Old 01-21-2008, 04:37 PM   #21
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
Ted, click on the forums tab at the top of this page. Look down thru there and you will find a sub-forum for windows. CLick on that link. At the top of the listings there will be a "new thread" button. Click on that and you should be able to figure it out. If not, come back here and we'll help you thru it.

Jim
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 04:46 PM   #22
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
I pretty much figured out this morning that I need to do what Markdoane is suggesting in post number 11. I don't like the idea of not being able to isolate the entire panel (without unplugging the Airstream from shore power). That will leave me with one 30 amp main, 1 20 amp for the Air Conditioner and one 20 amp for the remainder of the 110v outlets. I'm also going to add another 15 amp dedicated for just the microwave.

What got all this started is that for the past few days it's been very cold here and I've been working in the camper with a small (1000 watt) ceramic heater in there. I'm getting interior wire heating up a bit while running that heater. Warm, not hot. The 30 amp main that is plugged into the pedestal next to camper is getting a bit warm at the plug only. Just trying to look at everything and see where I can eliminate problem areas.

Thanks for the tips everybody.

Jim
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 06:02 PM   #23
3 Rivet Member
 
crowbar68's Avatar
 
1975 27' Overlander
fort wayne , Indiana
Join Date: Apr 2006
Posts: 184
30 amp panel

from what i understand you have a 4 circuit 30amp panel. it is directly wired to the bus w/ 2, 20amp brkrs and fed from the street w/ a 10ga. wire from a 30amp breaker(from house). this is fine and by code. the 30amp brkr protects the cord and the 20amp brkrs in your camper protect those devices. between the 2, 20 amp brkrs, if you draw potentially 40 amps the 30a brkr will pop protecting your camper. this is the cheesey way to do it.

you can however do what you said, add a 30 amp main, feed the panel thru the 30 amp brkr and thus the other breakers/panel. hope that helps.
__________________
" If everything is working, something is wrong ! "
crowbar68 is offline   Reply With Quote
Old 01-22-2008, 09:45 PM   #24
2 Rivet Member
 
Polecat1's Avatar
 
1979 29' Ambassador
Las Vegas , New Mexico
Join Date: Jan 2008
Posts: 21
Thank you, Jim. I knew there was a way.
__________________
Ted
Polecat1 is offline   Reply With Quote
Old 01-23-2008, 05:38 AM   #25
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,323
Amen!

Quote:
Originally Posted by empresley
....Qualified advice is needed here. Amateur electricians can burn things up.

martin.
Great point! I love the smell of sanity in the morning....

Thanks, Paula
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 01-23-2008, 06:19 AM   #26
2 Rivet Member
 
1967 22' Safari
Cheboygan , Michigan
Join Date: Nov 2005
Posts: 26
Aluminum wiring---should I be concerned

I have a '67, 22ft Safari and I noticed that the outside 110v was wired with aluminum wire--I think I've seem aluminum wire behind the control panel too.

Should I be concerned about this, the outside wiring seemed to be a bit brittle. In case I have to re-wire, what's my life looking like, how tough is it too change?

Fog
lundfog is offline   Reply With Quote
Old 01-23-2008, 06:27 AM   #27
4 Rivet Member
 
empresley's Avatar
 
1984 34' International
1977 Argosy 24
Central , Georgia
Join Date: Jun 2006
Posts: 492
Images: 15
4 Breaker configuration

Every thread needs a photo...

30A “main” breaker at top left wired to feed the panel.
(you can see the jumper wire connecting the main lugs looping under the breakers)
20A breaker at top right is for AC
15A breaker at bottom left handles the 12v converter & rear receps.
20A at bottom right handles the balance of receptacles including frig.

Note:
Check the tightness on all the connections (with power off). Loose lugs can cause overheating. Check the scorched jacket outside the box on the right. I think this
is from overheating on the old AC. There was a rubber strap holding the wire to the wall and at some point in it’s life the temp. was abnormal.
Attached Thumbnails
Click image for larger version

Name:	Arg~OrgPanel.JPG
Views:	151
Size:	125.9 KB
ID:	53044  
__________________
Travelers by aluminum roadships, loyalists to one species,
masters of convenience, herdsmen steeped in maintenance and restoration.


empresley is offline   Reply With Quote
Old 01-23-2008, 06:40 AM   #28
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
Thanks, Martin. Is this from your Argy? That panel looks an awful lot like mine, with a couple of extra breakers, or course. As I stated somewhere above, what got all of this started was the fact that some of my wall outlets are heating up. I spent some time last night looking at the 10/3 wire inside trying to find a weak spot where things might have over heated at some point. Haven't found it yet, but I need to do a better inspection in the daytime when I have more light to work with. I think the best idea at this point is to plan on changing out all of the wall outlets with new, rearrange the breaker panel and inspect the Romex very closly.

Jim
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-23-2008, 07:40 AM   #29
Rivet Master
 
byamcaravanner's Avatar
 
1967 28' Ambassador
1963 19' Globetrotter
1970 29' Ambassador
Waukesha , Wisconsin
Join Date: May 2007
Posts: 1,180
Quote:
Originally Posted by lundfog
I think I've seem aluminum wire behind the control panel too...Should I be concerned about this
Fog,

I also have a '67 with aluminum wire. The issue with aluminum wire is in the connections. There is a fix, but it is kind of expensive. I posted some links a while back in THIS POST. They include a few options for making the fix. Since I ultimately decided to re-skin my interior, I am going to do a re-wire.

Good luck!
__________________
Steve & the crew
'70 Ambassador International Twin
'63 19' Globetrotter TAC WI-1
https://byamcaravanner.blogspot.com/
byamcaravanner is offline   Reply With Quote
Old 01-23-2008, 07:55 AM   #30
Rivet Master
 
Phil and/or Sue's Avatar

 
1997 34' Limited
Young Harris , Georgia
Join Date: Feb 2003
Posts: 951
Images: 40
Quote:
Originally Posted by crowbar68
from what i understand you have a 4 circuit 30amp panel. it is directly wired to the bus w/ 2, 20amp brkrs and fed from the street w/ a 10ga. wire from a 30amp breaker(from house).

this is fine and by code.
Quite right.

Quote:
Originally Posted by crowbar68
the 30amp brkr protects the cord and the 20amp brkrs in your camper protect those devices.
Exactly!

Quote:
Originally Posted by crowbar68
between the 2, 20 amp brkrs, if you draw potentially 40 amps the 30a brkr will pop protecting your camper. this is the cheesey way to do it.
Right! This is the critical point about the protection: as designed, all devices downstream from the 30A breaker in the feed (whether that breaker is in your house or in the campground stand) are protected from overload by the 30 amp breaker.
- Until the electricity gets to another breaker (for example a 20A in your panel), the cord and every device the electricity flows through must be rated to handle the 30 amps.
- In the camper, the 10 gauge wire used for shore power and the little circuit breaker panel are both rated to handle 30 amps (or more).
- It is accepted (within a certain range) in a circuit breaker panel to have more amperage in breakers than the amperage rating of the main breaker. For example, a house may have a 100A main breaker, but have 16 20A breakers.

Quote:
Originally Posted by crowbar68
you can however do what you said, add a 30 amp main, feed the panel thru the 30 amp brkr and thus the other breakers/panel. hope that helps.
As noted and as Empresley has done, you can add a main breaker (or change out the panel to include a main breaker). That is a belt and suspenders type approach to power protection, and maybe, just maybe, with the overused and untested breakers in the campgrounds, a new and modern 30A breaker protecting your camper is not a bad idea.

Good points on this thread, but please make sure a qualified person verifies what you plan to do, and how it's done.

And aluminum wiring can be a concern. In some houses with aluminum wire, loads turning on and off caused some heating/cooling expansion/contraction and eventually loosened some wires under lugs. One thought: be aware of any warm or hot spots in receptacles that may be an indication of a loose connection causing heat.
__________________
Phil and/or Sue w/ Cheryl & Penny and Roger
(Buffett RIP 9/15/08, Gus RIP 12/22/2015)
1997 34' Excella WBCCI 5936
'09 Dodge Cummins Ram 3500 Crew 4x4 auto
AIR 1753
Phil and/or Sue is offline   Reply With Quote
Old 01-30-2008, 06:46 PM   #31
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
Thought I’d update this thread with what I figured out. The original panel from the factory can accept ˝ sized breakers, as the PO discovered. As discussed earlier in this thread, I decided to use those. The “main” coming in from shore power was wired to a 30 amp breaker. The air conditioner was wired back to its own 20 amp breaker. The “general circuit” that powers the rest of the 110v wall outlets was placed on another 20 amp breaker. I’m going to add a 15 amp ˝ sized breaker and a new dedicated circuit for the microwave. You can see these in the picture top to bottom. More in a few minutes.
Attached Thumbnails
Click image for larger version

Name:	breaker panel 2.jpg
Views:	117
Size:	183.1 KB
ID:	53452  
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-30-2008, 07:26 PM   #32
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
After rewiring the breaker panel, I noticed that the 110v wall receptacles were getting pretty warm. Hadn’t really worried about before, except to notice that it was happening. I’m using a 1000 watt ceramic heater out there because it’s cold, even in Georgia, in January. I had it plugged in, usually, in one of the front receptacles in the front of the camper. Many of the receptacles behind it, going back toward the breaker panel were getting warm. So back to inspecting the wiring, etc.

What I found was that the wire coming out of the polarity light junction box had burned thru at some point. To the point that the insulation on the plastic jacketed 12/2 Romex was completely gone and had to begun to corrode to the point that it had green stuff all over it (and the ground wire as well). The burn thru was on the back side of the wire, so I missed it first time around.

I replaced this wire in it’s entirely from the polarity light forward to the first wall receptacle. The wall receptacles were still getting very warm. Humm, ok, what next?
Attached Thumbnails
Click image for larger version

Name:	Breaker panel 3.jpg
Views:	102
Size:	130.7 KB
ID:	53453  
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-30-2008, 07:35 PM   #33
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
It turns out that the wall receptacles were actually bad (most of them). I wound up replacing all of them. Lesson learned is that even if things look good, after 35 years, they may not be. Everything is nice and “cool” now front to back. If anybody needs info on how the polarity light is supposed to be wired, let me know.

I do have a question for one of you out there with more knowledge than me. What is a good replacement for the wire nuts inside that box? I have zero faith that these things will stay in place after a few years of vibrations. As always thanks for the help, folks.

Jim
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-30-2008, 07:57 PM   #34
Rivet Master
 
overlander63's Avatar
 
1993 21' Sovereign
Colfax , North Carolina
Join Date: Jun 2003
Posts: 21,254
Quote:
Originally Posted by Jim & Susan
I do have a question for one of you out there with more knowledge than me. What is a good replacement for the wire nuts inside that box? I have zero faith that these things will stay in place after a few years of vibrations. As always thanks for the help, folks.

Jim
Dare I suggest new wire nuts? I seem to remember seeing some that had a gel inside for "moist locations", but i haven't seen them in years. Does anybody else remember them?
__________________
Terry
overlander63 is offline   Reply With Quote
Old 01-30-2008, 08:03 PM   #35
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
I did replace one of them with a brand spankin' new one, but it doesn't seem all that secure either. I suppose a bus bar arrangement could work, but would be very large and more or less on the order of the breaker box, minus the breakers, of course.
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-30-2008, 08:51 PM   #36
bilby05
 
bilby05's Avatar
 
1962 24' Tradewind
1962 24' Tradewind
Canyon , Texas
Join Date: Oct 2005
Posts: 264
Gel wire nuts

Quote:
Originally Posted by overlander63
Dare I suggest new wire nuts? I seem to remember seeing some that had a gel inside for "moist locations", but i haven't seen them in years. Does anybody else remember them?
I had some left over from rewiring a small brit car and used them the other day on the Airstream. They came from an autoparts place. The "filler" in these was more like latex caulk. Messy and by the time I got through trying to stuff all of the wires in it most of the glop was all over the place. Wiring has move down on my list. It rests near plumbing now.
cheers, bill b.
__________________
1962 Airstream Tradewind
2001 Ford 7.3 Diesel
bilby05 is offline   Reply With Quote
Old 01-30-2008, 09:15 PM   #37
Site Team
 
, Minnesota
Join Date: Aug 2003
Posts: 7,596
Images: 59
I use european wiring terminals. They're a bit smaller than domestic, but still able to accomodate up to #12 stranded.

If I use wire nuts, I twist the conductors together, trim the tip to a point, apply a little anti-ox paste, twist the wire nut on with pliers (use the hard plastic ones). I then wrap it with tape to keep the wire nut from vibrating loose. For stranded wire I use crimp fittings.
markdoane is offline   Reply With Quote
Old 02-10-2008, 07:34 PM   #38
Master of Universe
 
Gene's Avatar
 
2008 25' Safari FB SE
Grand Junction , Colorado
Join Date: Sep 2007
Posts: 12,040
Related 30 Amp question

Not wanting to start a new thread, this seemed close enough to mildly hijack.

I installed a 30 amp 125 v receptacle outside my shop (Colorado talk for really big garage). I connected it to a 30 amp single throw breaker. It has 2 hot connections. The receptacle tests at 120 v at each hot lug. It is the proper receptacle for my Safari.

I am probably being too cautious, but am afraid of 240 v somehow feeding into the trailer. I assume each leg goes to a different branch circuit or circuits and there is no way I could blow all circuits with 240 v. I don't really assume it because I wouldn't be asking this question if I did.

Also, I do wire nuts much like markdoane—twist the conductors together with a linesman's pliers and make them tight, screw the wire nut on and then make it as tight as possible with the pliers, then make sure none of the conductors are loose, then use electrical tape, first winding it around the wires really tightly too (the good stuff stretches) and then onto the wire nut (it's easier to unwind it if you have to from the wire nut). Sometimes I try to make the longest wire pointy because the spring inside the nut sometimes like that. Also it's important to use the right size wire nut.

And if you have aluminum wiring, replace it if you can. I forget how to deal with it if you aren't going to replace it, so find our how to make it as safe as can be. I wouldn't feel good with aluminum wiring in a trailer. The stuff causes enough fires in houses.

Gene
Gene is offline   Reply With Quote
Old 02-10-2008, 07:49 PM   #39
Think Freedom
 
Jim & Susan's Avatar

 
1973 27' Overlander
Third Rock from , Sol
Join Date: Oct 2004
Posts: 5,553
Images: 39
Where is this 30 amp, single throw, double wire breaker? In the camper or in the shop?

When all is said and done, from the breaker panel in the shop going towards the Airstream, you should have three wires.

1) Bare copper Ground wire connected to the ground lugs on both ends in both panels.

2) White Neutral wire connected to the Neutral lug in the breaker panel on both ends.

3) Black Hot wire that is connected to ONE of the lugs inside ONE 30 amp breaker in the panel in the shop, the other end will be tied to either a distribution bus inside the panel in the camper that the camper's breakers are plugged into, OR to a single breaker in the camper that feeds that same bus.

One hot wire and one neutral wire equals 110v.

Jim
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 02-10-2008, 08:04 PM   #40
Master of Universe
 
Gene's Avatar
 
2008 25' Safari FB SE
Grand Junction , Colorado
Join Date: Sep 2007
Posts: 12,040
Jim,

The breaker is in the subpanel in the shop. A 125 v, 30 amp. has 3 places to connect the conductors. 10 ga. wire has a black, red, white and bare ground. Bare ground get connected to the exterior box green screw. Black and red to the to female straight things for the spades on the make plug. White to the semi-round neutral on the receptacle. It doesn't feel right and maybe I should have ignored the 2nd connection on the breaker (one throw, not linked, but just a single one, 2 hot connections and the red wire and connected the bare ground to the box and the receptacle ground and white and black to the two other connections on the receptacle. But if so, why are there two connections on the breaker? The receptacle is on the shop wall for the shore power wire from the trailer.

Gene
Gene is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 / 50 AMP Question kleimanr Electrical - Systems, Generators, Batteries & Solar 7 11-03-2007 03:58 PM
Car & Driver Jan 07, Airstream & Benz Karyn Airstream "In the News" 14 12-04-2006 11:26 PM
Preztels & Beer or Biscotti & Cappuccino? GreggH Community Polls 26 02-20-2006 07:08 PM
Curb Side & Front Glass Window & Clips Oceancontainer 1965 Safari 2 07-28-2003 08:04 PM
Dumb Question regarding the bed & sheets kamadeca 2003 Safari 8 06-23-2003 03:24 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 03:13 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, Jelsoft Enterprises Ltd.