Generator grounding question.

I just purchased a pair of Ducar 2000 generators and the parallel kit. What do others that have a similar system do for grounding these? In theory a 4 foot copper rod is required, but in most place I camp, you would spend more time trying to put the rod in the ground than you would enjoying the time camping, not to mention the removal process. I always leave one stablizer jack, or the electric jack, touching earth when camping, even in campgrounds with electrical service. Am I worrying about nothing? With my old 3500 Honda, the steel frame was on the ground and I never worried. When connecting the parallel kit I will use the ground wire on the gen sets. Any and all thoughts appreciated!
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1976 31' Gone but fondly remembered
1976 22' Argosy
Hensley Hitch
CBWELL is offline   Reply With Quote
Old 03-01-2021, 09:05 AM   #2
Rivet Master
 
B. Cole's Avatar
 
1977 31' Sovereign
Rochester , WASHINGTON
Join Date: Sep 2020
Posts: 627
Ok, you'll get a lot of advice here.Some of it, won't be good.
There's a reason a copper grounding rod, driven 4 feet into the ground, with correct connection to generator,is proper earth grounding of a device generating 120 - 240 Volts.
If you read any generator Manuel ( which most dont)that is in there, per grounding code.
The #1 rule in electrical work, is don't become the pathway to ground.
People jump out of perfectly good aircraft from 1,000s of feet.They also have great reasons for that, similar to what I'm sure you'll see soon here.
Just like a combination vehicle with too small of a tow vehicle, everything is fine, until suddenly it isn't....
__________________
Airstream rodeo clown, it's my turn in the barrel 🤡
B. Cole is offline   Reply With Quote
Old 03-01-2021, 09:07 AM   #3
Rivet Master
 
ITSNO60's Avatar
 
Currently Looking...
Tucson , AZ
Join Date: May 2017
Posts: 1,163
Grounding a portable generator to earth accomplishes nothing, totally unnecessary. The generated power is not trying to go to the earth, it is trying to go back to the generating source. That's what makes it a complete circuit.
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 03-01-2021, 09:14 AM   #4
Rivet Master
 
B. Cole's Avatar
 
1977 31' Sovereign
Rochester , WASHINGTON
Join Date: Sep 2020
Posts: 627
Quote:
Originally Posted by ITSNO60 View Post
Grounding a portable generator to earth accomplishes nothing, totally unnecessary. The generated power is not trying to go to the earth, it is trying to go back to the generating source. That's what makes it a complete circuit.
Here they come...
__________________
Airstream rodeo clown, it's my turn in the barrel 🤡
B. Cole is offline   Reply With Quote
Old 03-01-2021, 10:10 AM   #5
Lost in America
 
mojo's Avatar
 
2015 27' FB International
2006 25' Safari FB SE
2004 19' International CCD
Santa Fe , New Mexico
Join Date: Feb 2007
Posts: 1,901
Just put on your tin foil hat and you will be fine!
__________________
This is the strangest life I've ever known - J. Morrison

2015 Airstream International Serenity 27FB
2017
Chevy Silverado 2500HD Duramax Diesel

mojo is offline   Reply With Quote
Old 03-01-2021, 11:45 AM   #6
Rivet Master
 
truckasaurus's Avatar
 
1960 33' Custom
Athens , Georgia
Join Date: Jun 2005
Posts: 1,324
Images: 25
How does an onboard generator get grounded in a motorhome? IIRC my Honda EU3000i has rubber feet and mentions consulting a qualified electrician before connection to ground.
__________________
1960 Sovereign 33' Pacific Railroad Custom
truckasaurus is offline   Reply With Quote
Old 03-01-2021, 11:47 AM   #7
Rivet Master
 
B. Cole's Avatar
 
1977 31' Sovereign
Rochester , WASHINGTON
Join Date: Sep 2020
Posts: 627
Quote:
Originally Posted by mojo View Post
Just put on your tin foil hat and you will be fine!
Mine is always on, ( special construction) in the event of a EMP or unusual Space weather, I'm grounded ..
__________________
Airstream rodeo clown, it's my turn in the barrel 🤡
B. Cole is offline   Reply With Quote
Old 03-01-2021, 11:52 AM   #8
Rivet Master
 
ITSNO60's Avatar
 
Currently Looking...
Tucson , AZ
Join Date: May 2017
Posts: 1,163
Quote:
Originally Posted by truckasaurus View Post
How does an onboard generator get grounded in a motorhome?
It is bonded to the MH chassis. This will clear a fault should a hot wire come into contact with metal parts of the RV, because the current always returns to the source, it never returns to the earth because it did not come from the earth. It has to return to the source or it wouldn't be a complete circuit and it would not be able to do any work.

Grounding and bonding is a much mis-understood subject and it takes a solid understanding of electrical theory (mainly Ohm's law) to understand it. It is a subject filled with mis-understanding and mis-information even by electricians and by equipment manufacturers.

Watch a few videos on the subject by Mike Holt, one of the world's leading experts on grounding and bonding.
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 03-01-2021, 12:26 PM   #9
CLOUDSPLITTER "Tahawus"
 
ROBERT CROSS's Avatar

 
2003 25' Classic
Zanadude Nebula , Milky Way
Join Date: Jun 2007
Posts: 17,130
Images: 1
I have never rod grounded our portable genset's. 35 yrs SFSG.

Bob
🇺🇸
Disclaimer.... I have an open neutral and am perfectly grounded.⚡️😂
Attached Thumbnails
Click image for larger version

Name:	3631EDC4-9E69-4A3F-B452-D71ED2A162E2_1_100_o.jpeg
Views:	11
Size:	290.7 KB
ID:	389650  
__________________
“I’ve always thought that over planning was just a firewall against not being sure of what you really want to do.”
RLC

Tahawus
🌤
ROBERT CROSS is offline   Reply With Quote
Old 03-01-2021, 01:01 PM   #10
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 5,532
Blog Entries: 1
At work we had 25 Honda EU 3000is. We never grounded them unless it was to eliminate electronic noise.
I'm not saying that's textbook, but nobody died. Now I have one and I won't be grounding it either.
Guess what? my 80 year old home has some ungrounded outlets. <gasp>

I want to watch as a customer drives that 4' copper rod through a campground water line or worse, direct burial electric cable. Bzzzzzzzz.
Mollysdad is offline   Reply With Quote
Old 03-01-2021, 01:09 PM   #11
Rivet Master
 
ITSNO60's Avatar
 
Currently Looking...
Tucson , AZ
Join Date: May 2017
Posts: 1,163
I don't know where this 4' rumor originated but NEC requires a ground rod to be 8' long minimum and 5/8" diameter minimum, installed at no greater than a 45 degree angle. We have driven hundreds of them and in over 30 years the only mishap was driving one right through a clay sewer line. We do get a Blue Stake before hand but private utilities are not included. NEC allows for up to a 45 degree angle or buried in a trench at least 30" below grade.
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 03-01-2021, 04:41 PM   #12
Rivet Master
 
ITSNO60's Avatar
 
Currently Looking...
Tucson , AZ
Join Date: May 2017
Posts: 1,163
Actually contrary to my statement in post #3 that grounding a portable generator to earth accomplishes nothing I should have said "it accomplishes nothing besides creating a hazard that didn't exist". If anything powered by the generator has a fault to a conductive case, the user could be standing on wet ground barefoot and as long as the generator is isolated from that wet ground he will feel nothing unless he touches the metal parts of the generator. Now introduce a ground rod and you have given a path for some of the fault current to return on and electrons will move through the person's body and follow this path back to it's source. The amount that flows will be proportional to the resistance of the path including the person's skin but it takes less than 10 milliamps to cause cardiac arrest.
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 03-01-2021, 05:01 PM   #13
4 Rivet Member
 
SailorSam205's Avatar
 
South East , Michigan
Join Date: Apr 2016
Posts: 399
I prefer to get electrical information from folks who have significant background. Mike Sokol writes a blog about RV Electricity. Here is a quote from him followed by a link to the full discussion.


"You DO NOT need to use an earth “grounding rod” for any portable generator that’s powering a single RV."


https://www.rvtravel.com/rv-electric...nding-bonding/
__________________
Al
2017 29' SOB, 2019 Platinum F-150 SCrew, ProPride
SailorSam205 is offline   Reply With Quote
Old 03-01-2021, 05:45 PM   #14
Rivet Master
 
CBWELL's Avatar
 
1994 34' Excella
Warren , Manitoba
Join Date: Apr 2006
Posts: 849
So, I am understanding that I don't need to drive a copper stake into the ground to be safe! I assumed that with the gen sets running and grounded to the parallel kit, which in turn would be connected to the Airstream by the 30 amp cord, and grounded to the Airstream, I would be safe. Not being an electrical guru and reading in the instructions that the gen set should be grounded, I figured best to ask people in the know. Thanks everyone.
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1976 31' Gone but fondly remembered
1976 22' Argosy
Hensley Hitch
CBWELL is offline   Reply With Quote
Old 03-03-2021, 09:26 AM   #15
4 Rivet Member
 
Chelsea , Maine
Join Date: Aug 2016
Posts: 297
I’ve never seen anyone driving a rod into the ground to use a generator.
I would think they would get kicked out of the parking lot (such as Charlotte Motor Speedway, or Daytona, etc) for doing so.
Hit a pipe or a wire and you’ll not be popular with the management.
Pulling it out when you leave is going to be a problem, too.
It’s just not done.
__________________
2017 FC 27FB
2017 F250 Lariat Crew Cab 6.2L
Equal-I-Zer 10K/1000
JMynes is offline   Reply With Quote
Old 03-03-2021, 05:58 PM   #16
3 Rivet Member
 
Collyn's Avatar
 
Church Point , NSW
Join Date: Jul 2013
Posts: 224
There is absolutely no point in grounding portable generators. Doing so will, if anything, literally introduce 'potential' issues.

My qualifications for saying the above: I cannot name it here, but I am the author of what is almost certainly the world's top selling book in the RV electrics area (and now in its 22nd year). The major Australian trade training institute (TAFE) adopted it as the manual for auto-electricians many years ago - and still use the current edition. It is used also in the USA.

Collyn
__________________
The problem is not so much what people do not know, it's what they think they know that simply is not true.
Collyn is offline   Reply With Quote
Old 03-03-2021, 08:42 PM   #17
3 Rivet Member
Commercial Member
 
2016 23' International
Long Beach , California
Join Date: Sep 2018
Posts: 198
Images: 9
Blog Entries: 1
stakes are for Buffy.
Seanlb is offline   Reply With Quote
Old 03-03-2021, 11:58 PM   #18
Rivet Master
 
B. Cole's Avatar
 
1977 31' Sovereign
Rochester , WASHINGTON
Join Date: Sep 2020
Posts: 627
Quote:
Originally Posted by Collyn View Post
There is absolutely no point in grounding portable generators. Doing so will, if anything, literally introduce 'potential' issues.

My qualifications for saying the above: I cannot name it here, but I am the author of what is almost certainly the world's top selling book in the RV electrics area (and now in its 22nd year). The major Australian trade training institute (TAFE) adopted it as the manual for auto-electricians many years ago - and still use the current edition. It is used also in the USA.

Collyn
That's a statement which is incorrect.Do you know what a transfer switch is? We arnt in Australia.50Amp + 30Amp transfer switches are commonly in use in North America.
"If the portable generator is providing power, via a transfer switch, to a structure(Home,office,shop, trailer, or similar) it must be connected to a grounding electrode system, such as a driven ground rod."
Grounding requirements for generators connected by transfer switches are covered by Article 250 of the National Electric Code (NEC)
You also arnt taking into consideration a failure of the integrity of connections between generator frame, and the grounded equipment circuits,of power receptacles.
Maybe a connection vibrates loose, or a rat or a dingo chews a grounding or neutral wire.Or Cousin Eddy worked on the receptacle.
Thats one reason why generator manufactures go with driven ground rod recommendation, in owners manual.
__________________
Airstream rodeo clown, it's my turn in the barrel 🤡
B. Cole is offline   Reply With Quote
Old 03-04-2021, 08:56 PM   #19
3 Rivet Member
 
Collyn's Avatar
 
Church Point , NSW
Join Date: Jul 2013
Posts: 224
Yes - I do know what a (USA) transfer switch is.

It is an electrical switch that switches between either of two sources.

It has nothing whatever to do with grounding a portable generator that is powering an RV directly - and only that.

Collyn
__________________
The problem is not so much what people do not know, it's what they think they know that simply is not true.
Collyn is offline   Reply With Quote
Old 03-04-2021, 09:25 PM   #20
3 Rivet Member
Commercial Member
 
2016 23' International
Long Beach , California
Join Date: Sep 2018
Posts: 198
Images: 9
Blog Entries: 1
Technically, the ground wire does go through the transfer switch box... just saying...
Seanlb is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is grounding portable generator necessary smsasf Generators & Solar Power 36 07-13-2020 05:28 PM
Grounding of generator Bait guy Generators & Solar Power 10 07-30-2013 11:18 AM
generator grounding to truck wolf146 Generators & Solar Power 11 05-24-2012 05:24 PM
Inverter Grounding Question for Electricians mello mike Batteries, Univolts, Converters & Inverters 6 02-07-2010 07:39 PM
generator grounding JK3500 Generators & Solar Power 23 06-19-2007 03:59 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 01:04 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, Jelsoft Enterprises Ltd.