Furnace issue turns out to be AS issue

A few weeks ago I found that the rear bedroom furnace was short cycling by way of the thermal over temperature switch. It was the first time I tried to use the furnace since I purchased the unit a year ago. The furnace would turn on normally, but 5 minutes after the furnace lit it would shut off the gas valve until it cooled down some. After a minute or so it would fire back up and the cycle would continue until the room reached the proper temp.

After some diagnosis I found that the thermal limit switch was opening up causing the furnace to short cycle. I checked everything that could cause the problem without buying parts. I checked the voltage level, propane pressure, cleaned burner and burner chamber and checked the blower chamber for some infestation, but still the same. Both bedroom ducts were putting out a reasonable amount of airflow so they were not clogged. I replaced the thermal limit switch and the blower motor thinking that the blower speed was too slow. After all this it still was doing the same thing.

I then calculated the air volume that was available through the 2 4" ducts that AS installed and found that AS installed a marginal amount of outlet ductwork! Atwood’s specifications said that the 16K BTU furnace needed a minimum of 24 square inches of outlet duct. With the two that were installed I only had 25 square inches and that was with two long duct runs and several 90 degree bends to get around the shower. Each 90-degree bend was equal to 10 additional feet of duct according to Atwood's installation guide. I ended up added a third 4" duct and BINGO... everything started to work correctly.

Moral of the story... Don't assume that AS did a good job at specing out and constructing your coach's systems. I wasted a lot of time thinking that the installed duct work must have been adequate so assumed that the problem must have been with the furnace it self. Could have saved me around $120 in parts if I had just calculated the airflow to start with. I can only assume that the furnace has always done this and the PO’s just thought it was normal.
92landyacht is offline   Reply With Quote
Old 11-28-2012, 02:24 PM   #2
Wise Elder
 
Jammer's Avatar
 
2010 30' Classic
Vintage Kin Owner
South of the river , Minnesota
Join Date: Dec 2009
Posts: 4,169
In general, RV furnaces are installed using the absolute minimum required ductwork, regardless of the RV manufacturer.

I've added ductwork and made extensive changes to the furnace installation to improve performance, evenness of heat, and noise.
__________________
To learn to see below the surface, you must adjust your altitude
Jammer is offline   Reply With Quote
Old 11-29-2012, 04:20 AM   #3
Rivet Master
 
gloran's Avatar
 
1993 33' Land Yacht
Midland , Michigan
Join Date: Sep 2005
Posts: 508
Where did you add the extra 4" duct?
__________________
gloran - 1993 LY MH 33' - Banks System, Steer Safe, IPD front stabilizer, Super Steer - Bell Cranks, Motion Control, Coil

https://s1290.photobucket.com/user/gl...58808196506793
gloran is offline   Reply With Quote
Old 11-29-2012, 06:31 AM   #4
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,796
I added the duct below my hallway closet just before the shower. Same place I added the CO/LP alarm.
92landyacht is offline   Reply With Quote
Old 11-29-2012, 09:51 AM   #5
65th Anniversary CLIPPER
 
masseyfarm's Avatar
 
1996 36' Clipper Bus
Tub City , British Columbia
Join Date: May 2009
Posts: 3,309
Images: 64
Would it not have been easier to just put a connector in the rear furnace duct system and join it to the existing front furnace ducting? They would seldom run at the same time unless you started them both together. And that would spread the heat throughout.

I have not experienced the same problem you have explained, but adding a new duct I envision as a major pain in my unit.

Dave
masseyfarm is offline   Reply With Quote
Old 11-29-2012, 02:52 PM   #6
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,796
Actually it was a lot easier to add the new duct then you might think. All it took was to cut a 4" hole at the base of the cabinet and run a short duct (~2 feet) to that opening. No big deal since all the area between the hole and the back of the furnace was open. I just knocked out one of the rear-prepunched cutouts on the furnace and inserted a duct adapter. I then ran a couple of feet of duct to the new grill. I used 4" hose clamps to secure the ductwork to the inlet/outlets.

The main system runs all along the roadside wall and the rear furnace only ran on the curbside so tying the two together would have been quite difficult. Tying them together would have also defeated the purpose of extracting additional air output from the rear furnace when the main furnace was on at the same time. And yes, both may be on at the same time on cold nights.
92landyacht is offline   Reply With Quote
Old 11-29-2012, 08:41 PM   #7
65th Anniversary CLIPPER
 
masseyfarm's Avatar
 
1996 36' Clipper Bus
Tub City , British Columbia
Join Date: May 2009
Posts: 3,309
Images: 64
Sounds easy enough.

On your unit, are the two furnaces not in the same location?

On the Clipper, the two furnaces are mounted together and are located below the fridge and HWT. The HWT would block and make it difficult to run a new duct to the same location under the wardrobe as you did and the pocket door would not allow snaking it around the front of the HWTank.

However, on the Clipper, it would be easy to run a new duct into the kitchen behind the drawer bank below the fridge if it was needed. I have actually eyed that cavity with the thought of putting in an electric 120 or 240 heater for when we are parked with power. I just have never had that need yet to justify the cost of installation.

Dave
Attached Thumbnails
Click image for larger version

Name:	IMG_8594.JPG
Views:	246
Size:	150.7 KB
ID:	173588  
masseyfarm is offline   Reply With Quote
Old 11-30-2012, 06:20 AM   #8
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,796
On my LY the furnaces are on opposite sides of the coach. Once located on the curbside under the furnace and one located aft of the kitchen.
92landyacht is offline   Reply With Quote
Old 11-30-2012, 05:33 PM   #9
Rivet Master
 
gloran's Avatar
 
1993 33' Land Yacht
Midland , Michigan
Join Date: Sep 2005
Posts: 508
I missed the point about it being the rear furnace in your first post, I only have one furnace, but it does cycle on and off quite frequently and is very noisy. Can anything be done about the recycling and noise level?
__________________
gloran - 1993 LY MH 33' - Banks System, Steer Safe, IPD front stabilizer, Super Steer - Bell Cranks, Motion Control, Coil

https://s1290.photobucket.com/user/gl...58808196506793
gloran is offline   Reply With Quote
Old 12-01-2012, 06:52 AM   #10
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,796
First you need to find out why it's recycling. Is the fan always running but the flame comes and goes until it reaches temp? Then it may be a similar issue as mine, which could be related to your noisy issue as well. With those symptoms it can be related to the following:
· Slow blower motor (Bad motor, damaged blower fan, debris on blower fan)
· Over temp switch (Weak)
· Insufficient outlet volume (Clogged output duct or marginal design)
· Insufficient inlet air (clogged air inlet or poor design)
· Intermittent sail switch (less likely)
· Too much LP pressure causing excessive flame

If the fan cuts off as well, then it's more likely related to your thermostat.

What kind of noise are you hearing? Could be a bad blower motor bearing causing the motor to be turning slower then required.
92landyacht is offline   Reply With Quote
Old 12-02-2012, 08:21 PM   #11
Rivet Master
 
blkmagikca's Avatar

 
1987 32' Excella
Nepean , Ontario
Join Date: Mar 2006
Posts: 1,415
I previously had a '94 LY. At one point, the furnace fan got progressively noisier. We determined that it was the bearings in the fan motor. That motor drives 2 fans, one on each side of it. Because the PO had had the moho in Florida, the salt air rusted that assembly so that it took about 1 week of daily dousing with penetrating oil to free it up. Once freed up, swapping out the old motor for the new was quick. The shop that worked on it told me that if they could not get the fan assembly out, it was going to be megabucks to replace the furnace. Thankfully, I was lucky.
__________________
VE3JDZ
AIR 12148
1987 Excella 32-foot
1999 Dodge Ram 2500HD Diesel
WBCCI 8080
blkmagikca is offline   Reply With Quote
Old 12-03-2012, 03:57 AM   #12
Rivet Master
 
gloran's Avatar
 
1993 33' Land Yacht
Midland , Michigan
Join Date: Sep 2005
Posts: 508
I was thinking it might be the thermostat, I'll try that first. When I said noisy I should have said loud. I don't hear any bearings or anything, just loud fan noise. Thanks for your replies.
__________________
gloran - 1993 LY MH 33' - Banks System, Steer Safe, IPD front stabilizer, Super Steer - Bell Cranks, Motion Control, Coil

https://s1290.photobucket.com/user/gl...58808196506793
gloran is offline   Reply With Quote
Old 12-03-2012, 06:20 AM   #13
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,796
When it cycles on/off, does the fan keep running? If so, then it's not the thermostat.
92landyacht is offline   Reply With Quote
Old 12-03-2012, 07:17 PM   #14
Rivet Master
 
gloran's Avatar
 
1993 33' Land Yacht
Midland , Michigan
Join Date: Sep 2005
Posts: 508
No, the fan turns off, thats why I think its the thermostat.
__________________
gloran - 1993 LY MH 33' - Banks System, Steer Safe, IPD front stabilizer, Super Steer - Bell Cranks, Motion Control, Coil

https://s1290.photobucket.com/user/gl...58808196506793
gloran is offline   Reply With Quote
Old 12-04-2012, 06:52 AM   #15
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,796
Yep, sounds like a thermostat issue to me too. I just picked up a pair of cheap non-programmable digital thermostats from HD for $24 each. The system only uses two wires so installation is a no brainier. The thermostat even included wiring instructions for the two-wire setup. I like knowing exactly what temp it’s set to as opposed to the slide and guess analog units.

92landyacht is offline   Reply With Quote
Old 12-04-2012, 05:33 PM   #16
Rivet Master
 
gloran's Avatar
 
1993 33' Land Yacht
Midland , Michigan
Join Date: Sep 2005
Posts: 508
Sounds like the same one I picked up.I'll let you know if it makes a difference.
__________________
gloran - 1993 LY MH 33' - Banks System, Steer Safe, IPD front stabilizer, Super Steer - Bell Cranks, Motion Control, Coil

https://s1290.photobucket.com/user/gl...58808196506793
gloran is offline   Reply With Quote
Old 01-20-2016, 10:19 PM   #17
Rivet Master
 
Mike1997's Avatar
 
1998 36' Land Yacht Widebody
Shepherdstown , West Virginia
Join Date: Jan 2016
Posts: 808
Images: 14
Had a somewhat similar problem with my 97 Land Yacht WB diesel. Furnace blower would cycle on as usual then you could hear the burner trying to light. After 5 automatic tries it stop till the main switch was reset off/on. The furnace would never stay fired up longer than 7-8 seconds.

RV mobile tech found the computer board, located outside, was defective. $125 later it was like new. In fact, tech said the furnace itself appeared to have never been in use. Considering the rig spent it's whole life in NC and FL, I suspect first owner only used the roof electric heat when necessary. That just was not enough heat for me in Montana
Mike1997 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:40 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.