their charger to CC/CV. I have the voltage max-out at 14.4V per there advice. I also turn the charger off at about 98% SOC as Renogy recommends not holding their lithium batteries at 100% SOC all the time.

Thanks, Dave
Attached Thumbnails
Click image for larger version

Name:	SOC Discepency.jpg
Views:	23
Size:	74.1 KB
ID:	400230  
__________________
DaveP
2004 Airstream Classic 28 "Willard"
2023 Ram 3500 4x4
DaveP is online now   Reply With Quote
Old 07-26-2021, 12:48 PM   #2
Rivet Master
 
DaveP's Avatar

 
2004 28' Classic
Monument , Colorado
Join Date: Nov 2015
Posts: 1,566
Question

I could really use some help here. I would like to understand what is going on so I know if sometime needs to be fixed or if this is just the way it is. Uncle Bob? GMFL? Lewster?
__________________
DaveP
2004 Airstream Classic 28 "Willard"
2023 Ram 3500 4x4
DaveP is online now   Reply With Quote
Old 07-26-2021, 01:59 PM   #3
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,740
Hi

How do you have each of them programmed? ( or can you even get at the programming ....).

If you take a look at a Victron BMV 712 there are roughly a dozen settings that impact what it thinks is "100%" change any of them and you change the results. Much of it is lead acid specific vs Lithium specific ( lead acid only uses 90 something % or the charge input, lithium uses > 99% .... lead acid only is "full" after charging for hours, lithium is "full" much faster ...).

So what settings do you have access to?

Bob
uncle_bob is offline   Reply With Quote
Old 07-26-2021, 02:36 PM   #4
4 Rivet Member
 
2019 30' Flying Cloud
Grass Lake , Michigan
Join Date: Aug 2018
Posts: 280
Bob nailed it. SOC is a calculated value, so unless both units are doing the calculations exactly the same from the same measured inputs, you are not likely to see the exact same value. It's the old "man with two watches" problem.
oldenavy is offline   Reply With Quote
Old 07-26-2021, 03:14 PM   #5
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,740
Hi

So, how would you set up a charge controller for lithium?

1) It's nearly 100% efficient so cancel out all the lead acid this and that effect stuff

2) When it gets to max voltage (14.4 or whatever ) it's full. Let the current come down some and then let it reset to 100%. No need to wait 4 hours looking at this or that.

3) The thing that always gets SOC reset on these gizmos is current going here or there. Often with lead acid this gets touchy and the settings are pretty low. No need for this with lithiums.

4) SOC is based on some input for "what's full" with lead acid, you might enter 100 AH and the gizmo decides 50AH is "full". This isn't right for lithium.

Yes this does go on and on. Thus the question of what settings you can actually get at.

Bob
uncle_bob is offline   Reply With Quote
Old 07-26-2021, 04:00 PM   #6
Rivet Master
 
DaveP's Avatar

 
2004 28' Classic
Monument , Colorado
Join Date: Nov 2015
Posts: 1,566
Bob,

Thanks for your inputs. I am starting to see the "light" for this issue. I was not thinking about what was going on in the right way.

The Renogy batteries have the SOC calculations built into their BMSs. I have four batteries networked together into their battery monitor. There are no settings I can adjust. I have to assume circuitry and algorithms are correct.

The Magnum ME-BMK is built for lead acid chemistry. I got the whole system five years ago when I had AGM batteries. The controller and charger do not have a lithium setting. I just re-looked at the instructions for the shunt and the only thing I can choose to control is charging efficiency. They recommended, I and choose, to set this setting to "automatic". It looks at the voltage a couple of hours after a complete charge cycle to recalculate "100% SOC". I can see how charging the batteries partially with solar then finishing with a generator (because of afternoon thunderstorms) would really mess up the calculations and cause the bigger discrepancies.

Thanks for getting me back on track. I think I will just ignore the Magnum SOC readings and use the Renogy readings for my charging decisions.

Thanks, Dave
__________________
DaveP
2004 Airstream Classic 28 "Willard"
2023 Ram 3500 4x4
DaveP is online now   Reply With Quote
Old 07-27-2021, 07:29 AM   #7
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,740
Quote:
Originally Posted by DaveP View Post
Bob,

Thanks for your inputs. I am starting to see the "light" for this issue. I was not thinking about what was going on in the right way.

The Renogy batteries have the SOC calculations built into their BMSs. I have four batteries networked together into their battery monitor. There are no settings I can adjust. I have to assume circuitry and algorithms are correct.

The Magnum ME-BMK is built for lead acid chemistry. I got the whole system five years ago when I had AGM batteries. The controller and charger do not have a lithium setting. I just re-looked at the instructions for the shunt and the only thing I can choose to control is charging efficiency. They recommended, I and choose, to set this setting to "automatic". It looks at the voltage a couple of hours after a complete charge cycle to recalculate "100% SOC". I can see how charging the batteries partially with solar then finishing with a generator (because of afternoon thunderstorms) would really mess up the calculations and cause the bigger discrepancies.

Thanks for getting me back on track. I think I will just ignore the Magnum SOC readings and use the Renogy readings for my charging decisions.

Thanks, Dave
Hi

No problem ....

Set the charge efficiency on your Magnum to 99 or 100%

Bob
uncle_bob is offline   Reply With Quote
Old 07-27-2021, 09:23 AM   #8
Rivet Master
 
DaveP's Avatar

 
2004 28' Classic
Monument , Colorado
Join Date: Nov 2015
Posts: 1,566
Bob,

Good idea on the charge efficiency. At least it will give me a number without trying to recalculate.

Thanks, Dave
__________________
DaveP
2004 Airstream Classic 28 "Willard"
2023 Ram 3500 4x4
DaveP is online now   Reply With Quote
Old 08-02-2021, 06:46 AM   #9
Rivet Master
 
DaveP's Avatar

 
2004 28' Classic
Monument , Colorado
Join Date: Nov 2015
Posts: 1,566
After 3 days camping (mostly overcast), some solar, lots of generator, the SOC from both monitors has been tracking within one percentage point. Good call on the charge efficiency reset! [emoji3]
__________________
DaveP
2004 Airstream Classic 28 "Willard"
2023 Ram 3500 4x4
DaveP is online now   Reply With Quote
Old 08-03-2021, 08:04 AM   #10
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,740
Hi

Even with two of the same model, staying within 1% over a couple of days would be doing well. Sounds like you have it running right.

Bob
uncle_bob is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Battery SOC, battery options, strategies, etc. Dennis C Batteries, Univolts, Converters & Inverters 29 11-06-2020 09:27 PM
Lifeline AGM SOC without a BMV-712 Smart smsasf Batteries, Univolts, Converters & Inverters 1 08-30-2020 08:47 PM
Just bought a 1977 28ft Argosy- Need Your Expert Advice GarrettRing All Argosy Trailers 18 05-15-2011 05:58 AM
Load distribution hitches-an analysis nickcrowhurst Hitches, Couplers & Balls 92 03-15-2010 06:41 PM
Need electrical system expert advice boondockdad Electrical - Systems, Generators, Batteries & Solar 25 11-16-2008 05:03 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 06:02 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.