House shore power...full usage inside?

FYI
2016 25' FB International

We need to live in our trailer next to our house for a while.

If I plug into the house 110 with an extension cord what appliances can I use?

Water heater? (yes I now I can use the propane for this)
Fridge? (yes I now I can use the propane for this)
Microwave?

Thanks,
Mike
kbmwrs is offline   Reply With Quote
Old 02-17-2021, 04:22 PM   #2
Rivet Master
 
B. Cole's Avatar
 
1977 31' Sovereign
Rochester , WASHINGTON
Join Date: Sep 2020
Posts: 621
Ok, it's like plugging multiple extension cords into a 30 Amp generator, instead of one main power cord, like from your Airstream.
You would want to run heaviest, shortest extension cords you can, from the house.Its done all the time, but do it as safe as possible.
And you want the cords to be plugged into different circuits in the house.
It's not ideal, but use outdoor use rated cords.
Plug into GFCI protected circuits, like in garage or kitchen, if possible.
__________________
Airstream rodeo clown, it's my turn in the barrel 🤡
B. Cole is offline   Reply With Quote
Old 02-17-2021, 04:24 PM   #3
Rivet Master
 
Belegedhel's Avatar
 
1973 21' Globetrotter
Houston , Texas
Join Date: Sep 2009
Posts: 2,854
You can run pretty much anything that you would normally run in your house, on regular AC current, but not all at the same time. The only thing that is probably an "absolutely not" would be the air conditioner, but if you outfit it with an EasyStart, you could run that too.

Of equal importance, make sure you are using an outlet that has the largest possible breaker on it. For example in my house most of the circuits that serve lighting are only 15A circuits, whereas the outlets in the garage are a 20A circuit. Sometimes utility rooms and outlets under the kitchen sink are on a 20A circuit as well. Secondly, you want your extension cord to be as short as possible, and as thick of gauge (think 10-12 gauge wires) as you can reasonably get. No use in losing a large percentage of your power due to line losses in the cord.

good luck!
Belegedhel is offline   Reply With Quote
Old 02-17-2021, 04:34 PM   #4
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,175
Fridge for sure.
Microwave,Water heater, maybe, one at a time if they are the only thing running on the circuit you plug into. Water heater takes 1400 watts, or around 12 amps on a 15 amp plug. The microwave in convection mode also uses 1400 watts but I can't find any data on the microwave mode. It has 900 watts output but it takes substantially more than 900 watts of electricity to generate 900 watts of microwaves.


For either of those two you will need a short, heavy duty extension cord, at least 14 gauge wire and preferably 12.
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 02-17-2021, 04:42 PM   #5
Site Team
 
azflycaster's Avatar

 
2002 25' Safari
Dewey , Arizona
Join Date: Mar 2005
Posts: 14,567
Images: 62
Blog Entries: 1
A 20 amp outlet would be better that a 15 amp.
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is online now   Reply With Quote
Old 02-17-2021, 05:31 PM   #6
3 Rivet Member
 
kbmwrs's Avatar
 
2016 25' International
Morgan Hill , California
Join Date: Mar 2013
Posts: 146
Great thanks.
Laundry room has 30amp (not the dryer outlet) and garage has 20amp.

Now to buy a thick gauge ext cord.
kbmwrs is offline   Reply With Quote
Old 02-17-2021, 05:34 PM   #7
Site Team
 
azflycaster's Avatar

 
2002 25' Safari
Dewey , Arizona
Join Date: Mar 2005
Posts: 14,567
Images: 62
Blog Entries: 1
I use a 30amp RV extension cord. I also travel with it and it has come in hand a couple of times.
__________________

Richard

Wally Byam Airstream Club 7513
azflycaster is online now   Reply With Quote
Old 02-17-2021, 05:44 PM   #8
Rivet Master
 
ITSNO60's Avatar
 
Currently Looking...
Tucson , AZ
Join Date: May 2017
Posts: 1,163
Quote:
Originally Posted by kbmwrs View Post
Great thanks.
Laundry room has 30amp (not the dryer outlet) and garage has 20amp.

Now to buy a thick gauge ext cord.
Something is wrong if the laundry has a 30 amp breaker (single pole) that's not for a dryer. Household receptacle circuits are limited to 20 amps, if you have a 30 amp breaker on a standard receptacle I suspect someone changed the breaker creating a hazard as the wiring will only be rated for 15 or 20 amps as will the receptacle.
Required 20 amp residential circuits since many years back are receptacles that serve the kitchen counter tops (min 2 circuit required), dining room, pantry (although dining & pantry are allowed to share with countertops and almost always do) and the clothes washer/laundry. In homes built under the 1996 NEC the bathroom outlets became 20 amps and most recently the garage requires a 20 amp circuit with at least one receptacle for each parking spot.
Is there a way you can get a 30 amp TT outlet installed at your electric panel?
__________________
Brian
ITSNO60 is offline   Reply With Quote
Old 02-17-2021, 07:46 PM   #9
3 Rivet Member

 
2015 25' Flying Cloud
Schaumburg , Illinois
Join Date: Jun 2020
Posts: 151
agree, the "best" solution is a properly installed 30A outlet (RV 30A outlets are unique, they require knowledge to be installed safely). Handymen can do it, but there are things you need to be careful about so with that in mind ....

I am not living in my trailer, but I store it next to my house, and I power it with a standard 110V cord (standard outlet). I have an adapter that goes between 30A to 20A, then use a thick gauge wire, get the thickest wire you can find. Get 12ga for sure, 10 if you can get it.

I can run anything, including the AC, as long as I don't run high demand items simultaneously. I have no need for simultaneous use, so in my case its a non issue, but the basic answer for you is that you can run *anything* with the possible exception of the AC unit. It all depends on the start-up current surge for your particular AC, there is some variance from one unit to the next. I also have an "Easy-start" module, but that is a recent addition, I was running the AC without the "Easy-start" on the standard 20A circuit.

Even with a 30A outlet, there is a chance you will trip a breaker if you run too many high draw loads simultaneous, its just more rare to have that happen.
1StreamDream is online now   Reply With Quote
Old 02-18-2021, 09:51 AM   #10
Bob
 
1988 29' Excella
Lorena , Texas
Join Date: Aug 2017
Posts: 50
I’m in Texas. We use Bella year round. It’s parked outside. I put in a dedicated 20 amp outlet in the garage at the breaker box because that was easy. 10 gauge cords to the coach.

I use one of the AC or microwave, but the coach only allows one or the other. In the summer I run a separate smaller cord (14 gauge) to the refrigerator. Any time things change I get out the ammeter and measure the current.

An aside, but my biggest struggle has been the 30 amp cord connections. Any little water, plugging in with power turned on, dirt, etc will begin to compromise the connector contact. That leads to heating and will eventually melt the connector. So I’d recommend minimizing the number of connections, protecting the connections from weather and movement, and turning power off before connecting up.
lemley is offline   Reply With Quote
Old 02-18-2021, 09:56 AM   #11
2 Rivet Member
 
John & Roberta's Avatar
 
2018 30' Flying Cloud
Cameron Park , California
Join Date: Sep 2019
Posts: 81
Shore Power at Home

Heavy-duty extension cord (2 conductor + ground) is very smart. You’ll know “heavy” when you feel it. Probably like nothing you already own. Mine’s long (100 feet) and fat and orange. Hook into a garage tool bench circuit if you have one (you’ll see that one’s protected by a 20-amp breaker if you check the panel). Be careful you don’t overload your chosen circuit by using it (with power tools, for instance) whilst loading up inside the trailer.

Your house circuit will be protected at the panel and your trailer circuits are protected, with breakers. A combination load from the trailer can still pop the house breaker. If possible, avoid using air conditioner in trailer. (That appliance will definitely “warm” the line.)
John & Roberta is offline   Reply With Quote
Old 02-18-2021, 10:10 AM   #12
Half a Rivet Short
 
2017 30' Classic
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 9,201
Hi

If you have a 30A outlet in your laundry room, I'd bet it's a 230V 30A outlet. It would be a really good idea to check it before you go plugging this and that in ....

Bob
uncle_bob is offline   Reply With Quote
Old 02-18-2021, 10:47 AM   #13
Rivet Master
 
waninae39's Avatar

 
2017 22' Sport
NCR , Ontario
Join Date: Feb 2017
Posts: 2,439
we plug it into a 20A outside circuit over the winter.
it never needs more than a few amps
waninae39 is offline   Reply With Quote
Old 02-18-2021, 11:43 AM   #14
3 Rivet Member
 
2014 25' FB Flying Cloud
Hillsborough , North Carolina
Join Date: Dec 2015
Posts: 229
What distance?

What is the cable run length of the drop cord you will need?
What is the length of the wire from your 30 amp outlet to the main breaker panel?
To total length will help determine the guage wire recommended.

Amazon does sell a nice 6 ga SOOW outdoor rated cable:
6/3 SOOW SO 600V Portable Power Cord Outdoor Durable Flexible Wire Cable (6/3 SOOW Cable, 150')


Then Lowes sells the plugs to go on the end of the cable, and you can end up with a really good 30 amp feed to your trailer.

As those above have mentioned: Please detail the 30 amp outlet that you have to make sure it is 120 volt. A picture would be nice.

If you are up to running a new branch circuit, Lowes sells a nice RV outlet enclosure for a 30 amp receptacle that easily mounts to the side of the house.

And for what is worth: Lowes also sells a GFCI rated 30 amp Breaker.

Note: you should design to not run more than 80% of any circuit rating.
So if you plug into a 15 amp outlet, do not design for the total load of that branch circuit to not exceed 12 amps.
and likewise a 20 amp branch circuit should not have a designed load of grater than 16 amps. This includes all other outlets on those branch circuits, so be aware that you might be more limited than expected when plugging into an existing outlet.
GeeSag is offline   Reply With Quote
Old 02-18-2021, 11:52 AM   #15
4 Rivet Member
 
pjshier's Avatar

 
2017 27' International
Wasilla , Alaska
Join Date: Feb 2018
Posts: 297
30A AS cord?

Couldn't you use the 30A cord that came with your AS, adapted to plug into the house 110120 20A circuit? Unless you have a really long 30A cord, not sure you are saving much resistance by buying a dedicated 10 gauge or larger cord. But i may have misunderstood, and you have to run a cord longer than your AS 30A power cord will reach.
__________________
2017 Int'l Serenity 27FB
2020 F250 powered by converted solar
pjshier is offline   Reply With Quote
Old 02-18-2021, 12:28 PM   #16
Rivet Master
 
2018 28' International
Fayetteville , Georgia
Join Date: Jan 2018
Posts: 736
Have a 30 or 50 amp RV power post installed.
__________________
brick
2018 International Serenity
Cute wife...
brick1 is offline   Reply With Quote
Old 02-18-2021, 02:42 PM   #17
3 Rivet Member
 
kbmwrs's Avatar
 
2016 25' International
Morgan Hill , California
Join Date: Mar 2013
Posts: 146
Quote:
Originally Posted by pjshier View Post
Couldn't you use the 30A cord that came with your AS, adapted to plug into the house 110120 20A circuit? Unless you have a really long 30A cord, not sure you are saving much resistance by buying a dedicated 10 gauge or larger cord. But i may have misunderstood, and you have to run a cord longer than your AS 30A power cord will reach.
I will be using the 30amp AS cord with adapter to house connected cord. I will use the 20amp circuit. Not sure if that cord by itself will reach the 20amp outlet in the garage...I'll try.

I will NOT being using more than two appliance at a time. No A/C. probably just water heater for a shower, frig and on occasion the furnace blower. Possible two at once..frig & water heater or furnace.

Thanks
kbmwrs is offline   Reply With Quote
Old 02-18-2021, 09:29 PM   #18
2 Rivet Member

 
2017 25' International
West Lake Hills , Texas
Join Date: Dec 2020
Posts: 99
I agree with Brick1. Have the 30 amp RV hook-up installed as near the trailer as you can get it. If within 50 feet of the trailer but more than your existing cord, buy the 50-foot cord...no extension needed. Any electrician can do this.
Fungus is online now   Reply With Quote
Old 02-18-2021, 09:55 PM   #19
Site Team
 
wulfraat's Avatar

 
2017 30' International
Broomfield , Colorado
Join Date: Apr 2009
Posts: 2,811
Images: 1
House shore power...full usage inside?

Fridge is 400w when in a cooling cycle and water heater is about 1400w when heating so you are technically fine running those at the same time on a 20A circuit assuming 110v at the trailer with just some basic lights on otherwise. You’ll be close to limit so as a precaution if it were me I’d turn off the fridge for the 20 minutes it takes to heat your water.

Furnace is about 250watts or so when running. .

FYI you can use both propane and electric combined to heat your water faster.

Make sure your water heater off when you use the microwave. No problem. Stay warm. Hope your house is ok.
wulfraat is online now   Reply With Quote
Old 02-19-2021, 05:57 AM   #20
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 5,532
Blog Entries: 1
Quote:
Originally Posted by uncle_bob View Post
If you have a 30A outlet in your laundry room, I'd bet it's a 230V 30A outlet. It would be a really good idea to check it before you go plugging this and that in ....

Bob
A 30 amp dryer plug is different than a 30 amp RV plug. Where people get in trouble is when an electrician puts in a 30 amp RV plug, but wires it like a 30 amp dryer plug. (240)

---------------------------

BTW, Finding a way to dump your tanks will be a bigger problem than the 20 amp power.
Mollysdad is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interstate usage days and usage miles (#operationbulletproof) InterBlog Sprinter and B-van Forum 4 09-23-2019 09:03 AM
Shore power but no power inside or to appliances Travs17 Electrical - Systems, Generators, Batteries & Solar 1 09-01-2019 08:47 PM
Jury-rigging shore power at the house Belegedhel Electrical - Systems, Generators, Batteries & Solar 89 07-12-2016 10:04 AM
Long Term Shore Power and House Battery cbrittan Batteries, Univolts, Converters & Inverters 30 11-02-2015 01:15 AM
Air Conditioner tripping breaker in my house while on shore power Wgbarrbevco General Repair Forum 10 08-16-2012 06:07 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:36 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, Jelsoft Enterprises Ltd.