Furnace not relighting after switching propane tanks

We live (full-time) in our 1985 34' Excella. Our furnace worked great last night, but by morning it was blowing cold air. Sure enough the tank was empty, so I switched tanks. Water heater and furnace didn't relight. I adjusted water heater igniter till it lit, but when I checked igniter in the furnace, it doesn't seem that gas is getting to the chamber... Stove and water heater working fine. Help please. Thanks!
bradleyoder is offline   Reply With Quote
Old 09-25-2015, 04:33 PM   #2
Rivet Master
 
87MH's Avatar
 
1978 31' Sovereign
Texas Airstream Harbor , Zavalla, in the Deep East Texas Piney Woods on Lake Sam Rayburn
Join Date: Jan 2003
Posts: 2,435
Images: 292
Try the ignition sequence at least four or five more times.

Sometimes it takes a bit of patience to clear the lines of contaminated gas.

Please report back how you resolved the problem.
__________________
Dennis

"Suck it up, spend the bucks, do it right the first time."

WBCCI # 1113
AirForums #1737

Trailer '78 31' Sovereign

Living Large at an Airstream Park on the Largest Lake Totally Contained in Texas
Texas Airstream Harbor, Inc.
87MH is offline   Reply With Quote
Old 09-25-2015, 05:20 PM   #3
4 Rivet Member
 
Airline's Avatar
 
1972 29' Ambassador
grants pass , Oregon
Join Date: Jun 2011
Posts: 262
Images: 1
Blog Entries: 2
It seems like its hardest to get the air out of the furnace lines...

Keep trying.
__________________
1987 Avion 34X
Airline is offline   Reply With Quote
Old 09-25-2015, 07:14 PM   #4
2 Rivet Member
 
1985 34' Excella
Durham , North Carolina
Join Date: Feb 2015
Posts: 47
Ok. Will do. Thanks!
bradleyoder is offline   Reply With Quote
Old 09-25-2015, 07:33 PM   #5
Rivet Master
 
2015 30' FB FC Bunk
Ayer , Massachusetts
Join Date: Nov 2013
Posts: 1,114
This has happened to mine. Eventually it re-lit.
Ted S. is offline   Reply With Quote
Old 09-25-2015, 07:37 PM   #6
CRH
Rivet Master
 
1995 25' Excella
xxxxx , xxxxxx
Join Date: Apr 2015
Posts: 2,351
Light a stove eye for a bit to purge the lines.
CRH is offline   Reply With Quote
Old 09-25-2015, 08:27 PM   #7
2 Rivet Member
 
1985 34' Excella
Durham , North Carolina
Join Date: Feb 2015
Posts: 47
I did try the stove thing earlier, but not for several starting cycles. Sadly, six cycles did not do the trick tonight. I'll try with the stove tomorrow. Thankfully a Broan Big Heat (but very tiny) space heater is cranking away in lieu of the furnace, although I'm guessing propane is cheaper than kWh, which matters because it's our utility bill.
bradleyoder is offline   Reply With Quote
Old 09-26-2015, 01:36 PM   #8
Rivet Master
 
tjdonahoe's Avatar
 
2013 31' Classic
billings , Montana
Join Date: Feb 2010
Posts: 3,577
Make sure you have gas,turn on the valve, turn gas on stove until it lights.....works every time to fill the empty gas lines....
tjdonahoe is offline   Reply With Quote
Old 09-26-2015, 03:03 PM   #9
1 Rivet Member
 
2016 25' Flying Cloud
Weatherby Lake , Missouri
Join Date: Aug 2015
Posts: 11
Images: 1
If your tanks/system are relatively new they are probably equipped with an Overfill Protection Device and other safety devices. The excess flow valve part of this system (tank and regulator) can automatically prevent the flow of propane from the tank to your lines if it detects a sudden increase in gas flow. The idea is that it would prevent the flow of gas if one of your copper lines tore off the bottom of your trailer for example. The valve can accidentally trigger if you switch out propane tanks and open the valve on the new tank too quickly. This simulates the sudden propane demand that the safety feature was designed to address. If you just hook up and throw the valve wide open (like I used to on our BBQ grill) you are likely to encounter this problem every time you change tanks or close the valve for storage, etc.

I would close off the valve at the tank, light the stove for a minute to clear the propane and air out of the lines, then very slowly open up the valve on the propane tank. If you do nothing at all the situation should resolve itself once the pressure equalizes.

I'm not sure if that is your issue but something to consider...
SemperBadger is offline   Reply With Quote
Old 09-26-2015, 03:12 PM   #10
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
In my 1985 25' AS, the furnace circuit board gave up the ghost, and I had to replace it. Is your furnace original?
OTRA15 is offline   Reply With Quote
Old 09-26-2015, 04:28 PM   #11
coloradopete
 
coloradopete's Avatar
 
1988 25' Excella
Montrose , Colorado
Join Date: Sep 2007
Posts: 28
Furnace not ignighting

Be sure that the tank selector on the pressure regulator has been turned to the active tank. If you have access to a manometer, check the gas pressure at the furnace. Should be between 13-15 psi. If not, adjust the tank regulator to meet this standard. Also, you may need to replace the overheat cutoff safety switch. Easy to do and not expensive.
coloradopete is offline   Reply With Quote
Old 09-26-2015, 05:41 PM   #12
2 Rivet Member
 
1985 34' Excella
Durham , North Carolina
Join Date: Feb 2015
Posts: 47
Tried lighting with stove lit. No go. I think it's probably original. Terrified of having to replace something, or replacing the whole thing, because of having to possibly open up the floor to get to everything to disconnect and reconnect. Will keep trying the startup cycle with stove lit.
bradleyoder is offline   Reply With Quote
Old 09-26-2015, 05:43 PM   #13
2 Rivet Member
 
1985 34' Excella
Durham , North Carolina
Join Date: Feb 2015
Posts: 47
As an aside, I don't know why the bathroom duct is very low pressure. Probably have to tear open the floor to get to duct junctions?
bradleyoder is offline   Reply With Quote
Old 09-26-2015, 07:00 PM   #14
4 Rivet Member
 
Streamracer's Avatar
 
1986 25' Sovereign
Huntsville , Alabama
Join Date: Sep 2015
Posts: 283
A few years ago the heater on my 86 would not light. First off If your batteries are not charged the sail switch will not close and let the gas valve open. Mine was okay and I replaced the circuit board and it solved the problem a time or two. Finally I figured out the gas solenoid was sticking closed. After disassembling and cleaning it my problem was solved. That has been a couple of years ago.
Streamracer is offline   Reply With Quote
Old 09-26-2015, 07:29 PM   #15
Rivet Loser
 
Punch's Avatar
 
La Ronge , Saskatchewan
Join Date: Nov 2011
Posts: 328
I agree with Streamracer about the batteries. If your blower has been running for hours trying to warm things up, very likely the batteries are discharged. This is the simplest and most often overlooked explanation of your symptoms. Make sure you have a good 13 volts from both batteries before thinking of an alternative explanation. In addition, if your batteries are a few years old, their performance might be marginal in any case. The furnace sail switch needs pretty much full voltage if it is going to open.
__________________
Bob
1989 345LE
Punch is offline   Reply With Quote
Old 09-27-2015, 10:20 PM   #16
2 Rivet Member
 
1985 34' Excella
Durham , North Carolina
Join Date: Feb 2015
Posts: 47
Furnace not relighting after switching propane tanks

But we are plugged into our 30 amp outlet constantly. Could the batteries be the issue if that's the case? I hear our converter turn on every now and then, seemingly to charge the batteries if the batteries are low, and all our other low-voltage appliances are working properly.
bradleyoder is offline   Reply With Quote
Old 09-28-2015, 06:06 AM   #17
Rivet Loser
 
Punch's Avatar
 
La Ronge , Saskatchewan
Join Date: Nov 2011
Posts: 328
I am no expert on this, and I am sure an expert will be along shortly, but with the '94 LY that we owned, batteries turned out to be the problem. The non-ignition was happening even though we were plugged in to shore power. New batteries and Bingo!.... in business again.

My non-expert guess is that the furnace runs off the batteries and not the converter, and the furnace sail switch requires a higher voltage than any other DC appliance, and the converter doesn't kick in until the voltage is below that point. We had a mobile RV mechanic come out and diagnose our problem, which had been frustrating me for two cold trips in the MH.
__________________
Bob
1989 345LE
Punch is offline   Reply With Quote
Old 09-28-2015, 06:38 AM   #18
2 Rivet Member
 
1985 34' Excella
Durham , North Carolina
Join Date: Feb 2015
Posts: 47
Furnace not relighting after switching propane tanks

Thanks. I pulled out the igniter, and it seems to spark with plenty of gusto. It seems to me more gas issue, some sort of valve not opening or something like that… I don't smell any gas at all from the furnace when I'm doing the start up cycle… but it may be time for new batteries anyway!
bradleyoder is offline   Reply With Quote
Old 09-28-2015, 07:06 AM   #19
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
As we enter the winter months, if your batteries are more than a few years old, it may be a good insurance policy to replace them, especially with an older 34' unit which has multiple 12 volt appliances and lights. You can always keep the current batteries in reserve. Having new batteries will also eliminate one of the variables being discussed here.
OTRA15 is offline   Reply With Quote
Old 09-28-2015, 08:16 AM   #20
Rivet Loser
 
Punch's Avatar
 
La Ronge , Saskatchewan
Join Date: Nov 2011
Posts: 328
Quote:
Originally Posted by bradleyoder View Post
Thanks. I pulled out the igniter, and it seems to spark with plenty of gusto. It seems to me more gas issue, some sort of valve not opening or something like that… I don't smell any gas at all from the furnace when I'm doing the start up cycle… but it may be time for new batteries anyway!
Bradley... it all fits. The igniter has no problem. My igniter was snapping away happily too. It is the sail switch. No gas for the igniter to ignite, so yes you won't smell gas.
__________________
Bob
1989 345LE
Punch is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Propane Gas Detector Went off Last Week-Turns Out NOT the Propane breezyway Electrical - Systems, Generators, Batteries & Solar 4 08-16-2014 08:56 AM
heat pump not switching to furnace Alumitater Furnaces, Heaters, Fireplaces & Air Conditioning 5 02-01-2014 06:20 PM
Switching propane oven out with the mw/convenction oven Deb Trimble Airstream Lifestyle 17 09-27-2012 09:26 AM
Furnace not working after several problem solving attempts Rikh Furnaces, Heaters, Fireplaces & Air Conditioning 3 11-24-2010 03:58 PM
need opinion - switching out tanks kbryner1 LP Gas, Piping, Tanks & Regulators 7 05-24-2004 08:06 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:32 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.