20 Amp or 30 Amp, that's the question

Here's one for the experts to noodle out. The main circuit breaker coming into the 110v panel from the shore power is only a 20 amp breaker. Coming out of the panel there are two 20 amp breakers that feed the interior of the camper. One of these 20 amp branch circuits feeds the air conditioner. The other 20 amp branch circuit feeds all of the other 110v outlets.

So the question is, why only a 20 amp for the main, shouldn't it be a 30 amp? Is there any reason why I can't replace it with a 30 amp?

The shop manual isn't much help here. The wiring diagram in the manual shows the circuit layout to be exactly what I have (wiring only). The diagram of the breaker panel (panel only)shows only 2 20 amp breakers, one to the shore power and one to everything else inside the camper (obviously this isn't correct).

As always, thanks for the help!

Jim
__________________
Solve for X, Or is it Y?

www.nesa.org
Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 06:17 AM   #2
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
the reason for this is because the air conditioner is completely separate from the rest of the wires. The wiring in the trailer is only supposed to be able to handle 20 amps.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 01-21-2008, 06:23 AM   #3
Remember, Safety Third
 
Jim & Susan's Avatar

 
1973 27' Overlander
Catfish Corners , Georgia
Join Date: Oct 2004
Posts: 5,720
Images: 39
I understand that part of it; the air conditioner should have its own dedicated circuit from the panel. What I don't understand is why the shore power breaker is only 20 amp. If the camper is supposed to be 30 amp, why wouldn't the main breaker be a 30 amp? The mystery continues....
__________________
Solve for X, Or is it Y?

www.nesa.org
Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 06:26 AM   #4
Rivet Master
 
juel's Avatar

 
1976 31' Sovereign
Currently Looking...
Chandler , Oklahoma
Join Date: Oct 2004
Posts: 1,770
Images: 24
My trailer is the same; however, we had an additional plug installed on the AC circuit for use in the winter. Since we have the elect/LP water heater on the other circuit, we were limited in our use of the 20amps. In the winter we use the AC circuit for an electric heater. We have not put in a new furnace and have been hesitant about using the original central heat in the Argosy. Actually we don't use the trailer much in the really cold part of our winters, so with the cat heater and the electric space heater this has worked out well.
juel is offline   Reply With Quote
Old 01-21-2008, 06:32 AM   #5
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Jim,

Look at the guage of the wire that is feeding the breaker box from the street connection. The breaker on that lead should the wire guage.....20 amp for 12 guage and 30 amp for 10 guage.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 01-21-2008, 06:42 AM   #6
Remember, Safety Third
 
Jim & Susan's Avatar

 
1973 27' Overlander
Catfish Corners , Georgia
Join Date: Oct 2004
Posts: 5,720
Images: 39
I just went out and checked, the street connection is 10 guage and printed on the wire it reads "30 amp" service. SO that means that I can replace the 20 amp street side breaker with a 30 amp, right?
__________________
Solve for X, Or is it Y?

www.nesa.org
Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 07:06 AM   #7
4 Rivet Member
 
empresley's Avatar
 
1984 34' International
1977 Argosy 24
Central , Georgia
Join Date: Jun 2006
Posts: 492
Images: 15
Our '77 has 10 ga. service wire & 30A main breaker.

The individual circuits are protected at 20A so I (not being an electrician) would feel comfortable changing the main to 30A.

Seems like you should be able to maximize the use of 30A service offered by campsites.
For example:
If you are using the AC (has it's own 20A circuit) and a microwave (let's say 800 watt size) on the receptacle circuit; the 30A main would allow this when the existing 20A may not. right?

Qualified advice is needed here. Amateur electricians can burn things up.

martin.
__________________
Travelers by aluminum roadships, loyalists to one species,
masters of convenience, herdsmen steeped in maintenance and restoration.


empresley is offline   Reply With Quote
Old 01-21-2008, 07:14 AM   #8
Remember, Safety Third
 
Jim & Susan's Avatar

 
1973 27' Overlander
Catfish Corners , Georgia
Join Date: Oct 2004
Posts: 5,720
Images: 39
Well, I just went back out and looked at things again. Then looked back at the shop manual. Seems things got a little confused here because of a PO's "creative wiring". Let me see if I can explain.

First, there is no "main" breaker facing streetside. The shop manual shows a direct feed from the street to the main buss without a circuit breaker. Then, there are 2 20 amp breakers that feed the two branch circuits described above (one for the air conditioner, one for everything else). This is actually how things are wired in the panel.

Seems a PO rewired things and left an extra 20 amp breaker in there that is not wired to anything.

So I suppose the real question now is, should I rewire the streetside connection so that it actually has a true "main" circuit breaker that can trun the power off coming from the street. Weird.

Jim
__________________
Solve for X, Or is it Y?

www.nesa.org
Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 07:29 AM   #9
4 Rivet Member
 
empresley's Avatar
 
1984 34' International
1977 Argosy 24
Central , Georgia
Join Date: Jun 2006
Posts: 492
Images: 15
Jim,
Considering the age, capacity & limited utilization, I would suggest replacing
with something you can have confidence in.
Try an elec. supply house for a better selection of panels and... I bet you can get a small panel and necessary breakers for under $100. If McDonough doesn't have a large commerical supplier we have several in Macon & I can pick one up for ya.
__________________
Travelers by aluminum roadships, loyalists to one species,
masters of convenience, herdsmen steeped in maintenance and restoration.


empresley is offline   Reply With Quote
Old 01-21-2008, 07:38 AM   #10
Remember, Safety Third
 
Jim & Susan's Avatar

 
1973 27' Overlander
Catfish Corners , Georgia
Join Date: Oct 2004
Posts: 5,720
Images: 39
I think you're probably right, Martin. The idea of not being able to cut main power at the box isn't very appealing. On the other hand, I could just unplug the dang thing!
__________________
Solve for X, Or is it Y?

www.nesa.org
Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 08:20 AM   #11
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
If the service cord is connected directly to the buss, and the two 20a circuits are connected to the buss, you should install a 30a main breaker.

If the box has room for another breaker, you would install the 30a breaker on the buss, adjacent to the branch service breakers. Then you connect the hot wire from the service cord to 30a breaker.

It may look unusual. It will look like you are running the power "backwards" through the main breaker. This is how it is done.

Be sure that you have the ground and neutral wires separated. Sometimes a PO, or even a residential electrician, will bond the ground and neutrals together.
markdoane is offline   Reply With Quote
Old 01-21-2008, 09:09 AM   #12
Rivet Master
 
davidz71's Avatar
 
1986 25' Sovereign
Southern Middle , Tennessee
Join Date: Mar 2002
Posts: 3,319
Images: 23
Quote:
Originally Posted by markdoane
...Sometimes a PO, or even a residential electrician, will bond the ground and neutrals together.
This is exactly what happened about 7 years ago when I developed a short in the 30 amp power cord plug. It kept tripping the campground circuit GFIC so a well meaning factory maintenance electrician ran a jumper wire from ground to neutral. It kept tripping the campground circuit even after I replaced the power cord plug. Once home, I compared the breaker box to the schematics in my manual. Funny thing, there was an extra wire in there that was not there before. I know it was not there prior to this incident because I had replaced a 30 amp main breaker and decided to draw a diagram of the wiring just for the heck of it. Fortunately I kept the drawing and it matched the factory diagram. I removed the jumper and everything worked fine.
__________________
Craig

AIR #0078
'01 2500hd ext. cab, 8.1 litre gas, 5 sp. Allison auto
3.73 rear end
Mag-Hytec rear diff cover
Amsoil Dual by-pass oil filtration system
Amsoil synthetics all around
265 watt AM Solar, Inc. system
davidz71 is offline   Reply With Quote
Old 01-21-2008, 09:09 AM   #13
Rivet Master
 
Aerowood's Avatar
 
1971 21' Globetrotter
Currently Looking...
Currently Looking...
Currently Looking...
Arvada , Colorado
Join Date: May 2006
Posts: 3,530
I agree with EMPRESLEY on replacing the whole box with a new box. I am goimg to go a step further on my GT resto, and go with a 50 amp box to add a dedicated circut to the electric portion of the new hot water heater, fridge, and the micro wave, along with the air conditioning circut, and then a GFI breaker for all the regular outlets. The hot water heater will also have a GFI breaker. I am a strong believer in the saying "better to have and not need then to need and not have"

Kip
Aerowood is offline   Reply With Quote
Old 01-21-2008, 09:57 AM   #14
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
The limiting factor in your wiring is the wiring. you can't have more than a 20 amp breaker if the wiring will only handle 20 amps. From the breaker out to the pole the wiring is rated at 30. If you put a 30 amp inside the triler, the 20 amp rated wires will melt before the breaker will trip. The 20 amp main interior breaker is only for the trailer wiring, not the air conditioner, that wiring is completely seperate.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 01-21-2008, 11:06 AM   #15
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
Quote:
Originally Posted by overlander63
The limiting factor in your wiring is the wiring. you can't have more than a 20 amp breaker if the wiring will only handle 20 amps. From the breaker out to the pole the wiring is rated at 30. If you put a 30 amp inside the triler, the 20 amp rated wires will melt before the breaker will trip. The 20 amp main interior breaker is only for the trailer wiring, not the air conditioner, that wiring is completely seperate.
I'm suggesting that you add a 30a main breaker, and leave the two 20a branch breakers as they are. The 30a breaker limits the energy flow into the buss bar, and the two 20a breakers limit the energy flow out to the branch circuits. None of the trailer wiring other than the main 10 ga. service cord would be exposed to 30 amps.

The 10 ga. service cord is protected by the 30a breaker, and the only wiring between the main breaker and the 20a breakers is the buss bar.
markdoane is offline   Reply With Quote
Old 01-21-2008, 12:22 PM   #16
Retired.
 
Currently Looking...
. , At Large
Join Date: Jun 2003
Posts: 21,276
Quote:
Originally Posted by markdoane
I'm suggesting that you add a 30a main breaker, and leave the two 20a branch breakers as they are. The 30a breaker limits the energy flow into the buss bar, and the two 20a breakers limit the energy flow out to the branch circuits. None of the trailer wiring other than the main 10 ga. service cord would be exposed to 30 amps.

The 10 ga. service cord is protected by the 30a breaker, and the only wiring between the main breaker and the 20a breakers is the buss bar.
That would work, but I think it might be making something unduly complicated, adding another component that would then be able to fail.
Remember, if it ain't there, it can't break.
__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 01-21-2008, 01:09 PM   #17
Rivet Master
 
BIGED52's Avatar
 
1967 22' Safari
MILAN , Illinois
Join Date: Dec 2004
Posts: 2,013
Am I confused?

Are you really just going to install a 30 amp breaker in the service line as a "surge protector" for you breaker box? As Terry says... adding that would likely make just one more item to fail! I am confused as to what was said concerning a separate power source for the AC in your wiring. I have two 20 amp breakers in my box one for the AC and on for the 110 volt outlets. Is this what was meant by separate wiring? Also any power coming off the 20 amp breaker is on household 20 amp 12 gauge wire right? This is a standard way to wire an air conditioner (on its own circuit). If you were to run a third wiring source off a third 20 amp breaker for water heater/heater power there will have to be all new circuit wiring running to those items unless you can separate the circuit wiring at your terminal board. Is this not correct? I have an electrician who will be making all my final connections in my trailer but I would like to know ahead of time that I understand the way things should be. Someone please correct me if I'm wrong or misunderstand how the wiring is in these trailers. Happy Trails, Ed
__________________
1967 Safari Twin "Landshark" w/International trim package
2014 GMC Sierra 1500 Double Cab SLE
FORUMS MEMBER SINCE 12/16/2004AIR#7110
"My tire was thumping, I thought it was flat. When I looked at the tire, I noticed your CAT!" Burma Shave
BIGED52 is offline   Reply With Quote
Old 01-21-2008, 02:04 PM   #18
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
Quote:
Originally Posted by overlander63
That would work, but I think it might be making something unduly complicated, adding another component that would then be able to fail.
Remember, if it ain't there, it can't break.
It might be added complexity, but the code sometimes requires things for safety and this is one of them.

I understand that some early Airstreams may have had separate power connections for air conditioners. That was before 30a supply stands were common.

The current code (NEC 551.42 (C)) requires any unit with two to five, 15- or 20-ampere branch circuits to have a distribution panelboard rated at 120volts maximum with a 30-ampere rated main power supply assembly.

Without a thirty amp main breaker, it is possible to be pulling 40 amps (2x20amps) through the 30a rated service cord.

While most RV power stands have 30 breakers to protect the plug, they are not universal, and NEC requires only a disconnect.
markdoane is offline   Reply With Quote
Old 01-21-2008, 02:29 PM   #19
2 Rivet Member
 
Polecat1's Avatar
 
1979 29' Ambassador
Las Vegas , New Mexico
Join Date: Jan 2008
Posts: 21
20 amp?

If your wire into the trailer is #12 or better, it can handle a 30 amp breaker at the street. Each 20 amp breaker in your panel will take what ever it needs. The 30 amp breaker in the street will now be your "MAIN" breaker providing yoiur cord to the trailer is #12 stranded or better which it is I'm sure. I have never seen anything smaller than#10 stranded wire.
Retired electrician.
__________________
Ted
Polecat1 is offline   Reply With Quote
Old 01-21-2008, 02:41 PM   #20
2 Rivet Member
 
Polecat1's Avatar
 
1979 29' Ambassador
Las Vegas , New Mexico
Join Date: Jan 2008
Posts: 21
for the moderator::: how do I post my own question on this page. It has to do with removing a broken window? I know this is out of context but I am new and don't know how since there is not a means on this page to submit my own question. Thank you. Ted
__________________
Ted
Polecat1 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 / 50 AMP Question kleimanr Electrical - Systems, Generators, Batteries & Solar 7 11-03-2007 02:58 PM
Car & Driver Jan 07, Airstream & Benz Karyn Airstream "In the News" 14 12-04-2006 10:26 PM
Preztels & Beer or Biscotti & Cappuccino? GreggH Community Polls 26 02-20-2006 06:08 PM
Curb Side & Front Glass Window & Clips Oceancontainer 1960 - 1965 Safari 2 07-28-2003 07:04 PM
Dumb Question regarding the bed & sheets kamadeca 2000 - 2004 Safari 8 06-23-2003 02:24 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:27 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.