Electrical Fire after solar and inverter install

Just had a solar package install from the Airstream Dealership. The 1000 watt inverter is inline, so we don't have inverter outlets. I was told that we have to flip the converter breaker every time to off before turning on the inverter. I thought it was automatic.... Maybe I should have a manual on off instead of flipping a breaker?



Anyways, back to the dealership to determine why the negative wire melted and the bathroom gfi keeps tripping.
jasperkins is offline   Reply With Quote
Old 05-18-2014, 03:16 PM   #2
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Your dealer simply is incompetent and has not installed the inverter correctly. If they wired it so you have to turn off the converter breaker to use it, they did a very bad job.
idroba is offline   Reply With Quote
Old 05-18-2014, 03:39 PM   #3
3 Rivet Member
 
jasperkins's Avatar
 
2012 27' FB Eddie Bauer
2018 Tommy Bahama Interstate
Ouray , Colorado
Join Date: May 2013
Posts: 185
Can you explain how its supposed to be wired with still being able to use the existing outlets? Having to always turn off the converter breaker and worrying about fire scares us. It's the Zamp system, with 4 panels.
Attached Thumbnails
Click image for larger version

Name:	breakerfire.jpg
Views:	199
Size:	234.9 KB
ID:	212240  
jasperkins is offline   Reply With Quote
Old 05-18-2014, 04:14 PM   #4
3 Rivet Member
 
jasperkins's Avatar
 
2012 27' FB Eddie Bauer
2018 Tommy Bahama Interstate
Ouray , Colorado
Join Date: May 2013
Posts: 185
Tomorrow I am dropping our AS back off at the dealer, and getting this fixed. Sucks that I now have to turnaround from our Yellowstone trip, however I rather be safe then have a bigger fire- 5 days lost in vacation is better than lives lost.

I still haven't found a good Inverter install thread that shows or explains how the wiring should be done to use the existing outlets. I would agree, that having to turn off a breaker everytime just doesn't seem right. Yet I would think that the converter should be disconnected somehow.
jasperkins is offline   Reply With Quote
Old 05-18-2014, 04:36 PM   #5
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
To use the existing outlets with the inverter the would need to be on a sub panel which excludes the inverter from supplying power to things like the AC and the water heater (if you have an electric option one) microwave, and the converter/charger. In other words the inverter should only be able to supply power to the outlets alone and exclude the high power equipment. This also will require a transfer switch something like the ones used with a built in generator on a motorhome so those same outlets will function normally when on line power. Some inverters have that transfer switch built in. I don't have any idea if yours has that capacity.

This is one reason the new Airstreams have dedicated inverter outlets, rather than trying to use the same outlets with the much lower power output inverter.

This is not a trivial conversion, and as I stated above, your dealer does not appear to be capable of doing it properly. Sorry for that harsh judgment, but you already have indications of their ability.
idroba is offline   Reply With Quote
Old 05-18-2014, 05:46 PM   #6
4 Rivet Member
 
Mike91208's Avatar
 
2009 27' FB International
LA LA Land... , California
Join Date: Sep 2011
Posts: 290
Quote:
Originally Posted by idroba View Post
Your dealer simply is incompetent and has not installed the inverter correctly. If they wired it so you have to turn off the converter breaker to use it, they did a very bad job.
My AS dealership did something similar. They don't know solar or inverters. Take it to someone who specializes in solar/inverters! I didn't trust them to fix the mistake so I took it to someone who knows what they're doing. AS dealers don't have a clue.
Mike91208 is offline   Reply With Quote
Old 05-18-2014, 06:19 PM   #7
BAB
Rivet Master
 
BAB's Avatar
 
2015 30' Classic
2012 28' International
Greensboro , North Carolina
Join Date: Aug 2011
Posts: 1,708
I am amazed that any so called "professional" would do an install like this. It makes me wonder if he knows the difference between an "inverter" and a "converter" -- or even how A/S wires circuits. Ugh.
__________________
_________________
"SilverLeaf II" 2015 30' Classic
2019 RAM 2500 Limited 4x4 CC w/6.7L Cummins
ProPride 3P
AIR# 58452
WBCCI # 3430-Unit 21
BAB is offline   Reply With Quote
Old 05-18-2014, 08:49 PM   #8
3 Rivet Member
 
jasperkins's Avatar
 
2012 27' FB Eddie Bauer
2018 Tommy Bahama Interstate
Ouray , Colorado
Join Date: May 2013
Posts: 185
I had only heard great things about this AS dealership, and when I asked about Solar and an Inverter with the existing outlets, they said they could do it. As I needed a few other items fromt the dealership, I chose to use them for the install.

I am just surprised that after reading the forums that they didnt bypass the heavy electrical appliances and just put it on a dedicated breaker. I am also surprised they told me and my pregnant wife to open the breaker box evertime and turn on/off breakers when I am to use Solar.

The fire in the electric box was the last straw. My wife is 6 months pregnant, and we are traveling with 2 dogs. An electrical fire was not something we are prepared to deal with- especailly on our way to Yellowstone and then AlumaPalooza.

We are considering keeping the Zamp 320watt 4 Solar Panel package, and having them uninstall the inverter, and now fix the wiring that has caught on fire. Or do we just ask them to remove the whole setup.
jasperkins is offline   Reply With Quote
Old 05-18-2014, 09:20 PM   #9
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
Quote:
Originally Posted by jasperkins View Post
Can you explain how its supposed to be wired with still being able to use the existing outlets? Having to always turn off the converter breaker and worrying about fire scares us. It's the Zamp system, with 4 panels.
It appears to me that the fire was because the screw for the affected wire was loose.

While I don't necessarily think your install will win any awards, powering the converter from the inverter shouldn't damage anything, though it will cause battery drain.
__________________
To learn to see below the surface, you must adjust your altitude
Jammer is offline   Reply With Quote
Old 05-18-2014, 09:52 PM   #10
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Your solar may be just fine. There is no indication that it is involved in any of the fire situation. It is on the 12 volt battery side.

It is the inverter which is screwed up, on the 120 volt side.

Taking power from the batteries to run the inverter and then using that 120 volt power to run the converter/charger and charge the batteries may not do any damage as Jammer says, but it certainly will run the batteries down. It is not a perpetual motion machine.
idroba is offline   Reply With Quote
Old 05-18-2014, 09:54 PM   #11
3 Rivet Member
 
jasperkins's Avatar
 
2012 27' FB Eddie Bauer
2018 Tommy Bahama Interstate
Ouray , Colorado
Join Date: May 2013
Posts: 185
the first night we tried the inverter, everytime the converter fan kicked on the inverter would turn off. That's when we were told to flip off the converter breaker. I checked the nut for the burnt wire, and it was tight. If loose, I would have hoped a breaker would trip before it caught fire.
jasperkins is offline   Reply With Quote
Old 05-18-2014, 10:40 PM   #12
Rivet Master
 
ROBERTSUNRUS's Avatar

 
2005 25' Safari
Salem , Oregon
Join Date: Mar 2006
Posts: 8,376
Images: 18
Blog Entries: 55
Quote:
Originally Posted by jasperkins View Post
the first night we tried the inverter, everytime the converter fan kicked on the inverter would turn off. That's when we were told to flip off the converter breaker. I checked the nut for the burnt wire, and it was tight. If loose, I would have hoped a breaker would trip before it caught fire.
Hi, The screw for the burnt wire looks loose in your picture because it sticks out farther than the rest of them. All except the last white wire on the bottom seem to have been overheated as they look yellowish. An overload would trip a breaker, not a poor connection.
__________________
Bob 2005 Safari 25-B
"Le Petit Chateau Argent" Small Silver Castle
2000 Navigator / 2014 F-150 Eco-Boost / Equal-i-zer / P-3
YAMAHA 2400 / AIR #12144
ROBERTSUNRUS is offline   Reply With Quote
Old 05-18-2014, 10:49 PM   #13
Rivet Master
 
SSquared's Avatar
 
2013 25' FB Flying Cloud
Longmont , Colorado
Join Date: Jan 2012
Posts: 1,107
How to run inverter power to existing outlets

Here's how I think it can be done safely. This assumes the inverter does not have a charger or converter built into it, and does not have a transfer switch built into.

And I assume your trailer is wired similar to my 2013 25FB Flying Cloud. That means the existing converter is powered from the same breaker that feeds the bedroom outlets. Another breaker feeds the front outlets, including the fridge (but not the microwave, if you have a factory-installed microwave).

Based on those assumptions:
1) The output of the bedroom/converter breaker would be changed to only go to the converter.
2) For the other outlets, the wire coming from that breaker would be disconnected from the main breaker box.
3) A transfer switch would be installed. Two wires would feed it. One would come from the main breaker box where we disconnected the wire in step 2. The other would come from the inverter.
4) A new small breaker box would be installed. It would be fed from the new transfer switch. The new breaker box would have two output circuits. One would be the wire from step 2. The other would be the wire that feeds the bedroom outlets.
5) The affected breakers in the main box may need to be changed out for ones with different ratings.

Does the Eddie Bauer have two places on the outside where you can connect your shore power cord? (Most large modern AS trailers do). If so, that means you had a transfer switch already, and it is installed between those two input connectors and the original breaker box. When this dealer installed your inverter, did they keep both of the shore power connections active? Or perhaps they disconnected one of your shore power connectors, and wired the inverter into the existing transfer switch? If this is what they did, I think it was a bad idea. (But it would have been cheap and easy)
SSquared is offline   Reply With Quote
Old 05-18-2014, 11:18 PM   #14
3 Rivet Member
 
jasperkins's Avatar
 
2012 27' FB Eddie Bauer
2018 Tommy Bahama Interstate
Ouray , Colorado
Join Date: May 2013
Posts: 185
SSquared, I don't fully understand the configuration, but the front shore power now has a switch for Generator or Inverter. I have it flipped to Inverter, as when I use the Gennies, its on the side shore power. Its a new switch in the FB compartment next to the Inverter. This is a 2012 27FB model too.

The tech did move the bedroom electrical off of the Converter breaker to the Microwave breaker. They did that so I could manually flip the breaker and not kill the 3 outlets in the bedroom. I like the steps 2/3/4/5, but it just wasn't done. It makes sense for this type of install to only run the outlets and not have to flip breakers.

All- thanks again for the PM's and call. I will say I am traveling the US with a 6 month pregnant wife and 2 dogs, and the dealership that did the install was not in Denver :-) I have had good experience with the Denver dealership :-)
jasperkins is offline   Reply With Quote
Old 05-19-2014, 05:55 AM   #15
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
The top wire, that is burned, is the wire to the shore power connection. It is 10 gauge copper. There is no way that the inverter could produce enough current to cause that wire to overheat.

Problems like that come from the terminal being loose or from corrosion.

At this point, I would suggest having someone qualified remove the wire from the terminal, clean the wire and terminal with a wire brush, apply some antioxidant grease, and reassemble everything.

And if it were me I would closely watch the connection while running the trailer on shore power with a heavy electrical load for 10 minutes, and check temperatures with an IR thermometer.
__________________
To learn to see below the surface, you must adjust your altitude
Jammer is offline   Reply With Quote
Old 05-19-2014, 03:55 PM   #16
Rivet Master
 
SSquared's Avatar
 
2013 25' FB Flying Cloud
Longmont , Colorado
Join Date: Jan 2012
Posts: 1,107
jasperkins,

Your last post pretty well explained how your inverter is connected. It's on a manual transfer switch with your line from the outside generator connector. From that switch, the current flows to the existing automatic transfer switch, which selects between the rear shore power connector, and the generator/inverter switch. So when you are using your inverter, the power is fed to the main box, and 110 volt power is available to everything in the trailer. Even the air conditioner will get 110 volt power, although there will be no where near enough current to run the air conditioner.

Obviously you will not turn the air conditioner on with the inverter, so it is not really a problem for the air conditioner to have the inverter wired this way.

You will want to be careful not to switch your water heater on electric mode. That will either cause the inverter to shut down, or drain your batteries in no time flat.

In the standard configuration, the converter is powered directly from the breaker without a switch, and will always run when it sees 110 volt power coming to it. As someone else said above, this is not good. The dealer is right, you must always throw that breaker when you run the inverter. It should not be too hard to wire in a simple on/off switch for the converter, and put it in a more convenient place. Then you would not need to touch the breaker.

Good luck.
SSquared is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
FiRe, FiRe, FIRE, in the AiRsTrEaM!!!! TheBigRedTruck On The Road... 47 08-14-2021 05:30 PM
Solar Install AM Solar outdoors717 Generators & Solar Power 3 07-15-2012 07:11 PM
FIRE! Electrical Short and Slide-Out Controller Fire rjd Electronics & Connectivity 10 07-24-2009 07:47 AM
Fire(s) after the Dometic "fix"?? Kistler Refrigerators 1 08-11-2007 05:25 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 06:09 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.