Quote:
Originally Posted by DaveG View Post
Did some more digging for info and found one issue so far. Using a surge softening device located at the pedestal will place inverter (if you have one) in the middle between power source and load. Apparently an inline inverter is not happy with this and will shutdown at the leading edge of a ramping up A/C load.
You don't run an inverter though when you're on shore power...
RickBullotta is offline   Reply With Quote
Old 05-31-2023, 06:01 AM   #22
4 Rivet Member
 
2022 27' Globetrotter
Bethlehem , Pennsylvania
Join Date: Oct 2020
Posts: 361
Quote:
Originally Posted by DaveG View Post
Did some more digging for info and found one issue so far. Using a surge softening device located at the pedestal will place inverter (if you have one) in the middle between power source and load. Apparently an inline inverter is not happy with this and will shutdown at the leading edge of a ramping up A/C load.
I can appreciate the concern with potential impacts on other devices but why would one have the inverter turned on if you also have a generator running?
Merlintiaga is offline   Reply With Quote
Old 05-31-2023, 07:16 AM   #23
4 Rivet Member
 
2017 30' Classic
Cave Creek , Arizona
Join Date: Aug 2016
Posts: 282
Blog Entries: 1
EZ alternative to adding soft-start to AC

Quote:
Originally Posted by RickBullotta View Post
You don't run an inverter though when you're on shore power...


The Victron Multiplus 3000, a popular inverter, has a useful assist mode. If shore power is less than the the trailer full electrical demand, it will draw from the batteries to source additional 115V current. So for example when on 30A shore service, when two ACs or an AC and microwave turn on, the Multiplus can provide a short-term 50A equivalent service.
__________________
Pete B55
2017 Classic
2017 F-250
Pete B55 is offline   Reply With Quote
Old 05-31-2023, 07:29 AM   #24
Rivet Master
 
Boxite's Avatar
 
2008 22' Safari
Spicewood (W of Austin) , Texas
Join Date: Mar 2015
Posts: 2,987
It seems to me that some illogical thinking has crept into the conversation regarding this “soft start” device and an inverter shutting down due to that soft-start in-rush current:

First of all…an Inverter does not take IN alternating current. It’s source current is DC….which it “inverts” into Alternating Current…. AC.

Therefore, I doubt an on-board inverter will be affected by this soft-start device.
Boxite is offline   Reply With Quote
Old 05-31-2023, 08:38 AM   #25
4 Rivet Member
 
DaveG's Avatar
 
Here and There , West Coast
Join Date: Apr 2019
Posts: 433
Quote:
Originally Posted by daleyocum View Post
These devices aren’t, however, capacitors. They are microprocessor controlled waveform modifiers.
Okay, above my pay grade. I'll stay old school until all the players (microwave etc) agree to the same ideas for power. Often ideas get on shelves quickly and consumers become the testers. Don't know if this is the case with this device. Concept seems like a good one.
DaveG is offline   Reply With Quote
Old 05-31-2023, 08:44 AM   #26
4 Rivet Member
 
DaveG's Avatar
 
Here and There , West Coast
Join Date: Apr 2019
Posts: 433
Quote:
Originally Posted by Pete B55 View Post
The Victron Multiplus 3000, a popular inverter, has a useful assist mode. If shore power is less than the the trailer full electrical demand, it will draw from the batteries to source additional 115V current. So for example when on 30A shore service, when two ACs or an AC and microwave turn on, the Multiplus can provide a short-term 50A equivalent service.
This looks like what I read. The statement stated something like "tries to pick up the load".
DaveG is offline   Reply With Quote
Old 05-31-2023, 11:23 AM   #27
4 Rivet Member
 
2017 30' Classic
Cave Creek , Arizona
Join Date: Aug 2016
Posts: 282
Blog Entries: 1
EZ alternative to adding soft-start to AC

Quote:
Originally Posted by Boxite View Post
It seems to me that some illogical thinking has crept into the conversation regarding this “soft start” device and an inverter shutting down due to that soft-start in-rush current:



First of all…an Inverter does not take IN alternating current. It’s source current is DC….which it “inverts” into Alternating Current…. AC.



Therefore, I doubt an on-board inverter will be affected by this soft-start device.


I think this is a valid point. An inverter is not a real issue. However, Anytime you have a situation of limited power and reactive loads, active power factor correction devices become useful whether they are whole trailer devices like what the OP wrote about or Micro-Air type devices that are located at the appliance. The difference that I see is that local devices provide greater capability- these devices go through a learning mode to adjust themselves specifically for the attached appliance startup draw and reactive power factor - and ultimately provide for longer life of the appliance. The “whole trailer” device doesn’t have the same opportunity to learn and optimize because it is handling multiple power loads that vary depending on what and when you turn something on in the trailer.

Again, with limited power source this is better than nothing, but not as optimal as a local device.
__________________
Pete B55
2017 Classic
2017 F-250
Pete B55 is offline   Reply With Quote
Old 06-01-2023, 06:39 AM   #28
New Member
 
Washington , Illinois
Join Date: Sep 2021
Posts: 3
Yes, There is an app you download and it tells you the current draw
Underdoggie is offline   Reply With Quote
Old 06-01-2023, 10:45 AM   #29
Site Team
 
richard5933's Avatar

 
1994 25' Excella
Waukesha , Wisconsin
Join Date: Sep 2020
Posts: 5,580
Images: 5
My impression is that the more 'universal' a product tries to be the less it actually helps in the specific products.

Having a surge protector built into this plug-in device is good, but that's a far cry from what a device like a true EMS will do such as low-voltage protection, etc.

My money is on getting devices specific to the problem at hand.
__________________
Richard
11018
1994 Excella 25 Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser (Sold)
richard5933 is offline   Reply With Quote
Old 06-01-2023, 12:44 PM   #30
"Silver Shrek"
 
drairstream's Avatar
 
2000 27' Safari
Crestwood , Kentucky
Join Date: Jul 2016
Posts: 184
Thinking it would be a magnet for thieves.
drairstream is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Soft Start Kit For A/C 3bcamper Sprinter and B-van Forum 50 04-21-2024 10:26 AM
Soft Start - Easy Start - Smart Start..? JConsroe Generators & Solar Power 14 01-20-2023 04:44 PM
A/C start-up w/ soft start Pimms Furnaces, Heaters, Fireplaces & Air Conditioning 37 11-05-2022 03:46 AM
Soft start for air conditioner in the DFW metroplex cfishii Our Community 9 07-18-2019 08:09 PM
Soft start installation in the DFW Metroplex cfishii Electrical - Systems, Generators, Batteries & Solar 0 07-06-2019 02:27 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 05:27 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.