04-17-2013, 06:53 PM
|
#1
|
New Member
Kingsville
, Texas
Join Date: Feb 2013
Posts: 3
|
Home Electric Hookup
I'm installing a 30 amp circuit in my home's electric box in order to plug in my 2007 23' AS Safari. My electric guy tells me that it should be a simple matter of replacing an existing 50 amp circuit in the electric box (which the previous home owner used for a welding rig) with the appropriate 30 amp circuit. This circuit is wired to a receptacle on the other side of my house (where I have a parking area for the trailer). He will replace that receptacle with a plug that will accommodate my trailer's electric cable. I should then be able to plug the trailer into the side of my house for full electrical power.
This seems logical and straightforward to me, but I'm no electric expert. Does anyone see any problem with this setup? Thanks in advance.
|
|
|
04-17-2013, 07:01 PM
|
#2
|
Rivet Master
1974 Argosy 20
2014 20' Flying Cloud
Kooskia
, Idaho
Join Date: Jul 2009
Posts: 4,591
|
Only let the electrician do it if he understands that the 30 amp RV outlet is a 120 volt unit only, and have him demonstrate, to you in person, with a meter, that there is only 120 volts between the two angled slots in the outlet. Only then are you sure he has done it right.
There have been several reports here on the Forums from people who have had someone do the job for them, and when they plugged their rig in, they toasted everything inside as the outlet was wired for 240 volts, not 120.
Since you are starting with a 240 volt outlet, there is even a higher danger that it could be mis wired.
|
|
|
04-17-2013, 07:03 PM
|
#3
|
Rivet Master
1983 34' Excella
1967 24' Tradewind
Little Rock
, Arkansas
Join Date: Nov 2006
Posts: 3,825
|
Quote:
Originally Posted by idroba
Only let the electrician do it if he understands that the 30 amp RV outlet is a 120 volt unit only, and have him demonstrate, to you in person, with a meter, that there is only 120 volts between the two angled slots in the outlet. Only then are you sure he has done it right.
There have been several reports here on the Forums from people who have had someone do the job for them, and when they plugged their rig in, they toasted everything inside as the outlet was wired for 240 volts, not 120.
Since you are starting with a 240 volt outlet, there is even a higher danger that it could be mis wired.
|
Good advice!
__________________
Vaughan
|
|
|
04-17-2013, 07:07 PM
|
#4
|
Rivet Master
Southwestern
, Ohio
Join Date: Nov 2006
Posts: 1,671
|
Welcome to the forums!
Should work OK as long as the wire going to the old 50 A outlet is at least 10 gauge. (A 50 A circuit would normally have heavier wire than that, but as I recall the national electric code had an exception for welder service because the welder requires current only intermittently.)
The thing you need to make sure your electrician understands, though, is that the existing outlet is 240 Volts, 50 Amps and your trailer outlet is 120 Volts, 30 Amps. In other words, you will be replacing a two pole 50 Amp breaker with a single pole 30 Amp breaker.
.
|
|
|
04-17-2013, 07:37 PM
|
#5
|
Rivet Master
2000 25' Safari
Davidson County
, NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
|
Another way to say what is said above:
the trailer is 30 amp 120 v = one load wire
the welder is 50 amp 240v = two load wires
some people have burned up parts of the electrical distribution system and/or components (like converter, refrigerator, radio, etc.) inside their trailers when they wired their electric receptacles incorrectly
edit:
I suggest that you print these post and make sure that your electrician reads them prior to starting work
and, welcome to the forums
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
|
|
|
04-17-2013, 07:41 PM
|
#6
|
Rivet Master
, Minnesota
Join Date: Aug 2003
Posts: 7,721
|
I got a problem. Why don't you leave the 50a 120/240 receptacle as is and just buy a 50a to 30a adapter.?
|
|
|
04-17-2013, 07:50 PM
|
#7
|
Rivet Master
2000 25' Safari
Davidson County
, NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
|
Quote:
Originally Posted by markdoane
I got a problem. Why don't you leave the 50a 120/240 receptacle as is and just buy a 50a to 30a adapter.?
|
good idea, only if it is 4 wire circuit.
some older 240v circuits are 3 wire (no neutral). the three wire setup with an adapter could have a live load on the ground and if you would touch the trailer while standing outside you could be electrocuted.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
|
|
|
04-17-2013, 08:07 PM
|
#8
|
Rivet Master
2011 34' Classic
Westchester Cty.NY
, / Miami FL
Join Date: Jul 2007
Posts: 3,122
|
partial hijack........
once the outlet is wired......
if you plug a 30a to 15a rv adapter and test the line with an incandescent bulb the bulb would light normally, correct?
if it was wired incorrectly the bulb would flash brightly for a second and then burn out or would something else happen?
__________________
Ricky
2012 F150 Super Crew 5-1/2' bed Ecoboost 4x4 3.73 elec. lock diff. Propride hitch
give life. kidney & pancreas transplant 9/9/06
Ingrid-my unofficial '"World's Oldest Streamer" 1909-2008 R.I.P.
|
|
|
04-18-2013, 10:28 AM
|
#9
|
4 Rivet Member
1955 22' Flying Cloud
mapleton
, Utah
Join Date: Oct 2011
Posts: 464
|
After you are VERY sure the outlet is correctly wired you need to think about your batteries. if you dont have a 3 stage converter you must disconnect them or they will quickly cook and be ruined. Been there done that
tim
|
|
|
04-18-2013, 01:09 PM
|
#10
|
Rivet Master
, Minnesota
Join Date: Aug 2003
Posts: 7,721
|
Quote:
Originally Posted by A W Warn
good idea, only if it is 4 wire circuit.
some older 240v circuits are 3 wire (no neutral). the three wire setup with an adapter could have a live load on the ground and if you would touch the trailer while standing outside you could be electrocuted.
|
That's true, but then a 50a to 30a dogbone adapter won't fit, will it?
Just keeping it simple.
|
|
|
04-18-2013, 03:10 PM
|
#11
|
Lost in America
2015 27' FB International
2006 25' Safari FB SE
2004 19' International CCD
Santa Fe
, New Mexico
Join Date: Feb 2007
Posts: 2,151
|
I did the same hookup from a 50A to 30A RV receptacle using one of the hot legs. The other hot leg I used to wire a 20A regular plug receptacle to have handy to the trailer for tools, compressor, etc.
__________________
This is the strangest life I've ever known - J. Morrison
2015 Airstream International Serenity 27FB
2017 Chevy Silverado 2500HD Duramax Diesel
|
|
|
04-28-2013, 08:48 AM
|
#12
|
New Member
Kingsville
, Texas
Join Date: Feb 2013
Posts: 3
|
Well, I was finally able to get this circuit installed and get my Airstream plugged in to "shore power". Everything seems to be working (AC outlets, microwave, etc.), so I'm confident that it's set up correctly. However, if it hadn't been for the folks commenting here, I may have had a real problem.
My electric guy is very knowledgable about electric matters, but not experienced with RV's. If I hadn't printed the excellent advice from this forum and made him read it, he would have used a double pole 30 amp circuit and left the existing 240 wiring in place. When I showed him the comments I printed from the forum he kind of had an "aha" moment and understood the trailer's electrical requirements. We also turned off all the breakers inside the trailer before plugging in the electric cable and then tuned them on one by one just to be cautious. We encountered no problems when everything was turned back on and the appliances in the trailer were checked out.
Thank you all SO MUCH for your expert advise. What a great group of folks and a huge resource we have with this forum.
Steve
|
|
|
04-28-2013, 09:34 AM
|
#13
|
Rivet Master
2004 25' Classic
Prescott
, Arizona
Join Date: Jul 2008
Posts: 623
|
Quote:
Originally Posted by rumrunner
After you are VERY sure the outlet is correctly wired you need to think about your batteries. if you dont have a 3 stage converter you must disconnect them or they will quickly cook and be ruined. Been there done that
tim
|
Now that you are plugged in, the above is so true! I also can say, Been There Done That
__________________
Julia & Bob
W/ Deedee & Boo
AIR #30685
|
|
|
|