Wire Type from Roof Solar Panels to Controller

Hi folks - I've been scouring for ideas on what wire type to use from solar panels that are going in on the roof down to the solar controller inside the cabin. I'm looking for suggestions on what is suitable for outdoor use, first and foremost.

Home Depot has a good selection of wire but the folks there don't seem to think any of it is UV rated. From souring the web, I can't get a very good picture on what to use and people seem to be using all kinds of stuff.

Some options I've read about/considered...
-- "tray cable" (not sure exactly what that is)
-- welding cable
-- marine cable
-- something else from home depot
-- order something from a solar store
-- go to local electrical supply and ask for something

I will be installing about 200 watts of panels and can hook them up as 12, 24 or 48 nominal voltage. The Outback MPPT controller I purchased would prefer 24 or 48. (I read one post somewhere that suggested that 24 might be better than 48 since it isn't as drastic as a drop for the controller -- but I have not seen other info to back up that claim.

I'm inclined to go 48 volt since the higher the voltage, the less power is lost in transmission. I am thinking that I will use a minimum of 10 gauge cable for the short 1 foot jumpers between panels, and maybe that would be sufficient for the drop down to the controller. Some of the options in the list above, such as welding cable, would certainly provide a much heavier gauge for that run but seems like overkill if I am sending 48 volts across it.

The run from the controller to the batteries will likely be welding cable so the main question I have is what to use from the roof down to the controller?
CA_Tallguy is offline   Reply With Quote
Old 11-27-2012, 01:21 PM   #2
Rivet Master
 
DanielB's Avatar
 
1974 31' Excella 500
Charleston , South Carolina
Join Date: Nov 2010
Posts: 1,073
Blog Entries: 8
Good stuff here..

from The RV Battery Charging Puzzle « HandyBob's Blog
__________________
As I grow older, I pay less attention to what men say. I just watch what they do.
- Andrew Carnegie
DanielB is offline   Reply With Quote
Old 11-27-2012, 01:45 PM   #3
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Thanks - I was checking out that site last night. Have not had a chance to read it in total yet but in scanning it I can't see specific cable recommendations except "the main thing to worry about is a UV rated shield on the roof" -- and that is the difficulty I'm having right now. He also talks about using welding cable in parts of installations, and that is my plan for the 12 volt side of things from the controller to the batteries (and I am assuming that is what he is talking about too). It isn't clear to me from what I have read if you can find welding cable that is UV rated. I'm starting to think my best bet is to go to an electrical supply and tell them I need some #8 or larger UV rated cable.

I've found a few other sites that are detailed like that guy but unfortunately I can't seem to find explicit information on what UV rated cable to ask for and from where. But at the same time, TONS of people are installing their solar panels and I don't believe that they are stressing out over the cable as much as I am so I am thinking I am either missing something or people are going for other stuff.

Another route that may be promising is someone posted on here about using marine cable and that it is rated for just about everything. That sounds like an interesting lead.

From what I understand, most cable sold for solar installations is #10 and smaller. But maybe I should look at the vendor websites a little closer to be sure. I've just been trying to find something local so far.
CA_Tallguy is offline   Reply With Quote
Old 11-27-2012, 03:08 PM   #4
Rivet Master
 
DanielB's Avatar
 
1974 31' Excella 500
Charleston , South Carolina
Join Date: Nov 2010
Posts: 1,073
Blog Entries: 8
So this is what I have found:

At Wire and Cable they say "The single most important component of a wire or cable is its insulation" and "2. All outdoor wiring should be of type XLP/XHHW, TC (Tray cable), USE-2 or similar outdoor UV (sunlight) resistant insulation."

This link says what all the Xs, Ls and whatnot stand for: http://lib.store.yahoo.net/lib/wind-...decorner66.pdf
__________________
As I grow older, I pay less attention to what men say. I just watch what they do.
- Andrew Carnegie
DanielB is offline   Reply With Quote
Old 11-27-2012, 03:50 PM   #5
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Fantastic! Thanks so much... now I know what to ask for! Maybe home depot even has some of it and they just don't know that it is UV rated as that is part of one of the greater classifications. They do have underground cable, so maybe it is the USE-2 and they just don't know anything about the UV that might be part of that.

That PDF you posted says, "USE: Underground Service Entrance • 75°C, wet insulation rating • Heat and moisture resistant • Sunlight resistant, but not marked as such."

And "USE-2: As above, but with a 90°C, wet insulation rating. The most commonly recommended cable for PV module wiring."

Thanks again for the help!
CA_Tallguy is offline   Reply With Quote
Old 11-27-2012, 05:31 PM   #6
Rivet Master
 
2015 28' Flying Cloud
Durango , Colorado
Join Date: Oct 2010
Posts: 623
I've purchased solar cable and connectors from Solar Penny SolarPenny Renewable Energy Equipment in the USA.
__________________
Safe Travels,
Joe & Joan Donnaway
Durango, CO
JamuJoe is offline   Reply With Quote
Old 11-27-2012, 06:06 PM   #7
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Thanks, JamuJoe - I looked at that site just now and I think they only have #10 cable. They have MC3 and MC4 but I think they are still 10 gauge. That is the minimum size cable I would use but if I can find something a bit thicker that would allow me to avoid losing some of the juice in the feed to the controller.
CA_Tallguy is offline   Reply With Quote
Old 11-27-2012, 06:25 PM   #8
Rivet Master
 
1994 30' Excella
Mississauga , Ontario
Join Date: Jun 2004
Posts: 1,244
If you are running 200 watt panels at 48 volts that's a maximum of about 4 amps.
the 10 guage solar wire with mc4 connectors from panel to controller would be plenty.
The controller should be as close to the batteries as possible to minimize the length of heavy battery cable required.
Just a question for you guys; I assume that there should be a disconnect in the line from the panels to the controller?
Al
__________________
Al and Jean

TAC ON-3
BigAl is offline   Reply With Quote
Old 11-27-2012, 07:34 PM   #9
4 Rivet Member
 
steverino's Avatar
 
2018 30' Classic
Ivins , Utah
Join Date: Aug 2009
Posts: 424
Images: 9
I did install a disconnect on the feed from the panels to the controller. As the feed comes down the refrigerator flue, I found a convenient place to mount it behind the refrigerator access panel.

Steve
steverino is offline   Reply With Quote
Old 11-27-2012, 08:56 PM   #10
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
From what I have read, a disconnect/breaker should be installed on both panel and battery legs. I may just put a heavy fuse in the lines for now though. I'm not sure where I could put a mini breaker box to serve both except for next to the controller. I'm even having some issues deciding where to put the controller as there are not a lot of places to put it close to the batteries ( if I keep the front location for them).

Back to the wire question, I swung by Home Depot and asked about 5 or so options on the list posted previously and they didn't have any.

And on #10 size, yeah that would be OK I just wouldn't mind springing for something better for the main panel run. 10 is the absolute smallest I'd use.

I'll be making a run to some electric supply houses tomorrow.
__________________
WBCCI #1711
Texas Gulf Coast Unit, Texas Airstream Harbor
Angelina National Forest, Zavalla, TX
CA_Tallguy is offline   Reply With Quote
Old 11-27-2012, 10:30 PM   #11
4 Rivet Member
 
ddruker's Avatar
 
1999 27' Safari
Palo Alto , California
Join Date: Apr 2012
Posts: 321
Images: 1
48 volts is the way to go. Higher voltage, lower amps are always better, up to the limit of your charge controller.

There are plenty of calculators available on the internet that will tell you how much power loss you will see for the length of your run at various cable gauge sizes. Up to you how much you want to spend to wring out the very last watts out of your panels.

I think you would be fine with rubber SOOW cable from home depot - that's what I installed for my 290 watt, 70 volt system. Are you really expecting your install to last 20 years? Here's some language about SOOW -

Type SOOW Flexible Cords are designed for extra hard usage on industrial equipment, heavy tools, battery chargers, portable lights welding leads, marine dockside power, power extensions and mining applications.

Seems to me that if it's good enough for dockside power and mining, it will last for plenty long enough on top of my trailer...
__________________
- Dan

1999 27' Airstream Safari + 2011 Mercedes GL 350 Turbo-diesel + 2021 Ford F150 Platinum Hybrid w/ 7,200 Watt Pro Power
ddruker is offline   Reply With Quote
Old 11-28-2012, 08:18 AM   #12
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Thanks Dan! I'll look into the SOOW. I figured some of the stuff would be OK but the people at the store really had no clue about the ratings. It sure would be nice if they had some of the descriptions like that at the store.
CA_Tallguy is offline   Reply With Quote
Old 11-28-2012, 01:27 PM   #13
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
I'm becoming discouraged. I've been back to Home Depot, Lowes, and also to two electrical supply houses. I am shocked it is so hard to find outdoor cable. But it may be a California thing as they say that most outdoor cable is run in conduits here. I ran though 5 or 6 options listed and nada. One supply house normally stocked USE-2 in #10 but they were out.

I'm currently in the Palm Springs area so the selection isn't as good as what I might find in LA. Heading out that way is probably my next step, after researching online options after this post. I need to head to LA anyway for something else. Or, I might have my father pick up some marine cable since he is down in San Diego today.

I am posting photos of the cable charts from Lowes, which I think are identical to the Home Depot charts. They did have THWN-2 but I have not been able to tell if it is UV rated based on the PDF posted earlier in the thread and a few other quick web searches. I'm feeling like USE-2 is what I am after, or some other #6 or #8 cable that is UV rated.

Lowes did have SJOOW, but not SOOW. The PDF says that the SJ is "junior" hard service, vs "hard service" for just the SOOW. They only had #10 though. I may fall back to that as I'm getting desperate and I am itching to hook these panels up! I would really like to go with heavier gauge though to wring every last watt out.

Click image for larger version

Name:	photo 1(4).JPG
Views:	145
Size:	178.1 KB
ID:	173490

Click image for larger version

Name:	photo 2(4).JPG
Views:	195
Size:	177.2 KB
ID:	173491
CA_Tallguy is offline   Reply With Quote
Old 11-28-2012, 01:55 PM   #14
Rivet Master
 
AWCHIEF's Avatar
 
2006 23' Safari SE
Biloxi , Mississippi
Join Date: Nov 2011
Posts: 8,278
Images: 33
If you have a West Marine nearby check them for Marine Cable. It is UV protected. I have used it exposed on the deck for years on boats and have never had an issue with cover breakdown. I have about 50 ft that I salvaged from my last boat and plan on using it when I get around to installing my panels on the Bambi II.
__________________
MICHAEL

Do you know what a learning experience is? A learning experience is one of those things that says "You know that thing that you just did? Don't do that."
AWCHIEF is offline   Reply With Quote
Old 11-28-2012, 02:12 PM   #15
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Just talked to another electric supply and they also said it would be hard to find outdoor UV cable and he said "it ain't legal" here in CA. It is hard to imagine that is so, as I know that I've seen overhead cables strung many times here. Maybe that was only done under older codes though. They did say they special order some other stuff he couldn't remember what it was called for some solar guys though.

I've just checked West Marine's website and they have some stuff that looks promising -- they have 6-2, 8-2, and 10-2 "safety marine cable" for $5, $3, and $1.63 per foot respectively. Separately, the have just "duplex cable" that is about the same price. I don't know what the difference is between that and "safety" cable. They also have single conductor cable in #8 and #10 for $1.20 and $0.74 respectively.

The local store says they have a good selection in stock.

The cable is made by Ancor and I can't find specs that say UV resistant but I've seen some marketing copy on some websites that says it is....

"Ancor produces a wide line of specially designed marine grade electrical products engineered for the demands of marine environment and elements faced out on the water. It is important to remember that marine electrical systems are much different than standard electrical wiring. All parts in the wiring process must be waterproof, UV ray and corrosion resistant, as well as strong enough to stand up to extreme vibration and flexing. Ancor wiring components exceed these standards."

This is starting to sound like a good option that I might be able to get locally.
CA_Tallguy is offline   Reply With Quote
Old 11-29-2012, 08:59 PM   #16
4 Rivet Member
 
ddruker's Avatar
 
1999 27' Safari
Palo Alto , California
Join Date: Apr 2012
Posts: 321
Images: 1
Wierd. All three of the Home Depot stores near Palo Alto where I live carry SOOW cable, in lots of different gauges and conductor configurations.
__________________
- Dan

1999 27' Airstream Safari + 2011 Mercedes GL 350 Turbo-diesel + 2021 Ford F150 Platinum Hybrid w/ 7,200 Watt Pro Power
ddruker is offline   Reply With Quote
Old 11-29-2012, 11:28 PM   #17
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Yeah they only seemed to have the SJ variety here in Palm Springs and then only down to 10 gauge I think.

I ended up with marine cable as described from West Marine. (Trying to attach pic of selection from phone.) I'm very happy with it though it was expensive. Everything they have is uv rated. I got the 8-2 cable for about $3 per foot. In reality, only 6 feet or maybe less will be exposed so it would be possible to have a junction/combiner to transition to other cable just inside or right before the inside drop.

I have also been thinking about using trempro to attach it to the roof and another cable type might have worked fine if it were embedded and covered in it. That sounds potentially messy so I'm unsure about the idea.

Tomorrow will be running the cable and not sure how that will go and if trempro is the right way to adhere... And not sure what I am going to face with the fridge vent. Hope it all makes sense when I start poking around. If anyone has advice, please share!
Attached Thumbnails
Click image for larger version

Name:	image-3993323664.jpg
Views:	117
Size:	472.9 KB
ID:	173593  
__________________
WBCCI #1711
Texas Gulf Coast Unit, Texas Airstream Harbor
Angelina National Forest, Zavalla, TX
CA_Tallguy is offline   Reply With Quote
Old 12-04-2012, 04:26 PM   #18
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
Just wanted to correct myself about the wire types at Home Depot. The chart there is in fact different than Lowes and a pic is attached. They do have the SO type wire. It looks like it is 3 and 4 conductor but does go down to 6 guage. Didn't check the price though since I already went with marine cable.
Attached Thumbnails
Click image for larger version

Name:	image-95719221.jpg
Views:	106
Size:	549.4 KB
ID:	173901   Click image for larger version

Name:	image-3452511605.jpg
Views:	105
Size:	570.3 KB
ID:	173902  

__________________
WBCCI #1711
Texas Gulf Coast Unit, Texas Airstream Harbor
Angelina National Forest, Zavalla, TX
CA_Tallguy is offline   Reply With Quote
Old 12-04-2012, 04:35 PM   #19
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
One note about the marine cable. It is finely stranded, much more finely than what I think was some 8 gauge THHN cable I bought previously at Home Depot for my truck. That makes it pretty flexible. I would guess that the SO cable is pretty flexible too since it is kind of a power cord type application.

I vaguely recall reading in my research that electricity flows on the outside of the conductors or something so I wonder if the fine strands are better for that? I suppose there may be a purpose to choosing heavy strands over fine but maybe not and it is just a quality thing. [EDIT: upon further research it seems it may just have more to do with how flexible the cable is.] Maybe there is also a difference between AC and DC in how it travels on the wire and if fine vs thick strands matters. Of course, household wiring is generally not stranded for common romex runs and that is AC. [EDIT: I researched this concept of power flowing on the outside a bit more and it is called the "skin effect" and applies more to AC than DC]

The welding cable I got for the 12 volt run between the solar controller and the battery bank is also finely stranded.
CA_Tallguy is offline   Reply With Quote
Old 12-05-2012, 03:07 PM   #20
4 Rivet Member
 
CA_Tallguy's Avatar
 
1977 31' Excella 500
Zavalla , Texas
Join Date: Jul 2012
Posts: 497
One more little note -- although the Ancor brand #8 cable from West Marine was about $3 a foot, it was two conductor so it looks like it wasn't too much more expensive than the #10 single conductor wire sold by solar merchants online ($1 to $2 per foot for single conductor). Northern Arizona Solar has an outdoor rated #8 two conductor for $2.26/foot.

And West Marine had #8 single conductor cable for a bit over a buck a foot too.
CA_Tallguy is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.