Camping on the Outer Banks, NC last year and had a power surge due to a nearby lightning strike. No damage to the trailer, but the external PD-EMS unit started flashing an error code due to internal damage to the surge protection circuits.

A call to Progressive Dynamics and a new unit was shipped (no charge) to a campground we were headed to the next week. The ability to remove or replace the failing unit while traveling is a big plus.
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is offline   Reply With Quote
Old 04-06-2020, 11:24 AM   #22
Rivet Master
 
1972 23' Safari
Middletown , Rhode Island
Join Date: Sep 2016
Posts: 546
Quote:
Originally Posted by Sport 16 STL View Post
30 amp progressive internal. A little over a year, tripped once, I have remote led mounted at foot of bed. Zero humming noise. There is enough to worry about hook ups, one less thing if it is internal.
I have an internal 30amp progressive surge protector as well. Out of sight out of mind.
Mx468 is offline   Reply With Quote
Old 04-06-2020, 11:26 AM   #23
3 Rivet Member
 
2017 30' Classic
The Panhandle , Idaho
Join Date: Aug 2017
Posts: 112
Progressive Industries HW50C

Internal vs. External is kind of like Chevy vs. Ford. Opinions will vary depending upon experience, use, perceived convenience, etc.

We went with the Progressive Industries HW50C with the remote display/control. Have had zero issues with it, other than it noted a momentary voltage spike in one Canadian campground last summer. When I first installed it, I did notice a hum, but it has since disappeared. (Of I've learned to tune it out. )

I went with the internal unit as once installed, it eliminates one more thing to store. I have also seen where friends had to get creative at some campgrounds to secure their external unit. If you have the room for it, I'd go with the internal. Especially if the dealer is going to install it. Due to the incredibly poor wiring done under the seat, the rat's nest of wiring, finding room where our electrical penetrated the side wall under the dinette seat was the biggest challenge.
__________________
Hoagie '59
Hoagette '57
Whitney and Tobin -- The Aussie Posse
Hoagie is offline   Reply With Quote
Old 04-06-2020, 11:31 AM   #24
Moderator
 
jcanavera's Avatar

 
2004 30' Classic Slideout
Fenton , Missouri
Join Date: Mar 2002
Posts: 10,410
Images: 143
Send a message via AIM to jcanavera Send a message via Skype™ to jcanavera
Quote:
Originally Posted by Beewee View Post
Contrary to previous post there is NO lag time when hooking up to power.
I saw it on Amazon today for $325 - worth every penny.
I just checked the manual on line for the Progressive internal units and there is a setting for lag time. Minimum and factory default is 15 seconds. There is a time delay jumper that allows you to change that to 136 seconds. Those time delays are there to provide a delay for the air conditioner compressor to sit in case you get a brief power interruption. Some A/C units need a little time for internal pressures to equalize in case of a brief power interruption.

My external model that I have has an arbitrary power lag that occurs when power is first detected and is not adjustable. This again is for air conditioner compressor protection.

Jack
__________________
Jack Canavera
STL Mo.
AIR #56 S/OS#15
'04 Classic 30' S.O.,'03 GMC Savana 2500
jcanavera is offline   Reply With Quote
Old 04-06-2020, 11:56 AM   #25
Rivet Master
 
Vantair's Avatar
 
2005 25' International CCD
Westlake Village , California
Join Date: Sep 2014
Posts: 508
Images: 2
Internal Surge Protector

Quote:
Originally Posted by Sport 16 STL View Post
30 amp progressive internal. A little over a year, tripped once, I have remote led mounted at foot of bed. Zero humming noise. There is enough to worry about hook ups, one less thing if it is internal.
Agree with the PI 30 amp internal with others and just installed ours. (Per Best Converter recommendations) Absolutely NO Hum, internal readout/diagnostics and override switch all snugly inside.

Yes you must wire it in (1-2hours) but NO worries whatsoever if out hiking, around town or afterhours sleeping of it disappearing from a passing by lowest common denominator.
__________________
Relaxing is hard work.
Vantair
2005 25ft International CCD SS
2020 GMC Sierra Denali Diesel 2500 4X4 10 spd 3.43 Int sway/tow controller
1981 Honda Trail CT110 1X0..no sway control
Vantair is offline   Reply With Quote
Old 04-06-2020, 12:08 PM   #26
2 Rivet Member
 
2018 25' International
Doylestown , Pennsylvania
Join Date: May 2017
Posts: 20
external ( no need to say anything else )
77walter is offline   Reply With Quote
Old 04-06-2020, 12:29 PM   #27
Site Team
 
GCinSC2's Avatar

 
2007 30' Classic S/O
Somewhere , South Carolina
Join Date: Apr 2010
Posts: 6,436
And from this sofa, INTERNAL.

My logic:
Always connected.
Protected from elements and hands.
Same type power connection as primary power connection to trailer. Screw clamp vs blade and slots.
No additional plug and receptacle connections to burn up. I repaired one external units male plug for a buddy and they don’t leave you much cable to repair with.

If mine failed it might take 20-30 min to rewire straight to breaker. Slight hum was mitigated by mounting on rubber washers.

YMMV

Yup Ford vs Dodge

Gary
__________________
S/OS #001 2005 Dodge Ram 2500 5.9L 6 Speed
16" Michelins, Hi Spec Wheels, Max Brake, Dexter 4 Piston Disc Brakes, Carslile Actuator, Equal-I-Zer, Dill TPMS. Campfire cook. BMV-712. DEMCO 21K Lb Cast Iron coupler
GCinSC2 is offline   Reply With Quote
Old 04-06-2020, 12:33 PM   #28
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Hi

First off, the term "surge protector" gets used both for very basic spike clamping devices and for full blown EMS units. You very much *do* want a full up EMS. It will detect a number of issues and disconnect you from them. A spike clamp *may* protect you from lightning ... that's it.

We started with an external and now have an internal. Why?

1) The external is spending a lot of time out in the rain. Water and electricity are not a good combo. There never seemed to be a good way to keep it dry / safe / out of the way all at the same time.

2) The external was one more thing to drag out and hook up ( or put away) when setting up or tearing down camp. It also needed to store in (scarce) external storage. Easier is better in this case.

3) The external did not have any sort of remote readout. The internal has a nice little panel that sits where you can easily see it. Knowing what's going on without going outside is a nice thing. There are a number of "nice to know" things that display tells you.

4) Ours is mounted behind the power panel. Replacing it or taking it out of the circuit is maybe a 20 minute job. Not a big deal for a "once every hundred years" sort of thing.

5) Even after a couple years of use, the external was taking a beating. Rust was showing up on some of the parts. The plastic flip down cover over the plug was long gone. Warranty forever or not, at some point it would need to be replaced.

6) The odds of taking a direct hit to the RV and having the EMS blow up are (at least to me) pretty small. There are a multitude of ways things could go with a direct hit. The only thing that is reasonably sure is that you *will* have damage, regardless of your setup.

7) Neither the external unit or the internal have ever made any noticeable amount of noise under any conditions. There are various things that run in the RV from time to time. I do notice the noise from them. If the EMS makes noise, it's *way* down compared to the other gizmos.

8) There is a correct sequence to plugging / unplugging an RV from shore power. The breaker on the post is turned on last and turned off first. After a long tiring day (or a coffee deprived morning) one *might* not quite do the right thing. The internal EMS protects you from a couple of possible mistakes.

The big mistake in all this is not having an EMS. You very much do want to have one of these gizmos. I happen to like the Progressive units. I'm sure there are other good brands out there. The whole internal / external debate is *very* minor compared to the question of "do I get an EMS?".

Bob
uncle_bob is offline   Reply With Quote
Old 04-06-2020, 12:41 PM   #29
4 Rivet Member
 
2019 22' Sport
Carlsbad , California
Join Date: Nov 2018
Posts: 405
If it burns up doing its job handling a surge, do you want it burning up inside the trailer, or at the post?

I chose external after having that question posed to me 18 months ago
Prettygood is offline   Reply With Quote
Old 04-06-2020, 01:25 PM   #30
RJJ
3 Rivet Member
 
RJJ's Avatar
 
2016 26' Flying Cloud
2016 20' Flying Cloud
St Petersburg , Florida
Join Date: Oct 2016
Posts: 174
Internal with Remote Pendant

I have the Progressive Industries 30 amp EMS hard wired. I haven't had a worry with it at all. Love the remote pendant - it helps me to not overload power. Never worry about it walking away or accidentally leaving it behind. Just 2 things less to worry about. The business end is installed in the converter area and the remote is on the wall next to the range hood.

My unit is silent... never heard it hum, so I don't k ow what's up with that. 🤷🏽. Good luck with your choice.
Attached Thumbnails
Click image for larger version

Name:	PI_30AMP_WPENDANT_030218__01__01__01.jpg
Views:	52
Size:	248.1 KB
ID:	365054  
RJJ is offline   Reply With Quote
Old 04-06-2020, 03:29 PM   #31
Rivet Master
 
Silvr_Bullet's Avatar

 
2017 16' Sport
N/A , N/A
Join Date: Nov 2017
Posts: 1,789
Quote:
Originally Posted by uncle_bob View Post
Hi

First off, the term "surge protector" gets used both for very basic spike clamping devices and for full blown EMS units. You very much *do* want a full up EMS. It will detect a number of issues and disconnect you from them. A spike clamp *may* protect you from lightning ... that's it.

We started with an external and now have an internal. Why?

1) The external is spending a lot of time out in the rain. Water and electricity are not a good combo. There never seemed to be a good way to keep it dry / safe / out of the way all at the same time.

2) The external was one more thing to drag out and hook up ( or put away) when setting up or tearing down camp. It also needed to store in (scarce) external storage. Easier is better in this case.

3) The external did not have any sort of remote readout. The internal has a nice little panel that sits where you can easily see it. Knowing what's going on without going outside is a nice thing. There are a number of "nice to know" things that display tells you.

4) Ours is mounted behind the power panel. Replacing it or taking it out of the circuit is maybe a 20 minute job. Not a big deal for a "once every hundred years" sort of thing.

5) Even after a couple years of use, the external was taking a beating. Rust was showing up on some of the parts. The plastic flip down cover over the plug was long gone. Warranty forever or not, at some point it would need to be replaced.

6) The odds of taking a direct hit to the RV and having the EMS blow up are (at least to me) pretty small. There are a multitude of ways things could go with a direct hit. The only thing that is reasonably sure is that you *will* have damage, regardless of your setup.

7) Neither the external unit or the internal have ever made any noticeable amount of noise under any conditions. There are various things that run in the RV from time to time. I do notice the noise from them. If the EMS makes noise, it's *way* down compared to the other gizmos.

8) There is a correct sequence to plugging / unplugging an RV from shore power. The breaker on the post is turned on last and turned off first. After a long tiring day (or a coffee deprived morning) one *might* not quite do the right thing. The internal EMS protects you from a couple of possible mistakes.

The big mistake in all this is not having an EMS. You very much do want to have one of these gizmos. I happen to like the Progressive units. I'm sure there are other good brands out there. The whole internal / external debate is *very* minor compared to the question of "do I get an EMS?".

Bob


I would add that any charring is observed at the post plug-in don’t use it call the park manager.
Silvr_Bullet is offline   Reply With Quote
Old 04-06-2020, 03:46 PM   #32
"Cloudsplitter"

 
2003 25' Classic
Houstatlantavegas , Malebolgia
Join Date: Jun 2007
Posts: 20,000
Images: 1
I think brown-outs are just as important, if not more, than spikes and are a real concern for damage.
Make sure you have protection for both.👍

Bob
🇺🇸
__________________
I’m done with ‘adulting’…Let’s go find Bigfoot.
ROBERT CROSS is offline   Reply With Quote
Old 04-06-2020, 03:54 PM   #33
Site Team
 
azflycaster's Avatar

 
2002 25' Safari
Dewey , Arizona
Join Date: Mar 2005
Posts: 15,616
Images: 62
Blog Entries: 1
My EMS will not work with a generator because ground is missing. You can fool it by a bonding neutral to ground plug. Since my unit is external, I do not use it while on generator power.
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is offline   Reply With Quote
Old 04-06-2020, 04:18 PM   #34
Rivet Master
 
Silvr_Bullet's Avatar

 
2017 16' Sport
N/A , N/A
Join Date: Nov 2017
Posts: 1,789
Surge Protector: Internal vs. External?

Quote:
Originally Posted by azflycaster View Post
My EMS will not work with a generator because ground is missing. You can fool it by a bonding neutral to ground plug. Since my unit is external, I do not use it while on generator power.


Using an Inverter Generator doesn’t present that problem, you do not need the EMS. Grounding is still necessary.
Silvr_Bullet is offline   Reply With Quote
Old 04-06-2020, 04:21 PM   #35
Site Team
 
azflycaster's Avatar

 
2002 25' Safari
Dewey , Arizona
Join Date: Mar 2005
Posts: 15,616
Images: 62
Blog Entries: 1
Quote:
Originally Posted by Silvr_Bullet View Post
Using an Inverter Generator doesn’t present that problem
Why is that? I have 2 generators a Honda 1000 and a Yamaha 2400. Both inverter generators and both are missing ground.
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is offline   Reply With Quote
Old 04-06-2020, 04:58 PM   #36
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 9,180
My champion 3400 Dual Fuel Inverter genset is clearly marked, like most small generator sets (inverter or not) as having a floating neutral. Standard design.

So obtain or make a bonding plug, install it, and drive on. Easy to do.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 04-06-2020, 05:28 PM   #37
4 Rivet Member
 
Atomic_13's Avatar
 
1968 24' Tradewind
1968 26' Overlander
Detroit , Michigan
Join Date: May 2015
Posts: 467
I agree with the prior post, the most important thing is to use an EMS. Beyond that, it’s personal preference. For what it’s worth, installing an interior EMS isn’t all that hard. Here is picture of the EMS, main panel, and manual transfer switch that directs power to my Multiplus (option 1) or directly to my main AC distribution panel (option 2 which bypasses the Multiplus).

Click image for larger version

Name:	Adjustments.jpg
Views:	78
Size:	316.0 KB
ID:	365085

Also, for those curious here a the plug I made for an inverter generator whose neutral isn’t grounded.

Click image for larger version

Name:	IMG_7929.jpg
Views:	48
Size:	287.0 KB
ID:	365086

Click image for larger version

Name:	IMG_7930.jpg
Views:	42
Size:	208.2 KB
ID:	365087
__________________
Brian's AS renovation:
https://www.airforums.com/forums/f11...on-134984.html
Tow vehicle: 2019 F250 Lariat 6.7L CC SRW
Atomic_13 is offline   Reply With Quote
Old 04-09-2020, 10:16 AM   #38
Rivet Master
 
Boxite's Avatar
 
2008 22' Safari
Spicewood (W of Austin) , Texas
Join Date: Mar 2015
Posts: 2,987
The majority of portable generators have a “floating” neutral.... which your surge-protector/EMS unit will consider unsafe to complete the circuit.

The floating neutral is so-common because portable generator mfr’s have no control over how or where the consumer will utilize the generator...so they take the lowest-liability stance for themselves... which leaves the RV owner at a loss to determine how to get the generator to power the RV.

Here’s one of the better, more-complete explanations of how to solve the issue, but a simple ground-to-neutal external plug ...”plugged” into your spare generator socket... will solve the issue safely and properly:

https://www.rvtravel.com/rv-electric...onding-basics/
Boxite is offline   Reply With Quote
Old 04-12-2020, 11:10 AM   #39
Rivet Master
 
SailorSam205's Avatar
 
South East , Michigan
Join Date: Apr 2016
Posts: 552
I attended a seminar put on by Mike Sokol, the RV Electric guy. At the seminar last summer, Mike said that at that point, the Southwire brand EMS had recently added features not available on other brands and Southwire was patenting the method of adding the features. So his recommendation was Southwire over Progressive. Both have almost identical warranties.
In answer to a question about pure surge protection, Mike saw no issue with putting a common surge suppressor in front of an EMS.

I went with an internal PI EMS (3 years ago) mostly to prevent leaving it at a campground due to insufficient coffee uptake on some morning.

One other thing, Mike does recommend testing power before hooking up. This u-tube is his recommendation on some cheap tools to do the test:
https://www.rvtravel.com/rv-electric...outlet-tester/
__________________
Al
2017 29' SOB, 2022 Platinum F-150 SCrew, ProPride
SailorSam205 is offline   Reply With Quote
Old 04-12-2020, 11:19 AM   #40
Rivet Master
 
rodsterinfl's Avatar

 
2006 25' Safari
St. Augustine , Florida
Join Date: Oct 2011
Posts: 2,670
Images: 10
I purchased a Southwire Surgeguard and it has done its job twice- both times under voltage. My unit cycles through a power line test any time it is hooked up.
__________________
WBCCI 8653/AIR 60240
2022 Ford F150 PowerBoost Platinum w/7.2KW
rodsterinfl is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Surge Protector Protector...... terirdh Electrical - Systems, Generators, Batteries & Solar 11 08-06-2020 12:15 PM
internal Surge Protector Options rocco52 Batteries, Univolts, Converters & Inverters 23 04-26-2017 12:54 PM
I'm new. Need for surge protector? bcombs Member Introductions 14 11-09-2013 07:47 AM
surge protector pip8688 Batteries, Univolts, Converters & Inverters 15 08-09-2010 05:14 AM
internal charge wizard or external dragonnfly Electrical - Systems, Generators, Batteries & Solar 8 07-12-2006 02:18 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 05:20 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.