Isolator switches
I plan on not removing my Lithium batteries. I have a 80 watt solar panel on the roof. Should I have 2 isolator switches 1 for the solar panel and 1 for the DC system? My trailer will be installed indoors, I was thinking to make sure the batteries couldn’t be charged by the solar panel if the trailer was outdoors. Thanks
|
|
|
09-27-2023, 09:15 PM
|
#2
|
Rivet Master 
2022 25' Flying Cloud
NCR
, Ontario
Join Date: Feb 2017
Posts: 3,019
|
yes thats what i did . i used 4 switches as follows
1 for solar
1 for controlled DC
1 for all dc
1 for the front lift jack
__________________
2023 25' FB FC, hatch, Queen, 30A, 1AC, Awning pkg, Convection uwave.
Multiplus 12/3000-50, 700A Lion, MPPT 100/30, Orion-TR 30, Cerbo GX,GX touch 50, Lynx distributor, dual BMV-712, smart shunt 500A&1000A, RUUVI temp/humidity sensors
NCR , Ontario, VE3HIU since 1978
|
|
|
09-27-2023, 09:28 PM
|
#3
|
Rivet Master 
2007 30' Classic
Oswego
, Illinois
Join Date: Jul 2010
Posts: 13,543
|
My methodology is:
1 for solar panel input
1 for house dc only
1 for all dc
In addition the charger can be shut down independently with a switched outlet.
The solar controller can be shut down independently through the victron app.
The brake actuator is always hot in order to prevent an inadvertent loss of brakes. (Hydraulic e over h disc brakes)
__________________
-Rich-
"If the women don't find you handsome, they should at least find you handy." - Red Green
|
|
|
09-27-2023, 10:25 PM
|
#4
|
Site Team

1994 25' Excella
Waukesha
, Wisconsin
Join Date: Sep 2020
Posts: 5,259
|
Quote:
Originally Posted by Silvr_Bullet
I plan on not removing my Lithium batteries. I have a 80 watt solar panel on the roof. Should I have 2 isolator switches 1 for the solar panel and 1 for the DC system? My trailer will be installed indoors, I was thinking to make sure the batteries couldn’t be charged by the solar panel if the trailer was outdoors. Thanks
|
Don't understand - what's the reason you want to make sure your batteries can't be charged when the trailer is outdoors?
__________________
Richard
11018
1994 Excella 25 Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser (Sold)
|
|
|
09-28-2023, 07:55 AM
|
#5
|
Rivet Master 
2007 30' Classic
Oswego
, Illinois
Join Date: Jul 2010
Posts: 13,543
|
Quote:
Originally Posted by richard5933
Don't understand - what's the reason you want to make sure your batteries can't be charged when the trailer is outdoors?
|
I can think of one reason....for me. The solar controller, if left on partially cycles the batts every day. And runs through an absorption phase every day.
Now, in my case, if solar is turned off, and I have my charger on, it goes into a storage voltage mode, with a weekly absorption phase.
Less cycles over time = theoretical longer batt life. (AGM)
Is it a huge deal? Maybe not, but is logical to me.
__________________
-Rich-
"If the women don't find you handsome, they should at least find you handy." - Red Green
|
|
|
09-28-2023, 08:08 AM
|
#6
|
Rivet Master 
2007 30' Classic
Oswego
, Illinois
Join Date: Jul 2010
Posts: 13,543
|
Quote:
Originally Posted by dznf0g
My methodology is:
1 for solar panel input
1 for house dc only
1 for all dc
In addition the charger can be shut down independently with a switched outlet.
The solar controller can be shut down independently through the victron app.
The brake actuator is always hot in order to prevent an inadvertent loss of brakes. (Hydraulic e over h disc brakes)
|
Correction: I forgot I had made a change to this configuration. The master switch to shut off ALL 12V circuits, including jack and brakes. My revised thought is I can't drive away with the switch off, as I wouldn't be able to run the jack to hitch up, therefore forcing the brake actuator to be turned on.
__________________
-Rich-
"If the women don't find you handsome, they should at least find you handy." - Red Green
|
|
|
09-28-2023, 11:52 AM
|
#7
|
Site Team

1994 25' Excella
Waukesha
, Wisconsin
Join Date: Sep 2020
Posts: 5,259
|
Quote:
Originally Posted by dznf0g
I can think of one reason....for me. The solar controller, if left on partially cycles the batts every day. And runs through an absorption phase every day.
Now, in my case, if solar is turned off, and I have my charger on, it goes into a storage voltage mode, with a weekly absorption phase.
Less cycles over time = theoretical longer batt life. (AGM)
Is it a huge deal? Maybe not, but is logical to me.
|
Makes sense.
__________________
Richard
11018
1994 Excella 25 Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser (Sold)
|
|
|
09-28-2023, 09:58 PM
|
#8
|
Loco Airstreamer
1970 23' Safari
Denton
, Texas
Join Date: Sep 2005
Posts: 87
|
So what kind of switches are you using please?
|
|
|
09-28-2023, 11:24 PM
|
#9
|
Site Team

1994 25' Excella
Waukesha
, Wisconsin
Join Date: Sep 2020
Posts: 5,259
|
On my solar install I used a switchable DC circuit breaker as the master disconnect between my solar charge controller and the batteries, and a Blue Sea manual battery disconnect between the solar panels and the charge controller. This allows me to isolate parts of the system when needed for repair.
When trying to accomplish what dznf0g does (keeping the solar charge controller from starting from scratch every day) I used to use the Bluetooth app to turn off the solar charging.
But if my memory is correct there is a setting in the Victron solar charge controller which allows it to automatically shorten/bypass the absorption mode and go almost directly into maintain mode if it senses that there is no need for the higher output.
__________________
Richard
11018
1994 Excella 25 Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser (Sold)
|
|
|
09-29-2023, 06:41 AM
|
#10
|
Rivet Master 
2007 30' Classic
Oswego
, Illinois
Join Date: Jul 2010
Posts: 13,543
|
Quote:
Originally Posted by richard5933
On my solar install I used a switchable DC circuit breaker as the master disconnect between my solar charge controller and the batteries, and a Blue Sea manual battery disconnect between the solar panels and the charge controller. This allows me to isolate parts of the system when needed for repair.
When trying to accomplish what dznf0g does (keeping the solar charge controller from starting from scratch every day) I used to use the Bluetooth app to turn off the solar charging.
But if my memory is correct there is a setting in the Victron solar charge controller which allows it to automatically shorten/bypass the absorption mode and go almost directly into maintain mode if it senses that there is no need for the higher output.
|
Hmmm, I'll have to look for that.
__________________
-Rich-
"If the women don't find you handsome, they should at least find you handy." - Red Green
|
|
|
09-29-2023, 08:26 AM
|
#11
|
Rivet Master 
2007 30' Classic
Oswego
, Illinois
Join Date: Jul 2010
Posts: 13,543
|
Quote:
Originally Posted by richard5933
On my solar install I used a switchable DC circuit breaker as the master disconnect between my solar charge controller and the batteries, and a Blue Sea manual battery disconnect between the solar panels and the charge controller. This allows me to isolate parts of the system when needed for repair.
When trying to accomplish what dznf0g does (keeping the solar charge controller from starting from scratch every day) I used to use the Bluetooth app to turn off the solar charging.
But if my memory is correct there is a setting in the Victron solar charge controller which allows it to automatically shorten/bypass the absorption mode and go almost directly into maintain mode if it senses that there is no need for the higher output.
|
The only way I see to do that is to turn absorption time to zero and/or change absorption voltage to match float voltage. I see no storage voltage.
__________________
-Rich-
"If the women don't find you handsome, they should at least find you handy." - Red Green
|
|
|
09-29-2023, 03:09 PM
|
#12
|
Site Team

1994 25' Excella
Waukesha
, Wisconsin
Join Date: Sep 2020
Posts: 5,259
|
Quote:
Originally Posted by dznf0g
The only way I see to do that is to turn absorption time to zero and/or change absorption voltage to match float voltage. I see no storage voltage.
|
Isn't there a way to select a dynamic setting for the time it stays in absorption?
__________________
Richard
11018
1994 Excella 25 Follow the build on Gertie!
1999 Suburban LS 2500 w/7.4L V8
1974 GMC 4108a - Custom Coach Land Cruiser (Sold)
|
|
|
09-29-2023, 03:20 PM
|
#13
|
Rivet Master 
2007 30' Classic
Oswego
, Illinois
Join Date: Jul 2010
Posts: 13,543
|
Quote:
Originally Posted by richard5933
Isn't there a way to select a dynamic setting for the time it stays in absorption?
|
Yes, you can set it to zero, or set absorption voltage to equal float voltage. A little more convoluted than a radio button to turn off absorption. But you would still have some partial cycling every night when dark, unless you have a true master cutoff switch installed.
I have a pad at home with 30A, so I just turn off the solar and let the Victron charger remain in storage mode. That mode prevents gassing, has a weekly absorption (frequency is adjustable) and is temp compensated. Storage voltage is approx .46v below temperature compensated float voltage.
__________________
-Rich-
"If the women don't find you handsome, they should at least find you handy." - Red Green
|
|
|
 |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|

Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|