2020 Flying Cloud 2 ACs Behavior Question

Our FC has two air conditioners with "2 zones" and have found the way it works to be a bit odd and, therefore, have wondered if it is the expected behavior. It seems that no matter what AC is running, air is blowing out all the vents with most of the air going to the RB area. This means that the RB area cools down first. The other night the difference between the RB area and front lounge ended up being very significant. It was 76 up front and 64 in the back.
With two zones, I expected the air to stop blowing in the back when it reached the desired temperature, but that did not happen, although the Zone 1 AC did turn off.
DanHogHunter is offline   Reply With Quote
Old 08-04-2020, 10:53 AM   #2
4 Rivet Member
 
2017 27' Flying Cloud
London , Ontario
Join Date: Jul 2016
Posts: 250
The ducts throughout are attached therefore there is no discrete zone 1 and 2. Whatever flow is generated is dictated by the vents being open or closed. So, you could play with the flow to either area by opening or closing vents selectively. (BTW Zone 1 is the zone for the main thermostat.)

In our 27 FB, the thermistor for zone 2 (dinette/kitchen) is behind the TV. This zone is therefore always a few degrees "warmer" even when all windows are open and no AC is on. Therefore, to achieve equal temperatures, we find that we have to set zone 2 a couple of degrees warmer than zone 1.

Confusing.
__________________
-----
27FB 2017 Flying Cloud
F-150 Lariat

Ham Radio Callsign - VA3PGJ
Philip Jones is offline   Reply With Quote
Old 08-04-2020, 11:47 AM   #3
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,654
Blog Entries: 1
Quote:
Originally Posted by DanHogHunter View Post
Our FC has two air conditioners with "2 zones" and have found the way it works to be a bit odd and, therefore, have wondered if it is the expected behavior. It seems that no matter what AC is running, air is blowing out all the vents with most of the air going to the RB area.
The ducts are all one long tube. So some air from zone one will blow out of zone two. I find that just because of the longer distance more air from zone one will stay in zone one.
You could experiment by closing off some of the zone two vents.
If I run both ac's, to cool faster, I set the temperature slightly different. That stops both ac's from cycling on and off together.
At night to reduce noise, I'll run only zone one (living area) but still get some air in the bedroom.
Keep in mind, the thermostat is in zone one (at least on mine) and so it may be cooler there. Also if you set to 74f. it may cut on at 77f. and off at 72f. Usually, just about the time I think it's not coming on, it does.
What you wrote doesn't all match, so although you will get air in zone two from ac 1, it shouldn't be colder than zone one.
The fact that air is getting between zones makes me think there's no obstructions in the ducts.
Mollysdad is offline   Reply With Quote
Old 08-04-2020, 12:03 PM   #4
Rivet Master
 
2018 25' International
Slidell , Louisiana
Join Date: Sep 2017
Posts: 3,725
In addition to the common duct work as described, blown air back flows out the air intake on the unit that is off further distributing conditioned air to the unintended zone. Other than adjusting the vent dampers and offsetting the temperature settings (as others described) to get better balance I have yet to come up with any good ideas.

Continually running the fans is not a great solution especially while in a humid area works poorly because the airflow across the water pan and communication to the outside due to the overflow drain excessively raises the humidity inside the trailer.

Would love to hear some other ideas.
BayouBiker is offline   Reply With Quote
Old 08-04-2020, 01:19 PM   #5
2 Rivet Member
 
2020 30' Flying Cloud
Katy , Texas
Join Date: Jul 2020
Posts: 34
Quote:
Originally Posted by Mollysdad View Post
The ducts are all one long tube. So some air from zone one will blow out of zone two. I find that just because of the longer distance more air from zone one will stay in zone one.
You could experiment by closing off some of the zone two vents.
If I run both ac's, to cool faster, I set the temperature slightly different. That stops both ac's from cycling on and off together.
At night to reduce noise, I'll run only zone one (living area) but still get some air in the bedroom.
Keep in mind, the thermostat is in zone one (at least on mine) and so it may be cooler there. Also if you set to 74f. it may cut on at 77f. and off at 72f. Usually, just about the time I think it's not coming on, it does.
What you wrote doesn't all match, so although you will get air in zone two from ac 1, it shouldn't be colder than zone one.
The fact that air is getting between zones makes me think there's no obstructions in the ducts.

We seem to be getting more air in zone one (the bedroom in our trailer) no matter which air conditioner is running.


I plan to slightly close off the bedroom vents to see if I can balance the air flow a bit.


Thanks, the information that there is only one duct reassures me that there's not a problem with that part of the air conditioner.
DanHogHunter is offline   Reply With Quote
Old 08-04-2020, 01:22 PM   #6
2 Rivet Member
 
2020 30' Flying Cloud
Katy , Texas
Join Date: Jul 2020
Posts: 34
Quote:
Originally Posted by BayouBiker View Post
In addition to the common duct work as described, blown air back flows out the air intake on the unit that is off further distributing conditioned air to the unintended zone. Other than adjusting the vent dampers and offsetting the temperature settings (as others described) to get better balance I have yet to come up with any good ideas.

Continually running the fans is not a great solution especially while in a humid area works poorly because the airflow across the water pan and communication to the outside due to the overflow drain excessively raises the humidity inside the trailer.

Would love to hear some other ideas.

I was aware of the humidity problem when running the fan continuously (thanks Dad ). I will try adjusting the vent dampers.
DanHogHunter is offline   Reply With Quote
Old 08-04-2020, 01:58 PM   #7
Rivet Master
 
2019 25' Flying Cloud
Houston , Texas
Join Date: Jan 2019
Posts: 1,013
Quote:
Originally Posted by Mollysdad View Post
If I run both ac's, to cool faster, I set the temperature slightly different. That stops both ac's from cycling on and off together.
I thought I read somewhere that the thermostat keeps the A/C's from starting at the same time.
DCPAS is offline   Reply With Quote
Old 08-04-2020, 02:40 PM   #8
Rivet Master
 
2007 27' International CCD FB
San Diego , California
Join Date: Sep 2014
Posts: 2,123
I find a small 12V Cigarette lighter / USB fan aimed down the hallway does wonders to balance the temperatures in the Airstream. Suction cups to the ceiling so easy to setup and remove.

Click image for larger version

Name:	ASfan.jpg
Views:	57
Size:	193.6 KB
ID:	374932
pteck is online now   Reply With Quote
Old 08-04-2020, 05:44 PM   #9
3 Rivet Member
 
2016 25' Flying Cloud
z , Texas
Join Date: Oct 2017
Posts: 177
This may have been coved, but if on 30amp and running one AC, would it be beneficial to run just the fan on the other AC ? This is something I have not tried, but I will this weekend
5150mike is offline   Reply With Quote
Old 08-05-2020, 06:26 AM   #10
Rivet Master
 
2018 25' International
Slidell , Louisiana
Join Date: Sep 2017
Posts: 3,725
Quote:
Originally Posted by 5150mike View Post
This may have been coved, but if on 30amp and running one AC, would it be beneficial to run just the fan on the other AC ? This is something I have not tried, but I will this weekend
It distributes the heat and cold nicely but if it's humid, it pulls in moisture from the evaporator drip pan and outside overflow. The humidity will rise to nearly match that of the outside down south in the summer its not a good option.
BayouBiker is offline   Reply With Quote
Old 08-05-2020, 10:00 AM   #11
2 Rivet Member
 
2020 30' Flying Cloud
Katy , Texas
Join Date: Jul 2020
Posts: 34
Quote:
Originally Posted by pteck View Post
I find a small 12V Cigarette lighter / USB fan aimed down the hallway does wonders to balance the temperatures in the Airstream. Suction cups to the ceiling so easy to setup and remove.

Attachment 374932

I like this idea!!! Can you point to a fan that you are using?
DanHogHunter is offline   Reply With Quote
Old 08-05-2020, 10:33 AM   #12
Rivet Master
 
2007 27' International CCD FB
San Diego , California
Join Date: Sep 2014
Posts: 2,123
Happy to. I got this one on Amazon. There's lots of different varieties including USB and rechargeable ones.

https://www.amazon.com/Electric-Cool...b-8a79de2d236f
pteck is online now   Reply With Quote
Old 08-06-2020, 07:04 AM   #13
2 Rivet Member
 
2020 28' Flying Cloud
on the road , TN
Join Date: Jan 2006
Posts: 57
Hi All
We have the FC 2020 28ft model! On 30 amp can only run just One unit! On 50 amp could run Both units! Having the Two units! Maybe in Hotter country the second might come in handy? And no matter where we travel we use our electric power unit to avoid high electric surges!
We like just running One unit suits us fine so far! The bedroom gets cooler so i close a vent! Other then that perfect for us it was hot and high humidity in June and it was perfect inside our Cloud! See you down the road, safe travels!
oldwagon is offline   Reply With Quote
Old 08-07-2020, 07:14 AM   #14
Rivet Master
 
2019 25' Flying Cloud
Houston , Texas
Join Date: Jan 2019
Posts: 1,013
Quote:
Originally Posted by oldwagon View Post
On 30 amp can only run just One unit! On 50 amp could run Both units!
Being in way too hot parts of Texas and having state parks with with 30 amp service max, I put Easy Starts on both A/C's. That allows us to run both A/C's, but you do have to be careful with power management. Run the water heater and fridge on gas, for example and you need to turn an A/C off if you want to run the microwave. Expensive to add two Easy Starts, but I would do it again in a heartbeat.
DCPAS is offline   Reply With Quote
Old 08-09-2020, 12:14 PM   #15
3 Rivet Member
 
2016 25' Flying Cloud
z , Texas
Join Date: Oct 2017
Posts: 177
Quote:
Originally Posted by BayouBiker View Post
It distributes the heat and cold nicely but if it's humid, it pulls in moisture from the evaporator drip pan and outside overflow. The humidity will rise to nearly match that of the outside down south in the summer its not a good option.
I did confirm this this weekend when running zone 2 (living room) with fan set to low when the compressor would go off and fan keeps running of course, well the humidity would go extremely high, but after getting the fan to auto it brought the humidity down,
5150mike is offline   Reply With Quote
Old 08-09-2020, 01:29 PM   #16
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,654
Blog Entries: 1
A 120v fan is a good idea. It helps move the air evenly throughout the trailer.
I have this one. It can hang on a wall or sit on a counter.
Amazon $20.
I also have a clip fan that is powered by the USB port. Super quiet. I have it on the magazine rack by the bed.
Attached Thumbnails
Click image for larger version

Name:	710uLfhv0XL._AC_SL1500_.jpg
Views:	62
Size:	50.8 KB
ID:	375331   Click image for larger version

Name:	71hBWGVMC-L._AC_SL1200_.jpg
Views:	29
Size:	67.1 KB
ID:	375333  

Mollysdad is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic RM3862 Refrigerator Cooling Behavior nickmeloy Refrigerators 14 06-08-2013 08:32 PM
PD9260 strange behavior Skater Batteries, Univolts, Converters & Inverters 12 04-13-2012 11:44 PM
Strange Hot Water Behavior Jim Foster Water Heaters, Filters & Pumps 4 05-28-2010 08:43 PM
Strange 12v Behavior in '67 GT tphillips Electrical - Systems, Generators, Batteries & Solar 2 10-08-2009 05:58 PM
Explain this Dump Valve behavior..... Chuck Waste Systems, Tanks & Totes 2 08-28-2003 11:18 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 11:14 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.