Old 07-19-2018, 07:53 AM   #41
Half a Rivet Short
 
2017 30' Classic
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 9,056
Quote:
Originally Posted by gator.bigfoot View Post
If you have no load on in the trailer then plugging in or out shouldn't be an issue. Simply turn off the AC and the hot water heater and 90% of your loads are gone. Then you won't have to switch off the receptacle. I never switched off the receptacle and haven't had an issue from the that, just a worn out receptacle that causes a loose connection which in turn will melt your plug if you are drawing high amounts of current. If you want AC you are probably not going to care and are going to sacrifice the plug instead. What is the solution? Carry a spare? Complain to the park?

Good luck.
Hi

While that's true for a 30A setup, there is a gotcha with a 50A. If the neutral wire mates "last" as you hook things up, you have lord only knows what on each of the legs. If you have a large load only on one side, the "light" side may be pretty close to 240V. Even if it's only for a second or two .... not a good idea.

Bob
uncle_bob is offline   Reply With Quote
Old 07-19-2018, 07:06 PM   #42
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,004
Images: 2
Blog Entries: 5
Plug the power cord into a live outlet is asking for trouble.
Unless you turn off the main breaker in the coach. There are devices such as the converter, water heater, and the refer or perhaps the air conditioner that may be energized the moment you make contact with the receptacle.
Each arc degrades both the male and female part of the electrical system.
Not only this stuff above.
You are putting your life at risk plugging into a hot receptacle.
You eliminate the risk and plug/receptacle damage by shutting the breaker off.
Ask yourself this.
Do I test the pedestal power prior to plugging in my expensive coach? Probably not.
If you don't. How do you know if the receptacle is wired correctly?
I have worked in the electrical field for over 50 years.
One of the first things I was taught is not to grasp an electrical cord plug like you would a baseball.
The 30 amp and 50 amp plugs should be inserted using the palm of your hand.
This way if you were to get shocked your hand can be removed quickly. If your fist is closed around the plug you may not be able to open your hand to release the plug.
Think safe, be safe!
The life you save could be your own.
TG Twinkie is offline   Reply With Quote
Old 07-19-2018, 08:42 PM   #43
Rivet Master
 
2007 27' International CCD FB
San Diego , California
Join Date: Sep 2014
Posts: 1,593
Quote:
Originally Posted by Oldtrapper View Post
When possible, use a 50A by 30A dogbone and plug into the 50A receptacle, the 50A receptacles seem to have much less wear and tear and even if they do, you only have a dogbone at risk.

Quote:
Originally Posted by wmb View Post
The site in CO only had 30A, but you're suggestion is a good one that we'll apply in future when we're at a 50A spot.
Novel, this is not really that great of an idea. While this may sidestep the small potential issue to the plug, due to receptacle wear, it now hugely increases other risks, namely the whole circuit in your camper!

You no longer have a 30amp circuit breaker protecting the 30amp rated distribution wiring in your trailer. Now you've enabled a full 50amps of supply to potentially fry that circuit in your trailer in the event of an issue. And potentially the whole trailer along with it!

Too much overthinking in this thread. Electrical systems are well thought out. It's by design that things work and fail the way they do - in a controlled and safe fashion. They can and do wear. Once worn to failure, it's a cheap and easy fix.

Reinventing a "smarter" way might just invite other failure modes that are not typical and potentially much more disastrous.
__________________
Boondocking Rig: '07 27FB Ocean Breeze "See Turtle"
Lexus LX570 on 33's - $1k 300Ah Lithium Upgrade - Tongue Mount Honda eu2200i - Rear Hitch - Underbelly Storage - Blizzard NXT w/ EasyStart - 3" Lift
pteck is offline   Reply With Quote
Old 07-19-2018, 09:57 PM   #44
Rivet Master
 
2011 22' Sport
Portland , Oregon
Join Date: Aug 2017
Posts: 606
Quote:
Originally Posted by pteck View Post
Novel, this is not really that great of an idea. While this may sidestep the small potential issue to the plug, due to receptacle wear, it now hugely increases other risks, namely the whole circuit in your camper!

You no longer have a 30amp circuit breaker protecting the 30amp rated distribution wiring in your trailer. Now you've enabled a full 50amps of supply to potentially fry that circuit in your trailer in the event of an issue. And potentially the whole trailer along with it!

Too much overthinking in this thread. Electrical systems are well thought out. It's by design that things work and fail the way they do - in a controlled and safe fashion. They can and do wear. Once worn to failure, it's a cheap and easy fix.

Reinventing a "smarter" way might just invite other failure modes that are not typical and potentially much more disastrous.
I have mixed thoughts on this. If you look at the wiring to your house, there is no breaker upstream between the transformer and the meter on the side of your house. Your main breaker is sized to the feeder wire's capacity and prevents the downstream circuits from over-drawing the feeder. If we take that and apply it to your trailer, your trailer still has a 30-amp main that prevents the aggregate of loads in the trailer from loading beyond the 30-amp shore cord. Now if something was to happen between the pedestal receptacle and your main, then yes that is a risk that it takes a 50amp load to fail, but what scenario are we planning for?
SilverHouseDreams is offline   Reply With Quote
Old 07-19-2018, 10:12 PM   #45
Moderator
 
DKB_SATX's Avatar

 
2017 26' Flying Cloud
Alamo Heights , Texas
Join Date: Aug 2006
Posts: 7,738
Images: 1
Blog Entries: 7
Quote:
Originally Posted by pteck View Post
Novel, this is not really that great of an idea. While this may sidestep the small potential issue to the plug, due to receptacle wear, it now hugely increases other risks, namely the whole circuit in your camper!

You no longer have a 30amp circuit breaker protecting the 30amp rated distribution wiring in your trailer. Now you've enabled a full 50amps of supply to potentially fry that circuit in your trailer in the event of an issue. And potentially the whole trailer along with it!

Too much overthinking in this thread. Electrical systems are well thought out. It's by design that things work and fail the way they do - in a controlled and safe fashion. They can and do wear. Once worn to failure, it's a cheap and easy fix.

Reinventing a "smarter" way might just invite other failure modes that are not typical and potentially much more disastrous.
Well, you no longer have a 30A breaker protecting your shore-power cord. There's still the 30A main breaker in the Airstream, but a short between the pedestal and your Airstream panel could still slag the shore-power cord before the 50A pedestal breaker opened.
__________________
— David

Zero Gravitas — 2017 Flying Cloud 26U | WBCCI# 15566

He has all of the virtues I dislike and none of the vices I admire. — Sir Winston Churchill
DKB_SATX is offline   Reply With Quote
Old 07-19-2018, 10:59 PM   #46
wmb
2 Rivet Member
 
2013 25' Flying Cloud
Springfield , New Jersey
Join Date: Feb 2018
Posts: 64
Quote:
Originally Posted by AirstreamInc View Post
Hi wmb,

Please send us a direct message with your contact information and the last 6 digits of your VIN so we can share it with our Customer Service and Technical Support team. We look forward to helping you get this resolved.

You can also reach Airstream Customer Service and Technical Support at customer_support@airstream.com

Thank you.
Thanks, I left a few PMs with my info. Please let me know if there's any advice you guys have. I did read about a recall on this model year but I don't know if the previous owners had the issue addressed under that. They certainly never mentioned it to us.
wmb is offline   Reply With Quote
Old 07-20-2018, 12:45 AM   #47
Rivet Master
 
2007 27' International CCD FB
San Diego , California
Join Date: Sep 2014
Posts: 1,593
Quote:
Originally Posted by DKB_SATX View Post
Well, you no longer have a 30A breaker protecting your shore-power cord. There's still the 30A main breaker in the Airstream, but a short between the pedestal and your Airstream panel could still slag the shore-power cord before the 50A pedestal breaker opened.
Yup. The 30-amp cord. And the 30-amp plug and receptacle on the side of your airstream. And the 30-amp wire to the main breaker/breaker panel within your airstream. None of those are appropriately protected by that big 50-amp breaker.

Quote:
Originally Posted by SilverHouseDreams View Post
I have mixed thoughts on this. If you look at the wiring to your house, there is no breaker upstream between the transformer and the meter on the side of your house. Your main breaker is sized to the feeder wire's capacity and prevents the downstream circuits from over-drawing the feeder. If we take that and apply it to your trailer, your trailer still has a 30-amp main that prevents the aggregate of loads in the trailer from loading beyond the 30-amp shore cord. Now if something was to happen between the pedestal receptacle and your main, then yes that is a risk that it takes a 50amp load to fail, but what scenario are we planning for?
Shorts can happen anywhere in the chain, for unexpected reasons. User mistake, rodents, some act of murphy. The idea has always been that you want the breaker to trip. It's external, each to reach, easy to reset or fix. In the case of a trailer, along with the cord, there is an internal wire run from the side receptacle to the main panel. Why shouldn't that be appropriately protected? i surely don't ever want to risk that wire becoming the "breaker" in an unexpected situation.
__________________
Boondocking Rig: '07 27FB Ocean Breeze "See Turtle"
Lexus LX570 on 33's - $1k 300Ah Lithium Upgrade - Tongue Mount Honda eu2200i - Rear Hitch - Underbelly Storage - Blizzard NXT w/ EasyStart - 3" Lift
pteck is offline   Reply With Quote
Old 07-20-2018, 08:45 AM   #48
Rivet Master
 
gklott's Avatar

 
2004 30' Classic
Johnson City , Texas
Join Date: Jun 2003
Posts: 584
Images: 86
pteck is right. The issue is the wiring from the park's pedestal to your trailer's circuit panel. Using a 50A-to-30A dogbone, the pedestal's OCPD is 50A.

A normal 30A RV power cord is 3-conductor 10 AWG Type SOW. According to NEC Table 400.5(A)(1), 30A is the allowable ampacity at 30C (86F). If laying in the sun, the cord's rating is even lower. You then have a power inlet rated at 30A and 10 AWG NM-B cable from the inlet to your trailer's circuit panel. Your circuit panel may be only rated for 30A.

I do not recommend using a 50A male to 30A female "dogbone" adapter as regular practice. We do not carry one.

73/gus
__________________
Gus - KR4K : Mary - K5MCL
2004 30ft. Classic
2017 Infiniti QX80 Limited
ProPride 3P/Prodigy P3
gklott is offline   Reply With Quote
Old 07-20-2018, 10:47 AM   #49
Rivet Master
 
2011 22' Sport
Portland , Oregon
Join Date: Aug 2017
Posts: 606
We are all discussing what is "allowed for continuous safe amperage", that doesn't mean that a 30-amp cord couldn't sustain 50-amps long enough to trip a breaker with a direct short.
SilverHouseDreams is offline   Reply With Quote
Old 07-20-2018, 11:14 AM   #50
Rivet Master
 
SteveSueMac's Avatar

 
2012 27' Flying Cloud
W , New England
Join Date: Oct 2012
Posts: 7,397
Sounds like a million dollar industry to make a 50 to 30 dogbone with a breaker in the dogbone, no?
SteveSueMac is offline   Reply With Quote
Old 07-20-2018, 04:05 PM   #51
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
Am I bad if I mention that I think this conversation has gone a little off the edge?

It’s all pretty simple, a melted plug or a melted power inlet is going to be caused by the contacts on one end or the other of the connection being faulty or corroded.

If one side of the connection got hot so did the other side. The best move is to replace both the plug and the socket.

Most of the time failures like these can be averted by keeping the plug pins clean and free of corrosion.
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 07-20-2018, 05:40 PM   #52
3 Rivet Member
 
2000 25' Safari
Denver , North Carolina
Join Date: May 2016
Posts: 173
Images: 3
Blog Entries: 16
So I read this and went out to the trailer with 2 small pieces of sandpaper and cleaned. It took all of 10 minutes. Peace of mind.
mbubbaca is offline   Reply With Quote
Old 07-20-2018, 10:48 PM   #53
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 8,508
Blow out the dust and abrasive and conductive particles as well.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is online now   Reply With Quote
Old 07-21-2018, 10:42 AM   #54
wmb
2 Rivet Member
 
2013 25' Flying Cloud
Springfield , New Jersey
Join Date: Feb 2018
Posts: 64
I took some pictures
Attached Thumbnails
Click image for larger version

Name:	IMG_20180720_205956459.jpg
Views:	42
Size:	691.8 KB
ID:	317626   Click image for larger version

Name:	IMG_20180720_205932873.jpg
Views:	39
Size:	666.8 KB
ID:	317627  

wmb is offline   Reply With Quote
Old 07-21-2018, 10:54 AM   #55
wmb
2 Rivet Member
 
2013 25' Flying Cloud
Springfield , New Jersey
Join Date: Feb 2018
Posts: 64
Quote:
Originally Posted by Mollysdad View Post
If I read the OP correctly the failure was at the inlet of the Airstream not the power pedestal.
I've never seen anyone break the connection by pulling the cord out of the RV before disconnecting from the pedestal, regardless of the breaker.
Sounds to me like something was loose in the receptacle and constant arcing caused it to burn up. I've had it happen at home, replaced the outlet and all was fine.

We do in fact turn off the breaker in the pedestal before connecting and disconnecting, and I always check the power with the SurgeGuard before connecting the cord.
wmb is offline   Reply With Quote
Old 07-21-2018, 10:54 AM   #56
Slide Out Society #001
 
GCinSC2's Avatar
 
2007 30' Classic S/O
Somewhere , South Carolina
Join Date: Apr 2010
Posts: 4,136
Ouch.

I messed with one of those trailer receptacle ONE time so far. On the 2008 it had a big glob of sealant on the inside that was part of the sealing job I think. Dealing with that stuff was the nastiest part of the job.

Food for thought for carrying a spare. But my rig is gen prepped so I have two connection points.

Get 'er done!
__________________
S/OS #001
2005 Dodge Ram 2500 5.9L 6 Speed
16" Michelins, Hi Spec Wheels, Max Brake, Carslile Actuator, Equal-i-zer, Dill TPMS. Campfire cook.
GCinSC2 is offline   Reply With Quote
Old 07-21-2018, 10:58 AM   #57
wmb
2 Rivet Member
 
2013 25' Flying Cloud
Springfield , New Jersey
Join Date: Feb 2018
Posts: 64
Quote:
Originally Posted by 369goose View Post
Yes, when our Airstream was new we had a similar experience. Found out there indeed was a recall and Airstream took very good care of the repairs.
Would I still be able to get a repair under the recall if it's out of warranty and I'm the second owner?

Now that I know about the recall I'm concerned about using the second inlet on the front of the trailer, if that has the same problem. But we're in Utah and it's 100 F so we don't really have much of a choice.
wmb is offline   Reply With Quote
Old 07-21-2018, 11:01 AM   #58
wmb
2 Rivet Member
 
2013 25' Flying Cloud
Springfield , New Jersey
Join Date: Feb 2018
Posts: 64
Offtopic

By the way, I guess they come in fours, not threes, because we just found out yesterday that our truck has a head gasket problem and needs two weeks in the shop...
wmb is offline   Reply With Quote
Old 07-22-2018, 09:36 AM   #59
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
Quote:
Originally Posted by wmb View Post
By the way, I guess they come in fours, not threes, because we just found out yesterday that our truck has a head gasket problem and needs two weeks in the shop...


Bummer. Diesel?
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 07-22-2018, 08:59 PM   #60
Rivet Master
 
2016 30' International
redondo beach , California
Join Date: Feb 2017
Posts: 527
Quote:
Originally Posted by wmb View Post
By the way, I guess they come in fours, not threes, because we just found out yesterday that our truck has a head gasket problem and needs two weeks in the shop...
A vacation to remember forever!
__________________
Randy and Beth 15 F250, 16 30' International, ProPride, Dexter 3" lift, Michelin 16, Dill TPMS, Centramatics, Battleborn x4, Victron BMV and 1.2KW inverter, Orion DC/DC, BlueSolar MPPT, 300W solar, Alpine iLX, Polk MM1, Samsung smart 42"
mythbuster88 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
No Power to Trailer When Hooked to 30A Receptacle hwm Electrical - Systems, Generators, Batteries & Solar 2 05-21-2017 07:38 PM
Melted exterior floodlight cover wacnstac Lights - Interior & Exterior 14 03-26-2008 05:09 AM
30A Upgrade to 30A + 20A Wayne Olson Classic Motorhomes 10 12-12-2006 04:51 PM
Alternator wire melted airstream963 Mechanics Corner - Engines, Transmission & More... 5 05-07-2005 07:46 PM
Melted lens? Rickj Electrical - Systems, Generators, Batteries & Solar 3 01-03-2004 12:17 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 02:21 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, Jelsoft Enterprises Ltd.