Furnace operation at 7000' on 2015 Classic

We just purchased a new 2015 Classic a few weeks ago and did the first "shakedown" trip with it this past weekend. We camped up in the mountains at a 7000 foot elevation.

The primary problem we encountered with the new unit was that the Gas Furnace would not stay ignited at this elevation even though it worked fine down in the desert at 2000 feet. It would ignite for 3-4 seconds then go out followed by another similar cycle after Approx. 30 seconds and repeat over and over again. The thermostat was set far above the internal temperature at the time. All of other gas appliances worked fine including the Hot Water Heater. I'm guessing it's probably a fuel/air mixture problem. Has anyone encountered this, and if so, where can you adjust this or how did you solve the problem?

I also spoke with the Atwood (the furnace manufacturer and they also indicated a regulator adjustment (external to the furnace) would be needed for elevations over 4500 feet.

Any help would be greatly appreciated.
__________________

__________________
TonyGuyer is offline   Reply With Quote
Old 06-11-2015, 03:00 PM   #2
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
At one time about 10 to 15 years ago furnace and water heater makers said their equipment would not work above xxxx feet, usually in the 7000' range. That didn't go down well with western campers, and it seemed to quietly disappear from their manuals. I have not heard much about it lately, so I thought they had solved the issue. I know that I have not had it up to about 8000' in my rigs.

I will be interested to see what others say about it.
__________________

__________________
idroba is offline   Reply With Quote
Old 06-11-2015, 03:35 PM   #3
2 Rivet Member
 
2014 30' FB FC Bunk
Golden , Colorado
Join Date: Apr 2015
Posts: 35
We have a 2014 30' BH and the furnace works perfectly at our house, which is right at 8K feet in Colorado. Purchased from a Detroit dealer, and I can assure you that they didn't do anything to prepare it for our altitude.
__________________
bbdo is offline   Reply With Quote
Old 06-11-2015, 03:47 PM   #4
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,411
Images: 5
I'll bet your regulator is set low. Mine was.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 06-11-2015, 04:32 PM   #5
1 Rivet Member
 
jt1911man's Avatar
 
2015 16' Sport
Sierra Vista , Arizona
Join Date: Mar 2015
Posts: 18
Quote:
Originally Posted by dznf0g View Post
I'll bet your regulator is set low. Mine was.
So how do you fix it?
__________________
jt1911man is offline   Reply With Quote
Old 06-11-2015, 05:39 PM   #6
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,411
Images: 5
You have to get a low pressure gauge. Install it at the stove with the proper fittings. Turn on all the rest of the gas appliances and adjust the regulator to 11 inches. The adjustment screw is under a black cap on the regulator.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 06-11-2015, 05:54 PM   #7
TonyG
 
TonyGuyer's Avatar
 
2015 30' Classic
Cave Creek , Arizona
Join Date: Mar 2015
Posts: 13
Thanks for the help.

Since my original post, I had found an information tag attached to the regulator at the propane tanks that contained a short statement on how to adjust the pressure as you had described which led me to the conclusion that this may very well fix the problem.

Once you have adjusted it to 11 inches, will it work at lower elevations (say down to a 1000') or is this something you kind of have to tweek depending on the elevation you are at?
__________________
TonyGuyer is offline   Reply With Quote
Old 06-11-2015, 06:59 PM   #8
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,411
Images: 5
Should be fine at both. I adjusted mine when I got home from the Rockies, but haven't been back yet.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 06-11-2015, 07:16 PM   #9
Rivet Master
 
KJRitchie's Avatar

 
2008 25' Classic
Wichita Falls , Texas
Join Date: Nov 2012
Posts: 4,223
I was in North Rim Grand Canyon today and ran the furnace fine at 8200ft. I wonder if only the new furnaces have this limitation. I doubt the previous owner of my AS left Austin, TX during the years they owned it.

Kelvin
__________________
2008 Classic 25fb "Silver Mistress"
2015 Ram 2500 6.7L Cummins. Crew Cab, 4x4, Silver
KJRitchie is offline   Reply With Quote
Old 06-11-2015, 07:48 PM   #10
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 5,936
Images: 2
Replace regulator. You can have it tested for proper "pressure"...before but easier to change... Compare the flame output in stove to "before/after".... Our was "low pressure" until replaced....
__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 06-11-2015, 09:11 PM   #11
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,411
Images: 5
But I'm not confident they are properly calibrated off the shelf
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 06-12-2015, 09:19 AM   #12
Rivet Master
 
2016 30' Classic
Erie , Colorado
Join Date: Oct 2013
Posts: 1,245
Images: 1
Tony I am having the same issue and not just at higher elevations. Already deep into trouble shooting. Pretty simple system and getting into a local service center, well there are 8-10 week waits. Here's what I have found so far.

1. This is new furnace from Atwood and no one has manuals or parts.
2. Attaching the manual to this post.
3. Found that the electrode (starts and checks for flame) was misadjusted by 5mm. Carefully adjusted that.
4. Replaced the main circuit board.
5. Checked pressure. Was too high by 3 inches. Replaced pressure regulator with a Marshall.

This did not fix the issue.

Talked with Atwood, good support though you may be on hold for awhile. They are sending a new electrode. The electrode, besides being the spark for ignition, senses heat. If it has failed or is failing then it says to the board no heat after start and shuts down the gas solenoid. Then goes into a 15 second restart cycle.

If that fixes it great. If not really the only other thing easily replace is the the limit switch when senses and over temp. Again if it is failing that too could shut off the solenoids.

Never had a problem at higher elevations with my 2014 FC25. And coming back from Colonial to Colorado don't remember an issue.

And as I mentioned I've called a Camping World and another local Atwood dealer and they don't even have a manual nor parts/numbers or prices at this point.

Will post again if I get it fixed and reliable. Last resort will be an early fall trip back to Jackson Center.

Atwood Furnace 2015.pdf
__________________
Gary
2015 Classic
2015 GMC Sierra 2500HD Duramax
ProPride
NVPN
ghaynes755 is offline   Reply With Quote
Old 06-12-2015, 09:24 AM   #13
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,411
Images: 5
Quote:
Originally Posted by ghaynes755 View Post
Tony I am having the same issue and not just at higher elevations. Already deep into trouble shooting. Pretty simple system and getting into a local service center, well there are 8-10 week waits. Here's what I have found so far.

1. This is new furnace from Atwood and no one has manuals or parts.
2. Attaching the manual to this post.
3. Found that the electrode (starts and checks for flame) was misadjusted by 5mm. Carefully adjusted that.
4. Replaced the main circuit board.
5. Checked pressure. Was too high by 3 inches. Replaced pressure regulator with a Marshall.

This did not fix the issue.

Talked with Atwood, good support though you may be on hold for awhile. They are sending a new electrode. The electrode, besides being the spark for ignition, senses heat. If it has failed or is failing then it says to the board no heat after start and shuts down the gas solenoid. Then goes into a 15 second restart cycle.

If that fixes it great. If not really the only other thing easily replace is the the limit switch when senses and over temp. Again if it is failing that too could shut off the solenoids.

Never had a problem at higher elevations with my 2014 FC25. And coming back from Colonial to Colorado don't remember an issue.

And as I mentioned I've called a Camping World and another local Atwood dealer and they don't even have a manual nor parts/numbers or prices at this point.

Will post again if I get it fixed and reliable. Last resort will be an early fall trip back to Jackson Center.

Attachment 240491
3" too high with all gas appliances on or off? 14" is just about right with all the appliances off. I adjusted to 11" with everything (but the stove, since that's where the gauge is installed) on. After shutting everything off I have 14" static pressure.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 06-12-2015, 09:28 AM   #14
Rivet Master
 
dznf0g's Avatar

 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 9,411
Images: 5
Here's a step by step procedure:

How to Measure Propane Regulator Pressure | eHow
__________________

__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Kohler 7000 oil leak Keyair Generators & Solar Power 32 12-10-2012 09:08 PM
Best Tow Vehicle- '80's (7000#?) Airstream aaastircrazy Tow Vehicles 3 08-13-2009 08:27 PM
F150 (max 7000 tow rating) pulling Safari 25? Eckhart Tow Vehicles 9 04-03-2009 08:22 AM
staying warm at 7000 feet silverback Winter Living 4 11-04-2005 04:09 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:58 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.