07-07-2012, 11:08 AM
|
#21
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by zigzagguzzi
Was the inverter factory installed. I do not have one in mine. Jim
|
No, it was added when I added solar.
|
|
|
07-07-2012, 11:40 AM
|
#22
|
Master of Universe
2008 25' Safari FB SE
Grand Junction
, Colorado
Join Date: Sep 2007
Posts: 12,711
|
Glad to hear Lew called since he knows your system better than anyone.
It was sounding to me like your main breaker had failed. Your OP seems to say your wife had the A/C, microwave and waffle iron all on at the same time. That would surely trip the main, 30 amp, breaker, if I am reading it right. If the breaker does not reset, it blew out inside. But I defer to Lew.
Gene
|
|
|
07-07-2012, 11:50 AM
|
#23
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by CrawfordGene
Glad to hear Lew called since he knows your system better than anyone.
It was sounding to me like your main breaker had failed. Your OP seems to say your wife had the A/C, microwave and waffle iron all on at the same time. That would surely trip the main, 30 amp, breaker, if I am reading it right. If the breaker does not reset, it blew out inside. But I defer to Lew.
Gene
|
Everything works when I power on inverter. That wouldn't be the case if the main breaker failed ... would it???
|
|
|
07-07-2012, 12:06 PM
|
#24
|
Master of Universe
2008 25' Safari FB SE
Grand Junction
, Colorado
Join Date: Sep 2007
Posts: 12,711
|
Quote:
Originally Posted by UAPachyderm
Everything works when I power on inverter. That wouldn't be the case if the main breaker failed ... would it???
|
If the inverter is wired to bypass the converter main breaker, then everything would work. The inverter may have its own internal breaker to 120 v. and then the 120 v. from the inverter could go directly to the branch circuit breakers. That seems strange to me, but if the 120 v. supply from the inverter is attached to the buss bars after the main breaker, then that would mean the main breaker is bypassed. The buss bars are copper bars behind the breakers with one hot side and one common; breakers attach to the buss bars. If you have a multimeter (probably will have one soon) you can check each connection to see if it is hot.
I'm guessing (perhaps babbling); Lew knows all. There has to be some sort of switch to manage solar, shore power, inverter and converter. Each component may have a switch for these purposes and it sounds like the usual suspect is in the inverter.
Gene
|
|
|
07-07-2012, 01:20 PM
|
#25
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by CrawfordGene
If the inverter is wired to bypass the converter main breaker, then everything would work. The inverter may have its own internal breaker to 120 v. and then the 120 v. from the inverter could go directly to the branch circuit breakers. That seems strange to me, but if the 120 v. supply from the inverter is attached to the buss bars after the main breaker, then that would mean the main breaker is bypassed. The buss bars are copper bars behind the breakers with one hot side and one common; breakers attach to the buss bars. If you have a multimeter (probably will have one soon) you can check each connection to see if it is hot.
I'm guessing (perhaps babbling); Lew knows all. There has to be some sort of switch to manage solar, shore power, inverter and converter. Each component may have a switch for these purposes and it sounds like the usual suspect is in the inverter.
Gene
|
Haha, Gene ... you were right. Once I uninstalled the inverter a little button revealed itself on the lower side. Lew and I forgot about that little bugger! We now have air conditioning.
|
|
|
07-07-2012, 02:00 PM
|
#26
|
Master of Universe
2008 25' Safari FB SE
Grand Junction
, Colorado
Join Date: Sep 2007
Posts: 12,711
|
How did the reset breaker on the inverter trip? Was your wife using too many things while operating on batteries and inverter? It sounded like you were on shore power, but maybe 120 v. shore power is routed though the inverter and it would trip the breaker there instead of the converter main breaker.
Next time I see Lew I'll remind him that despite his master's degree in EE, he's still young and inexperienced by 11 years compared to me.
Glad to hear you are being cooled again. The owner's manual says not to run the A/C and a microwave or other high amp appliance at the same time. We have a smaller microwave and it may not combine to 30 amps with the A/C. A waffle iron certainly would if the other two are on. Most of the time we turn off the A/C when we run the microwave, but sometimes forget. It has never tripped the breaker, however.
Gene
|
|
|
07-07-2012, 02:16 PM
|
#27
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by CrawfordGene
How did the reset breaker on the inverter trip? Was your wife using too many things while operating on batteries and inverter? It sounded like you were on shore power, but maybe 120 v. shore power is routed though the inverter and it would trip the breaker there instead of the converter main breaker.
Next time I see Lew I'll remind him that despite his master's degree in EE, he's still young and inexperienced by 11 years compared to me.
Glad to hear you are being cooled again. The owner's manual says not to run the A/C and a microwave or other high amp appliance at the same time. We have a smaller microwave and it may not combine to 30 amps with the A/C. A waffle iron certainly would if the other two are on. Most of the time we turn off the A/C when we run the microwave, but sometimes forget. It has never tripped the breaker, however.
Gene
|
We know better than to run the air and another appliance, but somehow we simultaneously ran air, microwave, tv and a waffle iron this morning. Sooo, we experienced our mysterious power outage while on shore power. All the usual breakers and fuses remained in tact.
Yes, everything runs through my inverter. I isolated the issue to the inverter. I then completely uninstalled the inverter and bypassed it (with Lew's help over the phone) ... then noticed that cute little button was popped out. Called Lew, we laughed, then I put it all back together. The Silver Lining is that I now know how to make my air work if my inverter does decide to die. LOL ... Really enjoying the cool air now.
|
|
|
07-07-2012, 03:35 PM
|
#28
|
4 Rivet Member
2012 25' Flying Cloud
Eureka
, California
Join Date: Sep 2011
Posts: 321
|
Great ending! Dog gone reset button!
|
|
|
07-07-2012, 03:42 PM
|
#29
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by redwoodguy
Great ending! Dog gone reset button!
|
Yes indeed ... and I'll never forget that little button exists again!!!
|
|
|
07-07-2012, 05:57 PM
|
#30
|
Rivet Master
1988 32' Excella
Robbinsville
, New Jersey
Join Date: May 2012
Posts: 3,165
|
Wow lots of ambition in the heat. Once bypassed and working I would have left it bypassed until it cooled off.
|
|
|
07-09-2012, 04:26 AM
|
#31
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by CrawfordGene
How did the reset breaker on the inverter trip?
Gene
|
Well, it seems that this is still a question I don't know the answer to. Friday, the breaker on the inverter coming in from shore power tripped. All was well until Sunday evening.
At least twice Sunday night power went out and back on ... without tripping any breaker.
About 4am this morning the breaker on the site pole tripped. I inspected everything then reestablished power on the site pole.
A few minutes later the site pole breaker tripped again. However, this time I saw a small "flash" at my old converter. Oddly, nothing is wrong inside the Airstream (no bad fuses or tripped breakers) ... but the breaker on the site pole is tripped.
I tested the site pole and it appears to be in good order. I had maintenance come over and they said pole appeared good. However, I am not taking any chances and plan to change sites to be sure the problem isn't a surge issue from this site. I'm at Disney Fort Wilderness ... they are sending over their Forman of electricians at 8am.
Interestingly, when I turn my inverter on, everything works. So, I'm still having issues getting shore power and the cause is a mystery.
Perhaps it is the site. Could be I didn't reconnect everything super tight (double checking all that now). Could be my inverter as originally thought (it's been squirly since install and Lew and I have wondered if it had a bad board/relay). Perhaps it is some issue I haven't thought about yet.
Not hot here this Monday morning ... yet ...
|
|
|
07-09-2012, 05:48 AM
|
#32
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
No m
|
|
|
07-09-2012, 06:55 AM
|
#33
|
A.K.A "THE STREAM"
2010 25' FB International
Arlington
, Texas
Join Date: Dec 2009
Posts: 1,308
|
Glad things worked out,..little late reading here.
On the subject of running things,..we run our convection microwave,A/C, Television and charge our iPads and phones and turn the lights on and off At the same time,..and have never had any problems.
Are we asking for trouble?
Thanks,
Shane
|
|
|
07-09-2012, 06:59 AM
|
#34
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by THEPILL
Glad things worked out,..little late reading here.
On the subject of running things,..we run our convection microwave,A/C, Television and charge our iPads and phones and turn the lights on and off At the same time,..and have never had any problems.
Are we asking for trouble?
Thanks,
Shane
|
They say not to do it. We've never ha issues until I added an inverter.
|
|
|
07-09-2012, 07:01 AM
|
#35
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
BTW, the breaker on site was on the fritz. It's been replaced (my situation may have caused it to go or it may have caused my situation ... who knows). We are back up and running. Hopefully it stays that way!
|
|
|
07-09-2012, 07:27 AM
|
#36
|
Moderator
2017 26' Flying Cloud
Alamo Heights
, Texas
Join Date: Aug 2006
Posts: 8,534
|
Quote:
Originally Posted by CrawfordGene
How did the reset breaker on the inverter trip? Was your wife using too many things while operating on batteries and inverter? It sounded like you were on shore power, but maybe 120 v. shore power is routed though the inverter and it would trip the breaker there instead of the converter main breaker.
~~
Gene
|
My supposition is that since the inverter has an automatic switchover from 30A shore power to inverter power, it has a 30A breaker to protect that circuit (fits with the label on that button). It seems that the inverter's breaker is a little more sensitive than the trailer's main breaker.
UAPachyderm: Is that breaker inaccessible when the inverter is installed? Or just hidden from view?
__________________
David
Zero Gravitas 2017 Flying Cloud 26U | WBCCI# 15566
He has all of the virtues I dislike and none of the vices I admire. Sir Winston Churchill
|
|
|
07-09-2012, 02:37 PM
|
#37
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by DKB_SATX
My supposition is that since the inverter has an automatic switchover from 30A shore power to inverter power, it has a 30A breaker to protect that circuit (fits with the label on that button). It seems that the inverter's breaker is a little more sensitive than the trailer's main breaker.
UAPachyderm: Is that breaker inaccessible when the inverter is installed? Or just hidden from view?
|
Accessible ... just not in plain view. LOL, no worries, there's an obvious label and arrow on top now!
|
|
|
07-10-2012, 09:02 AM
|
#38
|
Master of Universe
2008 25' Safari FB SE
Grand Junction
, Colorado
Join Date: Sep 2007
Posts: 12,711
|
Double diagnosis is a bad approach to problem solving, but sometimes 2 things do go bad.
It sure sounds like:
1. The campground breaker was bad, and
2. The inverter has a pre-existing condition.
Even if the new campground breaker is fine, the inverter may still need a new circuit board. If the company will send you a replacement without asking you return the inverter, I'd go for it.
Gene
|
|
|
07-10-2012, 02:03 PM
|
#39
|
4 Rivet Member
2004 28' International CCD
Birmingham
, Alabama
Join Date: Sep 2007
Posts: 323
|
Quote:
Originally Posted by CrawfordGene
Double diagnosis is a bad approach to problem solving, but sometimes 2 things do go bad.
It sure sounds like:
1. The campground breaker was bad, and
2. The inverter has a pre-existing condition.
Even if the new campground breaker is fine, the inverter may still need a new circuit board. If the company will send you a replacement without asking you return the inverter, I'd go for it.
Gene
|
Yep, the plan is to replace the circuit board upon return.
|
|
|
07-10-2012, 02:39 PM
|
#40
|
Master of Universe
2008 25' Safari FB SE
Grand Junction
, Colorado
Join Date: Sep 2007
Posts: 12,711
|
Cool, literally.
Gene
|
|
|
|
|