Wiring A/C with a separate circuit for Gen ?

Wondering if you could put a transfer switch in place so that you could run (only) the A/C on a generator while all other loads would be carried by batteries and solar as applicable.

That way if your generator is capable of running the A/C (as our Honda 2200 on propane with the 13.5k A/C seems to be (up to 4,000 ft anyway)) you could avoid throwing additional load on it.

We do have 2 generators, but would prefer to carry only one. That said we often don't carry even one, but that is another subject.

What might be the potential problems with this idea?
__________________
2018 GMC Canyon CCSB V6 Mallet Supercharger
2006 Chevrolet CCSB 2500HD 6.6T LBZ
SYC2Vette is offline   Reply With Quote
Old 09-06-2021, 12:26 PM   #2
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
Yes - it is doable. Home generator backup systems do this all the time (select only certain legs to power).

Pitfall A is finding an electrician who understands RV power systems.

Pitfall B is finding/making space for the electrical box in which the breaker will be located.

Pitfall C is getting over a big hole being drilled in the side of your American Classic to accommodate the NEMA connector needed to mate with the generator.

Hope this helps,
Tom
TomW is offline   Reply With Quote
Old 09-06-2021, 12:33 PM   #3
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,736
Hi

Can you do this? Sure you can. It's only money

Should you do this? .... hmmm ....

All the 12V loads will run off of the battery "as is". No modifications are required. Running *anything* off the inverter is going to be power intensive. ( = you run the batteries down fast). What "other loads" might you run on the inverter?

Water heater? nope, run it on propane.

Fridge? propane again.

Microwave? Only if you have a pretty substantial inverter. Probably easier to turn off the A/C for the short time it's on.

Looking around the trailer ... not a lot left. The TV will run off the inverter without any re-wiring. You just flip a breaker and a switch.

I can't see a lot of benefits

Bob
uncle_bob is offline   Reply With Quote
Old 09-06-2021, 12:54 PM   #4
Rivet Master
 
2017 20' Flying Cloud
Williamson County , Texas
Join Date: Apr 2017
Posts: 813
Images: 1
Quote:
Originally Posted by uncle_bob View Post
Hi

Can you do this? Sure you can. It's only money

Should you do this? .... hmmm ....

All the 12V loads will run off of the battery "as is". No modifications are required. Running *anything* off the inverter is going to be power intensive. ( = you run the batteries down fast). What "other loads" might you run on the inverter?

Water heater? nope, run it on propane.

Fridge? propane again.

Microwave? Only if you have a pretty substantial inverter. Probably easier to turn off the A/C for the short time it's on.

Looking around the trailer ... not a lot left. The TV will run off the inverter without any re-wiring. You just flip a breaker and a switch.

I can't see a lot of benefits

Bob
Well now that you point all that out, you are of course correct. I have seen our current draw vary quite a bit when hooked up to shore power with A/C on, but of course we are not going to be running electric water heater or MW when on battery/solar/generator anyway. Yikes that seems so obvious now! I think I have only used the inverter twice in the last 3 years anyway and one time was just to verify it worked.
__________________
2018 GMC Canyon CCSB V6 Mallet Supercharger
2006 Chevrolet CCSB 2500HD 6.6T LBZ
SYC2Vette is offline   Reply With Quote
Old 09-06-2021, 01:35 PM   #5
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,736
Quote:
Originally Posted by SYC2Vette View Post
Well now that you point all that out, you are of course correct. I have seen our current draw vary quite a bit when hooked up to shore power with A/C on, but of course we are not going to be running electric water heater or MW when on battery/solar/generator anyway. Yikes that seems so obvious now! I think I have only used the inverter twice in the last 3 years anyway and one time was just to verify it worked.
Hi

For some things it helps if you are sitting in a trailer and looking at the loads in real time as you type ... ( one *might* call it cheating .... )

Bob
uncle_bob is offline   Reply With Quote
Old 09-07-2021, 09:22 AM   #6
Rivet Master
 
Hermes's Avatar
 
2016 28' International
Trois-Rivieres , Quebec
Join Date: Jun 2018
Posts: 701
Quote:
Originally Posted by SYC2Vette View Post
Wondering if you could put a transfer switch in place so that you could run (only) the A/C on a generator while all other loads would be carried by batteries and solar as applicable.
Airstream has made changes to the connections between the 12V circuit, the converter/charger and the batteries over the years, but with a 2017 model which should be like my 2016, I would switch off the converter breaker switch to make sure the generator is not powering the 12V circuit, then toggle the Use/Store switch to Use to connect the batteries to the 12V circuit and, as others have mentioned, run the fridge and hot water on propane, and you should be fine. And if your solar is set up like mine, it is directly connected to the batteries (via a cutoff switch) so there is nothing to be done there, it will keep charging your batteries.
__________________
2016 International Signature CCD, RBQ, Dual A/C, 28'
2018 GMC Sierra SLE 2500HD, 4x4, Crew Cab, Duramax Diesel, Leer cap
Lift kit, 16" wheels, Michelin Agilis CC LT
DIY Solar: 500W Renogy panels, AM Solar hdw, Blue Sky MPPT controller, 470ah Rolls battery bank, 2000W Renogy inverter.
Hermes is offline   Reply With Quote
Old 09-07-2021, 11:05 AM   #7
4 Rivet Member
 
DaveG's Avatar
 
Here and There , West Coast
Join Date: Apr 2019
Posts: 433
[QUOTE=SYC2Vette;2534818]Wondering

(as our Honda 2200 on propane with the 13.5k A/C seems to be (up to 4,000 ft anyway)


"4,000 feet" - What size wire?
Just curious.
DaveG is offline   Reply With Quote
Old 09-07-2021, 12:02 PM   #8
Rivet Master
 
2017 20' Flying Cloud
Williamson County , Texas
Join Date: Apr 2017
Posts: 813
Images: 1
Quote:
Originally Posted by Hermes View Post
Airstream has made changes to the connections between the 12V circuit, the converter/charger and the batteries over the years, but with a 2017 model which should be like my 2016, I would switch off the converter breaker switch to make sure the generator is not powering the 12V circuit, then toggle the Use/Store switch to Use to connect the batteries to the 12V circuit and, as others have mentioned, run the fridge and hot water on propane, and you should be fine. And if your solar is set up like mine, it is directly connected to the batteries (via a cutoff switch) so there is nothing to be done there, it will keep charging your batteries.
Yes, thought of that and much simpler than going to the trouble of a transfer switch! Thanks for confirming that makes sense.
__________________
2018 GMC Canyon CCSB V6 Mallet Supercharger
2006 Chevrolet CCSB 2500HD 6.6T LBZ
SYC2Vette is offline   Reply With Quote
Old 09-07-2021, 12:12 PM   #9
Rivet Master
 
waninae39's Avatar
 
2022 25' Flying Cloud
NCR , Ontario
Join Date: Feb 2017
Posts: 3,102
look at victron products

they support dual power coming into the Multiplus products
www.victronenergy.com
waninae39 is online now   Reply With Quote
Old 09-07-2021, 03:18 PM   #10
4 Rivet Member
 
Streamracer's Avatar
 
1986 25' Sovereign
Huntsville , Alabama
Join Date: Sep 2015
Posts: 283
Have you looked to see where your ac attaches to power? Mine is wired to a plug and plugged into a duplex above my refrigerator. I could run an extension cord thru the vent door and plug ac into that and hook to generator if needed.
Streamracer is offline   Reply With Quote
Old 09-07-2021, 08:39 PM   #11
:SPACE A" S/O 11 Air19745
 
guskmg's Avatar
 
2006 34' Classic S/O
Fort Worth , Texas
Join Date: Feb 2007
Posts: 1,766
A lot of us have wired an AC inlet (30/50) at the front of our trailers. That and with a tee, hose and propane quick disconnect we run our gennys in the pickup bed. Works great. BTW, I upgraded my Yamaha 3000 to a 6300 so now I can run both A/Cs for a quick cool down. I know, I'm spoiled with all these handy options.
guskmg
guskmg is offline   Reply With Quote
Old 09-09-2021, 08:47 AM   #12
4 Rivet Member
 
DaveG's Avatar
 
Here and There , West Coast
Join Date: Apr 2019
Posts: 433
[QUOTE=DaveG;2535097]
Quote:
Originally Posted by SYC2Vette View Post
Wondering

(as our Honda 2200 on propane with the 13.5k A/C seems to be (up to 4,000 ft anyway)


"4,000 feet" - What size wire?
Just curious.
I see a problem with wording in my impulse post > retry:
Are you experiencing a problem above 4000?
How are you connecting (gauge and length of wire)?
Softstart?
DaveG is offline   Reply With Quote
Old 09-09-2021, 10:03 AM   #13
Rivet Master
 
2017 20' Flying Cloud
Williamson County , Texas
Join Date: Apr 2017
Posts: 813
Images: 1
[QUOTE=DaveG;2535728]
Quote:
Originally Posted by DaveG View Post

I see a problem with wording in my impulse post > retry:
Are you experiencing a problem above 4000?
How are you connecting (gauge and length of wire)?
Softstart?
I have not installed a softstart although I have a kit sitting on my desk. 4000' altitude reference is because I have not tried it at higher altitude, it "might" work. We actually have 2 of the 2200 set up to parallel, but usually only carry one. I don't know the wire size, the cable is a pretty standard 30A cable.
__________________
2018 GMC Canyon CCSB V6 Mallet Supercharger
2006 Chevrolet CCSB 2500HD 6.6T LBZ
SYC2Vette is offline   Reply With Quote
Old 09-09-2021, 05:26 PM   #14
4 Rivet Member
 
DaveG's Avatar
 
Here and There , West Coast
Join Date: Apr 2019
Posts: 433
[QUOTE=SYC2Vette;2535757]
Quote:
Originally Posted by DaveG View Post

I have not installed a softstart although I have a kit sitting on my desk. 4000' altitude reference is because I have not tried it at higher altitude, it "might" work. We actually have 2 of the 2200 set up to parallel, but usually only carry one. I don't know the wire size, the cable is a pretty standard 30A cable.
Curiosity and questions are in regard to limitations of a smaller but easier to handle generator.
Thanks!!
DaveG is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a separate alternator for charging trailer batteries Streamside Batteries, Univolts, Converters & Inverters 12 01-04-2012 08:24 PM
TravelTrailer or MotorHome: Debate or just separate camps? BillWill General Motorhome Topics 32 12-17-2008 07:25 PM
How do you separate this? north dakota Doors & Locks 13 05-15-2008 09:42 PM
Is there a new separate oven bdogz Stoves, Ovens & Microwaves 5 08-29-2005 08:07 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 12:48 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.