Quote:
Originally Posted by Dena m
I just installed 4 100 watt panels. I have a Victron 30 charger controller. Will this set up charge my 4 12 volt batteries fully? ( 14 Vs) do I need to adjust anything, as to float mode, etc. to make this happen.
|
In honesty, I think the battery is hard pressed to know if the Absorb voltage is coming from a 30A controller or a 100A controller. Yes, you can charge 4 batteries...it just takes longer. The best thing you can do is manage your discharge level to make it possible to charge back up in a solar day.
Lifeline has a bit of guidance in their Technical manual for the AGM batteries. If...you routinely discharge more than 50%...use a minimum of 0.2C to charge back up. If your 4 batteries are 100A...your C would be 400...and 0.2 x 400 = 80A. If that isn't possible...they suggest an alternative is to have a constant 0.02C charge for an hour after absorb charge is done. I haven't tried that. I normally do not go more than 50% dod...so, I do t think this is applicable...depends on your usage.