Heat Pump blowing cool air?

Just checking the systems in my 07 25 Classic. I have the wall mounted control unit for my furnace and AC/ heat pump. If I set the control panel to heat pump and set the temp at say 70. it only blows cool air. I've tried temp settings below and above that with the same result. Any ideas?
craftsman is offline   Reply With Quote
Old 04-08-2008, 10:06 AM   #2
Rivet Master
 
TinShack's Avatar

 
2005 28' Safari S/O
Paradise , California
Join Date: Jul 2006
Posts: 3,446
Images: 28
How long did you let it run? Mine takes about 5-10 minutes to heat up initially. After it cycles off and back on again via the thermostat, it only takes a minute or two to heat up.
__________________
Steve
"THE OLDER I GET, THE BETTER I WAS"
TinShack is offline   Reply With Quote
Old 04-08-2008, 10:14 AM   #3
Rivet Master
 
CanoeStream's Avatar

 
2006 25' Safari FB SE
St. Cloud , Minnesota
Join Date: Aug 2003
Posts: 13,280
Images: 19
Blog Entries: 3
On a Classic? That should be a heat pump. My Safari SE only has the heat strip. It's fairly weak and only adds slightly warmer air. It aims to get the job done over time I guess. With the ducted breeze it's hard to tell it's any warmer but I've checked it with a thermometer. Your temps today shouldn't be too cold for the heat pump to function effectively.
__________________
Bob

5 meter Langford Nahanni

CanoeStream is offline   Reply With Quote
Old 04-08-2008, 10:18 AM   #4
Refurbished 89 Excella
 
DKDarrow's Avatar
 
1988 29' Excella
Sugar Valley , Georgia
Join Date: Feb 2005
Posts: 246
I have found that with my Dometic 15k in an 89 Excella that it takes a bit of time to start kicking out warmer air........Then downright HOT.............Let it run for 10 to 15 minutes.

As an aside, LOW voltage will definately case this timeline to lengthen.........It really likes a minimum of 110V..........

Have you checked your voltage???
__________________
Dennis & Susan
D&D Farms, Sugar Valley, Ga
Registered Boer goats
DKDarrow is offline   Reply With Quote
Old 04-08-2008, 10:52 AM   #5
Rivet Master
 
TinShack's Avatar

 
2005 28' Safari S/O
Paradise , California
Join Date: Jul 2006
Posts: 3,446
Images: 28
Quote:
Originally Posted by DKDarrow
As an aside, LOW voltage will definately case this timeline to lengthen.........It really likes a minimum of 110V..........

Have you checked your voltage???
I agree. It uses the compressor so has the same voltage requirements as the A/C.
__________________
Steve
"THE OLDER I GET, THE BETTER I WAS"
TinShack is offline   Reply With Quote
Old 04-08-2008, 11:51 AM   #6
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 10,475
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
As others have posted it takes a bit for the heat to generate. A lot to do with that is also the outside air temp. You start with a dead cold trailer in the upper 30's, it will take a while for that trailer to get to temp. Normally I'll let the furnace do the hard work in getting the trailer up to set point, then I'll switch over to heat pump. Note that once you start falling below 42 or so, the output will not be quite as hot. Normally once the heat pump starts cycling, the time it take to blow hot air is minimal.

Other things to note about the heat pumps. After a continuous run (I forgot exactly how long), the heat pump changes modes and the unit goes into cooling mode, without the fan running. This allows the external evaporator to defrost any accumulated ice on those outside coils. It's a little concerning the first time you experience this since the fan abruptly shuts down and you hear the internal workings clunk and then just the hum of the compressor running. You probably would experience this when you are attempting to bring the trailer up from a dead cold condition where the unit has to continually run.

The other issue is that in very cold humid conditions, the unit may run a lot, but not enough to trigger the defrost cycle. I had this happen in Branson one fall. I came back to the trailer only to find it in the 50's inside and the heat pump running, but only blowing out tempid air. I went outside and saw the coils were encrusted in a block of ice.

Jack
__________________
Jack Canavera
STL Mo.
AIR #56 S/OS#15
'04 Classic 30' S.O.,'03 GMC Savana 2500
jcanavera is online now   Reply With Quote
Old 04-08-2008, 12:12 PM   #7
4 Rivet Member
 
sander17's Avatar
 
1996 28' Excella
Okemos , Michigan
Join Date: Apr 2003
Posts: 305
Images: 42
Check the outside temp. The heat pump in our '96 has a thermal switch which prevents it from working if the outside temp is below 45 degrees. The fan just blows cool air, so it is not obvious.
__________________
Dave
Okemos, MI
T.V.:'05 Dodge Ram 2500 4x4 Quad Cab Cummins
AIR#2276
sander17 is offline   Reply With Quote
Old 04-08-2008, 12:14 PM   #8
Rivet Master
 
2007 25' Classic
Hydes
Join Date: Apr 2007
Posts: 713
Thanks. I actually let the furnace heat the interior first. The outside temp is in the low 40's today. I only let the heat pump run maybe 5 or so minutes so maybe I didn't give a chance to start warming. I'll try it again.
craftsman is offline   Reply With Quote
Old 04-08-2008, 01:52 PM   #9
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 10,475
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
Quote:
Originally Posted by sander17
Check the outside temp. The heat pump in our '96 has a thermal switch which prevents it from working if the outside temp is below 45 degrees. The fan just blows cool air, so it is not obvious.
The newer units have a cut over where the heat pump is automatically cut off and the furnace takes over. In my trailer however, that cut over takes place at too low a temperature. By that point the heat pump output becomes too tempid which makes me go over and switch to furnace manually.

Jack
__________________
Jack Canavera
STL Mo.
AIR #56 S/OS#15
'04 Classic 30' S.O.,'03 GMC Savana 2500
jcanavera is online now   Reply With Quote
Old 04-08-2008, 06:10 PM   #10
2 Rivet Member
 
2006 30' Classic
st louis , Missouri
Join Date: Dec 2006
Posts: 63
Pay attention to Jack He,s correct
2wired is offline   Reply With Quote
Old 04-08-2008, 07:01 PM   #11
Rivet Master
 
DEITZ645's Avatar
 
2006 30' Classic S/O
Currently Looking...
Mohrsville , Pennsylvania
Join Date: Jun 2006
Posts: 1,313
Images: 10
Learned The Hard Way

We learned the same thing the hard way in our '06. We woke up freezing one night. When I heard all the noises mentioned in an earlier post I figured it was time to re-read the heat pump / AC manual again. That is when I saw that it may not work so well when the outside air temperature drops below 40 (typical man, if all else fails...read the instructions). The heat pump is nice to take the edge off, but nothing beats that propane furnace.
__________________
Carl, Elaine & Finn The Beagle
2006 30' Classic W Slide & Limited Package Katarina
2006 GMC 2500 HD 6.6 Turbo Diesel Crew Cab 8' Bed
TAC PA-3
S/OS#042
AIR #14487
NQ3U (was KB3UOM)
DEITZ645 is offline   Reply With Quote
Old 04-08-2008, 07:01 PM   #12
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,514
Quote:
Originally Posted by craftsman
Thanks. I actually let the furnace heat the interior first. The outside temp is in the low 40's today. I only let the heat pump run maybe 5 or so minutes so maybe I didn't give a chance to start warming. I'll try it again.
C,

After trying the heat pump again for a longer period of run time and it is still blowing cold air, one of two things are happening:

1: the outside ambient air is just too cool for the heat pump to extract any more heat from it to put into the trailer (as stated above)

2: your relay board on the upper unit is stuck in the closed position. I say this, because ALL Dometic heat pumps actually have the reversing valve in the 'heat pump' position as it's normal rest state. When you call for cooling from the air conditioner, the relay (K-5 IIRC) closes and reverses the valve, thus creating the proper refrigerant flow for air conditioning. If you are only getting cold air from the unit, then K-5 is stuck closed and wil not allow the reversing valve to attain it's original state.

If this is the case, you need a qualified Dometic tech to look at your unit to determine if you need a new relay board. Hope you're still under warranty!!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 38 10-28-2016 08:58 PM
Dometic Penguine Air/Heat pump- 2006 Classic kleimanr 2006 - 2010 Classic (all lengths) 4 05-18-2015 03:41 PM
furnace blowing cold air canine camp Furnaces, Heaters, Fireplaces & Air Conditioning 55 07-27-2013 12:14 AM
Trouble shooting Furnace/Heat Pump/Air C? Kistler Furnaces, Heaters, Fireplaces & Air Conditioning 8 01-07-2007 01:13 AM
Furnaces blowing but no heat Dave Emmerich General Motorhome Topics 6 01-04-2003 08:53 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.