Champion inverter Internal & PD EMS need bonded neutral ?
Have a Champion 2800-3100 watt dual fuel inverter and recently installed an internal hardwired 30A Progressive Dynamics EMS.
Champion specs say it has a “floating” neutral whereas it’s neutral is NOT tied to the Gen frame/ground.
As the EMS must see proper electrical correctness for 15-20 secs before passing power through to the AS
Does anyone know it this Gen requires a bonding neutral plug adaptor at the Gen 120v outlet (tying the neutral to ground) to pass happy power through the EMS ?
Thanks in advance !
|
|
|
09-25-2021, 12:56 PM
|
#2
|
Half a Rivet Short
2017 30' Classic
2022 Interstate 24X
Carlisle
, Pennsylvania
Join Date: May 2017
Posts: 15,674
|
Hi
Something like 99% of the portable generators out there are (apparently) targeted at home use. They do not come with the neutral hooked to ground. That way you can hook them into the house and "run everything".
For RV use you need to bond the neutral to ground at the generator. The normal "use a plug" approach is typically used.
So yes, you need to bond / connect / strap / attach the neutral to ground at the generator.
Bob
|
|
|
09-26-2021, 08:28 AM
|
#3
|
Rivet Master
2005 25' International CCD
Westlake Village
, California
Join Date: Sep 2014
Posts: 508
|
Quote:
Originally Posted by uncle_bob
Hi
Something like 99% of the portable generators out there are (apparently) targeted at home use. They do not come with the neutral hooked to ground. That way you can hook them into the house and "run everything".
For RV use you need to bond the neutral to ground at the generator. The normal "use a plug" approach is typically used.
So yes, you need to bond / connect / strap / attach the neutral to ground at the generator.
Bob
|
Thanks for the reply Bob,
Well, did a home test and fired up the Gen to see if the PD EMS blocked or passes Gen power (sans bonding method). All came up proper with all AC items working/protected.
So, is neutral bonding at Gen still required in all or “some” cases and does the eliminate the hot / voltage potential to the AS frame ?
Thanks,
|
|
|
09-26-2021, 09:24 AM
|
#4
|
Half a Rivet Short
2017 30' Classic
2022 Interstate 24X
Carlisle
, Pennsylvania
Join Date: May 2017
Posts: 15,674
|
Quote:
Originally Posted by Vantair
Thanks for the reply Bob,
Well, did a home test and fired up the Gen to see if the PD EMS blocked or passes Gen power (sans bonding method). All came up proper with all AC items working/protected.
So, is neutral bonding at Gen still required in all or “some” cases and does the eliminate the hot / voltage potential to the AS frame ?
Thanks,
|
Hi
The neutral must *always* be bonded to ground. It *must* only be done at one point. The bond should never be done inside the trailer. The bond is always done at the main breaker panel in a building or house. At a construction site with a temporary distribution setup it may be bonded at the distribution panel.
With a system that is not tied to earth, you have some possibility for leakage. Pretty much nobody drives a 12' copper rod into the ground each time they fire up their generator. With a properly maintained generator, the level of leakage should be well below anything you can easily detect.
Even without the ground rod, the neutral / ground bond will take out any possible leakage to the frame. It all will "return" via the ground wire to the bond point.
Bob
|
|
|
09-26-2021, 09:36 AM
|
#5
|
Riveted...?
2004 25' Safari
Central Valley
, California
Join Date: Aug 2020
Posts: 69
|
Grounding Plug?
Quote:
Originally Posted by uncle_bob
Hi
The neutral must *always* be bonded to ground. It *must* only be done at one point. The bond should never be done inside the trailer. The bond is always done at the main breaker panel in a building or house. At a construction site with a temporary distribution setup it may be bonded at the distribution panel.
With a system that is not tied to earth, you have some possibility for leakage. Pretty much nobody drives a 12' copper rod into the ground each time they fire up their generator. With a properly maintained generator, the level of leakage should be well below anything you can easily detect.
Even without the ground rod, the neutral / ground bond will take out any possible leakage to the frame. It all will "return" via the ground wire to the bond point.
Bob
|
So, having been boondocking sparingly (with a lot more to come) but also needing my Champion dual fuel to run some circuits at the house (thanks PGE) should I invest in a grounding plug for the Champion? I was planning on running the 30A cord to a 110 plug adapter from the AS to the generator to run the AS and charge the batteries as needed...
Thx!
__________________
- Lots of people are engaging in risky behavior, but most of them just don't know how risky their behavior really is...
2013 Ram, 2500, Crew Cab, Cummins, 4x4, SRW, Short Box
2004 25', Safari LS w/ 3" Dexter Lift Kit on Henschen Axles,
Blue Ox
|
|
|
09-27-2021, 07:45 AM
|
#6
|
Half a Rivet Short
2017 30' Classic
2022 Interstate 24X
Carlisle
, Pennsylvania
Join Date: May 2017
Posts: 15,674
|
Quote:
Originally Posted by Justinhb
So, having been boondocking sparingly (with a lot more to come) but also needing my Champion dual fuel to run some circuits at the house (thanks PGE) should I invest in a grounding plug for the Champion? I was planning on running the 30A cord to a 110 plug adapter from the AS to the generator to run the AS and charge the batteries as needed...
Thx!
|
Hi
Yes, you need to run a grounding plug with the gen set when you are out and about. The plug comes out when you feed the house with it.
Bob
|
|
|
09-27-2021, 08:48 AM
|
#7
|
Rivet Master
2017 26' Flying Cloud
Tampa
, Florida
Join Date: Feb 2017
Posts: 7,620
|
It's simple.
I may be plugged into any outlet in the generator. It fools the EMS into thinking it's a house since your house has the neutral and ground tied together in the breaker box.
|
|
|
09-28-2021, 07:25 AM
|
#8
|
Rivet Master
2005 25' International CCD
Westlake Village
, California
Join Date: Sep 2014
Posts: 508
|
Made one !
Bought two types (one spare) one a larger but prefer the smaller Leviton with hefty #10 gauge jumper from ground to neutral. EASY. Will be a-boondocking leaving today for rest of the week to try it out.
Thanks for the confirmation all !
|
|
|
|