Thanks Jammer. Like I said, I've never used the 50 amp source. Seen the outlet in panels at CG, but didn't pay that much attention.
My guess would be if that the big rigs which require 50 amps went to a place that only had 30 amp and used an adaptor would only be able to use one A/C unit. Again, it's only a guess, since my rig is set up for 30 amps.
__________________

__________________
Knowledge: "A gift to be shared. A treasure to receive."
TG Twinkie is offline   Reply With Quote
Old 10-25-2012, 04:17 PM   #30
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 5,140
Images: 2
Blog Entries: 5
As stated above. An open neutral can be as much of a shock hazard as a hot wire. When a neutral is open, the voltage "stands" at the open connection. If you were to get between the open neutral and the point at which it connects to the neutral buss or earth ground, you would get shocked. If the open neutral wire were to come in contact with the trailer chassis and the chassis was not properly grounded. The trailer would become a shock hazard.
Of course the hot leg to the device would have to be powered. ie the switch closed to a light fixture etc..
__________________

__________________
Knowledge: "A gift to be shared. A treasure to receive."
TG Twinkie is offline   Reply With Quote
Old 10-25-2012, 05:10 PM   #31
banjobill
 
wmarsha's Avatar
 
2000 30' Limited
battle ground, , Washington
Join Date: Jun 2009
Posts: 510
nomenclature

one of the problems faced by anyone doing electrical work is the decades old usage of the word "ground." Today, there is "earth ground", a "multi-grounded neutral", a "grounding conductor", a conductor "bonded" to a "grounding conductor" or "grounding lug (connector)". My 1985 Airstream had a common neutral and grounding conductor bar. My 2000 has two separate bars; one for neutral conductors and one for grounding conductors-the grounding conductors and the neutral should be entirely separate. When connected to an RV park's pedestal, the RV receives a connection to earth ground via the park's AC system. If a separately derived prime source is used (a generator) then said source should have a driven rod earth ground connection, and the here-to-fore mentioned "sub-panel" in the RV now becomes a main service panel and the neutral of said panel should be bonded to the grounding bar within the panel. Now are you confused?
In DC systems, neither of the two leads required to operate a load are ground conductors, grounding conductors or bonded conductors. There is a battery lead, and a battery return lead. In sophisticated DC circuitry, there is a 3rd conductor which is indeed, a grounding conductor.

The confusion stems from the old(er) usage of 2 wire 120VAC circuitry & 3 wire 240VAC single phase circuitry, and 2 wire dc circuitry. Today, up to date facilities utilize 3 wire 120VAC circuits and 4 wire 240VAC single phase circuitry as well as 3 wire DC circuitry. AND, the extra conductor is a "grounding conductor" not "ground".

These terms (nomenclature) are found in article 100-Definitions of the 2011 National Electrical Code. The term "multi-grounded Neutral" is a Utility Power Source term used to define the neutral conductor in the Utility transmission systems.
__________________
wmarsha is offline   Reply With Quote
Old 10-25-2012, 06:55 PM   #32
Rivet Master
 
rogerdodger's Avatar
 
Vintage Kin Owner
Fresno/Clovis , California
Join Date: May 2008
Posts: 685
To sum it all up, for those of us still confused, can anyone put up a diagram of the correct wiring?
__________________
Roger
Air# 29488
rogerdodger is offline   Reply With Quote
Old 10-25-2012, 07:49 PM   #33
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 5,140
Images: 2
Blog Entries: 5
Just separate the ground and neutral buss'. Then connect the ground buss to the chassis with at least a #6 wire. Do Not connect the neutral buss to the ground buss or to the chassis.
__________________
Knowledge: "A gift to be shared. A treasure to receive."
TG Twinkie is offline   Reply With Quote
Old 10-25-2012, 08:08 PM   #34
3 Rivet Member
 
10Smiles's Avatar
 
2005 30' Classic
Kingston , Washington
Join Date: May 2011
Posts: 238
OK, here's a picture. The line (red and black) should come in on a 240V bridged circuit as the main breaker (you can keep it on the bus bars, but this gives a bit more protection).


The neutral (white) connects to the "floating" bar, and the ground (green) connects to the bar that is bonded to the panel.
Attached Thumbnails
Click image for larger version

Name:	Panel.png
Views:	64
Size:	8.8 KB
ID:	171347  
__________________
10Smiles is offline   Reply With Quote
Old 10-25-2012, 08:23 PM   #35
Rivet Master
 
1981 31' Excella II
New Market , Alabama
Join Date: Sep 2011
Posts: 5,648
Ok here is my version. In actuality the 50A breaker is installed in the breaker box and the power comes in with a different hot wire on each pole.

Perry



__________________

__________________
perryg114 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 Amp to 15 Amp Adapter to House Power Question Steamboatbob Batteries, Univolts, Converters & Inverters 29 04-09-2017 10:43 PM
2008 Airstream Classic 31! 50 Amp Service, 2 AC Units! eBay Watch Airstreams on eBay 0 08-30-2011 09:20 PM
3 Amp Availability gaylejoe WBCCI Forum 27 08-06-2011 04:38 PM
Question on using 50 amp sevice RLS Electrical - Systems, Generators, Batteries & Solar 16 02-04-2011 02:14 PM
New Electric Service - YAY!!! or Life is Better When Everything WORKS!!! bugnot1 Winter Living 6 01-23-2011 11:32 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 09:01 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.