Need Help Understanding BMV-712

I recently installed a BMV-712. My system now includes an IP43 12/50(1+1), an Orion XS, and a SmartSolar MPPT75/15 along with two Lifeline AGMs and a single factory solar panel.

My question is why does the BMV show the batteries at 65% charge when the battery voltage (with only parasitic loads) is at 12.05 volts. I thought 50% was around 12.2 volts for a lead acid battery.

Also, while towing, will the batteries be charged by both the Orion XS (DC-DC charger) and the solar? Everything is in the same VE network.

Thanks in advance, Mark
Attached Thumbnails
Click image for larger version

Name:	BMV-712 Screenshot_20250110_111248.jpg
Views:	12
Size:	76.8 KB
ID:	450045  
MSL is offline   Reply With Quote
Old 01-10-2025, 09:27 PM   #2
Rivet Master
 
1988 32' Excella
Robbinsville , New Jersey
Join Date: May 2012
Posts: 3,645
Are your batteries 100 amp hour each?
If they are only 80 AH each your BMV-712 is configured wrong.

How old are your batteries?
If your batteries are a few years old they may have lost some capacity. Also AGMs have less capacity in cold temps. What temp are the batteries at?

The batteries also need to be fully charged to sync at 100% charge(which can take more then 24 hours charging on shore power) before you can get an accurate reading..
Wazbro is offline   Reply With Quote
Old 01-11-2025, 09:03 AM   #3
MSL
4 Rivet Member
 
2019 22' Sport
Sharon , Massachusetts
Join Date: Apr 2019
Posts: 292
Wondering about Configuration

Quote:
Originally Posted by Wazbro View Post
Are your batteries 100 amp hour each?
If they are only 80 AH each your BMV-712 is configured wrong.

How old are your batteries?
If your batteries are a few years old they may have lost some capacity. Also AGMs have less capacity in cold temps. What temp are the batteries at?

The batteries also need to be fully charged to sync at 100% charge(which can take more then 24 hours charging on shore power) before you can get an accurate reading..
I was wondering about the configuration, but I think it's correct. Maybe sync? I did not do a manual sync; I just let it figure it out automatically. Photo of config is attached. Sorry, I should have included this with my original post.

I have two 80 Ah batteries, so I have capacity at 160Ah. Charged voltage is set to 13.2V. Battery temps are 20-30F and they're 5 years old.

Thanks, Mark
Attached Thumbnails
Click image for larger version

Name:	BMV-712 Config - 20250111_095202.jpg
Views:	8
Size:	119.1 KB
ID:	450058  
MSL is offline   Reply With Quote
Old 01-11-2025, 12:25 PM   #4
Rivet Master
 
JeffKim's Avatar

 
2023 25' Globetrotter
2021 16' Bambi
Forest Lake , Minnesota
Join Date: Mar 2021
Posts: 1,893
And as you know you're all set up for lithium batteries which have gotten pretty cheap and there's a number of good options that fit the battery box up to 300Ah.

With our Victron shunt I gave up on the automatic reset settings. I found it will reset after an "event" which might not be valid unless you fuss with the settings and get them just right. I turn this option off and do a manual reset occasionally after being plugged in for an extended time. I have never tested the stated capacity of our 400Ah of batteries to see if they really hold 400Ah, but we have never played it that close to where we are less than 20% or so of assumed capacity.

With the XS and solar, yes they both should be charging. I have a similar setup and with the VE.Smart Networking turned on they play together (make sure it's turned on at each device).
__________________
2023 Globetrotter 25FBT "Curly"
2017 Audi Q7 3.0T
WBCCI 6343
JeffKim is offline   Reply With Quote
Old 01-11-2025, 04:27 PM   #5
MSL
4 Rivet Member
 
2019 22' Sport
Sharon , Massachusetts
Join Date: Apr 2019
Posts: 292
Quote:
Originally Posted by JeffKim View Post
And as you know you're all set up for lithium batteries which have gotten pretty cheap and there's a number of good options that fit the battery box up to 300Ah.

With our Victron shunt I gave up on the automatic reset settings. I found it will reset after an "event" which might not be valid unless you fuss with the settings and get them just right. I turn this option off and do a manual reset occasionally after being plugged in for an extended time. I have never tested the stated capacity of our 400Ah of batteries to see if they really hold 400Ah, but we have never played it that close to where we are less than 20% or so of assumed capacity.

With the XS and solar, yes they both should be charging. I have a similar setup and with the VE.Smart Networking turned on they play together (make sure it's turned on at each device).
Yes, I have two LiTime 100Ah batteries ready to get installed; that's why I installed all the new Victron devices. I wanted to make sure the Victron items were installed correctly, and I understood the various configurations, prior to installing the batteries.

When you say, "I gave up on the automatic reset settings", I assume you are referring to the synchronization. After reading your post, I did a manual synchronization, so I'll test the 50% SOC reading in several days when I have time to keep an eye on things.

Regarding the VE Smart Networking, yes, I have all devices set up and the system shows they're all online. Thanks for letting me know they do in fact work together.

Thanks again, Mark
MSL is offline   Reply With Quote
Old 01-11-2025, 05:39 PM   #6
Rivet Master
 
1988 32' Excella
Robbinsville , New Jersey
Join Date: May 2012
Posts: 3,645
That seems strange, your first picture shows 81.8 Ah consumed and 65% charge. That would be close to 50% of 160 Ah.
Wazbro is offline   Reply With Quote
Old 01-11-2025, 06:34 PM   #7
Rivet Master
 
StogieMan's Avatar

 
2015 Interstate Grand Tour
Salem , New Hampshire
Join Date: Jun 2022
Posts: 1,115
Quote:
Originally Posted by MSL View Post
I was wondering about the configuration, but I think it's correct. Maybe sync? I did not do a manual sync; I just let it figure it out automatically.
Below is a very good detailed post on setting up the BMV 712 that was posted the other day on another forum. The poster is a darn Victron guru and I always seem to learn something from his posts. This is good information for everyone as there are always questions on Victron shunts.

https://diysolarforum.com/threads/vi...-others.97606/
__________________
"If you can't send money, send tobacco."
-George Washington
StogieMan is offline   Reply With Quote
Old 01-11-2025, 07:58 PM   #8
MSL
4 Rivet Member
 
2019 22' Sport
Sharon , Massachusetts
Join Date: Apr 2019
Posts: 292
Quote:
Originally Posted by Wazbro View Post
That seems strange, your first picture shows 81.8 Ah consumed and 65% charge. That would be close to 50% of 160 Ah.
Yes, that's why I created the original post; it didn't make sense to me.
Mark
MSL is offline   Reply With Quote
Old 01-11-2025, 10:45 PM   #9
Site Team
 
richard5933's Avatar

 
1994 25' Excella
Waukesha , Wisconsin
Join Date: Sep 2020
Posts: 6,365
Images: 5
In order for the BMS to be accurate ALL the negative cables must route through the shunt. If you have anything routing to the battery bank's negative connection which bypasses the shunt you will get inaccurate and confusing readings.

Are you sure that all your negative cables are routed through the shunt?
__________________
Richard
11018
1994 Excella 25 'Gertie' Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8 'Bert'
1974 GMC 4108a - Custom Coach Land Cruiser 'The Bus' (Sold)
richard5933 is offline   Reply With Quote
Old 01-12-2025, 09:47 AM   #10
MSL
4 Rivet Member
 
2019 22' Sport
Sharon , Massachusetts
Join Date: Apr 2019
Posts: 292
Quote:
Originally Posted by richard5933 View Post
In order for the BMS to be accurate ALL the negative cables must route through the shunt. If you have anything routing to the battery bank's negative connection which bypasses the shunt you will get inaccurate and confusing readings.

Are you sure that all your negative cables are routed through the shunt?
Yes, all loads go to the correct side of the shunt; only shunt connected to negative side of battery. Mark
MSL is offline   Reply With Quote
Old 01-12-2025, 09:49 AM   #11
MSL
4 Rivet Member
 
2019 22' Sport
Sharon , Massachusetts
Join Date: Apr 2019
Posts: 292
Quote:
Originally Posted by StogieMan View Post
Below is a very good detailed post on setting up the BMV 712 that was posted the other day on another forum. The poster is a darn Victron guru and I always seem to learn something from his posts. This is good information for everyone as there are always questions on Victron shunts.

https://diysolarforum.com/threads/vi...-others.97606/
Thanks. This is very informative, but I think I have everything configured correctly. I read thru the post, will do so again (and save it on my laptop).
Mark
MSL is offline   Reply With Quote
Old 01-13-2025, 11:50 AM   #12
Rivet Master
 
JeffKim's Avatar

 
2023 25' Globetrotter
2021 16' Bambi
Forest Lake , Minnesota
Join Date: Mar 2021
Posts: 1,893
Quote:
Originally Posted by MSL View Post
Yes, I have two LiTime 100Ah batteries ready to get installed; that's why I installed all the new Victron devices. I wanted to make sure the Victron items were installed correctly, and I understood the various configurations, prior to installing the batteries.

When you say, "I gave up on the automatic reset settings", I assume you are referring to the synchronization. After reading your post, I did a manual synchronization, so I'll test the 50% SOC reading in several days when I have time to keep an eye on things.
Sounds good! I think it might be simpler having the lithiums, the charging profile is simpler and don't have to worry about discharge temperature, etc.

Yes, the synchronization is what I meant. It would explain why you were seeing higher charge percentage if it reset at some point automatically. I might still dink around with the settings and make it automatic, but after getting burned before, I trust the manual reset more. If it resyncs automatically and it's wrong then I'm out of luck until we get to a place I can plug in and charge them up fully so I know they're at 100%.
__________________
2023 Globetrotter 25FBT "Curly"
2017 Audi Q7 3.0T
WBCCI 6343
JeffKim is offline   Reply With Quote
Old 01-15-2025, 10:34 AM   #13
MSL
4 Rivet Member
 
2019 22' Sport
Sharon , Massachusetts
Join Date: Apr 2019
Posts: 292
Quote:
Originally Posted by JeffKim View Post
Sounds good! I think it might be simpler having the lithiums, the charging profile is simpler and don't have to worry about discharge temperature, etc.

Yes, the synchronization is what I meant. It would explain why you were seeing higher charge percentage if it reset at some point automatically. I might still dink around with the settings and make it automatic, but after getting burned before, I trust the manual reset more. If it resyncs automatically and it's wrong then I'm out of luck until we get to a place I can plug in and charge them up fully so I know they're at 100%.
Thanks again, Jeff. I'm glad I went with Victron for all this stuff, but there definitely is a learning curve.
MSL is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
BMV-712 Smart issue with LED backlight....Need some input kittmaster Electrical - Systems, Generators, Batteries & Solar 0 10-02-2020 12:43 PM
Need some install advice on the Victron BMV-712 GoingPhishin Sprinter and B-van Forum 44 08-02-2020 01:00 PM
Going to JC, need a part ASAP. BMV-712 smart kittmaster General Repair Forum 5 07-20-2020 03:58 PM
Question regarding Victron BMV-712 billrector Batteries, Univolts, Converters & Inverters 26 05-30-2018 04:21 PM
Victron BMV-712 install in 2017 30 International dmcgaugh Batteries, Univolts, Converters & Inverters 3 03-09-2018 01:24 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:38 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.