Pre Wire in Refer Compartment

Al & Missy:

In my 2009 FC the pre-wire was not run into the ceiling--only to the bottom of the refer compartment.

You can see the yellow and green wires taped to end of plastic conduit in this photo. These wires end where the battery bus bars are located--in my unit under the queen bed. At the bus bars they are labeled as the solar pre-wire wires.

__________________

__________________
Best, Burnside

"To err is human, to air is devine."
Burnside Bob is offline   Reply With Quote
Old 10-30-2015, 02:56 PM   #58
Rivet Master
 
Al and Missy's Avatar

 
2002 30' Classic S/O
Melbourne Beach , Florida
Join Date: Nov 2013
Posts: 2,317
Thanks Bob,
I was hoping the text description of the prewire was correct so i could use the wires to power the fan instead of tapping off the light. Oh well, i guess i'm stuck with it the way it is.

Al
__________________

__________________

"You cannot reason someone out of a position they have not been reasoned into"

Al, K5TAN and Missy, N4RGO
2002 Classic 30 Slideout
S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
2001 Safari 25 RB Twin (Gone, but not forgotten)
WBCCI 1322, TAC FL-39, AIR 82265

Al and Missy is online now   Reply With Quote
Old 10-30-2015, 07:34 PM   #59
3 Rivet Member
 
Burnside Bob's Avatar
 
2009 25' FB Flying Cloud
1973 31' Sovereign
Mt Angel , Oregon
Join Date: Jul 2010
Posts: 198
Combining wire strands for higher ampacity

Quote:
Originally Posted by rodsterinfl View Post
I know that there is controversy here on wire size; however, I want to refer to this chart. The prewire should be able to handle up to around 200 watts.
I would like to add solar, so I've been following this discussion. I have been wondering if 200W of solar would be enough so the 10 gauge seems marginal to sketchy.

Since those #10 wires are there, its a shame not to use them. Why not combine them--two strands of #10 tied together are the same ampacity and resistance/foot as one strand of #7 and then run one strand of #6 to complete the solar circuit. Alternately, run two strands of #8 and wire one #8 and one #10 together to get the equivalent ampacity and resistance/foot of a circuit made entirely from #6?

Doing either would result in a circuit that could handle more watts of solar at lower cost with less voltage drop.
__________________
Best, Burnside

"To err is human, to air is devine."
Burnside Bob is offline   Reply With Quote
Old 10-30-2015, 07:40 PM   #60
Rivet Master
 
rodsterinfl's Avatar

 
2006 25' Safari
Fort Myers , Florida
Join Date: Oct 2011
Posts: 2,424
Images: 8
My pre wire was in the fridge compartment as well. The manual listed it and I found it.
__________________
WBCCI 8653
2017 Ford F-150 3.5 Ecobeast Gen 2 3.55 Platinum
rodsterinfl is offline   Reply With Quote
Old 10-30-2015, 07:44 PM   #61
Rivet Master
 
rodsterinfl's Avatar

 
2006 25' Safari
Fort Myers , Florida
Join Date: Oct 2011
Posts: 2,424
Images: 8
Solar pre-wire location

Figure out your run length and amperage then the actual loss. On a 25' my run was shorter than I expected. By the book up to 5% is acceptable. Consider too that the calculation is assuming maximum or perfect solar conditions.
__________________
WBCCI 8653
2017 Ford F-150 3.5 Ecobeast Gen 2 3.55 Platinum
rodsterinfl is offline   Reply With Quote
Old 10-30-2015, 11:40 PM   #62
Rivet Master
 
2015 30' Classic
Pleasanton , California
Join Date: Jan 2015
Posts: 616
Quote:
Originally Posted by Burnside Bob View Post
I would like to add solar, so I've been following this discussion. I have been wondering if 200W of solar would be enough so the 10 gauge seems marginal to sketchy.

Since those #10 wires are there, its a shame not to use them. Why not combine them--two strands of #10 tied together are the same ampacity and resistance/foot as one strand of #7 and then run one strand of #6 to complete the solar circuit. Alternately, run two strands of #8 and wire one #8 and one #10 together to get the equivalent ampacity and resistance/foot of a circuit made entirely from #6?

Doing either would result in a circuit that could handle more watts of solar at lower cost with less voltage drop.
10 gauge wire supports 400 W of solar with the loss due to the pre-wiring less than 2%! Just use a MPPT charger like the Solar Boost 3024iL MPPT and configure the panels in a serial/parallel arrangement. If you're only planning on 200 W then configure the panels in series. It's probably not worth your time and money to run additional wires just to save 2%. Better to spend the extra money on a battery monitor like the IPN remote so you can keep track of your energy consumption and battery state.
__________________
Al, K6IV
2015 30' Classic, "Chez Nu"
2014 RAM 2500 w/Cummins Diesel
ProPride Hitch, 400 W Solar
alano is offline   Reply With Quote
Old 01-08-2016, 05:05 PM   #63
2 Rivet Member
 
2014 27' FB International
1955 26' Cruiser Overlander
Las Vegas and Big Sky , Nevada / Montana
Join Date: Aug 2008
Posts: 53
Solar Pre Wire with two A/C units???

Has anyone found the Solar Green and Yellow prewires that are suppose to be just "to the rear of the front vent" on 2014 27FB with two AC's (no front vent) and the AC covers about 14-16" of the roof behind where the normal vent would sit. Can't see any marking on roof around the front AC unit but then again can't see under AC. Took off the inside AC cover and didn't see any sign of Green / Yellow wires and also removed three ceiling light between skylight and AC, no luck, and just wondered if anyone has done this before I start removing the AC and/or cutting holes in the roof. Thanks
__________________
tlcbuilder is offline   Reply With Quote
Old 01-08-2016, 06:13 PM   #64
Rivet Master
 
2015 30' Classic
Pleasanton , California
Join Date: Jan 2015
Posts: 616
I found mine from inside the trailer by removing the LED light. If you have a light near where AS describes the wires should be I would suggest dropping the light (unscrew the cover, then remove three screws) and feeling around for the wires.
__________________
Al, K6IV
2015 30' Classic, "Chez Nu"
2014 RAM 2500 w/Cummins Diesel
ProPride Hitch, 400 W Solar
alano is offline   Reply With Quote
Old 01-09-2016, 01:20 PM   #65
2 Rivet Member
 
2014 27' FB International
1955 26' Cruiser Overlander
Las Vegas and Big Sky , Nevada / Montana
Join Date: Aug 2008
Posts: 53
Solar pre wire 2014 27FB

Don't read the manual the pre wired solar on my 2014 27FB International 2 AC units was found under the rear Fantastic Fan Vent cover. So at least check that hiding spot before you look under the FRONT vent or AC unit.
__________________
tlcbuilder is offline   Reply With Quote
Old 01-09-2016, 07:35 PM   #66
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Some common misconceptions about voltage drop in wire sizing:

Based on the ABYC (American Boat and Yacht Council) recommendations for voltage drop in current carrying wires, Blue Sea Systems has generously provided this chart: https://www.bluesea.com/files/resour...on_chartlg.jpg

Example: If your Airstream solar pre-wire is located in the rear vent fan location of a 27FB, they terminate in the front of the trailer under the front bed at the bus bars. For a straight shot run (which it ISN'T), you get approx. 24' run and 8' drop from the ceiling to the floor, or a total of 32 feet.

ABYC electrical standard E-11 requires that you calculate the wire run from the power source AND BACK which effectively is double this length, or 64 feet, and then round up to the next available bracket.

Let's assume that we are looking at a 400 watt solar array, which should be capable of providing your 20 + amps to your charge controller. If your look at the table in the link (sorry, but I couldn't get it to reproduce here) at 3% voltage drop, a distance of 70 feet for a 20 amp load requires 4AWG cables! If you use the 10% voltage drop column for the same parameters (this time at the 65' bracket), you need 8AWG cables for a 20 amp load……..STILL larger than 10AWG.

Major solar charge controller manufacturers like Blue Sky Energy recommend that you use cable sizes from their chart: (taken from there manual for Blue Sky's 2512iX-HV solar charge controller, pg. 7) for specified cable run lengths as described below:

Blue Sky Energy - Solar Boost 2512i-HV and 2512iX-HV
BATTERY AND PV WIRING
A desirable installation will produce a total system wiring voltage drop of 3% or less. The lengths shown in Table 2 are one way from the PV modules to the battery with the 2512 located along the path. Length can be increased inversely proportional to actual PV IMP such that if current was reduced by 1/2 wire lengths could be doubled and still provide the same 3% voltage drop.

WIRE GAUGE AWG 3% VOLTAGE DROP 36 CELL MODULES
@ 20AMPS INPUT FEET / METERS
12 AWG 6.4 / 1.9
10 AWG 10.2 / 3.1
8 AWG 16.2 / 4.9
6 AWG 25.7 / 7.8
4 AWG 40.8 / 12.5

I maintain, (and so do the many people who write ampacity standards for the marine industry and solar industry) that Airstream's use of 10AWG cables for their solar prewire WILL NOT provide you with 3% voltage drop for any solar array above 100 watts (5 amps). The ABYC chart clearly shows a 5 amp load for 10AWG cable and 3% voltage drop to be limited to a circuit length of between 40-60'. This length must be divided by 2 to get the actual lineal length, or 20-30 feet…..just about what you find in most Airstreams today.

The tables cited above SPECIFICALLY address the issue of voltage drop in cable runs of varying amperage ratings and circuit lengths. Choose to believe AND USE what you want. The evidence is clear.
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 01-09-2016, 08:05 PM   #67
Rivet Master
 
2015 30' Classic
Pleasanton , California
Join Date: Jan 2015
Posts: 616
Lew, these tables are misleading. They assume solar panels produce 12 V. They don't. Take the Renology 36 cell panel. At maximum power it's producing 18.9 V at 5.29 A.

So, you want to build at 400 W system? Add four panels in a series/parallel configuration. This yields 37.8 V at 10.58 A.

Let's take your 3% voltage drop example. For this series/parallel 400 W system, 3% voltage drop corresponds to 3% * 37.8 V = 1.134 V = 10.58 A * R, therefore R = .107 ohms. Since 10 AWG is 1 milliohm/1000 ft this corresponds to wire length of 107 feet.

I've got no horse in this game except to educate folks and encourage them to DIY their solar systems.
__________________
Al, K6IV
2015 30' Classic, "Chez Nu"
2014 RAM 2500 w/Cummins Diesel
ProPride Hitch, 400 W Solar
alano is offline   Reply With Quote
Old 01-10-2016, 06:24 PM   #68
Tino
 
Tino643's Avatar
 
2013 27' FB International
Blainville , Quebec
Join Date: Sep 2009
Posts: 136
Hello Alano, I read yours post and I need some clarification. First of all, sory for the english. I am from the french part of Canada, so write in english it is not familiar to me. I have a 30 foot 2015 interna. and want to put like you for solar panel. I am very handy but not for the electricity. Like you i don't want to peut a biger cable. So I no where is the pre wire. And now this cable what do i do whit it???? I supose plug some where in the trailer. If it is possible to explane to me what you did it can be very helpfull for me. Thanks!
__________________
VW Touareg Diesel 2015
30´Airstream International 2015
27' Airstream 2014
25' Airstream 2012
20' Airstream 2009
Tino643 is offline   Reply With Quote
Old 01-10-2016, 07:29 PM   #69
Rivet Master
 
2015 30' Classic
Pleasanton , California
Join Date: Jan 2015
Posts: 616
Salut Tino,

I have a 30' 2015 Classic, so perhaps the solar pre-wires are near the same location. In my trailer I have a rear skylight window. In front of the rear skylight is an interior light. You can unscrew the dome, then remove three screws and drop the light fixture. If you reach up with your hand in the small space in the ceiling you should perhaps find the solar pre-wires. They are #10 AWG yellow and green.

If this doesn't help, I would suggest you contact your dealer and ask them exactly how to access the solar pre-wiring.
__________________
Al, K6IV
2015 30' Classic, "Chez Nu"
2014 RAM 2500 w/Cummins Diesel
ProPride Hitch, 400 W Solar
alano is offline   Reply With Quote
Old 03-05-2016, 11:52 PM   #70
Rivet Master
 
2016 30' Classic
Lorton , Virginia
Join Date: Jul 2015
Posts: 557
Quote:
Originally Posted by lewster View Post
Some common misconceptions about voltage drop in wire sizing:

Based on the ABYC (American Boat and Yacht Council) recommendations for voltage drop in current carrying wires, Blue Sea Systems has generously provided this chart: https://www.bluesea.com/files/resour...on_chartlg.jpg

Example: If your Airstream solar pre-wire is located in the rear vent fan location of a 27FB, they terminate in the front of the trailer under the front bed at the bus bars. For a straight shot run (which it ISN'T), you get approx. 24' run and 8' drop from the ceiling to the floor, or a total of 32 feet.

ABYC electrical standard E-11 requires that you calculate the wire run from the power source AND BACK which effectively is double this length, or 64 feet, and then round up to the next available bracket.

Let's assume that we are looking at a 400 watt solar array, which should be capable of providing your 20 + amps to your charge controller. If your look at the table in the link (sorry, but I couldn't get it to reproduce here) at 3% voltage drop, a distance of 70 feet for a 20 amp load requires 4AWG cables! If you use the 10% voltage drop column for the same parameters (this time at the 65' bracket), you need 8AWG cables for a 20 amp load……..STILL larger than 10AWG.

Major solar charge controller manufacturers like Blue Sky Energy recommend that you use cable sizes from their chart: (taken from there manual for Blue Sky's 2512iX-HV solar charge controller, pg. 7) for specified cable run lengths as described below:

Blue Sky Energy - Solar Boost 2512i-HV and 2512iX-HV
BATTERY AND PV WIRING
A desirable installation will produce a total system wiring voltage drop of 3% or less. The lengths shown in Table 2 are one way from the PV modules to the battery with the 2512 located along the path. Length can be increased inversely proportional to actual PV IMP such that if current was reduced by 1/2 wire lengths could be doubled and still provide the same 3% voltage drop.

WIRE GAUGE AWG 3% VOLTAGE DROP 36 CELL MODULES
@ 20AMPS INPUT FEET / METERS
12 AWG 6.4 / 1.9
10 AWG 10.2 / 3.1
8 AWG 16.2 / 4.9
6 AWG 25.7 / 7.8
4 AWG 40.8 / 12.5

I maintain, (and so do the many people who write ampacity standards for the marine industry and solar industry) that Airstream's use of 10AWG cables for their solar prewire WILL NOT provide you with 3% voltage drop for any solar array above 100 watts (5 amps). The ABYC chart clearly shows a 5 amp load for 10AWG cable and 3% voltage drop to be limited to a circuit length of between 40-60'. This length must be divided by 2 to get the actual lineal length, or 20-30 feet…..just about what you find in most Airstreams today.

The tables cited above SPECIFICALLY address the issue of voltage drop in cable runs of varying amperage ratings and circuit lengths. Choose to believe AND USE what you want. The evidence is clear.
You can't talk about wire gauge and amperage without talking about voltage. Voltage is a crucial part of the equation. It really depends on what solar panels you will use, what controller, what voltage, series/parallel.

A perfect example is a 1500 watt space heater I have here. About 8 foot of 16 gauge lamp cord is all it uses, because it's running 110v.
__________________

__________________
Zybane is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Location of Solar Pre-Wire. Where are the wires? kscherzi Generators & Solar Power 10 06-02-2013 05:06 PM
2010 28' International Solar Pre Wire ?? tlcbuilder 2006 - 2010 International 1 09-23-2012 04:02 PM
Solar pre-wire on a 2005 19' Bambi CCD JDL Generators & Solar Power 23 12-22-2010 06:50 AM
Solar pre wire bwaysteve Generators & Solar Power 7 11-21-2010 08:06 PM
Solar Pre-wire 2008 Safari 25 FB SE - Good enough? eheffa Generators & Solar Power 3 10-23-2009 11:30 AM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:04 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.