NEW Dometic A/C Crapped Out

When I picked up the Eddie Bauer at Colonial Airstream, the unit had an a/c that blew a compressor. Colonial replaced it with a unit off of a new Airstream in stock.

Today I woke up hot - the fan was running but not the compressor. After futzing around with the control panel and reading ALL of the misc. instructions for the Dometic 13500... I couldn't get it going. Why?
because the INSIDE temperature sensor says it's 32 F inside my unit. Not so. More like 88F!
I can get the heat pump to run though.
Called Dometic - voice mail. Paged colonial, No response. All I can think is that I've somehow iced over the compressor. I went to work and will wait several hours to see if the outside unit melts and I can get SOME air going.

Any other thoughts? BTW, How the heck to I get the inside cover off or loose enough to get the model number and serial number?

Paula
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 07-13-2013, 01:16 PM   #2
Rivet Master
 
2011 25' FB Flying Cloud
Anywhere & , Everywhere
Join Date: Aug 2006
Posts: 1,090
Suspect this is a thermostat problem but I'm no expert.

If the thermostat is telling the a/c that the temp in your trailer is 32F then the compressor will not come on.
Al - K4GLU is offline   Reply With Quote
Old 07-13-2013, 01:16 PM   #3
2 Rivet Member
 
mapley3's Avatar
 
1980 31' Excella II
Spring Hill , Florida
Join Date: Nov 2008
Posts: 67
Images: 1
Foiled Again -- I can only sympathize with you. We had a new A/C unit installed to replace our 33 year old Dometic and it ran great but, no cold air. You don't fix a new unit; you replace it. So, a new number 2 was installed. So far, so good. A lady down the street came over to chat and asked "What are you crabbing about? I'm on my 4th new unit in two weeks from the dealer in Fort Myers." It would seem that the quality of foreign made Dometic A/C's has gone down. I hope Colonial takes care of you.
mapley3 is offline   Reply With Quote
Old 07-13-2013, 01:43 PM   #4
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Paula,

Try a re-set on your t/stat before you do anything else. It seems that it is not reading the remote temp sensor correctly.

There are directions in the back of your Comfort Control II manual, or PM me for the sequence.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 07-13-2013, 02:03 PM   #5
Rivet Master
 
Crusty's Avatar
 
1992 34' Excella
Austin , Texas
Join Date: Mar 2007
Posts: 563
Images: 10
Yup, do what Lewster said - the CCC can lose communication with the outside unit. I'd almost bet money that a reset will make it work again.

If ya ain't got air conditionin', ya ain't cool.
__________________
Crusty
"If you come to a fork in the road, take it."
Lake Travis, TX
"Rancho Deluxe"
Crusty is offline   Reply With Quote
Old 07-13-2013, 02:12 PM   #6
4 Rivet Member
 
Morgan guy's Avatar
 
2007 27' Classic FB
Fredericksburg , Texas
Join Date: Jun 2011
Posts: 300
If your AC is like mine, when I pulled the lower panel off, a bar ran across the bottom that was right in line with the model and serial number are and I could not read it.
Good Luck. Not a good time of year to be without AC.
Morgan guy is offline   Reply With Quote
Old 07-13-2013, 02:26 PM   #7
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
paula, myself and others have had tis problem. it sounds like a sweaty communications connevtor. i'll' look up the thread.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 07-13-2013, 02:35 PM   #8
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
paula, here is the thread:
http://www.airforums.com/forums/f427...-ii-95934.html

the cover has some hidden screws in the slotted cover. i also had to slide out the filters. it is a simple fix if it is your problem.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 07-13-2013, 04:40 PM   #9
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,801
Lewster - tried reprogramming it, tried turning it off and back on, popped the circuit breaker too, Then set the fantastic fans on and LEFT for a cool office.

Still haven't unpacked my tools, so I'll need to borrow stuff from the office to get the inside cover of the A/C off. I've got the installation manual, etc. but they always seem to assume you can take the cover off the thermostat without breaking it. I'm waiting for sunset, then heading home and will try to find the phone lines and dry them out/reset them.

Thanks for all the help all y'all - good karma to you on this hot, hot day. It's 99% humidity and we had a heavy thunderstorm in the early morning. Wet connectors make sense.

Happy trails, Paula
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 07-13-2013, 04:52 PM   #10
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
try running on heat for a bit if you can stand it. it will help dry the humidity a bit. i ran mine on just fan and turmed it off at bedtime. by morning it ran ok but it did the same thing the next night when it was humid again.
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 07-13-2013, 06:33 PM   #11
Rivet Master
 
SilverGate's Avatar
 
2007 23' Safari SE
San Diego , California
Join Date: Apr 2006
Posts: 1,495
Re-setting the thermostat (posted by lewster, 9-22-10)
SilverGate is offline   Reply With Quote
Old 07-13-2013, 06:55 PM   #12
Rivet Master
 
Silver Goose's Avatar
 
2008 27' Classic FB
Burkburnett , Texas
Join Date: Jul 2010
Posts: 985
Just spotted this other thread with similar symptom. Maybe when they were swapping out the A/C unit the cable didn't get fully seated. Sure worth a look.

http://www.airforums.com/forums/f427...-ii-95934.html
__________________
AIR 47751
Silver Goose is offline   Reply With Quote
Old 07-13-2013, 09:23 PM   #13
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
That was was the reset procedure for the CCC-I. I believe that Paula's new unit is the CCC-II/ While the re-set is similar, the buttons are different. Basically, you turn off the t/stat, depress the 'mode' and 'zone' buttons at the same time, then turn the unit back on.

The t/stat should read 'init-1' if it has re-set.

If the unit works as a heat pump, then all of the communication functions are normal. If the t/stat is reading the interior temps at 32ºF instead of the actual ambient temps, it could be a problem with the remote temp sensor, the t/stat itself or the control board in the upper unit of the A/C.

A re-set is the first procedure to try. All of the connectors are probably good if the unit is operating in heat pump mode.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 07-14-2013, 10:17 PM   #14
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,801
All Better Now

Richinny - your link pointed out the problem "damp phone cable".

I left the unit all day with the fan running on high - everything else off, and one fantastic fan running exhaust with the other open and sucking air. (Neither are bi-directional YET). When I came home in the evening the inside and outside temps read accurately. I started the unit up with no problems.

I didn't note before that I might have tried to overcool - 70 degrees with outside temp over 95 and rain on and off for days. Humidity was 99% and the drain wasn't dripping but running solidly. When I restarted it I left it at 75 degrees and put the fan on high.

I regularly turn it up to 80 when I'm out. I want to keep it bearable, but don't need to come into an icebox.

Thanks for the help, Paula
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 07-15-2013, 05:56 AM   #15
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
i'm glad it worked out :-)
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 07-15-2013, 06:32 AM   #16
Vintage Kin
 
Fort Worth , Texas
Join Date: Nov 2006
Posts: 8,014
Images: 1
Quote:
Originally Posted by Foiled Again View Post

" . . I didn't note before that I might have tried to overcool - 70 degrees with outside temp over 95 and rain on and off for days. Humidity was 99% and the drain wasn't dripping but running solidly. When I restarted it I left it at 75 degrees and put the fan on high.

I regularly turn it up to 80 when I'm out. I want to keep it bearable, but don't need to come into an icebox . . . "
Why I run a big dehumidifer constantly. A target of interior 35-45% humidity and temp of 73F in the evenings. Daytime interior temps may reach 77-79F before shade covers the TT in late afternoon. Outside, 90+% humidity and temps of 95F. The dehumidifier runs the electric bill higher, but dry cool air is more easily obtained.

.
slowmover is offline   Reply With Quote
Old 07-15-2013, 07:49 AM   #17
Colonial Airstream NJ
Airstream Dealer
 
Colonial Airstream's Avatar
 
1961 16' Bambi
1997 19' "B" Van Airstream 190
Millstone Township , New Jersey
Join Date: Oct 2003
Posts: 578
Images: 79
Thank you for helping out another fellow Airstreamer and our customer when we were closed.
__________________
Patrick Botticelli - Colonial Airstream 595 State Hwy 33 Millstone Township, NJ 08535 - 1-800-265-9019 www.colonialairstream.com
Colonial Airstream is offline   Reply With Quote
Old 07-15-2013, 02:00 PM   #18
3 Rivet Member
 
2008 27' Safari FB SE
Pfafftown , North Carolina
Join Date: Oct 2010
Posts: 155
Saturday Hours ?

Quote:
Originally Posted by NeatAirstream View Post
Thank you for helping out another fellow Airstreamer and our customer when we were closed.
Is Colonial now closed on Saturdays?
sunnygirl is offline   Reply With Quote
Old 07-16-2013, 07:02 AM   #19
Colonial Airstream NJ
Airstream Dealer
 
Colonial Airstream's Avatar
 
1961 16' Bambi
1997 19' "B" Van Airstream 190
Millstone Township , New Jersey
Join Date: Oct 2003
Posts: 578
Images: 79
We are open Saturdays 9am to 6pm est.
__________________
Patrick Botticelli - Colonial Airstream 595 State Hwy 33 Millstone Township, NJ 08535 - 1-800-265-9019 www.colonialairstream.com
Colonial Airstream is offline   Reply With Quote
Old 07-16-2013, 08:33 PM   #20
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,801
Problem happened again. Now I guess we start the darned warranty process. CRAP.

I did call Colonial and get a suggestion to turn the battery switch to standby as well turning off the circuit breaker. The service department said that Dometic had a fire in it's Texas plant a while back, and quality control has been poor every since. Apparently the closest AUTHORIZED Dometic facility is in Ashland VA - over 100 miles from here. Pain in neck.

I did pull the cover off the thermostat and unplug/replug the phone cable connection to the ceiling unit. Accomplished zero.

Eventually when the fan runs long enough (and the outside temp gets low enough) the thing somehow resets itself and report the inside temp. accurately. Then the air conditioner will run - for a while. I'm about ready to pull the inside cover off the A/C and look for the phone connection in the ceiling unit. If there IS any sign of moisture I'll let you know, but I'm leaning to the inside sensor being defective.

Crap, crap, crap. HOT CRAP Paula
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:55 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.