AC icing up

I'm hoping for some perspectives on what's going wrong with my AC, which is icing up. Here are the details.

Last summer, it worked great. It's a 2015, ducted, and last summer was my first season using it to cool.
This summer, it cools for the first 60-90 minutes, but ice forms on the unit, which I can tell because there is no condensate via the weep tube. Then the ice layer becomes too much, and cooling fails.
If I turn on the heat pump to clear the fins, I get a flood of water via the weep tube (so the tubes are not blocked), and once the ice is off the unit, I can turn it to cool again for another 60-90 minutes.
When it's cooling, the humidity in the cabin goes from 55% to 30%. It goes back up while the heat pump is on (if I manually switch it to clear the ice), then it descends again to 30% when I turn the AC cool mode back on.

I've tried High fan speed only, on the theory there wasn't enough airflow, but it was fine on low last summer. And whether I use Hi or Low this time, it still ices up.
Visual inspection shows nothing obvious blocking airflow, either inside or out. The interior air filters are clean. It's pulling air through the intake vents OK.

I called the dealer who said there were some bad compressors in 2015. But if it's cooling and heating, would that really indicate a bad compressor?

And a local mobile repair person said he doesn't work on them, (but he'll replace them with new units), because Dometic units don't allow for a recharge if you lose the coolant. Is that accurate? Seems odd to me.

The air temperature coming out of the vents while cooling is 12-15° cooler than the air going in.

Complicating this is the fact I'm full-timing, and not wanting to tow it to a dealer. I'd want a mobile repair person, so it would be great to have an idea of the problem before setting up the repair...

thanks!
lbdesign is offline   Reply With Quote
Old 05-04-2017, 05:21 PM   #2
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by lbdesign View Post
I'm hoping for some perspectives on what's going wrong with my AC, which is icing up. Here are the details.

Last summer, it worked great. It's a 2015, ducted, and last summer was my first season using it to cool.
This summer, it cools for the first 60-90 minutes, but ice forms on the unit, which I can tell because there is no condensate via the weep tube. Then the ice layer becomes too much, and cooling fails.
If I turn on the heat pump to clear the fins, I get a flood of water via the weep tube (so the tubes are not blocked), and once the ice is off the unit, I can turn it to cool again for another 60-90 minutes.
When it's cooling, the humidity in the cabin goes from 55% to 30%. It goes back up while the heat pump is on (if I manually switch it to clear the ice), then it descends again to 30% when I turn the AC cool mode back on.

I've tried High fan speed only, on the theory there wasn't enough airflow, but it was fine on low last summer. And whether I use Hi or Low this time, it still ices up.
Visual inspection shows nothing obvious blocking airflow, either inside or out. The interior air filters are clean. It's pulling air through the intake vents OK.

I called the dealer who said there were some bad compressors in 2015. But if it's cooling and heating, would that really indicate a bad compressor?

And a local mobile repair person said he doesn't work on them, (but he'll replace them with new units), because Dometic units don't allow for a recharge if you lose the coolant. Is that accurate? Seems odd to me.

The air temperature coming out of the vents while cooling is 12-15° cooler than the air going in.

Complicating this is the fact I'm full-timing, and not wanting to tow it to a dealer. I'd want a mobile repair person, so it would be great to have an idea of the problem before setting up the repair...

thanks!
lb,

You are on the right track, but there are more issues with evaporator freezing than simply air flow across the evap. coils.

One major issues tha many neglect is improper mixing of return air with cooled exhaust air. If the return ducting is not properly sealed and this return air mixes with the cooed air exiting the eval. area of the unit, freezing can quickly occur.

In addition, every Dometic unit has a freeze sensor probe that should be placed directly into the eval. coils. Some are never properly placed by the installing tech and some fall out. That would be the first thing I would check with the separation of return and exhaust air next.

Also, while you have the eval section opened, I would definitely use a quality coil cleaning spray (available from any good A/C supply house) and clean bot the condenser and evaporator.

After doing the above (hopefully you found an issue), button it back up and see if you have it fixed.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 05-04-2017, 05:26 PM   #3
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
As for the "replace, not repair" statement, it is entirely correct. Nobody repairs most a/c unit issues, such as low refrigerant or bad compressor. A bad fan motor or some electronic componets are replaceable.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 05-04-2017, 07:30 PM   #4
3 Rivet Member
 
2004 22' International CCD
2015 30' International
Box Elder , South Dakota
Join Date: Mar 2011
Posts: 187
Quote:
Originally Posted by lewster View Post
lb,
One major issues tha many neglect is improper mixing of return air with cooled exhaust air. If the return ducting is not properly sealed and this return air mixes with the cooed air exiting the eval. area of the unit, freezing can quickly occur.

In addition, every Dometic unit has a freeze sensor probe that should be placed directly into the eval. coils. Some are never properly placed by the installing tech and some fall out. That would be the first thing I would check with the separation of return and exhaust air next.
Thank you! it's a total rat's nest of wires up in the ceiling, between the pretty intake covers that hide the mess, and the AC unit. I was surprised to find so many electrical wires criss-crossing this area, which means it's not sealed, otherwise how would the wires penetrate it? One of the wires is hanging down, and looks like it could be a probe. I'll examine it again.

And it does strike me that the entire cavity behind the intake covers is not sealed. Though it would be no less sealed this year than it was last year...
lbdesign is offline   Reply With Quote
Old 05-04-2017, 07:32 PM   #5
3 Rivet Member
 
2004 22' International CCD
2015 30' International
Box Elder , South Dakota
Join Date: Mar 2011
Posts: 187
One other possible bit of info:
I'm parked in full sun. When it's 82° inside and I turn the AC on, it's still just 70° outside. Could it be too cool outside for proper AC function?
lbdesign is offline   Reply With Quote
Old 05-04-2017, 08:22 PM   #6
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
No photo
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 05-04-2017, 08:28 PM   #7
3 Rivet Member
 
2004 22' International CCD
2015 30' International
Box Elder , South Dakota
Join Date: Mar 2011
Posts: 187
Sorry, it was not allowing images from my server.

Could this be the probe? There is a wrinkle/gap in the fins up in there where a probe might have been inserted, held in only by friction?
Attached Thumbnails
Click image for larger version

Name:	possible-ac-probe.jpg
Views:	87
Size:	119.5 KB
ID:	284769  
lbdesign is offline   Reply With Quote
Old 05-04-2017, 09:15 PM   #8
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by lbdesign View Post
Sorry, it was not allowing images from my server.

Could this be the probe? There is a wrinkle/gap in the fins up in there where a probe might have been inserted, held in only by friction?
Sure looks like a freeze sensor to me. Just jam that little device right back where it came from and hopefully, your problems will be solved.

I wold also check the separation of the return air from the cooled air blowing into the ductwork.......very important also!!!
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 05-04-2017, 09:49 PM   #9
3 Rivet Member
 
2004 22' International CCD
2015 30' International
Box Elder , South Dakota
Join Date: Mar 2011
Posts: 187
Fantastic! Thanks Lew!
Can hardly wait to try the AC tomorrow!
lbdesign is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:51 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.