How many series, how many parallel?

Looks like ten 100W solar panels on the roof is fairly common. If you have such an array, how are you wiring them? Would you do it any differently if you were to do it over again?
__________________
David Lininger, kb0zke
7490
2021 Flying Cloud 30 RBQ
kb0zke is offline   Reply With Quote
Old 01-31-2025, 10:38 PM   #2
Site Team
 
richard5933's Avatar

 
1994 25' Excella
Waukesha , Wisconsin
Join Date: Sep 2020
Posts: 6,443
Images: 5
We have four 100w panels on the roof, all laying flat, two along each side. The two on each side are wired in series, and the two pairs are wired parallel to each other.

The main reason I chose series/parallel is that it raises the voltage and helps eliminate voltage drop - it also allows a slightly smaller conductor.

Kind of a crap shoot which two panels were in series and which two were in parallel though. So, I put the two on each side in series assuming that the sun would usually be coming/going over our trailer in that way since most of the time we end up parked north/south on our favorite campgrounds.
__________________
Richard
11018
1994 Excella 25 'Gertie' Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8 'Bert'
1974 GMC 4108a - Custom Coach Land Cruiser 'The Bus' (Sold)
richard5933 is offline   Reply With Quote
Old 02-01-2025, 06:49 AM   #3
2 Rivet Member
 
2025 25' Trade Wind
Beaver Dam , Wisconsin
Join Date: Jan 2025
Posts: 78
Ten 100 watt panels on an RV is not very common. That would be 1000 watts.

Fewer higher capacity panels are becoming common for arrays that large. Some install 300 watt or so panels. Bigger panels may not work well on a curved roof.

My 2025 Trade Wind has 600 watts on the roof. I think they are longer, flexible panels. Still investigating.

1000 watts of 20 volt panels could deliver 50 amps. That requires 8 AWG cable or larger.

Putting them in serial pairs would reduce current to 25 amps at 40 volts. 25 amps requires 10 AWG gauge cable or larger. A solar preinstall may have 10 AWG cable already threaded through the roof.
PaulBristol is offline   Reply With Quote
Old 02-01-2025, 06:54 AM   #4
3 Rivet Member
 
2021 25' International
Plymouth , Michigan
Join Date: May 2021
Posts: 143
Quote:
Originally Posted by richard5933 View Post
We have four 100w panels on the roof, all laying flat, two along each side. The two on each side are wired in series, and the two pairs are wired parallel to each other.

The main reason I chose series/parallel is that it raises the voltage and helps eliminate voltage drop - it also allows a slightly smaller conductor.

Kind of a crap shoot which two panels were in series and which two were in parallel though. So, I put the two on each side in series assuming that the sun would usually be coming/going over our trailer in that way since most of the time we end up parked north/south on our favorite campgrounds.
I did the same arrangement with my 4 panels. Was concerned about 4 panel in parallel voltage drop with existing AS roof wire to MPPT gauge.
I also noted too, that with this config the solar controller to turns on sooner. There is a min voltage threshold for the MPPT to turn and turn off..so I noted that the array came online earlier in the day (took less light to reach threshold voltage) and same for system cutout later in day. But I’m sure that is traded off for partial shade inefficiency with series / parallel. 1 panel in shade effecting partner panel’s output in sun.
__________________
2021 International 25FBQ converted to FBT
2022 F-350 7.3 SRW CC LB
2018 F-350 6.7 SRW CC SB
SVTRIDE is offline   Reply With Quote
Old 02-01-2025, 08:33 AM   #5
2 Rivet Member
 
2020 25' Flying Cloud
Woodinville , Washington
Join Date: May 2022
Posts: 52
Another reason to consider is shading. Shading varies throughout the day and across the roof, especially on a moving RV. I have 8 x 100W Renogy panels on my 25' Airstream in a 4S2P configuration, which works well. It harnesses solar energy from sunrise to sunset, with minimal amounts during shoulder times. I'll be changing it to 2S4P for better shade efficiency, as my two air conditioning units partially shade the panels.
Nishad is offline   Reply With Quote
Old 02-01-2025, 08:46 AM   #6
4 Rivet Member
 
2025 25' Flying Cloud
2024 Interstate 19
Noblesville , Indiana
Join Date: Jun 2016
Posts: 278
10 100watt panels on the roof of any airstream 'is not' common. SMH
vanderwielen is offline   Reply With Quote
Old 02-01-2025, 09:25 AM   #7
Rivet Master
 
2021 30' Flying Cloud
Sioux Falls , South Dakota
Join Date: Mar 2011
Posts: 1,609
I had three 365W panels on the Reflection, and lacked only about 2" of being able to put the fourth one on. Last year, on our way to Escapade, we spent several days boondocking with those panels feeding out two 24V 200AH batteries. We had a 16 cf residential refrigerator and used the microwave and electric skillet just as if we were plugged in. No problems at all. Batteries never went below 60%.


The reason for asking now, even though I'm not going to do the upgrade until later, is that I want to do something with my current solar controller. It is a Victron, but no bludtooth, and just stuffed into a corner. There also is no disconnect between the panels and the controller. If I'm going to remount it I may as well add the disconnect and get the larger controller now.
__________________
David Lininger, kb0zke
7490
2021 Flying Cloud 30 RBQ
kb0zke is offline   Reply With Quote
Old 02-01-2025, 10:05 AM   #8
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 16,855
Hi

If you go to series connections, you need to make sure your controller will handle the max output voltage of the "stack". It's not always obvious just how high that voltage actually can be. We tend to focus on the loaded / max power output voltage. A *very* rough starting point for the sort of panels we tend to use would be 32V.

Why mention this? If you are shopping for a new solar controller, and *might* go series .... bump up to that higher voltage unit. Better to have some "room just in case".

Bob
uncle_bob is offline   Reply With Quote
Old 02-01-2025, 10:57 AM   #9
Rivet Master
 
2021 30' Flying Cloud
Sioux Falls , South Dakota
Join Date: Mar 2011
Posts: 1,609
That's my thinking, Bob. I could just buy the biggest Victron I can find and be fine, but I suspect that doing so may result in spending far more than necessary. I also don't want to buy one and then find that it is slightly too small. That's why I'm asking the experts.


I've gotten two suggestions: 2s5p and 5s2p. Each have some good arguments. Any preferences?
__________________
David Lininger, kb0zke
7490
2021 Flying Cloud 30 RBQ
kb0zke is offline   Reply With Quote
Old 02-01-2025, 11:09 AM   #10
Rivet Master
 
JeffKim's Avatar

 
2023 25' Globetrotter
2021 16' Bambi
Forest Lake , Minnesota
Join Date: Mar 2021
Posts: 1,953
A clarification, your solar wiring is 8AWG.

Maybe telling you what you already know department:

It sounds like you're trying to plan ahead and get a controller beefy enough to handle 10 panels on the roof and for now has the Smart capability. It's a pretty easy swap BTW.

Somebody tell me if I'm wrong: most 100W panels are in the 24V open circuit and 5A short circuit range. Looking at the scenarios, if you go with 5 in series connected in parallel that's roughly (5x24V) = 120V and 2x5A = 10A. All connected in parallel is 24V and 5Ax10 = 50A. However, the wire size calculator says 20' is about all you can go RT at 50A without rewiring, so doesn't seem like a good option. With 8 panels and 40A, possibly.

Soo... with the series/parallel at 120V/5A a Smart 150|35 should be fine (a Smart version of the standard issue 150|35). With the all parallel then there's a 100|50 ($184) version. Covering all bases is 150|60 but then it's about twice the cost ($350) of the 150|35 ($184).
__________________
2023 Globetrotter 25FBT "Curly"
2017 Audi Q7 3.0T
WBCCI 6343
JeffKim is offline   Reply With Quote
Old 02-01-2025, 11:14 AM   #11
2 Rivet Member
 
2020 25' Flying Cloud
Woodinville , Washington
Join Date: May 2022
Posts: 52
https://youtube.com/@cleversolarpower?feature=shared

https://youtube.com/@exploristlife?feature=shared

Both excellent resources.
Nishad is offline   Reply With Quote
Old 02-01-2025, 12:08 PM   #12
Rivet Master
 
JeffKim's Avatar

 
2023 25' Globetrotter
2021 16' Bambi
Forest Lake , Minnesota
Join Date: Mar 2021
Posts: 1,953
If anyone is following along, missed the 2s5p. That's 5x5A = 25A and 2x24V=48V and 8AWG is plenty. A 100|30 ($128) would be adequate. Or maybe I'm all wet?

With this configuration, what is the effect of shading?
__________________
2023 Globetrotter 25FBT "Curly"
2017 Audi Q7 3.0T
WBCCI 6343
JeffKim is offline   Reply With Quote
Old 02-01-2025, 12:46 PM   #13
4 Rivet Member
 
1985 31' Excella
st. Paul , mn
Join Date: May 2007
Posts: 263
A lot depends on what your upgrades are going to be .

One is higher voltage = lower gauge wire , now the voltage of the system - charge controller , batteries , inverter etc.

I've been doing alternative energy stuff since the 70s , it use to be stay under 48 volts - because arcing becomes an issue --- seems that has been left behind , and I do not have an answer for the higher voltages these day [ being ok ] ?

So seems choices are 24v or 48v , then lots of gear forces a choice of locking you into picking --- lots of gear [ like charge controllers will do 12v or 24v , but do not do 48 & below ? ] .

Another thing to research is shading , is helped or hindered by series or parallel , so depending on shading of at min. other things on the roof ?

Seems as though your current batteries are doing what you want - how are they wired - for 24v ?

I choose to stay at 24v for my trailer , if I was going to like a large class A - i would give 48v more thought ?

Victron has a BlueTooth add-on for your controller .

You can also use multiple Victon controllers - so just adding another for extra capacity .
__________________
85 Excella , 31' , electric brakes , R. twin [ would like it to be a single ] , future upgrades , composting toilet [ replace black water tank with a 2nd fresh ] , solar power , instant hot water heater .
Tow 94 Dodge Ram , 4x4 , Cummins , AT .
JohnTF is offline   Reply With Quote
Old 02-01-2025, 01:45 PM   #14
Jum
3 Rivet Member
 
Jum's Avatar
 
1975 Argosy 26
Louisville , Kentucky
Join Date: Jan 2024
Posts: 158
Quote:
Originally Posted by JeffKim View Post
If anyone is following along, missed the 2s5p. That's 5x5A = 25A and 2x24V=48V and 8AWG is plenty. A 100|30 ($128) would be adequate. Or maybe I'm all wet?

With this configuration, what is the effect of shading?

You're looking at the PV side only, but the 100|30 is solar input 100volts max and charge output 30amps max. 1000watts at ~14volts is 71.4amps, so the controller would limit it to 30amps max.

I am putting 800W (8x100 Renogy) on our Argosy and using 2x 100|30 MPPT with the panels 2S2P to each controller.
Jum is offline   Reply With Quote
Old 02-01-2025, 02:32 PM   #15
Rivet Master
 
OrangeCrush's Avatar
 
2017 25' Flying Cloud
Longmont , Colorado
Join Date: Jan 2017
Posts: 839
Quote:
Originally Posted by JeffKim View Post
If anyone is following along, missed the 2s5p. That's 5x5A = 25A and 2x24V=48V and 8AWG is plenty. A 100|30 ($128) would be adequate. Or maybe I'm all wet?

With this configuration, what is the effect of shading?
That is what I would do. Partly to minimize shade impact but mostly because I would not want to be messing with 120V DC open circuit potential with 5 series panels. I agree the 8 Gauge is fine for this as rough numbers (50 ft RT, 5 amps per panel, .63ohms/1000ft) is 5*5*.63*50/1000 =0.788 volts drop. That results in an approximate .788/40 ~ 2% loss which is reasonable to me.
OrangeCrush is offline   Reply With Quote
Old 02-01-2025, 03:16 PM   #16
3 Rivet Member
 
1976 Argosy 28
Buford , Georgia
Join Date: Aug 2019
Posts: 164
Quote:
Originally Posted by uncle_bob View Post
Hi

If you go to series connections, you need to make sure your controller will handle the max output voltage of the "stack". It's not always obvious just how high that voltage actually can be. We tend to focus on the loaded / max power output voltage. A *very* rough starting point for the sort of panels we tend to use would be 32V.

Why mention this? If you are shopping for a new solar controller, and *might* go series .... bump up to that higher voltage unit. Better to have some "room just in case".

Bob
Yup, agreed..
strangepod is offline   Reply With Quote
Old 02-02-2025, 06:25 AM   #17
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 16,855
Quote:
Originally Posted by kb0zke View Post
That's my thinking, Bob. I could just buy the biggest Victron I can find and be fine, but I suspect that doing so may result in spending far more than necessary. I also don't want to buy one and then find that it is slightly too small. That's why I'm asking the experts.


I've gotten two suggestions: 2s5p and 5s2p. Each have some good arguments. Any preferences?
Hi

If you go with 5 panels in series and use the "32V" number, you are up at 160V max voltage. That's more voltage than anything I know of in the Victron lineup. The normal configurations (as noted above) would be 2s, and 4s ( so 24 V and 48V).

Is the "real number" for max voltage on your panels below 32V? Maybe it is. It might be 28V. You then are about 10V *under* the rating on the high voltage Victron. Do make sure that the number you use is for *your* minimum temperature. A number at 70F is *not* what you want to use. Voltage goes up as temperature goes down.

You can do the math on the cable loss. Your output will vary over a wide range with a trailer mounted array. How much do you want to spend going from 4% wire loss to 1%? The efficiency of your solar converter is "unknown" if you want a "good to < 2%" sort of number. Yes, if you go crazy, you can exceed the wire ratings.

Ideally, I'd design for >20% below any rating either on current or voltage. Once you get to 40% below, that's probably "enough".

Fun !!!

Bob
uncle_bob is offline   Reply With Quote
Old 02-02-2025, 11:42 AM   #18
Rivet Master
 
JeffKim's Avatar

 
2023 25' Globetrotter
2021 16' Bambi
Forest Lake , Minnesota
Join Date: Mar 2021
Posts: 1,953
Quote:
Originally Posted by Jum View Post
You're looking at the PV side only, but the 100|30 is solar input 100volts max and charge output 30amps max. 1000watts at ~14volts is 71.4amps, so the controller would limit it to 30amps max.

I am putting 800W (8x100 Renogy) on our Argosy and using 2x 100|30 MPPT with the panels 2S2P to each controller.
Thanks, yes I'm all wet. I thought the numbers corresponded to the PV side. Please ignore any of the advice above.

Some links to solar controller calculators I found:
https://www.victronenergy.com/mppt-calculator
https://explorist.life/solar-charge-...er-calculator/
__________________
2023 Globetrotter 25FBT "Curly"
2017 Audi Q7 3.0T
WBCCI 6343
JeffKim is offline   Reply With Quote
Old 02-02-2025, 05:13 PM   #19
Rivet Master
 
2021 30' Flying Cloud
Sioux Falls , South Dakota
Join Date: Mar 2011
Posts: 1,609
Thanks, everyone. I'm leaning toward the 2s5p arrangement, but I suspect that I'll be at or slightly above the capacity of the wire from the roof to the solar controller, and I suspect that running a new wire is not going to be easy. I'll see if I can figure out exactly what wire I have coming into the existing solar controller. That will at least let me know what the maximum current I can have from the new array.


From what I've been able to glean from various sources, an Airstream's curved roof cuts down on solar panel efficiency quite a bit, so the more capacity up there I can start with the more I'll actually have going into the batteries.


Any more suggestions or ideas?
__________________
David Lininger, kb0zke
7490
2021 Flying Cloud 30 RBQ
kb0zke is offline   Reply With Quote
Old 02-02-2025, 08:45 PM   #20
Site Team
 
richard5933's Avatar

 
1994 25' Excella
Waukesha , Wisconsin
Join Date: Sep 2020
Posts: 6,443
Images: 5
Quote:
Originally Posted by kb0zke View Post
Thanks, everyone. I'm leaning toward the 2s5p arrangement, but I suspect that I'll be at or slightly above the capacity of the wire from the roof to the solar controller, and I suspect that running a new wire is not going to be easy. I'll see if I can figure out exactly what wire I have coming into the existing solar controller. That will at least let me know what the maximum current I can have from the new array.

From what I've been able to glean from various sources, an Airstream's curved roof cuts down on solar panel efficiency quite a bit, so the more capacity up there I can start with the more I'll actually have going into the batteries.

Any more suggestions or ideas?
This is only true if you're installing the panels so they lay along the roof's curve. Mine are mounted with higher mounts on the outside edge to keep them flat, and this is how I've seen many people mount rigid panels on an Airstream. Of course if you're using flexible/non-rigid panels this is not an option. By mounting them flat the curve of the roof is taken out of the equation.
__________________
Richard
11018
1994 Excella 25 'Gertie' Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8 'Bert'
1974 GMC 4108a - Custom Coach Land Cruiser 'The Bus' (Sold)
richard5933 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Series, Parallel, or Series+Parallel solar panel wiring Nishad Generators & Solar Power 26 11-15-2024 08:26 PM
300 watts Parallel or 400 series/Parallel JoeHTP Generators & Solar Power 4 08-08-2020 04:21 PM
Battery hook up, parallel or series iamscuba2 Furnaces, Heaters, Fireplaces & Air Conditioning 4 08-15-2011 09:33 AM
Parallel not-alike honda eu series generators malimish Generators & Solar Power 26 02-04-2009 10:26 PM
Series or parallel benwd Batteries, Univolts, Converters & Inverters 52 11-03-2007 08:19 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:52 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.