My house and yours has a bonded neutral inside the breaker box.
I have all my electronics going through UPS backups. All the UPS's complain of "no ground" because my old house has half the outlets ungrounded. Adding an earth ground makes no difference. I wonder if adding a bonded neutral plug into the unused outlet would trick the fault into going away?
|
If you connect ground and neutral inside of a house, then the ground conductor has the ability to carry current equally to the neutral. There could be hot surfaces of equipment that could be shocking if a person provided a path through their body to earth ground by touching it.
I would not do this.
Also, national electrical code prohibits bonding ground and neutral together anywhere except at the main distribution panel. There are instances where additional/extra earth ground can be provided at pieces of equipment, but not bonded to neutral.
ps:
So you will know where I'm coming from;
I am not a licensed electrician. I was, before retiring, a licensed (mostly industrial/commercial/institutional buildings) general contractor. I have read a large portion of the national electric codes, enough to design, draw plans for, and install residential electrical system. I have personally designed and wired several houses for myself, family, and friends that have passed inspection.