Old 07-12-2020, 01:09 PM   #21
4 Rivet Member
 
Currently Looking...
Lebanon , Tennessee
Join Date: Jul 2017
Posts: 250
smsasf, a 2 week wait is not bad considering most CW service departments are booked solid for a month or more. I went in to an AS dealer in...someplace out west, a larger and well known dealership, while traveling. I had ripped off my black waste valve and needed a bit of RV plumbing done. At most a 1 hour job. I know because that is how long it took me to do it after the dealership said, sure, no problem, we are five months back logged and will then schedule you. This after I noted I was traveling. They also did not have the part I needed. So I did it myself in the parking lot of a plumbing supply outlet.
Rzrbrn is offline   Reply With Quote
Old 07-12-2020, 01:30 PM   #22
3 Rivet Member
 
Tifton , Georgia
Join Date: Apr 2018
Posts: 148
Go to this site and read it. It will tell you how to safely ground your inverter with a N-G bond plug. You can make it yourself for about $3. Also you might want to subscribe to the No-Shock-Zone. Mike is recognized at THE authority on RV electric (AC and DC). Too many "experts" on forums know enough to get someone hurt or worse.

http://noshockzone.org/generator-gro...utral-bonding/
xyzabe is offline   Reply With Quote
Old 07-12-2020, 03:55 PM   #23
Rivet Master
 
1988 32' Excella
Robbinsville , New Jersey
Join Date: May 2012
Posts: 3,161
Quote:
Originally Posted by MaineStreamer View Post
So, I have learned from this conversation that I should not be putting plastic leveling pads under my stabilizer jacks and the front jack for the trailer, because the jacks serve as ground connections for the trailer. That is news to me.
I read this entire thread and didn't see anything that mentioned you shouldn't put plastic leveling pads under your stabilizer jacks and the front jack for the trailer so they could serve as a ground. It was only stated the stabilizer jacks and the front jack for the trailer had the potential to provide a ground.
Wazbro is offline   Reply With Quote
Old 07-12-2020, 05:10 PM   #24
Rivet Master
 
2018 25' International
Slidell , Louisiana
Join Date: Sep 2017
Posts: 3,725
Quote:
Originally Posted by xyzabe View Post
Go to this site and read it. It will tell you how to safely ground your inverter with a N-G bond plug. You can make it yourself for about $3. Also you might want to subscribe to the No-Shock-Zone. Mike is recognized at THE authority on RV electric (AC and DC). Too many "experts" on forums know enough to get someone hurt or worse.

http://noshockzone.org/generator-gro...utral-bonding/
FYI, Ground-Neutral Bonding links ground and neutral but does not actually ground the generator. Travel trailers using generator power are safe without an effective earth ground though by design. There is no harm done by employing a ground but safety is not enhanced by any significant degree with a ground.
BayouBiker is offline   Reply With Quote
Old 07-12-2020, 07:28 PM   #25
Wolfwhistle
 
Fair_Enough's Avatar
 
Margaritaville , Banana Republic
Join Date: Jul 2018
Posts: 705
From OSHA:

Grounding Requirements for Portable and Vehicle-mounted Generators
Under the following conditions, OSHA directs (29 CFR 1926.404(f)(3)(i)) that the frame of a portable generator need not be grounded (connected to earth) and that the frame may serve as the ground (in place of the earth):

The generator supplies only equipment mounted on the generator and/or cordand plug-connected equipment through receptacles mounted on the generator, § 1926.404(f)(3)(i)(A), and
The noncurrent-carrying metal parts of equipment (such as the fuel tank, the internal combustion engine, and the generator’s housing) are bonded to the generator frame, and the equipment grounding conductor terminals (of the power receptacles that are a part of [mounted on] the generator) are bonded to the generator frame, § 1926.404(f)(3)(i)(B).
Thus, rather than connect to a grounding electrode system, such as a driven ground rod, the generator’s frame replaces the grounding electrode.

If these conditions do not exist, then a grounding electrode, such as a ground rod, is required.

If the portable generator is providing electric power to a structure (emphasis, mine) by connection via a transfer switch to a structure (home, office, shop, trailer, or similar) it must be connected to a grounding electrode system, such as a driven ground rod. The transfer switch must be approved for the use and installed in accordance with the manufacturer’s installation instructions by a qualified electrician.

Grounding requirements for generators connected via transfer switches are covered by Article 250 of the National Electrical Code (NEC)
WW
__________________
Is taking it all with you, really getting away from it all?
Fair_Enough is offline   Reply With Quote
Old 07-12-2020, 09:47 PM   #26
3 Rivet Member
 
2020 20' Bambi
Clayton , North Carolina
Join Date: May 2020
Posts: 229
Quote:
Originally Posted by Rzrbrn View Post
smsasf, a 2 week wait is not bad considering most CW service departments are booked solid for a month or more. I went in to an AS dealer in...someplace out west, a larger and well known dealership, while traveling. I had ripped off my black waste valve and needed a bit of RV plumbing done. At most a 1 hour job. I know because that is how long it took me to do it after the dealership said, sure, no problem, we are five months back logged and will then schedule you. This after I noted I was traveling. They also did not have the part I needed. So I did it myself in the parking lot of a plumbing supply outlet.
Rzrbrn, thanks for sharing the experience. I suppose I should get used to this. Obviously, these service wait periods are part of the down-side of RV ownership that is not clear when researching purchase. Well, I suppose if you dig deep enough you can discover. I suppose it is also a warning to prepare yourself yo become self sufficient. I fear having something major happen and not having access to an expensive RV for months because you cannot get service. And I wonder, what if it is warranty repair, per the new trailer warranty, am I still looking at months on a wait list. If that is the case and I experience having to wait months for warranty repairs I might start to regret having made the purchase.
smsasf is offline   Reply With Quote
Old 07-12-2020, 10:04 PM   #27
Rivet Master
 
2018 25' International
Slidell , Louisiana
Join Date: Sep 2017
Posts: 3,725
Just remember a trailer is just a mini home on wheels. Nearly all the major repairs except maybe the aluminum body can be done by automotive, welding, Home HVAC, home appliance. electrical, plumping folks.

This may just be me, but I'm hell bent on not dragging my trailer back to a dealer if I can help it.
BayouBiker is offline   Reply With Quote
Old 07-13-2020, 06:42 AM   #28
Iron tepee #35
 
1993 34' Excella
andalusia , Illinois
Join Date: Apr 2016
Posts: 95
Once again, lightning seeks the earth, power from a generator does not. The current from your generator seeks to return to its source (the generator). You should be safely grounded through your three prong (positive, negative, ground) cord connection. In most cases, a ground rod’s useful purpose is to provide an effective path to earth for lightning.
Grounding is The most misunderstood and debated section of the National electric code, and while I’m not an electrical engineer, I am a licensed Master Electrician. I’m sure someone will disagree with my post anyway, cause that’s what people do here.
mikeoxlong is offline   Reply With Quote
Old 07-13-2020, 08:11 AM   #29
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,545
Quote:
Originally Posted by mikeoxlong View Post
Once again, lightning seeks the earth, power from a generator does not. The current from your generator seeks to return to its source (the generator). You should be safely grounded through your three prong (positive, negative, ground) cord connection. In most cases, a ground rod’s useful purpose is to provide an effective path to earth for lightning.
Grounding is The most misunderstood and debated section of the National electric code, and while I’m not an electrical engineer, I am a licensed Master Electrician. I’m sure someone will disagree with my post anyway, cause that’s what people do here.
Very well said, as a licensed electrical contractor myself I have spent countless hours trying to explain this simple fact to laymen and fellow electricians alike, many of whom do not get it. Sometimes I think it's hard for people to grasp a very simple fact because they expect it to be complex.
If current cannot return to it's source it will not flow, there cannot be a circuit if it is not complete back to the source. It will take every available path proportionately to it's conductance and every single electron will return to it's source, none of it "dissipates into the earth" or "gets used up".
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 07-13-2020, 08:21 AM   #30
Rivet Master
 
aftermath's Avatar
 
2006 25' Safari FB SE
Spokane , Washington
Join Date: Sep 2009
Posts: 1,857
I am a Honda guy and have been using mine without an extra ground. 15 years, two trailers and the same generator sitting on the ground. I find these discussions confusing. It is like the run with the propane on argument. Someone reads something somewhere and they become experts. If the major generator manufacturers don't require grounding, who are we to say that they are ALL wrong? Would they sell millions of generators knowing that you could electrocute yourself if you don't ground them? If they design a fridge to run down the road with the propane on, would they ever do this if they expected it to explode on the highway? AND....where is the actual data to support these supposedly dangerous acts?


The OP was not sure so he asked the question and that was the right thing to do. The answer is simply, no you don't have to ground the generator.
aftermath is offline   Reply With Quote
Old 07-13-2020, 08:35 AM   #31
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,653
Blog Entries: 1
In the real world, you're much more likely to regret pounding a 6' copper rod into a campground space than to do nothing with the generator. Especially when you hit the underground water pipe or power line.
If you're on your own property, and it makes you feel better, pound away.
Mollysdad is offline   Reply With Quote
Old 07-13-2020, 08:37 AM   #32
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
In response, a final word on grounding:

A point of great importance would be first to know: what is the capacity of the earth? And what charge does it contain if electrified? Though we have no positive evidence of a charged body existing in space without other oppositely electrified bodies being near, there is a fair probability that the earth is such a body, for by whatever process it was separated from other bodies — and this is the accepted view of its origin — it must have retained a charge, as occurs in all processes of mechanical separation.
-Nikola Tesla
markdoane is offline   Reply With Quote
Old 07-13-2020, 09:05 AM   #33
Rivet Master
 
mefly2's Avatar
 
2015 25' FB Eddie Bauer
2013 25' FB Eddie Bauer
2012 20' Flying Cloud
Small Town , *** Big Sky Country ***Western Montana
Join Date: Feb 2010
Posts: 2,860
No grounding with Honda gens for 10 years ... no skin leakage detected.
__________________
2015 25' Eddie Bauer Int'l FBQ / 2023 Ford Lightning ER
2022 Ford F350 6.2 V-8; equalizer hitch + Shocker air hitch
Honda Eu3200; AIR# 44105; formerly WBCCI 2015.1
Terminal Aluminitis; 2-people w/ 3+ dogs
mefly2 is offline   Reply With Quote
Old 07-13-2020, 09:14 AM   #34
4 Rivet Member
 
2019 28' Flying Cloud
Dripping Springs , Texas
Join Date: Dec 2019
Posts: 328
The only "grounding" I do with a generator is to connect the ground and neutral wires together on the extension cord I'm using to charge. This is because the surge protector otherwise won't permit charging (it detects an un-grounded condition and the generator output is ignored.)
Kalashnikov is offline   Reply With Quote
Old 07-13-2020, 10:01 AM   #35
diesel maniac
 
ITSNO60's Avatar
 
Airstream - Other
Tucson , AZ
Join Date: May 2017
Posts: 2,545
Quote:
Originally Posted by Mollysdad View Post
In the real world, you're much more likely to regret pounding a 6' copper rod into a campground space than to do nothing with the generator. Especially when you hit the underground water pipe or power line.
If you're on your own property, and it makes you feel better, pound away.
Make that 8 feet, standard ground rods are 8 feet. Here in Arizona they can sometimes take an hour or more apiece to install using a demolition hammer fitted with a ground rod driving attachment. We never drive them without first getting a Blue Stake.
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 07-13-2020, 10:23 AM   #36
"Cloudsplitter"

 
2003 25' Classic
Houstatlantavegas , Malebolgia
Join Date: Jun 2007
Posts: 20,000
Images: 1
Quote:
Originally Posted by ITSNO60 View Post
Very well said, as a licensed electrical contractor myself I have spent countless hours trying to explain this simple fact to laymen and fellow electricians alike, many of whom do not get it. Sometimes I think it's hard for people to grasp a very simple fact because they expect it to be complex.
If current cannot return to it's source it will not flow, there cannot be a circuit if it is not complete back to the source. It will take every available path proportionately to it's conductance and every single electron will return to it's source, none of it "dissipates into the earth" or "gets used up".
That is why the lightning ground 'strike' you actually can see is most often the ground reaching up to complete the circuit. ⚡️ 1001, 1002, 1003 boom.

Bob
🇺🇸
__________________
I’m done with ‘adulting’…Let’s go find Bigfoot.
ROBERT CROSS is offline   Reply With Quote
Old 07-13-2020, 05:28 PM   #37
3 Rivet Member
 
2020 20' Bambi
Clayton , North Carolina
Join Date: May 2020
Posts: 229
“Uncle”

As the original poster I recall when we boys wrestled when I was a kid and the boy about to win would force to boy about to be defeated to say “uncle” to give in. I don’t recall why. But I say “uncle”. As an aside, my adult son graduated top of his class in the Navy Aviation Electronics School down in Pensecola, FL some years back and has mostly worked in commercial and residential electrical and power and controllers and such ever since. His cable work into big boxes and controllers is like art. And he seems to be able to built anything. Anyway, he told me early on that I did not need to ground it. But of course, being the older and wiser (?) I felt I needed to ask some sages on the forum. I won’t use a ground even though I bought the rebar and wire. And if I get electrocuted while starting up the generator in a rain storm while barefoot nobody on the forum will be the wiser. Thanks to all, my confidence is raised.
smsasf is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
is an generator wit an inverter necessary?? Buzz1967 Boondocking 6 04-30-2018 06:49 PM
Is a Generator Necessary for Alaska Travel? kscherzi On The Road... 38 01-31-2016 05:56 AM
Grounding of generator Bait guy Generators & Solar Power 10 07-30-2013 11:18 AM
generator grounding to truck wolf146 Generators & Solar Power 11 05-24-2012 05:24 PM
generator grounding JK3500 Generators & Solar Power 23 06-19-2007 03:59 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 01:27 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.