12vDC wall connectors

I’m installing a Dometic RM2551 refrigerator in 64 Safari. What type plug/connector is typical to install in wall for 12vDC?



It requires a constant 12vDC line in addition to 110AC & propane. I have new 12v wires run inside wall to the frig area. I can run ground to wall stud/frame. I can install a polarized 110v type wall outlet easy but not sure it’s a good idea because it looks like 110v.

What’s used for 12v connectors M/F besides 12v lighter type socket?
walter1 is offline   Reply With Quote
Old 09-16-2004, 01:45 PM   #2
Still Working
 
smily's Avatar
 
1994 36' Classic 36
North Charleston , South Carolina
Join Date: Jul 2002
Posts: 1,686
Images: 19
On my unit the twelve volt conductors are connected to ta small terminal board.

I believe this is for the ignitor and the rollover feature (auto change from AC to DC)

Mine is not plugged into a wall socket for 12v.
It is however plugged into a wall outlet for the 110 volts connections.

I would not connect anything to the chassis, skin or studs.

Smily
smily is offline   Reply With Quote
Old 09-16-2004, 04:48 PM   #3
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
Quote:
Originally Posted by smily
...I would not connect anything to the chassis, skin or studs.
I basically agree with Ken's point; If you only have a +12 vdc line, it was probably installed by a previous owner. In my extremely limited experience with Airstreams, they have always complied with applicable electrical code by running two conductors for 12 vdc. I think you can run your ground to the frame with safe results, but it will not be to code.

In my opinion only, there is no need for a 12 vdc connector - the refrigerator should be hardwired directly to service as it is not something that should require frequent disconnection.

Tom
TomW is offline   Reply With Quote
Old 09-16-2004, 05:12 PM   #4
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
Tom,

What Code? I can't find it in NEC 551.10, where it says that metal chassis or frame shall be permitted as the return path to the source of supply.
markdoane is offline   Reply With Quote
Old 09-16-2004, 05:25 PM   #5
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
Quote:
Originally Posted by markdoane
What Code? I can't find it in NEC 551.10...
Well, I've been caught! I have boo-booed by not actually consulting the code; I was simply going by what seemed to make sense for situations I have encountered & what I have in my antique Airstream.

My apologies for misleading everyone.

Tom
TomW is offline   Reply With Quote
Old 09-16-2004, 05:59 PM   #6
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
Quote:
Originally Posted by tcwilliams
Well, I've been caught! I have boo-booed by not actually consulting the code; I was simply going by what seemed to make sense for situations I have encountered & what I have in my antique Airstream.

My apologies for misleading everyone.

Tom
Section 551.10 E (3) of the code says appliances shall be "installed in accordance with the manufacturer's instructions". ???

I agree that running two wires is preferred, and that's what I would do for all appliances except lighting.
markdoane is offline   Reply With Quote
Old 09-16-2004, 06:13 PM   #7
2 Rivet Member
 
Join Date: Feb 2004
Posts: 57
normally connectors are used to make removal and reinstallation easier. With an appliance like refrig. you are not going to be taking it in out on a regular basis . However if you just want it that way you can use an automotive connector of the proper gauge. I would use a ''weather pack'' type if I did to help prevent corrosion.
pieman
MikeL is offline   Reply With Quote
Old 09-16-2004, 06:44 PM   #8
Rivet Master
 
Condoluminum's Avatar
 
2016 25' Flying Cloud
Sunnyvale , California
Join Date: Jul 2003
Posts: 1,894
Images: 13
Send a message via AIM to Condoluminum
Question Related ?? Amps in socket?

Since several of you seem to have electrical codes and manuals out...

I'm contemplating direct plug of new Sharp LCD 14" Television into "Lighter socket" on wall of trailer next to TV connections at front of our Excella 25.. Unit (the TV) came with 110V to 12V transformer/power supply, but TV only requires about 45 continuous watts of 12V DC power to operate...

By my crude math, that seems like 4 amps of 12V DC power continuously running through the lighter outlet... Notwithstanding potential battery drain, is that circuit up to it, or should I consider the TV to be only useful when 110V power is available to drive the power transformer??

I may need to contact Sharp for adapter plug, since units I see at local electronic places for radar detectors and other small 12V gizmo's seem to be fused at 2 or 3 amps max...

John McG

p.s. TV is real easy to mount, picture is great, and it takes very little space
__________________
Condoluminum

In Theory, there's no difference between Theory and Practice, but in Practice, there is usually a difference...
Condoluminum is offline   Reply With Quote
Old 09-16-2004, 07:33 PM   #9
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
The cigarette lighter should have a fuse in a panel somewhere. Minimum wire size in any RV is 18 ga, I suspect the cigarette lighter socket is larger than that.
markdoane is offline   Reply With Quote
Old 09-17-2004, 06:02 PM   #10
3 Rivet Member
 
AirConditioner's Avatar
 
Join Date: Jul 2004
Posts: 153
Quote:
Originally Posted by walter1
I’m installing a Dometic RM2551 refrigerator in 64 Safari. What type plug/connector is typical to install in wall for 12vDC?



It requires a constant 12vDC line in addition to 110AC & propane. I have new 12v wires run inside wall to the frig area. I can run ground to wall stud/frame. I can install a polarized 110v type wall outlet easy but not sure it’s a good idea because it looks like 110v.

What’s used for 12v connectors M/F besides 12v lighter type socket?
Dometic publishes a minimum wire size in both their installation and troubleshooting manuals. As I recall they want a ground line on the newer models due to possibility of noise (rf and potentially AC) that might inhibit the function of the solid state control circuit. A few RV refrig companys mentioned in the forums have published these on their websites.

I nearly always run a separate ground line for electronically controlled gear.

About the connection. Check out a good electronics supply store or catalog for options. One option is a set of "banana" plugs and jacks. They handle a lot of current and are distinctive from other sockets. The rise in popularity of high-end car audio means that there area lot of 12VDC connectors and accessories now commonly available than a few years ago - including super heavy wire gauges and high quality corrosion-free terminals. I also wonder why you need a disconnect on this 12VDC circuit other than perhaps a switch that can handle the load.
AirConditioner is offline   Reply With Quote
Old 09-19-2004, 12:53 PM   #11
4 Rivet Member
 
walter1's Avatar
 
1964 22' Safari
Foresthill , California
Join Date: Aug 2004
Posts: 257
Thanks for all the help. The reason for a disconnect was to not have 12v hot wires just sticking out through wall to refrig. Run to connector mounted in wall instead. I had planned to splice to the 12vDC+ wire that runs to an old 12v lighter type outlet well above the refrigerator. It is old stock wiring, orange, and used a short white wire from the socket to the mounting screw (interior wall) for ground. I know a separate 12v- wire is preferred, but that entails 20 foot run through who knows where and I have found several places where frame is being used for ground of my 12v system. All appears stock. I know 12vDC and 24vDC systems often use chassis as ground (as in cars and military aircraft).


Walter
walter1 is offline   Reply With Quote
Reply

Tags
12v


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dometic refrigerator 12vDC operation walter1 Refrigerators 19 08-28-2013 11:47 PM
Installing stainless steel wall panels mcneon Cabinets, Counter Tops & Furnishings 25 04-13-2007 04:48 PM
Refrigerator 12vDC walter1 Refrigerators 2 09-16-2004 10:53 PM
Weak wall Pahaska 2002 - 2005 International 4 12-01-2002 09:00 PM
What the heck is that switch on the wall??? TRAPEZE Airstream Motorhome Forums 7 09-10-2002 04:05 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 02:37 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.