Old 04-17-2010, 08:49 PM   #1
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
what's going on here?

When our 08 27ft Classic is connected to an AC power source the electricty goes on and off intermittently. There is a "clunk" sound in the electrical panel when the juice goes off and the same noise when it comes back on. The noise is similar to a contacter for a large electric motor. Yes, it restores itself.

The breakers (Cutler Hammer), seem to be alright, snap on and off without being slushy and I replaced the GFCI. The problem is worse when the AC load is increased. Any ideas?
seacur50 is offline   Reply With Quote
Old 04-17-2010, 08:57 PM   #2
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,455
Images: 7
Do you have an inverter? Some inverters have a transfer switch that could be what you are hearing.

All power or just some outlets stop working?
__________________
Garry
garry is offline   Reply With Quote
Old 04-17-2010, 09:09 PM   #3
Moderator
 
moosetags's Avatar

 
2015 25' FB Flying Cloud
2012 23' FB Flying Cloud
2005 25' Safari
Santa Rosa Beach , Florida
Join Date: Jul 2006
Posts: 13,159
Images: 5
Greetings from the Florida Panhandle

First off, welcome to the Forums. We're glad to have you with us.

Are you connected to a dedicated 30 amp outlet? If you are connected to a standard 15 amp household outlet, you might be overloading the system causing it to react that way.

Brian
__________________
SuEllyn & Brian McCabe
WBCCI #3628 -- AIR #14872 -- TAC #FL-7
2015 FC 25' FB (Lucy) with ProPride
2020 Silverado 2500 (Vivian)
2023 Rivian R1T (Opal)
moosetags is online now   Reply With Quote
Old 04-18-2010, 10:13 AM   #4
1 Rivet Member
 
CountryBob's Avatar
 
2012 25' Flying Cloud
Manasquan , New Jersey
Join Date: Aug 2006
Posts: 16
Images: 1
Do you have a power monitor installed? It is installed prior to circuit breakers and will shutdown input current if certain requirements are not met like minimum voltage, bad ground etc....
CountryBob is offline   Reply With Quote
Old 04-18-2010, 12:46 PM   #5
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
No inverter Garry. The power failure seems to be complete when it occurs. Everything is working fine this morning (20A garage circuit). I'll hook up to the 2000i Companion when I'm back from fishing this PM. Should replicate the prob. The system pops off everytime the 30A outlet from the generator is used after about 3 minutes. Paralleled to a second 2000i same thing. Puzzleing.
seacur50 is offline   Reply With Quote
Old 04-18-2010, 12:58 PM   #6
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
20A from my garage Brian. The breaker at the garage subpanel does not trip. I am aware this source is underrated for the airconditioner/heat pump. It should run the other systems without any difficulties, it's working right now. The problem is at it's worst when I go to Honda power.--------Will post progress rpts. Tx Sea
seacur50 is offline   Reply With Quote
Old 04-18-2010, 01:09 PM   #7
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
I was not aware of such an animal Sir, but it meets all the criteria for prime suspect. I'll check it out this week. ------------Thanks
seacur50 is offline   Reply With Quote
Old 04-18-2010, 08:08 PM   #8
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,455
Images: 7
I was going to suggest other things (frig or freezer) on the garage circuit may be a problem but you say it happens on generator power also.

That makes it sound as if the problem has to be in the AS so I would pull the breaker panel cover and make sure ALL screws on the main, neutral and ground are good and tight. If that checks out I would suspect the shore power cord.
__________________
Garry
garry is offline   Reply With Quote
Old 04-19-2010, 09:49 AM   #9
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
Just finished tightening all terminations and the coverup plate removal inspection reveals disappointing findings. 1. The previous owner or unknown 3rd party has tighted the connections with an illfitting screwdriver 2. All terminations were tight 3. The vertical grounding bussbar on the lefthand side has been hot enough to melt point of contact on the plastic insulator that it is mounted on 4. The white insulation on some of the ground leads to the bussbar has been discolored from heat

The damage had to be prior to my owning this unit. I would think this would have had to produce smoke and excitement inside the trailer and we have not seen anything like that. Time to visit a pro and get this fixed. We're planning to tow the AS to Alaska next month and this won't cut it.

Thanks Garry and all. Will let you know what the culprit was when repairs are made. Sea
seacur50 is offline   Reply With Quote
Old 04-19-2010, 12:48 PM   #10
Rivet Master
 
richinny's Avatar
 
2011 34' Classic
Westchester Cty.NY , / Miami FL
Join Date: Jul 2007
Posts: 3,122
has this trailer ever been under water?
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
richinny is offline   Reply With Quote
Old 04-19-2010, 07:29 PM   #11
Rivet Master
 
garry's Avatar
 
1969 31' Sovereign
Broken Arrow , Oklahoma
Join Date: Jan 2003
Posts: 1,455
Images: 7
Sounds like it might have been plug into a 220 circuit sometime in the past.
You may need a new breaker panel.

Most electricians are very good at what they do but I have seen situations where the ground and neutral wires were bonded the same as in your house this is a no no for any camper.
The ground and neutral wires "must" be on separate bars.
__________________
Garry
garry is offline   Reply With Quote
Old 04-19-2010, 07:30 PM   #12
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
Nothing to indicate that. Near showroom condition.
seacur50 is offline   Reply With Quote
Old 04-20-2010, 05:51 AM   #13
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
Ground and neutral are on seprate buss bars. Wireing was done in a workmanlike manner. Very clean job.

I've got an appt. with the dealer in OR next week. That's the nearest Airstream tech support for us.

Thanks, Sea
seacur50 is offline   Reply With Quote
Old 04-20-2010, 08:17 AM   #14
Ready-to-Travel
 
pmclemore's Avatar

 
2012 30' International
Walkerton , Virginia
Join Date: Dec 2003
Posts: 3,168
Are the connections at the bus bar tight? A loose connection there would explain heat and a fluky system.

Pat
__________________
--------------------------------------
Somebody, please, point me to the road.

AIR 3987
TAC VA-2
WBCCI 4596
pmclemore is offline   Reply With Quote
Old 04-20-2010, 05:10 PM   #15
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
Yup, tight and dry. I'm going to remove all the conductors and coat the skinned copper with noalox and reinstall same in the buss bars. Copper to Alum. or Alum. alloy connections without corrosion inhibitor brushed on will eventually degrade dielectrically. We are less than a mile from the Pacific Ocean so plenty of good cold salt air here.

Thanks for the reminder, Sea
seacur50 is offline   Reply With Quote
Old 06-18-2010, 10:42 AM   #16
1 Rivet Member
 
Cutten , California
Join Date: Nov 2009
Posts: 10
Hello from Alaska,
The techs at Sutton RV in eugene, OR could not find anything amiss w/the AS electrical system. After staying in parks in 6 states and 3 provinces w/no problems whatsoever I'm happy to say I agree with em.

Traveling the Alaska Highway (Alcan) is still a great adventure. There are a great many improvements to the road since I last pulled a TT over it in 95. The r/w's are cut back a couple of hundred feet on either side of the road now so visibility is excellent. Lot's of flora and fauna, including griz.

Roadside camping still attracts fellow travelers like a magnet; safety in numbers I guess. Many of the rock pits used for road construction have been closed but there are still good locations available. My hat's off to the bike guys and gals sleeping in the 3 mil nylon tents. (landlocked shark chum). Earlier this week a fellow was pulled off his bicycle and mauled by a brown bear in an Anchorage city park. AKF&G recommeneds the city close the park, go figger. All I'll say about that.

Thanks to all who have taken the time to assist me w/the electrical glitch and thanks to the Airstream Forums system admin. folks for providing this service.

Seacur
seacur50 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off