Old 06-26-2016, 10:19 AM   #1
Rivet Master
 
SuzyHomemakr's Avatar
 
1972 29' Ambassador
Boynton Beach , Florida
Join Date: Dec 2013
Posts: 568
A/C keeps throwing breaker

Ack! My not-quite-two-year-old Dometic DUO THERM Brisk II RV Compact Air Conditioner 15000 BTU keeps intermittently throwing its 20A breaker. I've got a EMS-HW30C surge-dip protector in-line, and sometimes that drops out, which then kicks the A/C breaker when it restores the power. Also, typically when the A/C is turned on, the inverter kicks into invert mode for a minute, even though the trailer is still plugged in.

This happens mostly on hot days, rarely at home, more often in camp.

All this points to a huge power draw... I installed the hard-start kit, but little joy there. The A/C otherwise works fine, an R/V tech came out and pronounced it working well. Granted, all he did was stick a thermometer in it.

Is there some sort of super-capacitor that I can get? This is Florida in the summertime, I gotta get my system more reliable! Help this sweaty camper, please!
SuzyHomemakr is offline   Reply With Quote
Old 06-26-2016, 10:27 AM   #2
Rivet Master
 
Currently Looking...
Mantua , Ohio
Join Date: Jul 2005
Posts: 7,062
Blog Entries: 2
20 amp for a 15000? Might be overloaded in hot weather. Is your home circuit 20 or 15 amp?
xrvr is offline   Reply With Quote
Old 06-26-2016, 10:37 AM   #3
Rivet Master
 
2007 27' Classic FB
Ridgefield , Washington
Join Date: Jul 2010
Posts: 580
Images: 11
We had a similar problem in the past. When using the A/C, we put the hot water heater and fridge on LP. No popped circuit breaker on the A/C when we do this. Hope that helps.
__________________
John
Woosch is offline   Reply With Quote
Old 06-26-2016, 10:52 AM   #4
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 7,070
Images: 12
The common reason is Low Voltage. Many campgrounds are not wire for the current day number of units using lots of power.

Memorial Day weekend we were in a campground with recently upgraded power, 50 amp. We had low voltage, 102 volts on a 30 amp breaker, and could not use the AC. Even those attempting to keep up are falling behind.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 06-26-2016, 11:44 AM   #5
Rivet Master
 
HiHoAgRV's Avatar

 
1991 34' Excella
1963 26' Overlander
1961 26' Overlander
Central , Mississippi
Join Date: Nov 2006
Posts: 5,919
Images: 29
Blog Entries: 49
For under $10, try replacing the 20A breaker with a new one. We had a similar problem with a '77 and the old breaker was simply worn out.
__________________
Hi Ho Silver RV! Vernon, Sarah, Mac the Border Collie(RIP) -
A honkin' long 34' named AlumaTherapy https://www.airforums.com/forums/f20...num-54749.html
and a 26' '63 Overlander, Dolly https://www.airforums.com/forums/f10...ome-71609.html
HiHoAgRV is offline   Reply With Quote
Old 06-26-2016, 11:45 AM   #6
2 Rivet Member
 
2012 27' FB Eddie Bauer
Laguna Niguel , California
Join Date: Jun 2011
Posts: 23
Same thing with my Eddie Bauer 27ft. I cant run the A/C when the water heater is on electric power or POP Goes the breaker and if its real hot you my need to put the frig on propane too.
TSOMMY is offline   Reply With Quote
Old 06-26-2016, 12:22 PM   #7
Rivet Master
 
SuzyHomemakr's Avatar
 
1972 29' Ambassador
Boynton Beach , Florida
Join Date: Dec 2013
Posts: 568
Now it's popping all of the time, here at home. Heat index is 100. It's plugged into a 30A circuit, the trailer all by itself. Fridge and inverter are running, but that's about it. Fridge is already cold. I can watch the voltage drop as the compressor struggles, until the surge/dip protector chops the circuit.

I'm beginning to think that I have a bad compressor. Fan part of the A/C works fine.
SuzyHomemakr is offline   Reply With Quote
Old 06-26-2016, 12:32 PM   #8
4 Rivet Member
 
1977 31' Sovereign
Lynnwood , Washington
Join Date: Jan 2015
Posts: 311
I presume your 15K AC is an upgrade from 13.5K, correct??

Granted, the 1.5K upgrade doesn't seem like much. But when push comes to shove, something's gotta give. In this case, your 20 amp breaker is working as intended.

As they say, "Lunch is never free."

Try replacing with a new 20 amp. Your original breaker may be old and tired.

BTW - You've gotta resist the temptation of installing a higher amperage breaker.

Tom
TomKirk is offline   Reply With Quote
Old 06-26-2016, 01:01 PM   #9
4 Rivet Member
 
1973 31' Sovereign
Middletown , California
Join Date: Oct 2013
Posts: 424
There is not much you can do if the problem is low voltage except try another source for the power. Maybe move to another space? Good idea about the breaker being old, or it could be making poor contact with the bus bar. Check to see if the breaker is pushed on all the way and feel it when AC is running normal and if it's very warm that could be the problem. Always a good idea to keep a volt meter handy to see what you've got coming in for volts. The service guy you called should have checked the volts and amps or if he was good he should own a watt meter. The manufacturers of AC's usually publish a table of watts used at specific temperatures of operation and that is vital info when having problems like this. The most difficult type of problem to fix is things like this which are working, but not quite good enough!
ijustlee is offline   Reply With Quote
Old 06-26-2016, 01:01 PM   #10
3 Rivet Member
 
iowaroots's Avatar
 
Currently Looking...
Dallas Center/Des Moines , Iowa
Join Date: May 2004
Posts: 142
Progressive Ind

Perhaps give a call to Progressive Industries. It sounds like the EMS is doing its job and protecting your equipment from low voltage.
iowaroots is offline   Reply With Quote
Old 06-26-2016, 02:17 PM   #11
BradT
 
2007 27' Safari FB SE
Milton , Georgia
Join Date: Nov 2013
Posts: 71
Some electrical things I would check-

Check the shore power cord to be sure the end plugged into the campsite power is not getting hot. Sometimes the molded plug can get a weak connection causing low voltage.

Tighten screw terminals at your breaker box, but make sure power is off to do this. They can loosen from vibration on the road.

There is a run capacitor for the AC fan. If it is weak, fan will still run but draw more current than usual. Capacitors degrade over time. Lightning spikes and excessive heat speed up decline.

Compressor has run cap too. Separate from start cap where you added hard start kit already.

The only supercapacitor I know to suggest is a good name brand like GE and a step higher voltage, like 440Vac. Higher voltage cap will last longer. Keep the same capacitance value. If a cap is cheap & weak to start with, it can fail early. Weak caps are very common HVAC failure causes.

If your low voltage protector system turns off power to AC unit, it needs to wait 5 minutes before restarting compressor to let pressure drop. If it is attempting to restart right away, that will surely blow breaker.

12vdc thermostat controls might need to be reset at same time as 120vac is switched off to insure 5 minute delay before compressor re-start.

Use a voltmeter to measure your voltage to make sure the low voltage protector is behaving properly. It could be nuisance tripping and need adjustment or repair.

If inverter has been running while power was off, it will draw down house batteries. When AC power is restored, the converter will momentarily draw a lot of ac power to recharge the batteries. This would occur at the same time as the compressor is attempting to start. Try to manually turn inverter off and other loads while trouble shooting this problem. It will reduce the number of things happening at once.

Hope, eventually, you can stay cool.

Bradt
bradt is offline   Reply With Quote
Old 06-26-2016, 02:29 PM   #12
Rivet Master
 
Currently Looking...
Mantua , Ohio
Join Date: Jul 2005
Posts: 7,062
Blog Entries: 2
If you ran the air on low voltage, twenty amp for a long time, the compresser may be toast.
xrvr is offline   Reply With Quote
Old 06-26-2016, 02:39 PM   #13
3 Rivet Member
 
crestonrv's Avatar
 
1948 16' Wee Wind
1964 26' Overlander
2007 19' Bambi
crossville , Tennessee
Join Date: Jun 2006
Posts: 190
Images: 7
Blog Entries: 5
might want to have a real tech put an amp meter on compressor feed at roof !
note has 3 year war. sounds like compressor is going out and current repair is to replace a/c ( if still in war need to have checked at dometic warr station )
most rv dealers have dometic warr statis .
we don't recharge / replace charged system components anymore , thanks to epa/ snap protocol. if amp draw to comp exceeds spec or flutters is bad comp .
could from sound of it be bad time delay relay . I do know that dom. is having some problems . we have recently replaced 3 a/cs that were under warr 1 was for bad compressor 2 for loosing charge .
crestonrv is offline   Reply With Quote
Old 07-01-2016, 06:02 AM   #14
Rivet Master
 
SuzyHomemakr's Avatar
 
1972 29' Ambassador
Boynton Beach , Florida
Join Date: Dec 2013
Posts: 568
It looks like it was a bad compressor. I took the trailer into the good folks at Stomski Trailer in Lake Worth, FL. After much back and forth with Dometic (on Stomski's part), the entire upper unit is being replaced under warranty.

At least it happened one month before the warranty was due to expire!

Thanks to all for the suggestions! Now I get to wait on parts to arrive...
SuzyHomemakr is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Throwing code P0544 on quick startup dre00 Sprinter and B-van Forum 1 05-17-2014 03:15 PM
Throwing in the DIY towel captmatt 1984 - 1989 Sovereign 12 05-02-2014 07:46 PM
Comfy with 12V, but 120V is throwing me... SafariFaye Batteries, Univolts, Converters & Inverters 19 05-06-2012 07:29 PM
Throwing money at it, or not? funkill Tow Vehicles 28 06-13-2010 01:55 PM
GFI breaker keeps tripping. Van Electrical - Systems, Generators, Batteries & Solar 10 08-06-2005 11:33 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 07:55 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.