Electrician Help! Wiring to RV Power Pedestal

I just added a parking pad to my backyard to store my trailer. I am going to run full hookups out to it (for convenience and so it can be a guesthouse / AirBnB).

My question is for the electricians in the group - what is the appropriate wiring out to the power pedestal? My trailer is only 30A, but I have a 100A pedestal on its way (with one each 50A, 30A and 20A circuits). My wire run will be 65' in the ground, plus another 45' through a basement crawl space.

I'm getting confused looking at ampacity/voltage drop tables - do I need to use 100A in the tables, or 50A since that is what each of the two hot wires will carry.

My option A is to use 2-2-4-6 USE (Aluminum) Mobile Home Feeder. Is that large enough?

Another issue is USE needs to be in a conduit inside the house based on my understanding of the NEC. Is there an easier option (such as going right to a junction box inside the house and then using a wire type that does not need conduit through the house)? Suggestions on type of junction box / bus bar inside it / wire type?

I understand electricity, just not the NEC!!!

Thanks.
matthorr is offline   Reply With Quote
Old 09-02-2015, 07:26 PM   #2
Rivet Master
 
dbj216's Avatar

 
1986 34' Limited
1975 27' Overlander
1969 21' Globetrotter
Conifer , Colorado
Join Date: Jun 2009
Posts: 8,319
Images: 1
I'm going to bump this thread to the front of the line as I think you have an interesting question. We need an electrician Airstreamer to help out.

I ran a 30 amp circuit to my trailer pad. We had the house wired for a 30 amp RV connection when it was built. I simply ran outdoor conductor underground about 25 feet and wired it to a 30 amp receptacle. It was a much easier job than you are undertaking.

I think your trailer will make a great Airbnb location. It will be a lot more interesting than a Super 8.

David
dbj216 is offline   Reply With Quote
Old 09-02-2015, 07:43 PM   #3
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
Not an electrician, but a stationary engineer listening in ...
Wondering why not a 30 or 50 amp box for a 30 amp trailer?
Curious about what the electrician will say about the capacity of the source box and total load.
Guessing 2-2-4-6 (hot-hot-neutral-ground) in conduit - both in the house and underground.
We used nothing but copper when doing additions in hospitals, but I never asked why.
nrgtrakr is offline   Reply With Quote
Old 09-02-2015, 08:06 PM   #4
Rivet Master
 
jdalrymple's Avatar
 
2009 27' FB Flying Cloud
1982 31' International
1991 35' Airstream 350
Jay , Oklahoma
Join Date: Oct 2006
Posts: 1,706
I am not an licensed electrician, but I too understand electricity.


For 50 amp RV loads, each of the conductors must carry a full 50 amp load. Because none of the appliances are 240 volts, the neutral conductor gauge must equal to the line conductors.

I believe you are on the right track on using romex in the stud walls and splicing to the 2 ga inside an approved box in the crawl space.



We shall see what others say.


Regards,


JD
__________________
Jeff & Cindy
'09 27FB Flying Cloud;'82 31 International
'91 350 LE MH; '21 Interstate 24GT


jdalrymple is offline   Reply With Quote
Old 09-02-2015, 08:26 PM   #5
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
The only comments I can make to this thread are:

• Retain the services of a licensed local electrician who is not only familiar with NEC, but also local electrical requirements

• I wouldn't use aluminum if you gave it to me for free

• I would have ALL conductors the same gauge. This is a requirement on marine wiring, and IMHO, should be followed on ANY wiring project! Minimal gauge neutrals and especially grounds are a recipe for problems. I would never use anything else for myself or my clients.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 09-02-2015, 08:39 PM   #6
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
When I remember the hospital renovations, the wire was always the same gauge. I wonder why the code changes?
Give me Lewster's aluminum wire, I'll take it to recycle, buy copper.
Some places will let the property owner do their own work, but you still need a permit and pass inspections.
Now where is that electrician?
nrgtrakr is offline   Reply With Quote
Old 09-02-2015, 08:45 PM   #7
4 Rivet Member
 
Hiho Silver's Avatar
 
2016 27' Flying Cloud
Overland Park , Kansas
Join Date: Mar 2013
Posts: 365
Quote:
Originally Posted by lewster View Post
The only comments I can make to this thread are:



• Retain the services of a licensed local electrician who is not only familiar with NEC, but also local electrical requirements



• I wouldn't use aluminum if you gave it to me for free



• I would have ALL conductors the same gauge. This is a requirement on marine wiring, and IMHO, should be followed on ANY wiring project! Minimal gauge neutrals and especially grounds are a recipe for problems. I would never use anything else for myself or my clients.

Just wondering about the aluminum,
Lewster. I had a licensed electrician install a pedestal with 50amp on our rural property, aluminum was half the price, and the panel is almost 200' away from the pedestal so the savings was significant. ( can't remember what gauge, I would have to check). Works great, with everything on, 2 a/c's, electric water heater, microwave, and everything else I could turn on at once. I have a surge protector and the voltage is good. Just wondering, am I going to have problems in the future because I used aluminum?


Sent from my iPhone using Airstream Forums
Hiho Silver is offline   Reply With Quote
Old 09-02-2015, 08:55 PM   #8
4 Rivet Member
 
kennethowens's Avatar
 
1975 Argosy 24
Malakoff , Texas
Join Date: Apr 2009
Posts: 490
#6 Awg COPPER has 0.3951 Ohms per 1000ft

you are using 1/10th of 1000ft

at 30 amps usage...Volts=Amps X Ohms

V=30A X .03951Ohms = 1.1853 Volts dropped along 100ft

That is less than 1% of 120Volts

It will work.

Electricians onboard?
kennethowens is offline   Reply With Quote
Old 09-02-2015, 08:55 PM   #9
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,673
I'm not an electrician either, but I have done some NEC work. I believe you need only to size the wire for the highest capacity receptacle, i.e. 50A.

338.12B says USE shall not be used above ground except for transitioning to another cable type in an approved box.

I'm having trouble finding the voltage drop calculations, but I presume that is why you went to #2 as #6 would be good for 50A at 30 degrees C per the ampacity tables.

Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 09-02-2015, 09:08 PM   #10
4 Rivet Member
 
kennethowens's Avatar
 
1975 Argosy 24
Malakoff , Texas
Join Date: Apr 2009
Posts: 490
You wrestle a #2 wire awhile...write back about the experience.
Stiff bugger will KICK YO BOOOOO-DEE
Try it
Ol #6 aint no punk
Refer to the calcs above
kennethowens is offline   Reply With Quote
Old 09-02-2015, 09:08 PM   #11
4 Rivet Member
 
kennethowens's Avatar
 
1975 Argosy 24
Malakoff , Texas
Join Date: Apr 2009
Posts: 490
You wrestle a #2 wire awhile...write back about the experience.
Stiff bugger will KICK YO BOOOOO-DEE
Try it
Ol #6 aint no punk
Refer to the calcs above
kennethowens is offline   Reply With Quote
Old 09-03-2015, 08:12 AM   #12
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Heck, I wrestled 6ga through conduit in the basement and up the outside of the house and that was bad enough. It was over kill for a 45' run, but the supply house was out of 8ga and I was impatient. It was only a 30 amp circuit.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 09-03-2015, 08:58 AM   #13
Rivet Master
 
israndy's Avatar
 
2005 39' Skydeck
Alameda , California
Join Date: May 2015
Posts: 558
Images: 2
Blog Entries: 1
I am surprised you could not find a 30 amp pedestal, they seem to be at MANY campgrounds. If you plan on having people stay in your backyard next to your trailer I can see wiring for 50 amps, but if you are only running 30 amps, it is much easier. Breaker only draws from one side of the panel, no confusing wires.

I think technically if you do wire up the 50 amp you actually need a second run of wire for the 30 amp outlet. If you put a full draw on the 50 and ALSO put a draw on the 30 you would be overcapacity and run your wire hot until the breaker went. Same for the 20/15 amp outlet. If you are ignoring code and never intend to use more than one outlet label it so. There should be a lockout to prevent more than one working, but I don't know of any pedestal that supports a lockout, they just have the extra circuits run.

Aluminum is GREAT. Copper bends easier as it doesn't need to be as thick for the same rating, and it's generally a softer metal. But aluminum is LIGHT, and CHEAP. Don't diss aluminum, it's why there are metal airplanes instead of coated fabric.

-Randy
__________________
2007 LTV Serenity beater 2005 Airstream SkyDeck
Also a 1999 Jeep Grand Cherokee, 2000 Honda Hybrid Insight
And all electric: March 2018 Tesla Model ☰, a 2012 Mitsubishi i-Miev and two 2007 Vectrix VX1 motorcycles
israndy is offline   Reply With Quote
Old 09-03-2015, 09:06 AM   #14
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
If it were me, I'd send the 100 amp box back, get a 30 amp box and run wire accordingly - much cheaper, easier.
Where is that electrician?
nrgtrakr is offline   Reply With Quote
Old 09-03-2015, 09:50 AM   #15
Rivet Master

 
, Minnesota
Join Date: Aug 2003
Posts: 7,721
Images: 59
You can use aluminum outside, just run the cable from pedestal to the outside of the house. Use conduit where its day lighted.
Use copper inside the dwelling and to the outside wall where it meets the aluminum. Use proper Al/Cu connectors.


Sent from my iPhone using Airstream Forums
markdoane is offline   Reply With Quote
Old 09-03-2015, 12:51 PM   #16
Rivet Master
 
greghoro's Avatar
 
2013 25' Flying Cloud
Wheaton , Illinois
Join Date: Aug 2014
Posts: 649
You need to anticpate what your largest draw will be in the future. Are there thoughts of upsizing where you would need 50A? Or possibly hosting more than one guest at a time?

While what you ordered is overkill for now, it may not be in the future. The incremental cost of overbuilding now will save time and money in the future. The wire you run now will be the limiting factor for future expansion.

The breaker you put in your main panel must be smaller or equal to the ampicity of the wire you run, taking into account the length of the run. It is this breaker that ultimately protects the wire in the run to your pedistal sub panel.


Greg
greghoro is offline   Reply With Quote
Old 09-03-2015, 01:42 PM   #17
Rivet Master
 
greghoro's Avatar
 
2013 25' Flying Cloud
Wheaton , Illinois
Join Date: Aug 2014
Posts: 649
Quote:
Originally Posted by israndy View Post
I think technically if you do wire up the 50 amp you actually need a second run of wire for the 30 amp outlet.
Most likely not true. Most RV pee-assembled pedestals are considered subpanels and use a common bus to feed all of the circuit breakers. There is no provision to add an additional 30A feed in addition to the 50A feed. You need to size the feed wires to meet the overall utilization need of the pedestal. For what the original poster is installing, at minimum the feed needs to be capable of supplying 50A and 100A if all three outlets are to be used at the same time.


Greg
greghoro is offline   Reply With Quote
Old 09-03-2015, 01:48 PM   #18
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,673
Quote:
Originally Posted by israndy View Post
I think technically if you do wire up the 50 amp you actually need a second run of wire for the 30 amp outlet. If you put a full draw on the 50 and ALSO put a draw on the 30 you would be overcapacity and run your wire hot until the breaker went. Same for the 20/15 amp outlet. If you are ignoring code and never intend to use more than one outlet label it so. There should be a lockout to prevent more than one working, but I don't know of any pedestal that supports a lockout, they just have the extra circuits run.

....

-Randy
Randy is right. For a normal RV pedestal there would only be either a 50A connection or a 30A connection. If there is any thought of using both connectors simultaneously the 30A receptacle should be fed by its own conductor, should have its own neutral, and should be protected by its own breaker.

Reviewing greggoro's response (shame on you for dragging in reality) the pedestal may not be wired to allow the use of the 50A and 30A circuits simultaneously. If not, using larger wires and a larger breaker at the source may not be a good idea.

Regarding the wire selection of 2/2/4/6, as I read the code, if he needs #2 for the hot wires (I don't think he does) then he should be using #2 for neutral. A different wire size for neutral is only permitted for 240V loads. The 50A RV setup is split 120 loads and so should have the same size neutral as the primary conductors.

Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 09-03-2015, 03:29 PM   #19
Rivet Master
 
greghoro's Avatar
 
2013 25' Flying Cloud
Wheaton , Illinois
Join Date: Aug 2014
Posts: 649
Matthorr - much speculation in assisting you can be put to rest if we knew exactly what pedistal you purchased.

Manufacturer and model, please.


Greg
greghoro is offline   Reply With Quote
Old 09-03-2015, 03:40 PM   #20
Newbie
 
joemikeb's Avatar
 
2013 Interstate Coach
Fort Worth , Texas
Join Date: May 2013
Posts: 290
Check your local standards. No municipality in our area and maybe in the entire state permits new or add-on wiring using Aluminum. CoAlR switches and outlets or copper pigtails to existing aluminum wiring are permitted but only when the wiring is grandfathered under the code. Sometimes jackleg electricians will use aluminum wiring but when there is a fire and that is found, the fire insurance companies will not pay off. Aluminum may seem cheaper in the short term but in the long run it can be VERY expensive.
__________________
Make errors — otherwise the Great Spirit realizes
you have finished your purpose on earth.

— Navajo saying
joemikeb is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need help with pedestal…..help! FromDad Sprinter and B-van Forum 4 04-02-2014 11:05 PM
Airstream Electrician in S. California needed bunnyfamily Batteries, Univolts, Converters & Inverters 5 05-20-2013 08:31 PM
Need an Electrician in Houston, Texas jennthevexer Electrical - Systems, Generators, Batteries & Solar 7 10-31-2012 04:58 PM
Oregon electrician recommendation? SpaceEgg Electrical - Systems, Generators, Batteries & Solar 0 06-30-2011 06:09 AM
Finding an Electrician amalgamator Electrical - Systems, Generators, Batteries & Solar 5 06-09-2010 08:11 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 03:44 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.