Odd problem w/Suburban NT-34SP furnace

We have been renovating a 29' 1976 Airstream. 18 months ago I installed a Suburban NT-34SP furnace. Did all of the measurements for the ducting and installed per the instructions. First time we fired it up it worked and has kept us warm even when temps get into the single digits (F).

It has continued to work for the past 18 months but yesterday it started doing something odd. When I move the thermostat up to 75F the fan goes on and air can be felt coming through the ducting at both ends of the trailer. After about 15 seconds there is a click. The air and ducting actually get slightly warm and then cold as it cycles through for 10 minutes before the fan shuts down.

Took the front cover off. No extra parts laying around and fan is pushing lots of air out of the open end. Looked through the flame "port hole". The flame is visible but then it stops and then it restarts. It goes through this cycle for 10 minutes and then the furnace shuts down.

The flame looks like the drawing of the "Incorrect Flame" in the Installation Instructions. Conclusion is that it is getting 12V and propane (tank is full) but for some reason the flame is not burning like the image of the "Correct Flame". Thinking that it may be an air bubble I have restarted the furnace many many many times. Does not seem to have any effect on the flame.

Any suggestions welcome. Fortunately we have two 110V heaters that are working so we are not desperate - yet.
Eagle & Bear is offline   Reply With Quote
Old 01-14-2020, 08:43 AM   #2
Rivet Master
 
Foiled Again's Avatar
 
2012 25' FB Eddie Bauer
Vintage Kin Owner
Virginia Beach , Virginia
Join Date: Sep 2004
Posts: 7,801
Try turning on the stovetop for a few minutes to clean any air in the lines. If the stovetop burns poorly look at your propane bottles, regulator and the flex lines that connect the bottles to the regulator. Buy or make a nanometer to check gas pressure (YouTube for how to videos) Low gas pressure means adjusting or replacing the regulator, or if the flex hoses are over 5 years old, they may be leaking and need replacement.

If everything is normal on the propane supply side, the furnace sail switch and control board are likely suspects... and I chicken out and call a pro at this point.
__________________
Today is a gift, that's why they call it the present.
Foiled Again is offline   Reply With Quote
Old 01-14-2020, 09:06 AM   #3
Rivet Master
 
CBWELL's Avatar
 
1994 34' Excella
Warren , Manitoba
Join Date: Apr 2006
Posts: 1,253
Most propane cylinders have an overflow protection valve. If the tank valve is opened too quickly the flow of propane will be restricted. Try shutting the cylinder valves, try to light stove, and then reopening the cylinder valves slowly. This has happened to me a couple of times. Your furnace has a lot more flow than your fridge or stovetop. If that doesn't solve the problem, a check of the burner orfice should be considered. Spiders love propane, as well as other critters. If all of the above don't solve the problem, then "Foiled Again's" suggestions should be looked at. I always look to the most simple options (cheapest) first!!! Good luck.
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1994 Excella 34'
1987 Limited 34', 1976 31', 1976 Argosy 22' Gone to new homes
Hensley Hitch
CBWELL is offline   Reply With Quote
Old 01-14-2020, 09:36 PM   #4
4 Rivet Member
 
Eagle & Bear's Avatar
 
1976 29' Ambassador
Madison , Officially SD but are traveling full time.
Join Date: Sep 2007
Posts: 335
Images: 1
CBWELL "Try shutting the cylinder valves, try to light stove, and then reopening the cylinder valves slowly."

I loosened the nut on the hose that connects it to the regulator (cylinder that is currently providing propane to the furnace). Let a few seconds of propane escape, tightened the nut that holds the hose onto the regulator and then closed the primary valve on top of the propane tank. Opened the valve and went back inside. Lit a stove top burner, made sure it had a good flame and then turned the burner off. Set the furnace thermostat to 80F. I have no idea why but the furnace is now working. This strategy saved me from buying a new regulator only 3 years after I installed the current one. Thank you both for responding.
Eagle & Bear is offline   Reply With Quote
Old 01-15-2020, 07:55 AM   #5
Rivet Master
 
CBWELL's Avatar
 
1994 34' Excella
Warren , Manitoba
Join Date: Apr 2006
Posts: 1,253
Glad things worked out. Sometimes it is the simple things that happen and are easily repaired. I always look for the easiest and cheapest way first. A lot of my fixes are from past experience
__________________
ACI #7394
2012 GMC 2500 HD Duramax Denali
1994 Excella 34'
1987 Limited 34', 1976 31', 1976 Argosy 22' Gone to new homes
Hensley Hitch
CBWELL is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Odd but serious electrical problem bnsonger47 Flat-Front (Cutter, Clipper, XC, XL & Skydeck) Motorhomes 11 12-20-2012 04:18 PM
Odd A/C problem ranns ammee Furnaces, Heaters, Fireplaces & Air Conditioning 2 08-31-2011 10:27 AM
NT-34SP installed in '71 Safari - Success! pickerdd Furnaces, Heaters, Fireplaces & Air Conditioning 0 04-27-2010 11:28 AM
Odd suburban furnace problem...any help out there? Couldn't find a similar thread! 101scout Furnaces, Heaters, Fireplaces & Air Conditioning 1 12-19-2008 09:51 PM
surburban nt-34sp help needed brummie Furnaces, Heaters, Fireplaces & Air Conditioning 7 06-27-2006 07:24 AM