I have a '91 B190 I bought last summer. I'm having a problem with the furnace: when it starts up, there's a nasty squealing noise for a few minutes, then it'll go away. The furnace works fine otherwise (sometimes the squeal will return for a moment while it's running).
Here's the issue: I'm living out of the B190 full-time at the moment, and will be doing so for another week, and temperatures are getting into the 30s F at night. I went without heat last night, but I'd rather not do it again.
I did a search and found a couple threads but the only one that specifically mentioned this noise involved a motor replacement that may or may not have fixed the problem.
Since the furnace is right under the couch in the 190, I'm hoping I can simply unbolt the couch and remove it to work on the furnace without having to remove it entirely.
I'm guessing the problem is either the bearings on the motor or the fan hitting its shroud. Does anyone have any thoughts or tips? I hate to call this an emergency, but it's a pretty serious problem that I need to at least temporarily fix. (I'm only staying in the motorhome for another 7 days, after which I'll be in my new house and can work on this at my leisure.)
Thanks.
--RJ
P.S. Note - I do have a heat strip, but it doesn't work that well. Also, I can borrow a friend's electric space heater, but my experience with them in the camper is that they don't work very well, either (the confined but relatively drafty spaces seem to mess with the thermostats). I really want the furnace working correctly... Thanks!
__________________
1991 Airstream B190
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel
|
|
|
03-24-2006, 08:51 AM
|
#2
|
Rivet Master
1956 22' Safari
2015 27' Flying Cloud
Vintage Kin Owner
Conifer/Evergreen
, Colorado
Join Date: Feb 2002
Posts: 12,777
|
I would start with taking it apart and cleaning everything. A build-up of "gunk" could be causing the motor to labor on intial start-up. You may then also be able to see if a new motor is a viable fix.
If the cleaning works, your home free. If not and you do need a new motor, I would invest in one of two things either an inexpensive ceramic heater (assuming you have electric hook-ups) or a good set of earplugs to get you through the next couple of nights.
Shari
|
|
|
03-24-2006, 08:53 AM
|
#3
|
Rivet Master
1993 30' Excella
whitewater
, north of cheddar curtain
Join Date: Jun 2003
Posts: 1,259
|
hi rj,
id check to see if the squirrel cage is loose on the shaft...if so reseting and adjusting should do it. i believe that most likely is your problem
norby
__________________
Illegitimous noncarborundum(dont let the bastards wear you down)
The only true nobility is found through giving good food to your friends- Anton Careme
beauty is in the eye of the beerholder-cosmo fishhawk
if something is too good to be true, its usually gone before i get there-mister boffo
|
|
|
03-24-2006, 12:23 PM
|
#4
|
Rivet Master
1979 30' Argosy
Havelock
, where we park it
Join Date: Jun 2003
Posts: 1,652
|
RJ. Same thing happened to us about a month ago on our 5th wheel, if I went outside and hit the side of the trailer near the exaust it would quit squeeking, after a few times of that I took it out and the fan motor bearings were going bad and replaced the motor. $106.00 later it works great. It would only make this noise at start up. Hope this helps.
__________________
Marvin & Annie
Niki (fur baby)
1979 Argosy 30 (Costalotta)
WBCCI 10103
"Happiness is a warm Puppy" Charles Schulz
|
|
|
03-24-2006, 01:14 PM
|
#5
|
Rivet Master
1995 30' Excella
Bowie
, Maryland
Join Date: Apr 2005
Posts: 2,346
|
Hitting it doesn't help the squeaking. When I hit it, it stops squeaking for a only for very brief moment - which gives evidence to the squirrel cage misalignment theory, I hope.
__________________
1991 Airstream B190
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel
|
|
|
03-28-2006, 07:34 PM
|
#6
|
Rivet Master
1995 30' Excella
Bowie
, Maryland
Join Date: Apr 2005
Posts: 2,346
|
Hey, everyone - the squeal woke me up several times one night, so I went the following night without heat at all (yeah, it got kind of cold). I called a service guy who came out to the camper, pulled the unit, and replaced the motor (and cleaned the furnace). Works GREAT now - I can barely even hear it running. Thanks for the advice and suggestions - your comments helped me understand what to expect when the bill arrived.
Funny story: When we put it back in and tested it, it initially wouldn't stay lit - it would spark then shut right down. After a few minutes of both of us scratching our heads, I went out to make sure I had actually turned on the gas, and I noticed that the tape he'd put over the exhaust while the furnace was out was still in place. I pulled off the tape and it fired right up. We had to laugh.
__________________
1991 Airstream B190
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel
|
|
|
03-28-2006, 07:58 PM
|
#7
|
Rivet Master
1956 22' Safari
2015 27' Flying Cloud
Vintage Kin Owner
Conifer/Evergreen
, Colorado
Join Date: Feb 2002
Posts: 12,777
|
Glad to hear you are warm & toasty in your toaster once again!
Shari
|
|
|
03-28-2006, 09:02 PM
|
#8
|
Rivet Master
Commercial Member
Vintage Kin Owner
Naples
, Florida
Join Date: Dec 2005
Posts: 7,512
|
Quote:
Originally Posted by Skater
Hey, everyone - the squeal woke me up several times one night, so I went the following night without heat at all (yeah, it got kind of cold). I called a service guy who came out to the camper, pulled the unit, and replaced the motor (and cleaned the furnace). Works GREAT now - I can barely even hear it running. Thanks for the advice and suggestions - your comments helped me understand what to expect when the bill arrived.
Funny story: When we put it back in and tested it, it initially wouldn't stay lit - it would spark then shut right down. After a few minutes of both of us scratching our heads, I went out to make sure I had actually turned on the gas, and I noticed that the tape he'd put over the exhaust while the furnace was out was still in place. I pulled off the tape and it fired right up. We had to laugh.
|
That IS a good one. They don't work too well when the exhaust path is blocked. At least now you know that the ECO (high temp limit switch)on the furnace is working .
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
|
|
|
12-23-2009, 07:30 PM
|
#9
|
Rivet Master
1995 30' Excella
Bowie
, Maryland
Join Date: Apr 2005
Posts: 2,346
|
Hi. Time to dredge up an old thread. Unfortunately the problem is back, which is rather frustrating. I'm thinking it's time to replace the motor (again) and both fan blades - I'm just tired of dealing with it. Anyone have any more thoughts on this?
I've played with it on several occasions. There's a metal clip on the one set of blades, which I believe is intended to be a counterweight. I'm not sure if the problem is that the clip is loose or what. My theory is that one or both of the blades is off balance, which kills the bearings on the motor...
__________________
1991 Airstream B190
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel
|
|
|
03-02-2010, 06:50 PM
|
#10
|
Rivet Master
1995 30' Excella
Bowie
, Maryland
Join Date: Apr 2005
Posts: 2,346
|
Another update on this: I bought a new motor and a new combustion blade; the squirrel cage blade was no longer available for sale.
The motor I pulled out may have been the original motor - I'm not sure if the guy replaced it or not. He told me he did, but there was some rust on the shaft that didn't look to me like it'd be just a few years old. Also, I had to bend the metal combustion blades to get the set screw loose...which makes me wonder how he would've been able to do it. I managed to break an allen wrench off in the set screw while trying to loosen it!
The new combustion blades are actually plastic. I put them in with the new motor and it's running quiet again! Hopefully it stays that way this time. Part of me hopes that the guy didn't actually replace the motor the first time, because then that means this should fix it ... but it would also mean that he lied to me, which doesn't make me very happy. I suspect he took it apart in his warm shop, cleaned it, put it back together and found the squealing gone (which makes sense because it didn't squeal when it was warm), and called it good.
Thanks again for the help. I hope this is the last time I ever have to update this thread.
__________________
1991 Airstream B190
1995 Airstream Classic 30' Excella 1000
2014 Ram 2500 Crew Cab with Cummins 6.7L Diesel
|
|
|
01-24-2011, 07:00 AM
|
#11
|
2 Rivet Member
1992 34' Excella
riverhead
, New York
Join Date: Jan 2006
Posts: 72
|
Squealing Furnace Syndrom!
I have a 1992 34' Excella and my furnace is starting to squeal from time to time, usually on start up and rarely while running. My buddy has the same rig as we do except his is a 1993. He has the squealing issue for about a year. The difference between the two of us is that we are Full Timers.
Anyway, I appreciate the thread and all the contributors and at least feel up to the challenge that seems to be ahead of me. The only question I have is the Skater, it seems that you replaced the motor - what went wrong after less than 3 years? Was it the squirrel cages that perhaps should have been replaced when you did the motor? Are the plastic squirrel cages better than the metal?
__________________
Joe Colao 50th Anniversary President of Metro NY WBCCI # 30916
KC2RAR
|
|
|
01-24-2011, 07:26 AM
|
#12
|
Rivet Idiot
1999 34' Excella
Currently Looking...
Currently Looking...
On The Lake
, Georgia
Join Date: Apr 2009
Posts: 1,000
|
Hi Joe,
I just replaced my fan motor in my NT 30 furnace last week. Wasn't to bad of a job once I figured out how to get everything out. If you need help, send me a PM or I'll be watching this thread. I think the place I got my motor from had the metal squirrel cages as well.
regards,
Joe
__________________
Annette
|
|
|
01-24-2011, 08:03 AM
|
#13
|
Rivet Master
Airstream Dealer
Corona
, California
Join Date: Feb 2002
Posts: 16,497
|
The squeal noise from the furnaces, is some what common.
It's caused by the bearings in the motor becoming "'dry".
If your handy, you can disassemble the motor and lube the bearings, several times, so that the oil can soak in.
Andy
|
|
|
01-24-2011, 08:51 AM
|
#14
|
3 Rivet Member
1997 30' Limited
Omaha
, Nebraska
Join Date: Aug 2009
Posts: 119
|
I, too, had a squealing Atwood furnace motor last October, while in Moab. The squeal was so loud I thought we'd wake the neighbors! The temps were in the low 30's so the furnace was cycling pretty often. Kept me awake. The nearest motor was in Durango, CO.
http://www.airforums.com/forums/f313...per-70157.html
This link helped me replace the motor. This motor comes as a kit with new mounting brackets and a metal piece that keeps the motor from coming out of the bracket. New blower wheels probably are unnecessary. I did put a mat on the ground under the heater to catch dropped screws and was glad I did. The project took about two beers to complete.
The new motor seemed noticeably quieter than the squealer before it started squealing.
__________________
Rig: '97 30' Limited
Towed by: '19 Silverado 2500 Duramax
WBCCI #22116
|
|
|
01-24-2011, 09:18 AM
|
#15
|
Wise Elder
2010 30' Classic
Vintage Kin Owner
South of the river
, Minnesota
Join Date: Dec 2009
Posts: 4,169
|
DC blower motors usually do fail due to bearing failure caused by seal failure and loss of lubrication.
When a replacement motor is unavailable or excessively costly it is possible to disassemble the motor and lubricate the bearings. I have done this several times on cars, trucks, and ag equipment, though never on a furnace. My experience has been that it doesn't always help (sometimes the bearings are too far gone for lubrication to help), and at best it's a fix that will last a few years. After all, it's the seal failure that led to the problem in the first place, and squirting some oil in there doesn't do anything to fix that.
I had a planter (for corn) that had individual electric blowers for each row to provide air for the metering system. I ended up drilling holes on the outside of the motors so I could drizzle in some oil every year. It worked out OK but then the motors were easily accessible.
I'm guessing Skater's rv tech may have re-oiled the bearings for similar reasons. It can be nearly impossible to remove a badly rusted blower wheel without damaging it and without a replacement wheel in hand it would be tempting to take shortcuts.
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
Similar Threads
|
Thread |
Thread Starter |
Forum |
Replies |
Last Post |
72 Airstream International Furnace parts
|
loechli |
Furnaces, Heaters, Fireplaces & Air Conditioning |
7 |
08-20-2008 07:17 PM |
Furnace stuff...
|
Chuck |
Furnaces, Heaters, Fireplaces & Air Conditioning |
11 |
12-02-2002 05:36 PM |
Jingle Bell Furnace Fix
|
Pahaska |
Furnaces, Heaters, Fireplaces & Air Conditioning |
5 |
11-19-2002 09:59 PM |
Forced Air furnace
|
Joan D'Andrea |
Furnaces, Heaters, Fireplaces & Air Conditioning |
16 |
11-02-2002 09:41 PM |
Furnace problems...
|
Andy R |
Furnaces, Heaters, Fireplaces & Air Conditioning |
3 |
04-01-2002 08:29 PM |
|
Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|