I noticed that the circuit checker device that plugs into my electrical receptacle is not showing a Ground when the trailer is hooked up to my running Yamaha EF3000iSEB generator. There is a stud on the panel where I have hooked up a 2' stranded wire, wrapped it around a nail and stuck it into the ground.

Is there a more appropriate way to ground the generator or am I doing something wrong? What gauge wire is needed or do I need to use a steel spike?
__________________
Craig

AIR #0078
'01 2500hd ext. cab, 8.1 litre gas, 5 sp. Allison auto
3.73 rear end
Mag-Hytec rear diff cover
Amsoil Dual by-pass oil filtration system
Amsoil synthetics all around
265 watt AM Solar, Inc. system
davidz71 is offline   Reply With Quote
Old 01-28-2007, 11:55 AM   #2
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
I think you need to use a much longer nail, made out of copper.

Even then, I don't know if it will read properly on your tester because the ground and neutral are not bonded.
markdoane is offline   Reply With Quote
Old 01-28-2007, 12:10 PM   #3
Site Team
 
azflycaster's Avatar

 
2002 25' Safari
Dewey , Arizona
Join Date: Mar 2005
Posts: 15,618
Images: 62
Blog Entries: 1
local code will determine how long a rod you would need. You should be fine with 6 to 10 feet depending on soil conditions. markdoane raises an interesting question about the circut teater and not being tied together. In your home the ground is tied to nuetral at one point in the service pannel. The instructions for my Honda EU1000i recomend that you have a certified electrician perform any grounding required.
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is offline   Reply With Quote
Old 01-28-2007, 12:29 PM   #4
4 Rivet Member
 
Motoman's Avatar
 
2005 25' International CCD
1960 18' "Footer"
1959 26' Overlander
Riverside , California
Join Date: Oct 2006
Posts: 339
Images: 3
I agree with Markdoane, the tester will not indicate a proper ground if the neutral and ground are not bonded in the generator. I don't believe that driving any kind of ground rod into the earth will help at all unless you also bond the trailer to it or drive a separate ground rod into the earth for it. Lacking that you could bond the ground connection on the generator to the trailer and then see if it indicates properly.

The same question came up about a 10 KW WWII surplus generator that our local amateuir radio club uses. We protected the supply to the two 120/240 volt outlets with a 120/240 volt 50 amp ground-fault interrupter typically used for a spa. The ground and the neutral were bonded to the frame of the generator prior to the connection to the ground-fault. Also each cable carries both 120/240 hot leads, neutral and ground out to the junction boxes that supply power to our equipment.

However, now that you have mentioned it I will have to check my EU 2000i and 3000i generators to see if the ground and neutral are bonded.
__________________
Don (KD6UVT) & Gail Williams

What do you want to be in life, a spectator or a participant?

SNU #157
FCU #004
Motoman is offline   Reply With Quote
Old 01-28-2007, 12:50 PM   #5
Rivet Master
 
1975 29' Ambassador
Reno , Nevada
Join Date: May 2003
Posts: 1,351
RV genset grounding has its own codes. See Wiring your generator ground
and genset grounding at the SNUZE weblog or the OSHA 2 page factsheet Grounding Requirements for Portable Generators
bryanl is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
SAFETY : >>>>Lightning Strikes<<<< hex Our Community 36 12-18-2005 11:34 AM
Well grounded in reality krowsea Electrical - Systems, Generators, Batteries & Solar 6 07-19-2005 04:18 PM
Battery Dead/Power jack question jcanavera Jacks, Stabilizers, Lifting and Leveling 34 08-16-2002 01:51 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 01:11 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.