Airstream Chat Room Airstream Links Campground & Product Reviews Airstream Classifieds Airstream Articles Blogs Photo Gallery Forum Listings Portal - Home Page

Go Back   Airstream Forums > Airstream Community Forums > Full-Timing & Winter Living > Winter Living




Find out what's going on and meet up with other Airstreamers in your area through our Clubs & Groups Directory.

Quick Links
- Forum Listings
- Register - it's FREE!
- View Member's Map
- Airstream Articles
- "Live" Chat Room
- View Classifieds
- Post a Classified
- Airstream @ eBay
- Upcoming Rallies
   - Add A Rally
- Rally Discussions
- Repair Discussions
- Search Forums
- Member List
- AIR # Directory
- Member Search
- Profile Photos
- Airstream Photo
- Airstream Links
- Fun & Games
- WBCCI Websites
- WBCCI Unit Forums
- Courtesy Parking
- Campgrounds
- Support & FAQs
- Community Policies
- Helpers Needed




Reply
 
Thread Tools Display Modes
Old 04-21-2008, 07:46 PM   #15
full-timer

 
DreamStreamr's Avatar
Profile:  2005 25' International CCD
Everywhere , North America
Posts: 165
Images: 42

Neil,
We also purchased the Hunter digital thermostat. Ours is not programmable and only connects to two wires, so won't work for some Airstreams. Apparently the Airstreams with just a furnace, for example, are perfect for this.

The one we purchased won't work to replace the thermostats which control roof unit and furnace all in one.


Ours, though, is a wonderful improvement over the cheap Atwood bimetallic. One of the simplest and most effective changes we've wrought on our rolling home.

__________________
Jim N5RTG & Deb KI4OKI
WBCCI #4822 / WBCCI ARC/ RV SVC Network
Escapees full-timing in our CCD 25 blue streak
sometimes seen behind the magnificent 2500HD 8.1L/Allison 6spd 3.73

visit us at http://dreamstreamr.com
DreamStreamr is offline   Reply With Quote
Old 04-21-2008, 08:10 PM   #16
3 Rivet Member
Commercial Vendor

 
Andrew T's Avatar
Profile:  2008 34' Classic
1960 17' Pacer
London , Ontario
Posts: 192

Hi Gowyn

Next time you bring the Airstream in for service remind me of the heating situation. We can often improve the temperature differential, sometimes there are pinched ducts or ducts with too much hose that reduces the air flow to the bedroom.

See you then.

Andy
Andrew T is offline   Reply With Quote
Old 04-21-2008, 11:02 PM   #17
Rivet Master

 
Westfalia's Avatar
Profile:  2008 27' International CCD FB
Boerne, TX / , Evergreen, CO
Posts: 624
Images: 35

Send a message via AIM to Westfalia Send a message via Skype™ to Westfalia
Quote:
Originally Posted by safari 28
It is a pitiful system as I examine it further. It meets standards in homes that were in the 60s. Anyway, it will not quiet it down, but will help on longer runs to transfer more heat to that area. in the end, it leaks throughout the coach so no energy savings to speak of. This industry need some help big time regarding HVAC products.
I have the trailer now. The furnace is MUCH quieter than the last one. I can hear the woosh of air when its on, but little of the actual blower noise unless you are sitting over it. I am looking at what I can do to quiet it down the rest of the way. I'll likely wrap the furnace in a combination of glass and bubble wrap to muffle the blower sound coming from the unit, and well and sound insulate the inside of the cabinet. I need to do something about insulating the long runs of the above floor venting. The temp drop is pretty large when cold. All that heat is heating the bottom of my cabinets instead of bedroom.
__________________
Chris - Boerne, TX / Evergreen, CO

2008 27'FB Int'l Signature CCD - Thank You Airstream of Arkansas!
2008 Dodge Ram 2500 6.7 CTD Mega Cab
1977 VW Westfalia Camper, hardtop 'Weekender'::Pictures


"Keeping an open mind is important, but not so open that your brain falls out."
Westfalia is offline   Reply With Quote
Old 05-02-2008, 10:37 PM   #18
New Member
Profile:  Currently Looking...
Longmont , Colorado
Posts: 1

Has anyone thought of building a small solar generator and just hooking it up to a nice portable electric oil heater? I think you can put one together for under 500 dollars and you can use the amps in the summer for a A/C unit as well.
Liberty Girl is offline   Reply With Quote
Old 05-03-2008, 08:10 AM   #19
3 Rivet Member
Profile:  1973 25' Tradewind
Romulus , New York
Posts: 139

My electric oil heater has two settings. 1800watts and 1000watts. This really needs shore power
jayray5 is offline   Reply With Quote
Old 05-03-2008, 09:38 AM   #20
4 Rivet Member

 
safari 28's Avatar
Profile:  2004 28' Safari
holland , Michigan
Posts: 416
Images: 1

The problem with any portable electric is the high wattage. Strip heat or a large toaster,same design, is very efficient (99%) but needs lots of juice/ possibly sola/wind generator to 4 deep cycle batteries and then to a 3k inverter would give heat for say 4-6 hours and then your out of luck.

I like this idea. An all electric unit. Same 4 deep cycle batteries, same 3-5k inverter and then a very quit built in 3k generator, diesel mounted on the toungue where the propane tanks are. Then a electric tankless water heater, and a package high velocity system similar to a unit made by Espi Tech//Called velocity plus with a hot water coil and strip heat. This could provide all your heating and cooling, would require a frame mounted cond unit/ side discharge that could go where the gas water heater is.. Now the roof is free of the ugly unit on top, quiet very well insulated air delivery system. No propane ever.
safari 28 is offline   Reply With Quote
Old 08-16-2008, 07:59 PM   #21
Rivet Master

 
cameront120's Avatar
Profile:  1972 25' Tradewind
North Vancouver , British Columbia
Posts: 1,998
Images: 23

If I heat my Tradewind with an oil filled heater, rather than use the furnace, will the heat circulate enough to keep water lines and storage tanks from freezing? I don't really trust the furnace, as it's one of the recall models and I don't know that the fix was done. At this point I can't afford to replace the furnace and will need to look at alternatives.
__________________
Cameron & the Labradors
Kai & Samm
North Vancouver, BC
Canada

AIR #11529

http://northvancouvermodern.blogspot.com/
cameront120 is offline   Reply With Quote
Old 08-16-2008, 08:54 PM   #22
Well-Preserved

 
overlander63's Avatar

Profile:  1974 31' Sovereign
. , .
Posts: 14,528

Quote:
Originally Posted by cameront120 View Post
If I heat my Tradewind with an oil filled heater, rather than use the furnace, will the heat circulate enough to keep water lines and storage tanks from freezing? I don't really trust the furnace, as it's one of the recall models and I don't know that the fix was done. At this point I can't afford to replace the furnace and will need to look at alternatives.
I would block off the air ducts to outdoors (cold air leak) with a small piece of sheet aluminum, run the oil filled heater, and run the coach furnace on fan only. It will pull the warmer air in from the living area, and blow it across the holding tanks. An alternative to this is to get a couple lengths of "freeze tape", pull the belly pan down, and lay the freeze tape in a pattern in the slots in the foam insulation under the bottom of the tanks.
__________________
Terry

(No Longer at Inland RV)
overlander63 is offline   Reply With Quote
Old 08-16-2008, 10:02 PM   #23
Rivet Master

 
cameront120's Avatar
Profile:  1972 25' Tradewind
North Vancouver , British Columbia
Posts: 1,998
Images: 23

Thanks for the tips, Terry.
__________________
Cameron & the Labradors
Kai & Samm
North Vancouver, BC
Canada

AIR #11529

http://northvancouvermodern.blogspot.com/
cameront120 is offline   Reply With Quote
Old 11-16-2008, 08:47 PM   #24
2 Rivet Member
Profile:  1976 31' Sovereign
Blairsville , Georgia
Posts: 44

My '76 Soveriegn has a duct going under the bed to the rear bath. I'm thinking of putting in a "T" and running a short duct from under the bed into the bedroom. It would be easy to do this and it could be closed to direct the heat to the bathroom when needed there. Anyone done this?
Chip Arnold is offline   Reply With Quote
Old 11-25-2008, 05:31 PM   #25
Louie
Profile:  2008 27' Classic FB
Hope Valley , Rhode Island
Posts: 10

Send a message via Yahoo to bizetwo
Hi,
I have an 08,27'FB. Its real cold in the bedroom area. We put a electric mattress pad on the bed it really helped out. I just purchased a Pelonis ceramic heater 1500w hoping this will heat up the mid area. Yes the furnace just keeps on running.
Louis
bizetwo is offline   Reply With Quote
Old 11-25-2008, 06:12 PM   #26
3 Rivet Member

 
gowyn's Avatar
Profile:  2007 27' Safari FB SE
London , ontario
Posts: 171

Well here is my solution. I took a couple aluminum pie plates, cut small hole in them and blocked of ducts in dinette and kitchen.

I also installed one of these in the bedroom.

I also have a mattress warmer so as long as we're plugged in we should be nice and toasty.

Also plan on running a small fan to circulate air inside the trailer, it will sit on the dining table pointed back towards bedroom.
gowyn is offline   Reply With Quote
Old 11-26-2008, 05:10 AM   #27
Louie
Profile:  2008 27' Classic FB
Hope Valley , Rhode Island
Posts: 10

Send a message via Yahoo to bizetwo
In my 27'FB the duct in toilet room blows rather cool air. Did the pie plate method help to divert warm air to the toilet area also?? I think I will try this it makes good sense. I took out the closet deck to inspect the H2O pump and heat ducting what a mess. I also noticed a big hole cut under the shower area for the water trap. Well this got me busy patching the floor with 3 "styrofoam. What a difference that made in keeping out the cold,now the shower floor is warm.
bizetwo is offline   Reply With Quote
Old 11-27-2008, 08:43 AM   #28
4 Rivet Member

 
safari 28's Avatar
Profile:  2004 28' Safari
holland , Michigan
Posts: 416
Images: 1

I have actually looked into making systems that would work in these puppies and have contacts in the industry. The problem is cost. Even high end units like Airstream will not change unless we demand quieter designs. From what iI can see some of the central units by winnebago and in floor heating on diesel rigs is a huge step in the right direction. Sadly, our 60k trailers have the same set up as 10k SOB. i say shame on the mother ship.
safari 28 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the heat pump/heat strip instead of furnace. crazylev On The Road... 37 07-16-2009 10:08 PM
Absence of Heat... STREAMTEAM Off Topic Forum 20 12-30-2007 02:17 PM
The Heat is ON!! GlenCoombe Mechanics Corner - Engines, Transmission & More... 5 10-09-2005 04:48 PM
need heat whistler Furnaces, Heaters, Fireplaces & Air Conditioning 3 06-07-2004 02:32 PM
radiant heat Piper Furnaces, Heaters, Fireplaces & Air Conditioning 3 06-19-2003 11:30 PM

Powered by vBadvanced CMPS v3.0.1

All times are GMT -6. The time now is 03:42 PM.

Other Social Knowledge forum communities:
Cooking Forum - Sailing Forum - Early Retirement - Airstream Trailer - Aquarium Forum - Royal Forum - Book Forum - Volkswagen Touareg Forum - Jeep Wrangler Forum - Whitewater Kayaking & Rafting Forum - Fiberglass RV Forum - RV Forum - Truck Conversion - U2 Music Forum
Social Knowledge Networks
Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.

eXTReMe Tracker

Other recommended RV/Travel Trailer sites:
Airstream Classifieds - Airstream Central - Airstream Photos - Fiberglass RV Forum - iRV2 RV Forum

© copyright 2002-2009 Social Knowledge, LLC All Rights Reserved.